Re: [RE-wrenches] Conduit supports on sloped composite shingle roofs

2014-09-24 Thread Bill Hennessy
DPW Easy Feet are cost effective and work well, but plan well cut the stickem 
layer gives you only one chance.  Turn an L foot upside down, fasten it to the 
easy foot and use a mini on the L.
United Electric Supply in Delaware stocks and ships fast.

 
Bill Hennessy
Berks Solar, LLC



 From: Carl Adams swingjun...@gmail.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org 
Sent: Monday, September 22, 2014 8:22 PM
Subject: Re: [RE-wrenches] Conduit supports on sloped composite shingle roofs
 


Chris,
You might consider the DPW EasyFeet. They mount to comp shingles with five 
course thread torques screws. Kind of a wide L foot.
 
http://dpwsolar.com/images/PDFs/ApplicationInformation/Easy_Feet_Installation_Guidelines_Version_1_Rev_E.pdf
 You can come off of that with a piece of DPW P6 aluminum channel or square 
aluminum rail and then mount stainless steel mini for conduit supported at any 
height you wish.  Lead time on the easy feat is sometimes long. 


With Regards
Carl Adams, President
SunRock Solar513.290.9072 (cell)
513.766.6025 (office)




On Sep 22, 2014, at 7:57 PM, Chris Mason cometenergysyst...@gmail.com wrote:


In a hurricane region, we can't use glued supports.
Caddy supports are for flat roofs. These are 30 degree roofs.
I think I am going to use unistrut with two holes bored in it, washered screws 
and sealant, and a HDG conduit clamp.





On Mon, Sep 22, 2014 at 7:49 PM, August Goers aug...@luminalt.com wrote:

Hi Chris,
 
There are a few common methods to run conduit along the roof surface.
 
1.   Blocks made of Trex or another similar wood substitute with conduit 
fastened with 1-hole straps. Trex is typically only glued to the roof with 
roofing sealant (no penetrations)
2.   A more professional support such as the Chem Link KnuckleHead: 
http://www.chemlink.com/index.php/chemlink-products/knuckleheads or Erico 
Caddy: http://www.erico.com/public/library/Fixing/LT1058.pdf  - there are 
other manufacturers as well
3.   Quickmount classic conduit comp mount: 
http://www.quickmountpv.com/downloads/datasheet/QMPV-datasheet-QMCC-Conduit-web.pdf
 
For residential projects we typically use Trex. For commercial projects we 
typically use the Erico Caddy. If the roof is really steep and the blocks 
won’t stay put then we use the Quickmount product.
 
For getting through the roof we typically use a standard pipe flashing or a 
SolaDeck.
 
Best,
 
August
 
Luminalt
 
From:RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Chris Mason
Sent: Monday, September 22, 2014 2:43 PM
To: RE-wrenches
Subject: [RE-wrenches] Conduit supports on sloped composite shingle roofs
 
I'm curious what methods people are using to mount, flash and stand-off 
conduit from the comp. shingle roofs. We don't do a lot of shingle, mostly 
metal and concrete, so we are less that familiar with the options. We used 
SnapNRack flashed mounts for the rail system, but they need a rafter under 
them and the conduit run will not be above rafters.
As it is very hot here, I want to get some air between the conduit and the 
roof.

 
-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
 
www.cometsolar.com
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





-- 

Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org___
List sponsored by Redwood Alliance

List Address: RE

Re: [RE-wrenches] Conduit supports on sloped composite shingle roofs

2014-09-23 Thread Jason Szumlanski
I'm surprised this hasn't really come up for us. I can't remember the last
time we ran conduit along a pitched roof other than very short runs to an
eave where we penetrate the roof and soffit to run down an exterior wall.
I'm guessing you are dealing with an inaccessible attic. We just about
always get into the attic right from the j-box location. I think I'd use
the QuickMount solution if we had to do this.

Jason Szumlanski
Fafco Solar



On Mon, Sep 22, 2014 at 7:57 PM, Chris Mason cometenergysyst...@gmail.com
wrote:

 In a hurricane region, we can't use glued supports.
 Caddy supports are for flat roofs. These are 30 degree roofs.
 I think I am going to use unistrut with two holes bored in it, washered
 screws and sealant, and a HDG conduit clamp.




 On Mon, Sep 22, 2014 at 7:49 PM, August Goers aug...@luminalt.com wrote:

 Hi Chris,



 There are a few common methods to run conduit along the roof surface.



 1.   Blocks made of Trex or another similar wood substitute with
 conduit fastened with 1-hole straps. Trex is typically only glued to the
 roof with roofing sealant (no penetrations)

 2.   A more professional support such as the Chem Link KnuckleHead:
 http://www.chemlink.com/index.php/chemlink-products/knuckleheads or
 Erico Caddy: http://www.erico.com/public/library/Fixing/LT1058.pdf  -
 there are other manufacturers as well

 3.   Quickmount classic conduit comp mount:
 http://www.quickmountpv.com/downloads/datasheet/QMPV-datasheet-QMCC-Conduit-web.pdf



 For residential projects we typically use Trex. For commercial projects
 we typically use the Erico Caddy. If the roof is really steep and the
 blocks won't stay put then we use the Quickmount product.



 For getting through the roof we typically use a standard pipe flashing or
 a SolaDeck.



 Best,



 August



 Luminalt



 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
 Behalf Of *Chris Mason
 *Sent:* Monday, September 22, 2014 2:43 PM
 *To:* RE-wrenches
 *Subject:* [RE-wrenches] Conduit supports on sloped composite shingle
 roofs



 I'm curious what methods people are using to mount, flash and stand-off
 conduit from the comp. shingle roofs. We don't do a lot of shingle, mostly
 metal and concrete, so we are less that familiar with the options. We used
 SnapNRack flashed mounts for the rail system, but they need a rafter under
 them and the conduit run will not be above rafters.

 As it is very hot here, I want to get some air between the conduit and
 the roof.



 --

 Chris Mason

 NABCEP Certified Solar PV Installer(tm)

 Solar Design Engineer

 Generac Generators Industrial technician



 www.cometsolar.com http://www.cometenergysystems.com

 264.235.5670

 869.662.5670

 Skype: netconcepts


 --
 Chris Mason
 NABCEP Certified Solar PV Installer(tm)
 Solar Design Engineer
 Generac Generators Industrial technician

 www.cometsolar.com http://www.cometenergysystems.com
 264.235.5670
 869.662.5670
 Skype: netconcepts

 _
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Conduit supports on sloped composite shingle roofs

2014-09-22 Thread Chris Mason
I'm curious what methods people are using to mount, flash and stand-off
conduit from the comp. shingle roofs. We don't do a lot of shingle, mostly
metal and concrete, so we are less that familiar with the options. We used
SnapNRack flashed mounts for the rail system, but they need a rafter under
them and the conduit run will not be above rafters.
As it is very hot here, I want to get some air between the conduit and the
roof.

-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com http://www.cometenergysystems.com
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conduit supports on sloped composite shingle roofs

2014-09-22 Thread Solar
I always use the quickmount conduit flashing. It doesn't give a lot of room 
between the roof and raceway however.  Maybe the foam block supports typically 
used for raceways on flat rubber roofs?

Jesse 

Sent from my iPhone

 On Sep 22, 2014, at 4:43 PM, Chris Mason cometenergysyst...@gmail.com wrote:
 
 I'm curious what methods people are using to mount, flash and stand-off 
 conduit from the comp. shingle roofs. We don't do a lot of shingle, mostly 
 metal and concrete, so we are less that familiar with the options. We used 
 SnapNRack flashed mounts for the rail system, but they need a rafter under 
 them and the conduit run will not be above rafters.
 As it is very hot here, I want to get some air between the conduit and the 
 roof.
 
 -- 
 Chris Mason
 NABCEP Certified Solar PV Installer™
 Solar Design Engineer
 Generac Generators Industrial technician
 
 www.cometsolar.com
 264.235.5670
 869.662.5670
 Skype: netconcepts
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conduit supports on sloped composite shingle roofs

2014-09-22 Thread August Goers
Hi Chris,



There are a few common methods to run conduit along the roof surface.



1.   Blocks made of Trex or another similar wood substitute with
conduit fastened with 1-hole straps. Trex is typically only glued to the
roof with roofing sealant (no penetrations)

2.   A more professional support such as the Chem Link KnuckleHead:
http://www.chemlink.com/index.php/chemlink-products/knuckleheads or Erico
Caddy: http://www.erico.com/public/library/Fixing/LT1058.pdf  - there are
other manufacturers as well

3.   Quickmount classic conduit comp mount:
http://www.quickmountpv.com/downloads/datasheet/QMPV-datasheet-QMCC-Conduit-web.pdf



For residential projects we typically use Trex. For commercial projects we
typically use the Erico Caddy. If the roof is really steep and the blocks
won’t stay put then we use the Quickmount product.



For getting through the roof we typically use a standard pipe flashing or a
SolaDeck.



Best,



August



Luminalt



*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Chris Mason
*Sent:* Monday, September 22, 2014 2:43 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Conduit supports on sloped composite shingle roofs



I'm curious what methods people are using to mount, flash and stand-off
conduit from the comp. shingle roofs. We don't do a lot of shingle, mostly
metal and concrete, so we are less that familiar with the options. We used
SnapNRack flashed mounts for the rail system, but they need a rafter under
them and the conduit run will not be above rafters.

As it is very hot here, I want to get some air between the conduit and the
roof.



-- 

Chris Mason

NABCEP Certified Solar PV Installer™

Solar Design Engineer

Generac Generators Industrial technician



www.cometsolar.com http://www.cometenergysystems.com

264.235.5670

869.662.5670

Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conduit supports on sloped composite shingle roofs

2014-09-22 Thread Chris Mason
In a hurricane region, we can't use glued supports.
Caddy supports are for flat roofs. These are 30 degree roofs.
I think I am going to use unistrut with two holes bored in it, washered
screws and sealant, and a HDG conduit clamp.




On Mon, Sep 22, 2014 at 7:49 PM, August Goers aug...@luminalt.com wrote:

 Hi Chris,



 There are a few common methods to run conduit along the roof surface.



 1.   Blocks made of Trex or another similar wood substitute with
 conduit fastened with 1-hole straps. Trex is typically only glued to the
 roof with roofing sealant (no penetrations)

 2.   A more professional support such as the Chem Link KnuckleHead:
 http://www.chemlink.com/index.php/chemlink-products/knuckleheads or Erico
 Caddy: http://www.erico.com/public/library/Fixing/LT1058.pdf  - there are
 other manufacturers as well

 3.   Quickmount classic conduit comp mount:
 http://www.quickmountpv.com/downloads/datasheet/QMPV-datasheet-QMCC-Conduit-web.pdf



 For residential projects we typically use Trex. For commercial projects we
 typically use the Erico Caddy. If the roof is really steep and the blocks
 won’t stay put then we use the Quickmount product.



 For getting through the roof we typically use a standard pipe flashing or
 a SolaDeck.



 Best,



 August



 Luminalt



 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
 Behalf Of *Chris Mason
 *Sent:* Monday, September 22, 2014 2:43 PM
 *To:* RE-wrenches
 *Subject:* [RE-wrenches] Conduit supports on sloped composite shingle
 roofs



 I'm curious what methods people are using to mount, flash and stand-off
 conduit from the comp. shingle roofs. We don't do a lot of shingle, mostly
 metal and concrete, so we are less that familiar with the options. We used
 SnapNRack flashed mounts for the rail system, but they need a rafter under
 them and the conduit run will not be above rafters.

 As it is very hot here, I want to get some air between the conduit and the
 roof.



 --

 Chris Mason

 NABCEP Certified Solar PV Installer™

 Solar Design Engineer

 Generac Generators Industrial technician



 www.cometsolar.com http://www.cometenergysystems.com

 264.235.5670

 869.662.5670

 Skype: netconcepts

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org





-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com http://www.cometenergysystems.com
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conduit supports on sloped composite shingle roofs

2014-09-22 Thread Carl Adams
Chris,
You might consider the DPW EasyFeet. They mount to comp shingles with five 
course thread torques screws. Kind of a wide L foot.
 
http://dpwsolar.com/images/PDFs/ApplicationInformation/Easy_Feet_Installation_Guidelines_Version_1_Rev_E.pdf
 You can come off of that with a piece of DPW P6 aluminum channel or square 
aluminum rail and then mount stainless steel mini for conduit supported at any 
height you wish.  Lead time on the easy feat is sometimes long. 

With Regards
Carl Adams, President
SunRock Solar
513.290.9072 (cell)
513.766.6025 (office)

On Sep 22, 2014, at 7:57 PM, Chris Mason cometenergysyst...@gmail.com wrote:

In a hurricane region, we can't use glued supports.
Caddy supports are for flat roofs. These are 30 degree roofs.
I think I am going to use unistrut with two holes bored in it, washered screws 
and sealant, and a HDG conduit clamp.




 On Mon, Sep 22, 2014 at 7:49 PM, August Goers aug...@luminalt.com wrote:
 Hi Chris,
 
  
 
 There are a few common methods to run conduit along the roof surface.
 
  
 
 1.   Blocks made of Trex or another similar wood substitute with conduit 
 fastened with 1-hole straps. Trex is typically only glued to the roof with 
 roofing sealant (no penetrations)
 
 2.   A more professional support such as the Chem Link KnuckleHead: 
 http://www.chemlink.com/index.php/chemlink-products/knuckleheads or Erico 
 Caddy: http://www.erico.com/public/library/Fixing/LT1058.pdf  - there are 
 other manufacturers as well
 
 3.   Quickmount classic conduit comp mount: 
 http://www.quickmountpv.com/downloads/datasheet/QMPV-datasheet-QMCC-Conduit-web.pdf
 
  
 
 For residential projects we typically use Trex. For commercial projects we 
 typically use the Erico Caddy. If the roof is really steep and the blocks 
 won’t stay put then we use the Quickmount product.
 
  
 
 For getting through the roof we typically use a standard pipe flashing or a 
 SolaDeck.
 
  
 
 Best,
 
  
 
 August
 
  
 
 Luminalt
 
  
 
 From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On 
 Behalf Of Chris Mason
 Sent: Monday, September 22, 2014 2:43 PM
 To: RE-wrenches
 Subject: [RE-wrenches] Conduit supports on sloped composite shingle roofs
 
  
 
 I'm curious what methods people are using to mount, flash and stand-off 
 conduit from the comp. shingle roofs. We don't do a lot of shingle, mostly 
 metal and concrete, so we are less that familiar with the options. We used 
 SnapNRack flashed mounts for the rail system, but they need a rafter under 
 them and the conduit run will not be above rafters.
 
 As it is very hot here, I want to get some air between the conduit and the 
 roof.
 
  
 
 --
 
 Chris Mason
 
 NABCEP Certified Solar PV Installer™
 
 Solar Design Engineer
 
 Generac Generators Industrial technician
 
  
 
 www.cometsolar.com
 
 264.235.5670
 
 869.662.5670
 
 Skype: netconcepts
 
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org



-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conduit supports on sloped composite shingle roofs

2014-09-22 Thread Benn Kilburn
How high are you wanting to get the conduit (EMT?) off the roof?
I have been using Kinetic flashings and rails for mounting PV these days. Great 
stuff. 
There is a base that mounts directly onto the shingle and then a flashing goes 
over it. The base that goes under the flashing has two holes for lags bolts or 
in your case a couple bolts you can attach to be roof sheeting and then it has 
a stud for mounting the L-foot (or whatever you want to attach to the stud. 
You could use a standard 3 L-foot and either use the provided oblong hole or 
drill your own. If you want to get more height then they also have 4 and 5 
L-feet. 

http://kineticsolar.com/

benn

benn
 On Sep 22, 2014, at 3:43 PM, Chris Mason cometenergysyst...@gmail.com wrote:
 
 I'm curious what methods people are using to mount, flash and stand-off 
 conduit from the comp. shingle roofs. We don't do a lot of shingle, mostly 
 metal and concrete, so we are less that familiar with the options. We used 
 SnapNRack flashed mounts for the rail system, but they need a rafter under 
 them and the conduit run will not be above rafters.
 As it is very hot here, I want to get some air between the conduit and the 
 roof.
 
 -- 
 Chris Mason
 NABCEP Certified Solar PV Installer™
 Solar Design Engineer
 Generac Generators Industrial technician
 
 www.cometsolar.com
 264.235.5670
 869.662.5670
 Skype: netconcepts
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org