Re: [RE-wrenches] Corrugated roofing mounts

2013-02-18 Thread Chris Worcester
We use the SDS galv up here in the mountains, they are tough, haven't
snapped one, the engineer loves spec'ing them.

 

Sincerely,

Chris Worcester

Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503

C: 530-448-9692
Fax: 530-582-4603
www.solarwindworks.com <http://www.solarwindworks.com/> 
ch...@solarwindworks.com
"Proven Energy Solutions"

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Monday, February 18, 2013 10:42 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Corrugated roofing mounts

 

The Simpson screws look very similar to the Headloks.  I just looked at the
Simpson SDS, and I see they are available in 316 Stainless as well.
That would be my choice near the ocean, but I'm guessing they're spendy.



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified, Licensed Contractor
808 269-7491

On 2/18/2013 11:08 AM, William Miller wrote:

Ray:

We use the Simpson 1/4 by X" "Strong Drive"  (SDS series).  We get them in
the hot dip galvanize version.  They are readily available locally.  I think
building officials like the Simpson name on structural products.  They self
drill and we have had no instance of them snapping off while being driven.

William Miller

At 09:26 AM 2/18/2013, Ray Walters wrote:



I've got a project right now on a steel roof.  I was just at a trade show
last week, so I got to look at the latest gizmo from S5. 
I didn't like it at all, it didn't go into the valleys like the old mount,
but drilled 4 holes into the side of the ridge, and just counted on the
roofing to hold the modules.
I wanted to use the new ZEP rack, but never heard back from them, I guess my
project is too small (4 Kw).
I'm going with SnapNRack blocks through the ridge top, and I'm going to go
through the purlins into rafters or 2x blocking as needed.

Also,  a related subject, I'm using the new HeadLok Lags from FastenMaster.
They claim to be stronger than a 3/8" lag, but they have a 3/16"D shaft.
I've had trouble with regular cheap Home Depot lags twisting off, so at
least these have actual strength ratings, and don't require predrilling.
They also have a no rust guarantee
Has anybody else used these? (or the similar Timberlok)?

Thanks,

R.Ray Walters






___
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Corrugated roofing mounts

2013-02-18 Thread Ray Walters
The Simpson screws look very similar to the Headloks.  I just looked at 
the Simpson SDS, and I see they are available in 316 Stainless as well.

That would be my choice near the ocean, but I'm guessing they're spendy.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified, Licensed Contractor
808 269-7491

On 2/18/2013 11:08 AM, William Miller wrote:

Ray:

We use the Simpson 1/4 by X" "Strong Drive"  (SDS series).  We get 
them in the hot dip galvanize version.  They are readily available 
locally.  I think building officials like the Simpson name on 
structural products.  They self drill and we have had no instance of 
them snapping off while being driven.


William Miller

At 09:26 AM 2/18/2013, Ray Walters wrote:
I've got a project right now on a steel roof.  I was just at a trade 
show last week, so I got to look at the latest gizmo from S5.
I didn't like it at all, it didn't go into the valleys like the old 
mount, but drilled 4 holes into the side of the ridge, and just 
counted on the roofing to hold the modules.
I wanted to use the new ZEP rack, but never heard back from them, I 
guess my project is too small (4 Kw).
I'm going with SnapNRack blocks through the ridge top, and I'm going 
to go through the purlins into rafters or 2x blocking as needed.


Also,  a related subject, I'm using the new HeadLok Lags from 
FastenMaster.  They claim to be stronger than a 3/8" lag, but they 
have a 3/16"D shaft.
I've had trouble with regular cheap Home Depot lags twisting off, so 
at least these have actual strength ratings, and don't require 
predrilling.

They also have a no rust guarantee
Has anybody else used these? (or the similar Timberlok)?

Thanks,

R.Ray Walters



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Corrugated roofing mounts

2013-02-18 Thread William Miller

Ray:

We use the Simpson 1/4 by X" "Strong Drive"  (SDS series).  We get them in 
the hot dip galvanize version.  They are readily available locally.  I 
think building officials like the Simpson name on structural 
products.  They self drill and we have had no instance of them snapping off 
while being driven.


William Miller

At 09:26 AM 2/18/2013, Ray Walters wrote:
I've got a project right now on a steel roof.  I was just at a trade show 
last week, so I got to look at the latest gizmo from S5.
I didn't like it at all, it didn't go into the valleys like the old mount, 
but drilled 4 holes into the side of the ridge, and just counted on the 
roofing to hold the modules.
I wanted to use the new ZEP rack, but never heard back from them, I guess 
my project is too small (4 Kw).
I'm going with SnapNRack blocks through the ridge top, and I'm going to go 
through the purlins into rafters or 2x blocking as needed.


Also,  a related subject, I'm using the new HeadLok Lags from 
FastenMaster.  They claim to be stronger than a 3/8" lag, but they have a 
3/16"D shaft.
I've had trouble with regular cheap Home Depot lags twisting off, so at 
least these have actual strength ratings, and don't require predrilling.

They also have a no rust guarantee
Has anybody else used these? (or the similar Timberlok)?

Thanks,

R.Ray Walters


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Corrugated roofing mounts

2013-02-18 Thread Ray Walters
I've got a project right now on a steel roof.  I was just at a trade 
show last week, so I got to look at the latest gizmo from S5.
I didn't like it at all, it didn't go into the valleys like the old 
mount, but drilled 4 holes into the side of the ridge, and just counted 
on the roofing to hold the modules.
I wanted to use the new ZEP rack, but never heard back from them, I 
guess my project is too small (4 Kw).
I'm going with SnapNRack blocks through the ridge top, and I'm going to 
go through the purlins into rafters or 2x blocking as needed.


Also,  a related subject, I'm using the new HeadLok Lags from 
FastenMaster.  They claim to be stronger than a 3/8" lag, but they have 
a 3/16"D shaft.
I've had trouble with regular cheap Home Depot lags twisting off, so at 
least these have actual strength ratings, and don't require predrilling.

They also have a no rust guarantee
Has anybody else used these? (or the similar Timberlok)?

Thanks,

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified, Licensed Contractor
808 269-7491

On 2/18/2013 9:25 AM, William Miller wrote:

Chris:

We have used the S5 corrugated product before and choose not to repeat 
the experiment for these reasons:


1. Making roof perforations in any valley defies common sense.

2. The threaded mounting holes stripped very easily.

3. I have determined that most common wavelength of corrugated roofing 
we have encountered is 2.67".  If you don't have purlins, this is not 
a problem since a rafter is 1.5" wide.  Worse case scenario, if a 
rafter is not under the peak of the corrugation you scab a piece of 
2X8 next to the rafter and achieve a mounting member to fasten to.  
This is much easier than adding blocking to create purlins.  This 
only  works if you are installing a fastener through the peak of the 
corrugation.  With the S5 product you have to find framing under two 
locations, not one.


William Miller


At 02:04 PM 2/16/2013, you wrote:
The S-5 bracket looked interesting until I realized that, on a rafter 
roof, you would never consistently find the rafter under the holes. 
Even with the SnapNRack single hole unit, getting it over 2 x 8 
rafters is a nightmare. I have never seen rafters that would allow 
for holes through two valleys. So the only other way would be to 
fasten to the purloins. 3/4" purloin strips are not going to give you 
a lot of embed.



On Sat, Feb 16, 2013 at 7:18 PM, August Goers > wrote:


Hi William,

You may have already seen this corrugated bracket from S-5:

http://www.s-5.com/clamps/index_2624.cfm

I believe it's best to have the screws go into purlins. These are
fairly low cost; contact me offlist if you want me to send you
distributor contact info.

As far as figuring out what manufacturer/model of roof you have
that can be tough. Maybe find original building drawings or a
sticker somewhere on the underside? I've also found that the
folks at S-5! are good at figuring out manufacturers.

Good luck! -August 





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Corrugated roofing mounts

2013-02-18 Thread William Miller

Chris:

We have used the S5 corrugated product before and choose not to repeat the 
experiment for these reasons:


1. Making roof perforations in any valley defies common sense.

2. The threaded mounting holes stripped very easily.

3. I have determined that most common wavelength of corrugated roofing we 
have encountered is 2.67".  If you don't have purlins, this is not a 
problem since a rafter is 1.5" wide.  Worse case scenario, if a rafter is 
not under the peak of the corrugation you scab a piece of 2X8 next to the 
rafter and achieve a mounting member to fasten to.  This is much easier 
than adding blocking to create purlins.  This only  works if you are 
installing a fastener through the peak of the corrugation.  With the S5 
product you have to find framing under two locations, not one.


William Miller


At 02:04 PM 2/16/2013, you wrote:
The S-5 bracket looked interesting until I realized that, on a rafter 
roof, you would never consistently find the rafter under the holes. Even 
with the SnapNRack single hole unit, getting it over 2 x 8 rafters is a 
nightmare. I have never seen rafters that would allow for holes through 
two valleys. So the only other way would be to fasten to the purloins. 
3/4" purloin strips are not going to give you a lot of embed.



On Sat, Feb 16, 2013 at 7:18 PM, August Goers 
<aug...@luminalt.com> wrote:

Hi William,

You may have already seen this corrugated bracket from S-5:

http://www.s-5.com/clamps/index_2624.cfm

I believe it's best to have the screws go into purlins. These are fairly 
low cost; contact me offlist if you want me to send you distributor 
contact info.


As far as figuring out what manufacturer/model of roof you have that can 
be tough. Maybe find original building drawings or a sticker somewhere on 
the underside? I've also found that the folks at S-5! are good at figuring 
out manufacturers.


Good luck! -August
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Corrugated roofing mounts

2013-02-16 Thread Chris Mason
The S-5 bracket looked interesting until I realized that, on a rafter roof,
you would never consistently find the rafter under the holes. Even with the
SnapNRack single hole unit, getting it over 2 x 8 rafters is a nightmare. I
have never seen rafters that would allow for holes through two valleys. So
the only other way would be to fasten to the purloins. 3/4" purloin strips
are not going to give you a lot of embed.


On Sat, Feb 16, 2013 at 7:18 PM, August Goers  wrote:

> Hi William,
>
> You may have already seen this corrugated bracket from S-5:
>
> http://www.s-5.com/clamps/index_2624.cfm
>
> I believe it’s best to have the screws go into purlins. These are fairly
> low cost; contact me offlist if you want me to send you distributor contact
> info.
>
> As far as figuring out what manufacturer/model of roof you have that can
> be tough. Maybe find original building drawings or a sticker somewhere on
> the underside? I’ve also found that the folks at S-5! are good at figuring
> out manufacturers.
>
> Good luck! -August
>
>
>
>  *From:* William Miller 
> *Sent:* February 15, 2013 6:49 PM
> *To:* RE-wrenches 
>
> *Subject:* [RE-wrenches] Corrugated roofing mounts
>
> Friends:
>
> I am trying to specify attachments for a corrugated roof.  This is the
> type with the sine wave shape.
>
> I want to try the DPW CMB product line.  I have been instructed to provide
> measurements of the corrugation from peak to peak and also the height from
> valley to peak.  The problem is that the measurements vary from point to
> point on this roof.  In some places the peak to peak is 2.75" and in others
> it is in the 2.6" range.  The height varies from 0.625 to 0.5 inches.
>
> I have looked on-line and I find that a common dimension for roofing peak
> to peak is 2.67".  There are products with height measurements of 0.5 and
> 0.875.
>
> I have a few questions:
>
> 1. How do I figure out which roofing product I have?
> 2. Does it matter if the spacing varies from one location to the next?
> 3. Does anyone have experience with the CMB product.
>
> Thanks in advance.
>
> William Miller
>
> Miller Solar
> Voice :805-438-5600
> email: will...@millersolar.com
> http://millersolar.com
> License No. C-10-773985
>
> __**_
> List sponsored by Home Power magazine
>
> List Address: 
> re-wrenc...@lists.re-wrenches.**org
>
> Options & settings:
> http://lists.re-wrenches.org/**options.cgi/re-wrenches-re-**wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> List-Archive: http://lists.re-wrenches.org/**pipermail/re-wrenches-re-**
> wrenches.org<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.**htm<http://www.re-wrenches.org/etiquette.htm>
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Corrugated roofing mounts

2013-02-16 Thread August Goers
Hi William,

You may have already seen this corrugated bracket from S-5:

http://www.s-5.com/clamps/index_2624.cfm

I believe it’s best to have the screws go into purlins. These are fairly
low cost; contact me offlist if you want me to send you distributor contact
info.

As far as figuring out what manufacturer/model of roof you have that can be
tough. Maybe find original building drawings or a sticker somewhere on the
underside? I’ve also found that the folks at S-5! are good at figuring out
manufacturers.

Good luck! -August



 *From:* William Miller 
*Sent:* February 15, 2013 6:49 PM
*To:* RE-wrenches 
*Subject:* [RE-wrenches] Corrugated roofing mounts

Friends:

I am trying to specify attachments for a corrugated roof.  This is the type
with the sine wave shape.

I want to try the DPW CMB product line.  I have been instructed to provide
measurements of the corrugation from peak to peak and also the height from
valley to peak.  The problem is that the measurements vary from point to
point on this roof.  In some places the peak to peak is 2.75" and in others
it is in the 2.6" range.  The height varies from 0.625 to 0.5 inches.

I have looked on-line and I find that a common dimension for roofing peak
to peak is 2.67".  There are products with height measurements of 0.5 and
0.875.

I have a few questions:

1. How do I figure out which roofing product I have?
2. Does it matter if the spacing varies from one location to the next?
3. Does anyone have experience with the CMB product.

Thanks in advance.

William Miller

Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985

__**_
List sponsored by Home Power magazine

List Address: 
re-wrenc...@lists.re-wrenches.**org

Options & settings:
http://lists.re-wrenches.org/**options.cgi/re-wrenches-re-**wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

List-Archive: http://lists.re-wrenches.org/**pipermail/re-wrenches-re-**
wrenches.org<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>

List rules & etiquette:
www.re-wrenches.org/etiquette.**htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Corrugated roofing mounts

2013-02-15 Thread Greg McPheeters
The SnapNrack Corrugated Roof Block will work with that roof - I'm sure DPW has 
one that will work as well but can't say which size - 

http://www.snapnrack.com/metal-roof-mounts


Greg McPheeters  





 From: William Miller 
To: RE-wrenches  
Sent: Friday, February 15, 2013 6:47 PM
Subject: [RE-wrenches] Corrugated roofing mounts
 
Friends:

I am trying to specify attachments for a corrugated roof.  This is the type 
with the sine wave shape.

I want to try the DPW CMB product line.  I have been instructed to provide 
measurements of the corrugation from peak to peak and also the height from 
valley to peak.  The problem is that the measurements vary from point to point 
on this roof.  In some places the peak to peak is 2.75" and in others it is in 
the 2.6" range.  The height varies from 0.625 to 0.5 inches.

I have looked on-line and I find that a common dimension for roofing peak to 
peak is 2.67".  There are products with height measurements of 0.5 and 0.875.

I have a few questions:

1. How do I figure out which roofing product I have?
2. Does it matter if the spacing varies from one location to the next?
3. Does anyone have experience with the CMB product.

Thanks in advance.

William Miller

Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Corrugated roofing mounts

2013-02-15 Thread William Miller

Friends:

I am trying to specify attachments for a corrugated roof.  This is the type 
with the sine wave shape.


I want to try the DPW CMB product line.  I have been instructed to provide 
measurements of the corrugation from peak to peak and also the height from 
valley to peak.  The problem is that the measurements vary from point to 
point on this roof.  In some places the peak to peak is 2.75" and in others 
it is in the 2.6" range.  The height varies from 0.625 to 0.5 inches.


I have looked on-line and I find that a common dimension for roofing peak 
to peak is 2.67".  There are products with height measurements of 0.5 and 
0.875.


I have a few questions:

1. How do I figure out which roofing product I have?
2. Does it matter if the spacing varies from one location to the next?
3. Does anyone have experience with the CMB product.

Thanks in advance.

William Miller

Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org