Re: [RE-wrenches] FW250

2009-08-27 Thread Nick Lucchese
I agree that the FW250 has a few shortcomings however it does work  
out quite well on the AC side. My own system has a FW500 DC and a  
FW250 on the AC side outputting to the existing service panel. It is  
a bit crowded in the FW250 especially with the FW-SP-250 (surge  
protector) however I can honestly say with the pre-made jumpers  
Outback supplies there were no bloody knuckles involved. Also, as far  
as I know Outback is now shipping built up FW250 power panels and I  
believe they've addressed the shunt and negative bus issues. I  
certainly like the E-Panel but the FW250 does have it's place on  
certain systems and should remain as a viable option in a designer's  
bag o' tricks.


Nick A Lucchese


On Aug 26, 2009, at 6:48 PM, Bruce Geddes wrote:


Hello Wrenches,

There is a potential customer that purchased some equipment,  
including a FW250 box, that goes on the end of the  VFX inverter.


http://www.outbackpower.com/pdf/manuals/900-0060-1_REV_A.pdf

I've not installed one of these yet.  Looking at the manual, it looks  
extremely tight, especially on the DC side.  Has anyone had  
experience with these?  Is there sufficient wire bending space?



Thanks,
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] FW250

2009-08-26 Thread Chris Worcester
Hi Drake,

I did one of these when they first appeared in the spring of 2007, and swore
them off. There is inadequate circuit breaker space on the AC  DC side
especially when you are integrating  a GFP, requiring breakers be installed
on both sides of the unit, back to back, which really eats into your working
room! The lack of positive and negative DC busses and AC in or AC out busses
left me using multi hole Polaris Insultaps or tying onto the top of the
inverter's DC posts as recommended by OB tech support.. There were other
issues too as you mention wire bending space. 

Go with the MidNite Solar E panel and you'll be fine.

 

Sincerely,

Chris Worcester

Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com http://www.solarwindworks.com/ 
ch...@solarwindworks.com
Proven Energy Solutions

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
Chamberlin
Sent: Wednesday, August 26, 2009 5:42 AM
To: RE-wrenches
Subject: [RE-wrenches] FW250

 

Hello Wrenches, 

There is a potential customer that purchased some equipment, including a
FW250 box, that goes on the end of the  VFX inverter. 

http://www.outbackpower.com/pdf/manuals/900-0060-1_REV_A.pdf

I've not installed one of these yet.  Looking at the manual, it looks
extremely tight, especially on the DC side.  Has anyone had experience with
these?  Is there sufficient wire bending space? 


Thanks,



Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer 
Office - 740-448-7328
Mobile - 740-856-9648 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] FW250

2009-08-26 Thread Darryl Thayer
I did one this spring, i do not remember a particular problem, i m going to 
that site this weekend i will take a look and see if I remember anything.
daryl

--- On Wed, 8/26/09, Chris Worcester ch...@solarwindworks.com wrote:

 From: Chris Worcester ch...@solarwindworks.com
 Subject: Re: [RE-wrenches] FW250
 To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
 Date: Wednesday, August 26, 2009, 10:20 AM
 
 
 
  
  
 
 
 
 
 
 
  
 
 
 
 Hi Drake, 
 
 I did one of these when they
 first appeared in the spring of
 2007, and swore them off. There is inadequate circuit
 breaker space on the AC
  DC side especially when you are integrating  a
 GFP, requiring
 breakers be installed on both sides of the unit, back to
 back, which really
 eats into your working room! The lack of positive and
 negative DC busses and AC
 in or AC out busses left me using multi hole Polaris
 Insultaps or tying onto
 the top of the inverter’s DC posts as recommended by
 OB tech support..
 There were other issues too as you mention wire bending
 space.  
 
 Go with the MidNite Solar E
 panel and you’ll be fine. 
 
    
 
 
 
 Sincerely,
 
 
 
 Chris Worcester 
 
 Solar Wind Works
 
 NABCEP Certified PV Installer
 
 Phone: 530-582-4503
 
 Fax: 530-582-4603
 
 www.solarwindworks.com
 
 ch...@solarwindworks.com
 
 Proven Energy Solutions 
 
 
 
    
 
 
 
 
 
 From:
 re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
 Behalf Of Drake
 Chamberlin
 
 Sent: Wednesday, August 26, 2009 5:42 AM
 
 To: RE-wrenches
 
 Subject: [RE-wrenches] FW250 
 
 
 
 
 
    
 
 Hello Wrenches, 
 
 
 
 There is a potential customer that purchased some
 equipment, including a FW250
 box, that goes on the end of the  VFX inverter. 
 
 
 
 http://www.outbackpower.com/pdf/manuals/900-0060-1_REV_A.pdf
 
 
 
 I've not installed one of these yet.  Looking
 at the manual, it looks
 extremely tight, especially on the DC side.  Has
 anyone had experience
 with these?  Is there sufficient wire bending space? 
 
 
 
 
 
 Thanks,
 
 
 
  
 
 Drake Chamberlin
 
 Athens Electric
 
 OH License 44810
 
 CO License 3773
 
 NABCEP TM  Certified PV Installer 
 
 Office - 740-448-7328
 
 Mobile - 740-856-9648  
 
 
 
  
 
 
 
 -Inline Attachment Follows-
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 


  
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] FW250

2009-08-26 Thread Brian Teitelbaum
Drake,

I completely agree with Chris here. The Midnight Solar E-Panels are far 
superior, in my opinion,  to the OutBack FW-250 boxes, and by the time that you 
add up all of the needed parts to make the FW-250 boxes work (cables, wire, 
breakers, shunt, etc.), they are about the same cost. The E-Panels are much 
easier to install and service. They also come with a shunt, whereas with the 
FW-250 boxes, if you need a shunt, you have to mount it on the inverter, below 
the top cover. This only works with the vented inverters, as the turbo cover 
on the sealed units don't have the clearance. On top of that, the shunt ends up 
only about 2-3 from the negative battery post, and is a hell of a hassle to 
connect with 2/0 or 4/0 cable.

 Brian Teitelbaum
AEE Solar



From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Worcester
Sent: Wednesday, August 26, 2009 8:21 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] FW250

Hi Drake,
I did one of these when they first appeared in the spring of 2007, and swore 
them off. There is inadequate circuit breaker space on the AC  DC side 
especially when you are integrating  a GFP, requiring breakers be installed on 
both sides of the unit, back to back, which really eats into your working room! 
The lack of positive and negative DC busses and AC in or AC out busses left me 
using multi hole Polaris Insultaps or tying onto the top of the inverter's DC 
posts as recommended by OB tech support.. There were other issues too as you 
mention wire bending space.
Go with the MidNite Solar E panel and you'll be fine.

Sincerely,

Chris Worcester
Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.comhttp://www.solarwindworks.com/
ch...@solarwindworks.commailto:ch...@solarwindworks.com
Proven Energy Solutions

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake Chamberlin
Sent: Wednesday, August 26, 2009 5:42 AM
To: RE-wrenches
Subject: [RE-wrenches] FW250

Hello Wrenches,

There is a potential customer that purchased some equipment, including a FW250 
box, that goes on the end of the  VFX inverter.

http://www.outbackpower.com/pdf/manuals/900-0060-1_REV_A.pdf

I've not installed one of these yet.  Looking at the manual, it looks extremely 
tight, especially on the DC side.  Has anyone had experience with these?  Is 
there sufficient wire bending space?


Thanks,

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] FW250

2009-08-26 Thread R. Walters
We've looked at both, and the E-panel wins every time for single  
inverter installs where space and cost are issues. (Midnite includes  
cables, and breakers, and lots of extra goodies, while Outback keeps  
leaving more things  out) We do use the larger Outback stuff, when we  
are using multiple inverters, or doing a more complex off grid system  
(DC loads, wind, etc).
Midnite's E-panel and battery box make for a very clean Grid tie w/  
battery backup system. We just couldn't fit systems in such small  
spaces before.


R. Walters
Solarray.com
NABCEP # 04170442   



On Aug 26, 2009, at 9:20 AM, Chris Worcester wrote:


Hi Drake,

I did one of these when they first appeared in the spring of 2007,  
and swore them off. There is inadequate circuit breaker space on  
the AC  DC side especially when you are integrating  a GFP,  
requiring breakers be installed on both sides of the unit, back to  
back, which really eats into your working room! The lack of  
positive and negative DC busses and AC in or AC out busses left me  
using multi hole Polaris Insultaps or tying onto the top of the  
inverter’s DC posts as recommended by OB tech support.. There were  
other issues too as you mention wire bending space.


Go with the MidNite Solar E panel and you’ll be fine.



Sincerely,

Chris Worcester

Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com
ch...@solarwindworks.com
Proven Energy Solutions



From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches- 
boun...@lists.re-wrenches.org] On Behalf Of Drake Chamberlin

Sent: Wednesday, August 26, 2009 5:42 AM
To: RE-wrenches
Subject: [RE-wrenches] FW250



Hello Wrenches,

There is a potential customer that purchased some equipment,  
including a FW250 box, that goes on the end of the  VFX inverter.


http://www.outbackpower.com/pdf/manuals/900-0060-1_REV_A.pdf

I've not installed one of these yet.  Looking at the manual, it  
looks extremely tight, especially on the DC side.  Has anyone had  
experience with these?  Is there sufficient wire bending space?



Thanks,


Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re- 
wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] FW250

2009-08-26 Thread Drake Chamberlin
Thanks for the replies.  I am also happy with the Midnight E-Panel, 
and am strongly urging the customer to get one, having forwarded your 
posts.   The AC/DC 250 looks like it should come with a box or two of bandages.




Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] FW250

2009-08-26 Thread ryan
Do your self a huge favor and use the Midnite solar Epanel. one thing is 
for sure you wont install 2 FW250's 
___

List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] FW250

2009-08-26 Thread Bruce Geddes
Did one FW250 and that was it.  No space for bus bars and it can be an issue 
remebering each bit you need to order for a job.  Also, the breakers are not 
supposed to be mounted facing up or down in order to work properly so that 
means the install has to run vertically up the wall or be on a shelf where the 
inverter led indicators are not visible.  E panel wins hands down even outside 
the USA!

Bruce Geddes
PowerOn___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org