I have found this Electricenter accessory part # ECSBPK01. to be very useful 
with locally available load centers.  labelled for Siemens and Murray.  Fits 
well on Eaton tho not listed for that brand.

Available locally for $32 or so lately.
Does the same thing the Generac sub panel does for the price of the interlock 
only.

For an image try:
https://www.homedepot.com/p/Siemens-Standby-Power-Interlock-Kit-ECSBPK01/203197660#overlay

> On Mar 2, 2023, at 9:46 AM, Kristopher Schmid via RE-wrenches 
>  wrote:
> 
> Hi All,
> 
> I have a stand alone system that was upgraded from an FX inverter to a Radian 
> WITHOUT  the companion load center.  I would like to add an inverter bypass 
> circuit to operate the house on generator power.  There used to be a 4 slot 
> breaker panel (SqD?) with the rocker switch preventing both breakers from 
> being in the on position simultaneously.  I have not been able to find it on 
> the interweb.  Anyone know of something out there that would meet my needs?
> 
> Kris
> 
> 
> Shine On!
> 
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com 
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Inverter bypass

2023-03-03 Thread Mac Lewis via RE-wrenches
You can also build them with the interlock kits for (almost) whatever load
center you like.  https://interlockkit.com/shop/
Some of these are UL listed, some are not.

The disadvantage of this route is that they are typically made for a high
ampacity main circuit breaker, probably overkill for most applications like
this.

On Thu, Mar 2, 2023 at 9:37 PM Jerry Shafer via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Wrenches
> It might be easier to use the wire cabinet for the radian, but hey thats
> just me
>
> On Thu, Mar 2, 2023, 9:47 AM Kristopher Schmid via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Hi All,
>>
>> I have a stand alone system that was upgraded from an FX inverter to a
>> Radian WITHOUT  the companion load center.  I would like to add an inverter
>> bypass circuit to operate the house on generator power.  There used to be a
>> 4 slot breaker panel (SqD?) with the rocker switch preventing both breakers
>> from being in the on position simultaneously.  I have not been able to find
>> it on the interweb.  Anyone know of something out there that would meet my
>> needs?
>>
>> Kris
>>
>>
>> Shine On!
>>
>> Kris Schmid
>> Legacy Solar, LLC
>> 137 West 1st Avenue
>> Luck, WI 54853
>> www.legacysolar.com
>> 715-653-4295
>> NABCEP Certified PV Installation Professional
>> Licensed Wisconsin Master Electrician
>> BSEE
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Jerry Shafer via RE-wrenches
Wrenches
It might be easier to use the wire cabinet for the radian, but hey thats
just me

On Thu, Mar 2, 2023, 9:47 AM Kristopher Schmid via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi All,
>
> I have a stand alone system that was upgraded from an FX inverter to a
> Radian WITHOUT  the companion load center.  I would like to add an inverter
> bypass circuit to operate the house on generator power.  There used to be a
> 4 slot breaker panel (SqD?) with the rocker switch preventing both breakers
> from being in the on position simultaneously.  I have not been able to find
> it on the interweb.  Anyone know of something out there that would meet my
> needs?
>
> Kris
>
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Ray Walters via RE-wrenches
Here's a 100 amp version of the Reliance box.  Cheap, lots of room, easy 
to wire up, but NEMA 1.


https://www.electricgeneratorsdirect.com/Reliance-Controls-TCA1006D/p1102.html

On 3/2/2023 6:10 PM, Howie Michaelson via RE-wrenches wrote:
Does anyone know of any bypass switch/breaker setup for anything 
greater than 60 amps for 2 poles, other than large DPDT switches which 
get pricey and hard to source especially for 200 amps?

Howie

On Thu, Mar 2, 2023, 6:23 PM Ray Walters via RE-wrenches 
 wrote:


I probably still have one of the old QO boxes on the shelf, but I
never liked them.  Single pole, very tight, and you had to double
lug or use a weird split bolt arrangement with exposed copper out
past the breaker.

I started using these 60A T switches from Northern:

https://www.northerntool.com/shop/tools/product_200653609_200653609

Midnite makes small 30A and 60A T switches as well:


https://www.midnitesolar.com/productPhoto.php?product_ID=416&productCat_ID=29&sortOrder=3&act=p



Ray Walters

On 3/2/2023 11:57 AM, Sindelar Solar via RE-wrenches wrote:

Kris, It was SqD QO403, and it was a 3-pole load
center/disconnect, not 4-pole. You may recall that the
dual-inverter Trace Power Panels of long ago used two of these,
each one serving as an inverter bypass switch to one 120V AC leg.

On 3/2/2023 11:46 AM, Kristopher Schmid via RE-wrenches wrote:

Hi All,

I have a stand alone system that was upgraded from an FX
inverter to a Radian WITHOUT  the companion load center.  I
would like to add an inverter bypass circuit to operate the
house on generator power.  There used to be a 4 slot breaker
panel (SqD?) with the rocker switch preventing both breakers
from being in the on position simultaneously.  I have not been
able to find it on the interweb.  Anyone know of something out
there that would meet my needs?

Kris


Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com 
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE



-- 


*Allan Sindelar*
al...@sindelarsolar.com 

(No longer) NABCEP Certified PV Installation Professional
(Still) New Mexico EE98J Journeyman Electrician
(Retired) Founder, Positive Energy, Inc.
(Retired) Founder, Sindelar Solar
*505 780-2738 cell*


___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the 
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wren

Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Kristopher Schmid via RE-wrenches
Thanks for the help and suggestions!

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE

On Thu, Mar 2, 2023, 7:40 PM John Blittersdorf via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

>
> Howie,
>I use the QO612 small breaker box with two double pole breakers and the
> QO2DTI toggle.
>
> John Blittersdorf
>
> On Thu, Mar 2, 2023 at 8:11 PM Howie Michaelson via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Does anyone know of any bypass switch/breaker setup for anything greater
>> than 60 amps for 2 poles, other than large DPDT switches which get pricey
>> and hard to source especially for 200 amps?
>> Howie
>>
>> On Thu, Mar 2, 2023, 6:23 PM Ray Walters via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> I probably still have one of the old QO boxes on the shelf, but I never
>>> liked them.  Single pole, very tight, and you had to double lug or use a
>>> weird split bolt arrangement with exposed copper out past the breaker.
>>>
>>> I started using these 60A T switches from Northern:
>>>
>>> https://www.northerntool.com/shop/tools/product_200653609_200653609
>>>
>>> Midnite makes small 30A and 60A T switches as well:
>>>
>>>
>>> https://www.midnitesolar.com/productPhoto.php?product_ID=416&productCat_ID=29&sortOrder=3&act=p
>>>
>>> Ray Walters
>>> On 3/2/2023 11:57 AM, Sindelar Solar via RE-wrenches wrote:
>>>
>>> Kris, It was SqD QO403, and it was a 3-pole load center/disconnect, not
>>> 4-pole. You may recall that the dual-inverter Trace Power Panels of long
>>> ago used two of these, each one serving as an inverter bypass switch to one
>>> 120V AC leg.
>>>
>>> On 3/2/2023 11:46 AM, Kristopher Schmid via RE-wrenches wrote:
>>>
>>> Hi All,
>>>
>>> I have a stand alone system that was upgraded from an FX inverter to a
>>> Radian WITHOUT  the companion load center.  I would like to add an inverter
>>> bypass circuit to operate the house on generator power.  There used to be a
>>> 4 slot breaker panel (SqD?) with the rocker switch preventing both breakers
>>> from being in the on position simultaneously.  I have not been able to find
>>> it on the interweb.  Anyone know of something out there that would meet my
>>> needs?
>>>
>>> Kris
>>>
>>>
>>> Shine On!
>>>
>>> Kris Schmid
>>> Legacy Solar, LLC
>>> 137 West 1st Avenue
>>> 
>>> Luck, WI 54853
>>> 
>>> www.legacysolar.com
>>> 715-653-4295
>>> NABCEP Certified PV Installation Professional
>>> Licensed Wisconsin Master Electrician
>>> BSEE
>>>
>>>
>>> --
>>>
>>> *Allan Sindelar*
>>> al...@sindelarsolar.com
>>> (No longer) NABCEP Certified PV Installation Professional
>>> (Still) New Mexico EE98J Journeyman Electrician
>>> (Retired) Founder, Positive Energy, Inc.
>>> (Retired) Founder, Sindelar Solar
>>> *505 780-2738 cell*
>>>
>>>
>>>
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & 
>>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:http://www.members.re-wrenches.org
>>>
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archiv

Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread John Blittersdorf via RE-wrenches
Howie,
   I use the QO612 small breaker box with two double pole breakers and the
QO2DTI toggle.

John Blittersdorf

On Thu, Mar 2, 2023 at 8:11 PM Howie Michaelson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Does anyone know of any bypass switch/breaker setup for anything greater
> than 60 amps for 2 poles, other than large DPDT switches which get pricey
> and hard to source especially for 200 amps?
> Howie
>
> On Thu, Mar 2, 2023, 6:23 PM Ray Walters via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> I probably still have one of the old QO boxes on the shelf, but I never
>> liked them.  Single pole, very tight, and you had to double lug or use a
>> weird split bolt arrangement with exposed copper out past the breaker.
>>
>> I started using these 60A T switches from Northern:
>>
>> https://www.northerntool.com/shop/tools/product_200653609_200653609
>>
>> Midnite makes small 30A and 60A T switches as well:
>>
>>
>> https://www.midnitesolar.com/productPhoto.php?product_ID=416&productCat_ID=29&sortOrder=3&act=p
>>
>> Ray Walters
>> On 3/2/2023 11:57 AM, Sindelar Solar via RE-wrenches wrote:
>>
>> Kris, It was SqD QO403, and it was a 3-pole load center/disconnect, not
>> 4-pole. You may recall that the dual-inverter Trace Power Panels of long
>> ago used two of these, each one serving as an inverter bypass switch to one
>> 120V AC leg.
>>
>> On 3/2/2023 11:46 AM, Kristopher Schmid via RE-wrenches wrote:
>>
>> Hi All,
>>
>> I have a stand alone system that was upgraded from an FX inverter to a
>> Radian WITHOUT  the companion load center.  I would like to add an inverter
>> bypass circuit to operate the house on generator power.  There used to be a
>> 4 slot breaker panel (SqD?) with the rocker switch preventing both breakers
>> from being in the on position simultaneously.  I have not been able to find
>> it on the interweb.  Anyone know of something out there that would meet my
>> needs?
>>
>> Kris
>>
>>
>> Shine On!
>>
>> Kris Schmid
>> Legacy Solar, LLC
>> 137 West 1st Avenue
>> 
>> Luck, WI 54853
>> 
>> www.legacysolar.com
>> 715-653-4295
>> NABCEP Certified PV Installation Professional
>> Licensed Wisconsin Master Electrician
>> BSEE
>>
>>
>> --
>>
>> *Allan Sindelar*
>> al...@sindelarsolar.com
>> (No longer) NABCEP Certified PV Installation Professional
>> (Still) New Mexico EE98J Journeyman Electrician
>> (Retired) Founder, Positive Energy, Inc.
>> (Retired) Founder, Sindelar Solar
>> *505 780-2738 cell*
>>
>>
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & 
>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the 
>> other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:http://www.members.re-wrenches.org
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.o

Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Howie Michaelson via RE-wrenches
Does anyone know of any bypass switch/breaker setup for anything greater
than 60 amps for 2 poles, other than large DPDT switches which get pricey
and hard to source especially for 200 amps?
Howie

On Thu, Mar 2, 2023, 6:23 PM Ray Walters via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> I probably still have one of the old QO boxes on the shelf, but I never
> liked them.  Single pole, very tight, and you had to double lug or use a
> weird split bolt arrangement with exposed copper out past the breaker.
>
> I started using these 60A T switches from Northern:
>
> https://www.northerntool.com/shop/tools/product_200653609_200653609
>
> Midnite makes small 30A and 60A T switches as well:
>
>
> https://www.midnitesolar.com/productPhoto.php?product_ID=416&productCat_ID=29&sortOrder=3&act=p
>
> Ray Walters
> On 3/2/2023 11:57 AM, Sindelar Solar via RE-wrenches wrote:
>
> Kris, It was SqD QO403, and it was a 3-pole load center/disconnect, not
> 4-pole. You may recall that the dual-inverter Trace Power Panels of long
> ago used two of these, each one serving as an inverter bypass switch to one
> 120V AC leg.
>
> On 3/2/2023 11:46 AM, Kristopher Schmid via RE-wrenches wrote:
>
> Hi All,
>
> I have a stand alone system that was upgraded from an FX inverter to a
> Radian WITHOUT  the companion load center.  I would like to add an inverter
> bypass circuit to operate the house on generator power.  There used to be a
> 4 slot breaker panel (SqD?) with the rocker switch preventing both breakers
> from being in the on position simultaneously.  I have not been able to find
> it on the interweb.  Anyone know of something out there that would meet my
> needs?
>
> Kris
>
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
>
>
> --
>
> *Allan Sindelar*
> al...@sindelarsolar.com
> (No longer) NABCEP Certified PV Installation Professional
> (Still) New Mexico EE98J Journeyman Electrician
> (Retired) Founder, Positive Energy, Inc.
> (Retired) Founder, Sindelar Solar
> *505 780-2738 cell*
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the 
> other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Ray Walters via RE-wrenches
I probably still have one of the old QO boxes on the shelf, but I never 
liked them.  Single pole, very tight, and you had to double lug or use a 
weird split bolt arrangement with exposed copper out past the breaker.


I started using these 60A T switches from Northern:

https://www.northerntool.com/shop/tools/product_200653609_200653609

Midnite makes small 30A and 60A T switches as well:

https://www.midnitesolar.com/productPhoto.php?product_ID=416&productCat_ID=29&sortOrder=3&act=p

Ray Walters

On 3/2/2023 11:57 AM, Sindelar Solar via RE-wrenches wrote:
Kris, It was SqD QO403, and it was a 3-pole load center/disconnect, 
not 4-pole. You may recall that the dual-inverter Trace Power Panels 
of long ago used two of these, each one serving as an inverter bypass 
switch to one 120V AC leg.


On 3/2/2023 11:46 AM, Kristopher Schmid via RE-wrenches wrote:

Hi All,

I have a stand alone system that was upgraded from an FX inverter to 
a Radian WITHOUT  the companion load center.  I would like to add an 
inverter bypass circuit to operate the house on generator power.  
There used to be a 4 slot breaker panel (SqD?) with the rocker switch 
preventing both breakers from being in the on position 
simultaneously.  I have not been able to find it on the interweb.  
Anyone know of something out there that would meet my needs?


Kris


Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com 
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE



--

*Allan Sindelar*
al...@sindelarsolar.com 

(No longer) NABCEP Certified PV Installation Professional
(Still) New Mexico EE98J Journeyman Electrician
(Retired) Founder, Positive Energy, Inc.
(Retired) Founder, Sindelar Solar
*505 780-2738 cell*


___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Sindelar Solar via RE-wrenches
Kris, It was SqD QO403, and it was a 3-pole load center/disconnect, not 
4-pole. You may recall that the dual-inverter Trace Power Panels of long 
ago used two of these, each one serving as an inverter bypass switch to 
one 120V AC leg.


On 3/2/2023 11:46 AM, Kristopher Schmid via RE-wrenches wrote:

Hi All,

I have a stand alone system that was upgraded from an FX inverter to a 
Radian WITHOUT  the companion load center.  I would like to add an 
inverter bypass circuit to operate the house on generator power.  
There used to be a 4 slot breaker panel (SqD?) with the rocker switch 
preventing both breakers from being in the on position 
simultaneously.  I have not been able to find it on the interweb.  
Anyone know of something out there that would meet my needs?


Kris


Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com 
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE



--

*Allan Sindelar*
al...@sindelarsolar.com 

(No longer) NABCEP Certified PV Installation Professional
(Still) New Mexico EE98J Journeyman Electrician
(Retired) Founder, Positive Energy, Inc.
(Retired) Founder, Sindelar Solar
*505 780-2738 cell*
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Lloyd Hoffstatter via RE-wrenches
https://www.zoro.com/square-d-cb-accessory-interlock-attachment-qou2dtila/i/G0840896/?utm_source=google&utm_medium=surfaces&utm_campaign=shopping%20feed&utm_content=free%20google%20shopping%20clicks&gclid=CjwKCAiAr4GgBhBFEiwAgwORrQ7ciEpSjpyftUryryWGfWJ7kiFdpiRnJ1DZ3k9ifEZYYBQJ_KYULBoC9qQQAvD_BwE

Best regards,
Lloyd
Lloyd Hoffstatter
Sunstruck Consulting

Get Outlook for iOS<https://aka.ms/o0ukef>

From: RE-wrenches  on behalf of 
Kristopher Schmid via RE-wrenches 
Sent: Thursday, March 2, 2023 12:46:43 PM
To: RE-wrenches 
Cc: Kristopher Schmid 
Subject: [RE-wrenches] Inverter bypass

Hi All,

I have a stand alone system that was upgraded from an FX inverter to a Radian 
WITHOUT  the companion load center.  I would like to add an inverter bypass 
circuit to operate the house on generator power.  There used to be a 4 slot 
breaker panel (SqD?) with the rocker switch preventing both breakers from being 
in the on position simultaneously.  I have not been able to find it on the 
interweb.  Anyone know of something out there that would meet my needs?

Kris


Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com<http://www.legacysolar.com>
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Inverter bypass

2023-03-02 Thread Kristopher Schmid via RE-wrenches
Hi All,

I have a stand alone system that was upgraded from an FX inverter to a
Radian WITHOUT  the companion load center.  I would like to add an inverter
bypass circuit to operate the house on generator power.  There used to be a
4 slot breaker panel (SqD?) with the rocker switch preventing both breakers
from being in the on position simultaneously.  I have not been able to find
it on the interweb.  Anyone know of something out there that would meet my
needs?

Kris


Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Inverter bypass

2012-06-10 Thread Allan Sindelar

  
  
Mac,
This is the unformatted, cut-n-pasted content from a pdf file, from
which you may extract the info you need.  This was offered by Greg
Smith of SMA to those who attended the Sunny Island seminar at the
recent NABCEP Continuing Education Conference. The Nottagutter is
your recommended solution.


Recommended Third Party Components
Current Shunt:
Deltec MKB 500-50 – 500 Amp 50 mV Current Shunt
http://www.solar-electric.com/mkb-500-50.html
Auxiliary Relay: Dayton Ice Cube Relay SPDT (Single Pole Double
Throw) With 120 V Coil (Part # 1EHC4)
http://www.grainger.com/Grainger/DAYTON-Relay-1EHC4
5 Pin Socket For Dayton Ice Cube Relay (Part # 1EGP6)
http://www.grainger.com/Grainger/DAYTON-Relay-1EGP6
Magnecraft Power Relay SPDT (Single Pole Double Throw) With 120 V
Coil (Part # 9AS5A52-120)
http://www.grainger.com/Grainger/MAGNECRAFT-Relay-6CWZ1
Bypass Switch:
Midnight Solar Nottagutter
http://www.midnitesolar.com/products.php?menuItem=products&productCat_ID=11&productCatName=Nottagutter
Eaton Breaker Based Maintenance Bypass Switch
Automatic Transfer Switch
Eaton Residential ATS
http://www.eaton.com/Electrical/USA/Support/Documentation/Catalogs/idcplg?IdcService=GET_FILE&RevisionSelectionMethod=LatestReleased&Rendition=Primary&dDocName=VOL01_TAB03
(Page 120)
Eaton Commercial ATS (Contactor Based or Breaker Based) With ATC-100
Controller
http://www.eaton.com/Electrical/USA/Support/Documentation/Catalogs/idcplg?IdcService=GET_FILE&RevisionSelectionMethod=LatestReleased&Rendition=Primary&dDocName=VOL02_TAB12
(Contactor Based – Page 538; Breaker Based – Page 556; ATC-100 –
Page 594)

Allan


  
  
  Allan Sindelar
  al...@positiveenergysolar.com
NABCEP Certified Photovoltaic
  Installer
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder and Chief Technology Officer
  Positive Energy, Inc.
  3209 Richards Lane (note new address)
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com
  
  
  
   

On 6/10/2012 3:46 PM, mac Lewis wrote:
Hello wrenches,
  
  
  I am interested in input about an inverter bypass assembly
for a dual Sunny Island 5048-US system with a 30 kW generator.
 SMA does not offer anything for this, but I think its an
important part of the design.  Any input would be appreciated.
  
  
  Thanks


-- 



  


Mac Lewis


  
"Yo solo sé que
no sé nada." -Sócrates

  
  
  
  
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Inverter bypass

2012-06-10 Thread mac Lewis
Hello wrenches,

I am interested in input about an inverter bypass assembly for a dual Sunny
Island 5048-US system with a 30 kW generator.  SMA does not offer anything
for this, but I think its an important part of the design.  Any input would
be appreciated.

Thanks

-- 



Mac Lewis

*

"Yo solo sé que no sé nada." -Sócrates
*
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org