Hi Jeff:
I have had some similar issues with the Kohler generators in recent years, 
after installing hundreds of air cooled and water cooled generators from them.  
I have heard that they are less reliable now, and the company is harder to deal 
with now.
Recently, I tried a Generac in an off-grid project, which I have found is 
even more difficult to work with.  They don't warranty the product for off-grid 
applications, it requires hard wiring a battery charger, and it starts and 
stops based on utility sensing, which required installation of a relay to 
switch the sensing circuit on and off.  It was a pain to deal with, and 
required a few more trips to the site than I would have liked.
On a similar note, Xantrex provided the Auto Gen Start module, but it did 
not support 2-wire start!  Isn't that the most common gen start configuration?  
The newer versions do offer that now. 

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037





From: Jeff Yago jry...@netscape.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Mon, March 29, 2010 7:53:18 AM
Subject: Re: [RE-wrenches] Kohler Generator Issues


Although we have specified and included Kohler RES models in all our off-grid 
and battery based solar projects for over 15 years, we have seen a real decline 
in the suitability of the Kohler line in the past few years for use in 
solar/battery/generator applications.  First they killed off the 1800 RPM units 
under 15 kW.  We had many older systems that would not work when we replaced an 
aging 1800 RPM unit with their same kW size new 3600 RPM units, which made 
inverters go nuts with under-voltage and over-current errors.

Then several years ago they got rid of the battery charging alternator or 
whatever that re-charged the battery when the generator was running as a way to 
reduce costs, so now the only way to keep the battery charged was to plug in a 
full time float charger. This 24/7 electrical load is not a good idea for 
smaller off-grid systems and requires another set of wires out to the generator 
to supply this outlet.  Finally, Kohler added a diagnostic electronics panel 
that adds another 24/7 electrical load.  We kill this off during installation 
on any off-grid application as we cannot justify this 24/7 standby load.  There 
is a software switch to do this, but its not easy to find in the instructions.

Funny thing was the other day I received a call from the main Kohler factory 
about some marketing issues and I finally let loose with the above rant.  I 
really complained that so far they have done everything they could NOT to serve 
this very large and growing off-grid market, and I pointed out that most of 
their recent design improvements made their generators LESS suitable for this 
market, not better.  This guy was absolutely dumb-struck, and it appears to me 
that they have made no effort to understand this market.  Their more recent 
efforts to void warranties is just another reason to look for a different 
generator supplier.

Has anyone on this list had any contact from Kohler central office about 
finding out what features this industry needs?   The guy I talked with may be 
just blowing smoke, but he promised to have a followup call in next few weeks 
to learn more about what they can do.  According to him, he thinks they can add 
a software switch in the programming for little or no cost like on/grid - 
off/grid that we could access during setup that would adjust generator 
parameters and standby losses when used in an inverter-battery application.   
In case he really does followup, are there any other rants I could include from 
you guys that have been a problem for you when using Kohler generators.  I will 
assume we are limiting this to their non-water cooled units under 15 kW.

While ranting on generators, the main reason we liked to use Kohler was the 
easy 2-wire start/stop connections you can connect to the aux relay in most 
inverters, while many other generator brands were not easy to remote start from 
an inverter or required multi-step starting relays.  Has this changed, and are 
there now other brands of generators in the 8 to 15 kW range that work well for 
backup of solar/battery charging applications and the manufacturer does not 
have warranty issues when used in off-grid applications?

Thanks,

Jeff Yago

_
Netscape.  Just the Net You Need.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios

Re: [RE-wrenches] Kohler Generator Issues

2010-03-30 Thread boB Gudgel

Nick Soleil wrote:

Hi Jeff:
I have had some similar issues with the Kohler generators in 
recent years, after installing hundreds of air cooled and water cooled 
generators from them.  I have heard that they are less reliable now, 
and the company is harder to deal with now.
Recently, I tried a Generac in an off-grid project, which I have 
found is even more difficult to work with.  They don't warranty the 
product for off-grid applications, it requires hard wiring a battery 
charger, and it starts and stops based on utility sensing, which 
required installation of a relay to switch the sensing circuit on and 
off.  It was a pain to deal with, and required a few more trips to the 
site than I would have liked.
On a similar note, Xantrex provided the Auto Gen Start module, but 
it did not support 2-wire start!  Isn't that the most common gen start 
configuration?  The newer versions do offer that now.
 



Is this no warranty if used off grid in writing from these 
manufacturers, or is it just some salespeople saying this ?


Why would you need a generator if you have grid available ?

boB





Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037



*From:* Jeff Yago jry...@netscape.com
*To:* RE-wrenches re-wrenches@lists.re-wrenches.org
*Sent:* Mon, March 29, 2010 7:53:18 AM
*Subject:* Re: [RE-wrenches] Kohler Generator Issues


Although we have specified and included Kohler RES models in all our 
off-grid and battery based solar projects for over 15 years, we have 
seen a real decline in the suitability of the Kohler line in the past 
few years for use in solar/battery/generator applications.  First they 
killed off the 1800 RPM units under 15 kW.  We had many older systems 
that would not work when we replaced an aging 1800 RPM unit with their 
same kW size new 3600 RPM units, which made inverters go nuts with 
under-voltage and over-current errors.


Then several years ago they got rid of the battery charging alternator 
or whatever that re-charged the battery when the generator was running 
as a way to reduce costs, so now the only way to keep the battery 
charged was to plug in a full time float charger. This 24/7 electrical 
load is not a good idea for smaller off-grid systems and requires 
another set of wires out to the generator to supply this outlet.  
Finally, Kohler added a diagnostic electronics panel that adds another 
24/7 electrical load.  We kill this off during installation on any 
off-grid application as we cannot justify this 24/7 standby load.  
There is a software switch to do this, but its not easy to find in the 
instructions.


Funny thing was the other day I received a call from the main Kohler 
factory about some marketing issues and I finally let loose with the 
above rant.  I really complained that so far they have done everything 
they could NOT to serve this very large and growing off-grid market, 
and I pointed out that most of their recent design improvements made 
their generators LESS suitable for this market, not better.  This guy 
was absolutely dumb-struck, and it appears to me that they have made 
no effort to understand this market.  Their more recent efforts to 
void warranties is just another reason to look for a different 
generator supplier.


Has anyone on this list had any contact from Kohler central office 
about finding out what features this industry needs?  The guy I talked 
with may be just blowing smoke, but he promised to have a followup 
call in next few weeks to learn more about what they can do.  
According to him, he thinks they can add a software switch in the 
programming for little or no cost like on/grid - off/grid that we 
could access during setup that would adjust generator parameters and 
standby losses when used in an inverter-battery application.  In case 
he really does followup, are there any other rants I could include 
from you guys that have been a problem for you when using Kohler 
generators.  I will assume we are limiting this to their non-water 
cooled units under 15 kW.


While ranting on generators, the main reason we liked to use Kohler 
was the easy 2-wire start/stop connections you can connect to the aux 
relay in most inverters, while many other generator brands were not 
easy to remote start from an inverter or required multi-step starting 
relays.  Has this changed, and are there now other brands of 
generators in the 8 to 15 kW range that work well for backup of 
solar/battery charging applications and the manufacturer does not have 
warranty issues when used in off-grid applications?


Thanks,

Jeff Yago

_
Netscape.  Just the Net You Need.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Re: [RE-wrenches] Kohler Generator Issues

2010-03-30 Thread Jason Szumlanski
Bob,

I guess you don't live in a hurricane prone area! Grid-tied or off-grid,
backup generators are common in this neck of the woods.

Jason Szumlanski
Fafco Solar
Southwest Florida

Original Message
Message: 3
Date: Tue, 30 Mar 2010 12:07:28 -0700
From: boB Gudgel b...@midnitesolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Kohler Generator Issues
Message-ID: 4bb24bf0.7000...@midnitesolar.com
Content-Type: text/plain; charset=ISO-8859-1; format=flowe

Is this no warranty if used off grid in writing from these 
manufacturers, or is it just some salespeople saying this ?

Why would you need a generator if you have grid available ?

boB



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Kohler Generator Issues

2010-03-30 Thread boB Gudgel

Jason Szumlanski wrote:

Bob,

I guess you don't live in a hurricane prone area! Grid-tied or off-grid,
backup generators are common in this neck of the woods.
  

Yes, of course, Jason.
But, wouldn't it  be more of a generator run time issue ??
After all, the grid isn't really there when the power is out... is it ?

I guess that's subject to interpretation.  We deal with generator 
installations
so I would still like to know if there is something in writing or if it 
has been only verbal
at this point.  Something sounds fishy to me.   Oh, and 3 tubs of tartar 
with that fish, please.


Thanks guys.
boB




Jason Szumlanski
Fafco Solar
Southwest Florida

Original Message
Message: 3
Date: Tue, 30 Mar 2010 12:07:28 -0700
From: boB Gudgel b...@midnitesolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Kohler Generator Issues
Message-ID: 4bb24bf0.7000...@midnitesolar.com
Content-Type: text/plain; charset=ISO-8859-1; format=flowe

Is this no warranty if used off grid in writing from these 
manufacturers, or is it just some salespeople saying this ?


Why would you need a generator if you have grid available ?

boB



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


  


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Kohler Generator Issues

2010-03-30 Thread Brian Teitelbaum
Hi boB,

The issue is whether the generator is rated for use as prime power or rated 
as back-up power. Prime power units will get considerably more run-time hours 
on them then generators used in back-up. At least that is what the generator 
manufacturers think.

Once upon a time it didn't matter. The engines were heavy cast iron, and 
running at slow speeds, usually 1800RPM, but sometimes as low as 1200RPM, and 
lasted for thousands of hours of run time. As the manufacturers switched to 
cheaper aluminum engines running at 3600, the amount of hours before a major 
rebuild was required decreased. Honda, and others, were able to bring aluminum 
engines back up to fairly long life-spans, but they are still not as rugged as 
those old hunks of iron. Emission regulations further destroyed the old iron 
engines, unless you get one big enough to have 4-cylinders.

There is no reason, other than cost, for Kohler to not make a 4-cylinder, cast 
iron, 1800RPM, prime-power unit, but maybe they feel that there just isn't 
enough of a market for them to build it. I think that they are wrong, but I 
don't know the true numbers.

The real problem is that the generator manufacturers don't understand how 
off-grid systems work these days. 20 years ago, you could expect an off-grid 
generator to rack up considerable hours in a short time. These days, we get PV 
to do that, and the genny is just used for back-up. If the system is designed 
properly, the genny should get minimal hours per year, and the manufacturer 
should be able to warranty them. They need to be educated.

Brian Teitelbaum
AEE Solar




-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of boB Gudgel
Sent: Tuesday, March 30, 2010 12:07 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Kohler Generator Issues

Nick Soleil wrote:
 Hi Jeff:
 I have had some similar issues with the Kohler generators in 
 recent years, after installing hundreds of air cooled and water cooled 
 generators from them.  I have heard that they are less reliable now, 
 and the company is harder to deal with now.
 Recently, I tried a Generac in an off-grid project, which I have 
 found is even more difficult to work with.  They don't warranty the 
 product for off-grid applications, it requires hard wiring a battery 
 charger, and it starts and stops based on utility sensing, which 
 required installation of a relay to switch the sensing circuit on and 
 off.  It was a pain to deal with, and required a few more trips to the 
 site than I would have liked.
 On a similar note, Xantrex provided the Auto Gen Start module, but 
 it did not support 2-wire start!  Isn't that the most common gen start 
 configuration?  The newer versions do offer that now.
  


Is this no warranty if used off grid in writing from these 
manufacturers, or is it just some salespeople saying this ?

Why would you need a generator if you have grid available ?

boB




 Nick Soleil
 Project Manager
 Advanced Alternative Energy Solutions, LLC
 PO Box 657
 Petaluma, CA 94953
 Cell: 707-321-2937
 Office: 707-789-9537
 Fax: 707-769-9037


 
 *From:* Jeff Yago jry...@netscape.com
 *To:* RE-wrenches re-wrenches@lists.re-wrenches.org
 *Sent:* Mon, March 29, 2010 7:53:18 AM
 *Subject:* Re: [RE-wrenches] Kohler Generator Issues


 Although we have specified and included Kohler RES models in all our 
 off-grid and battery based solar projects for over 15 years, we have 
 seen a real decline in the suitability of the Kohler line in the past 
 few years for use in solar/battery/generator applications.  First they 
 killed off the 1800 RPM units under 15 kW.  We had many older systems 
 that would not work when we replaced an aging 1800 RPM unit with their 
 same kW size new 3600 RPM units, which made inverters go nuts with 
 under-voltage and over-current errors.

 Then several years ago they got rid of the battery charging alternator 
 or whatever that re-charged the battery when the generator was running 
 as a way to reduce costs, so now the only way to keep the battery 
 charged was to plug in a full time float charger. This 24/7 electrical 
 load is not a good idea for smaller off-grid systems and requires 
 another set of wires out to the generator to supply this outlet.  
 Finally, Kohler added a diagnostic electronics panel that adds another 
 24/7 electrical load.  We kill this off during installation on any 
 off-grid application as we cannot justify this 24/7 standby load.  
 There is a software switch to do this, but its not easy to find in the 
 instructions.

 Funny thing was the other day I received a call from the main Kohler 
 factory about some marketing issues and I finally let loose with the 
 above rant.  I really complained that so far they have done everything 
 they could NOT to serve this very large and growing off-grid market, 
 and I

Re: [RE-wrenches] Kohler Generator Issues

2010-03-30 Thread boB Gudgel

Brian Teitelbaum wrote:

Hi boB,

The issue is whether the generator is rated for use as prime power or rated as 
back-up power. Prime power units will get considerably more run-time hours on them then 
generators used in back-up. At least that is what the generator manufacturers think.

Once upon a time it didn't matter. The engines were heavy cast iron, and 
running at slow speeds, usually 1800RPM, but sometimes as low as 1200RPM, and 
lasted for thousands of hours of run time. As the manufacturers switched to 
cheaper aluminum engines running at 3600, the amount of hours before a major 
rebuild was required decreased. Honda, and others, were able to bring aluminum 
engines back up to fairly long life-spans, but they are still not as rugged as 
those old hunks of iron. Emission regulations further destroyed the old iron 
engines, unless you get one big enough to have 4-cylinders.

There is no reason, other than cost, for Kohler to not make a 4-cylinder, cast 
iron, 1800RPM, prime-power unit, but maybe they feel that there just isn't 
enough of a market for them to build it. I think that they are wrong, but I 
don't know the true numbers.

The real problem is that the generator manufacturers don't understand how 
off-grid systems work these days. 20 years ago, you could expect an off-grid 
generator to rack up considerable hours in a short time. These days, we get PV 
to do that, and the genny is just used for back-up. If the system is designed 
properly, the genny should get minimal hours per year, and the manufacturer 
should be able to warranty them. They need to be educated.

Brian Teitelbaum
AEE Solar

  



Thanks Brian.  Yes, I do believe they need to be educated that these 
days, their generators, even backup rather than prim power classes, are 
more of
a backup.  If they wanted to, they could just use the run time meter to 
decide if it is warranty or not, maybe.


Thanks again,
boB












-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of boB Gudgel
Sent: Tuesday, March 30, 2010 12:07 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Kohler Generator Issues

Nick Soleil wrote:
  

Hi Jeff:
I have had some similar issues with the Kohler generators in 
recent years, after installing hundreds of air cooled and water cooled 
generators from them.  I have heard that they are less reliable now, 
and the company is harder to deal with now.
Recently, I tried a Generac in an off-grid project, which I have 
found is even more difficult to work with.  They don't warranty the 
product for off-grid applications, it requires hard wiring a battery 
charger, and it starts and stops based on utility sensing, which 
required installation of a relay to switch the sensing circuit on and 
off.  It was a pain to deal with, and required a few more trips to the 
site than I would have liked.
On a similar note, Xantrex provided the Auto Gen Start module, but 
it did not support 2-wire start!  Isn't that the most common gen start 
configuration?  The newer versions do offer that now.
 




Is this no warranty if used off grid in writing from these 
manufacturers, or is it just some salespeople saying this ?


Why would you need a generator if you have grid available ?

boB




  

Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037



*From:* Jeff Yago jry...@netscape.com
*To:* RE-wrenches re-wrenches@lists.re-wrenches.org
*Sent:* Mon, March 29, 2010 7:53:18 AM
*Subject:* Re: [RE-wrenches] Kohler Generator Issues


Although we have specified and included Kohler RES models in all our 
off-grid and battery based solar projects for over 15 years, we have 
seen a real decline in the suitability of the Kohler line in the past 
few years for use in solar/battery/generator applications.  First they 
killed off the 1800 RPM units under 15 kW.  We had many older systems 
that would not work when we replaced an aging 1800 RPM unit with their 
same kW size new 3600 RPM units, which made inverters go nuts with 
under-voltage and over-current errors.


Then several years ago they got rid of the battery charging alternator 
or whatever that re-charged the battery when the generator was running 
as a way to reduce costs, so now the only way to keep the battery 
charged was to plug in a full time float charger. This 24/7 electrical 
load is not a good idea for smaller off-grid systems and requires 
another set of wires out to the generator to supply this outlet.  
Finally, Kohler added a diagnostic electronics panel that adds another 
24/7 electrical load.  We kill this off during installation on any 
off-grid application as we cannot justify this 24/7 standby load.  
There is a software switch to do this, but its not easy to find in the 
instructions

Re: [RE-wrenches] Kohler Generator Issues

2010-03-30 Thread jason pozner
Jeff,

When we purchased a 12K unit for a client, the distributor conveniently
waited until after the purchase to mention the fact that Kohler wouldn't
warranty off-grid usage, and to instruct our customer to not ever mention
anything other than it was used for grid-connected standby.  To pacify the
perfectly crafted words I had for him, he mentioned that Kohler had an off
grid unit coming available in the next couple of months addressing all of
the fore-mentioned concerns.  This was about 2 years ago, and I now see
where he intended his smoke to go.  I have never heard of such a unit again.

When that same client needed another generator we shopped around and found
Cummins-Onan to be great to deal with.  Simple start up procedure, quieter
than that Kohler 12K, 2-wire start, and their price for a 30K generator was
800.00 cheaper than my Kohler distributor could give to me even though it
was our first purchase with them. Thus far I have been pleased with Onan.

To answer your question, we have never been contacted by Kohler.

Jay Pozner
Nunatak Alternative Energy Solutions
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Kohler Generator Issues

2010-03-30 Thread dan
I'm told Kohler has an 1800 RPM 10  15K Diesel unit that ties in nicely with a Hot water heating system.Dan BrownPresidentFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44


 Original Message 
Subject: Re: [RE-wrenches] Kohler Generator Issues
From: jason pozner zzyyzz...@gmail.com
Date: Tue, March 30, 2010 5:11 pm
To: jry...@netscape.com, RE-wrenches
re-wrenches@lists.re-wrenches.org

Jeff,When we purchased a 12K unit for a client, the distributor conveniently waited until after the purchase to mention the fact that Kohler wouldn't warranty off-grid usage, and to instruct our customer to not ever mention anything other than it was used for grid-connected standby. To pacify the perfectly crafted words I had for him, he mentioned that Kohler had an off grid unit coming available in the next couple of months addressing all of the fore-mentioned concerns. This was about 2 years ago, and I now see where he intended his smoke to go. I have never heard of such a unit again. When that same client needed another generator we shopped around and found Cummins-Onan to be great to deal with. Simple start up procedure, quieter than that Kohler 12K, 2-wire start, and their price for a 30K generator was 800.00 cheaper than my Kohler distributor could give to me even though it was our first purchase with them. Thus far I have been pleased with Onan.  To answer your question, we have never been contacted by Kohler.Jay PoznerNunatak Alternative Energy Solutions ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Kohler Generator Issues

2010-03-29 Thread All Solar, Inc. Jeremy Rodriguez

Jeff,
check out Gillette Generators.
Prime power warranty. and 'ok with inverter'
Jeremy
- Original Message - 
From: Jeff Yago jry...@netscape.com

To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Monday, March 29, 2010 8:53 AM
Subject: Re: [RE-wrenches] Kohler Generator Issues




Although we have specified and included Kohler RES models in all our 
off-grid and battery based solar projects for over 15 years, we have seen 
a real decline in the suitability of the Kohler line in the past few years 
for use in solar/battery/generator applications.  First they killed off 
the 1800 RPM units under 15 kW.  We had many older systems that would not 
work when we replaced an aging 1800 RPM unit with their same kW size new 
3600 RPM units, which made inverters go nuts with under-voltage and 
over-current errors.


Then several years ago they got rid of the battery charging alternator or 
whatever that re-charged the battery when the generator was running as a 
way to reduce costs, so now the only way to keep the battery charged was 
to plug in a full time float charger. This 24/7 electrical load is not a 
good idea for smaller off-grid systems and requires another set of wires 
out to the generator to supply this outlet.  Finally, Kohler added a 
diagnostic electronics panel that adds another 24/7 electrical load.  We 
kill this off during installation on any off-grid application as we 
cannot justify this 24/7 standby load.  There is a software switch to do 
this, but its not easy to find in the instructions.


Funny thing was the other day I received a call from the main Kohler 
factory about some marketing issues and I finally let loose with the above 
rant.  I really complained that so far they have done everything they 
could NOT to serve this very large and growing off-grid market, and I 
pointed out that most of their recent design improvements made their 
generators LESS suitable for this market, not better.  This guy was 
absolutely dumb-struck, and it appears to me that they have made no effort 
to understand this market.  Their more recent efforts to void warranties 
is just another reason to look for a different generator supplier.


Has anyone on this list had any contact from Kohler central office about 
finding out what features this industry needs?   The guy I talked with may 
be just blowing smoke, but he promised to have a followup call in next few 
weeks to learn more about what they can do.  According to him, he thinks 
they can add a software switch in the programming for little or no cost 
like on/grid - off/grid that we could access during setup that would 
adjust generator parameters and standby losses when used in an 
inverter-battery application.   In case he really does followup, are there 
any other rants I could include from you guys that have been a problem for 
you when using Kohler generators.  I will assume we are limiting this to 
their non-water cooled units under 15 kW.


While ranting on generators, the main reason we liked to use Kohler was 
the easy 2-wire start/stop connections you can connect to the aux relay in 
most inverters, while many other generator brands were not easy to remote 
start from an inverter or required multi-step starting relays.  Has this 
changed, and are there now other brands of generators in the 8 to 15 kW 
range that work well for backup of solar/battery charging applications and 
the manufacturer does not have warranty issues when used in off-grid 
applications?


Thanks,

Jeff Yago

_
Netscape.  Just the Net You Need.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Kohler Generator Issues

2010-03-29 Thread Darryl Thayer
Although the 48 volt output from the Cummings small gen is unusual, I like the 
Propane option, and perhaps it is suitable.  It is small, 5 kW but also 
batteries last longer on a slow charge.  It also has a controlled output to do 
battery charging.  
Darryl

--- On Mon, 3/29/10, All Solar, Inc. Jeremy Rodriguez allso...@scswifi.net 
wrote:

 From: All Solar, Inc. Jeremy Rodriguez allso...@scswifi.net
 Subject: Re: [RE-wrenches] Kohler Generator Issues
 To: jry...@netscape.com, RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Monday, March 29, 2010, 12:52 PM
 Jeff,
 check out Gillette Generators.
 Prime power warranty. and 'ok with inverter'
 Jeremy
 - Original Message - From: Jeff Yago jry...@netscape.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Sent: Monday, March 29, 2010 8:53 AM
 Subject: Re: [RE-wrenches] Kohler Generator Issues
 
 
  
  Although we have specified and included Kohler RES
 models in all our off-grid and battery based solar projects
 for over 15 years, we have seen a real decline in the
 suitability of the Kohler line in the past few years for use
 in solar/battery/generator applications.  First they
 killed off the 1800 RPM units under 15 kW.  We had many
 older systems that would not work when we replaced an aging
 1800 RPM unit with their same kW size new 3600 RPM units,
 which made inverters go nuts with under-voltage and
 over-current errors.
  
  Then several years ago they got rid of the battery
 charging alternator or whatever that re-charged the battery
 when the generator was running as a way to reduce costs, so
 now the only way to keep the battery charged was to plug in
 a full time float charger. This 24/7 electrical load is not
 a good idea for smaller off-grid systems and requires
 another set of wires out to the generator to supply this
 outlet.  Finally, Kohler added a diagnostic electronics
 panel that adds another 24/7 electrical load.  We
 kill this off during installation on any off-grid
 application as we cannot justify this 24/7 standby
 load.  There is a software switch to do this, but its
 not easy to find in the instructions.
  
  Funny thing was the other day I received a call from
 the main Kohler factory about some marketing issues and I
 finally let loose with the above rant.  I really
 complained that so far they have done everything they could
 NOT to serve this very large and growing off-grid market,
 and I pointed out that most of their recent design
 improvements made their generators LESS suitable for this
 market, not better.  This guy was absolutely
 dumb-struck, and it appears to me that they have made no
 effort to understand this market.  Their more recent
 efforts to void warranties is just another reason to look
 for a different generator supplier.
  
  Has anyone on this list had any contact from Kohler
 central office about finding out what features this industry
 needs?   The guy I talked with may be just
 blowing smoke, but he promised to have a followup call in
 next few weeks to learn more about what they can do. 
 According to him, he thinks they can add a software switch
 in the programming for little or no cost like on/grid -
 off/grid that we could access during setup that would
 adjust generator parameters and standby losses when used in
 an inverter-battery application.   In case he
 really does followup, are there any other rants I could
 include from you guys that have been a problem for you when
 using Kohler generators.  I will assume we are limiting
 this to their non-water cooled units under 15 kW.
  
  While ranting on generators, the main reason we liked
 to use Kohler was the easy 2-wire start/stop connections you
 can connect to the aux relay in most inverters, while many
 other generator brands were not easy to remote start from an
 inverter or required multi-step starting relays.  Has
 this changed, and are there now other brands of generators
 in the 8 to 15 kW range that work well for backup of
 solar/battery charging applications and the manufacturer
 does not have warranty issues when used in off-grid
 applications?
  
  Thanks,
  
  Jeff Yago
  
 
 _
  Netscape.  Just the Net You Need.
  ___
  List sponsored by Home Power magazine
  
  List Address: RE-wrenches@lists.re-wrenches.org
  
  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  
  List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
  
  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm
  
  Check out participant bios:
  www.members.re-wrenches.org
  
  
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re