Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-12-02 Thread Jeff Clearwater via RE-wrenches
Actually up to 1500 amps available including 1000 amp version as well. It’s 
hidden in the spec sheets under large fuse holders. 

Sent from my iPhone

> On Dec 2, 2022, at 5:20 PM, Glenn Burt via RE-wrenches 
>  wrote:
> 
> 
> I recently found that Victron makes DC bus bars for battery work with studs 
> already on them. Up to 600A models are available.
> 
> -Glenn
> Sent from my 'smart'phone, so please excuse typos and spelling errors.
> 
> -- Original message--
> From: William Miller via RE-wrenches
> Date: Fri, Dec 2, 2022 3:42 PM
> To: RE-wrenches;
> Cc: William Miller;
> Subject:Re: [RE-wrenches] Large current battery combiners, UL Listing
> 
> Colleagues:
> 
>  
> 
> I am gearing up to tap some more copper.  I assume this is a pertinent 
> subject since bus bars are going to be needed frequently for any storage work.
> 
>  
> 
> I bought the fancy drill press with the tapping function and I am setting it 
> up.  I ran a few tests and the functionality of the tool is pretty amazing.  
> I still need to work on programming it to reverse when needed.  I am close.  
> I also ordered a cross vise for part holding.
> 
>  
> 
> I found this tutorial on line that has provided me with some valuable insight 
> on different styles of taps. 
> 
>  
> 
> William
> 
>  
> 
> Miller Solar
> 
> 17395 Oak Road, Atascadero, CA 93422
> 
> 805-438-5600
> 
> www.millersolar.com
> 
> CA Lic. 773985
> 
>  
> 
>  
> 
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On 
> Behalf Of Michael Morningstar via RE-wrenches
> Sent: Monday, September 12, 2022 7:39 PM
> To: RE-wrenches
> Cc: Michael Morningstar
> Subject: Re: [RE-wrenches] Large current battery combiners, UL Listing
> 
>  
> 
> No, I haven't. I'll do some testing tomorrow as we have 60 holes/taps to do 
> in the above mentioned bussing
> 
>  
> 
> On Mon, Sep 12, 2022 at 7:54 AM frenergy via RE-wrenches 
>  wrote:
> 
> Michael,
> 
>  Are you using kerosene as a cutting fluid?  We've had 
> better luck with that in softer than steel metals.
> 
> Bill
> 
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> 
> On 9/11/2022 7:00 PM, Michael Morningstar via RE-wrenches wrote:
> > We've gotten around needing UL listings for one-off in house 
> > fabrication by running things through a licensed engineer. Right now 
> > we are building a gutter bus which has two 1/2" x 4" x 20' copper bars 
> > in a 10" x 10" gutter. We are using 2" x 9" x 9" UDPM plates with 
> > slots routed out for the bars as insulators. This is for 24 Discover 
> > AES and 8 Sol-Ark's. It usually costs about 1K to have an engineer 
> > sign off on our designs.
> >
> > I'd be interested in learning tricks for tapping 3/8" in thick copper. 
> > I've never been able to get consistent results and resort to 
> > thru-bolting.
> 
> 
> -- 
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
> 
> 
>  
> 
> --
> 
> Michael Morningstar
>  
> Morningstar Electric
> PO Box 1494
> Mount Shasta, CA 96067
> 530-921-0560
> mjmornings...@gmail.com
> 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wren

Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-12-02 Thread Jerry Shafer via RE-wrenches
Wrenches, William
I did a few back up systems for data hubs, we had 250+ kWhr systems. We had
to have a firewall between the batteries and everything else. We used
copper stock 1/2 x 2" and 20' long, each bank connected to the buss with
its own 250 a breaker, the buss was above the batteries mounted to SS strut
using 1000 volt insulators on both positive and negative. The power
conditioners were on the opposite side of the wall again all connected to
the buss going to each unit and again protected. Was very clean, no line
loss, very clean and was duplicated in several locations. We also had a 125
k cummins  genny outside that would take over to keep us all connected.
Jerry
PS, we did not tap and we used brass bolts and nuts, l dont recall why but
it may have not been able to torg enough.


On Fri, Dec 2, 2022, 12:42 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Colleagues:
>
>
>
> I am gearing up to tap some more copper.  I assume this is a pertinent
> subject since bus bars are going to be needed frequently for any storage
> work.
>
>
>
> I bought the fancy drill press with the tapping function and I am setting
> it up.  I ran a few tests and the functionality of the tool is pretty
> amazing.  I still need to work on programming it to reverse when needed.  I
> am close.  I also ordered a cross vise for part holding.
>
>
>
> I found this tutorial
> <https://www.youtube.com/watch?v=bkrUzGooA9k_channel=HaasAutomation%2CInc.>
> on line that has provided me with some valuable insight on different styles
> of taps.
>
>
>
> William
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Michael Morningstar via RE-wrenches
> *Sent:* Monday, September 12, 2022 7:39 PM
> *To:* RE-wrenches
> *Cc:* Michael Morningstar
> *Subject:* Re: [RE-wrenches] Large current battery combiners, UL Listing
>
>
>
> No, I haven't. I'll do some testing tomorrow as we have 60 holes/taps to
> do in the above mentioned bussing
>
>
>
> On Mon, Sep 12, 2022 at 7:54 AM frenergy via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Michael,
>
>  Are you using kerosene as a cutting fluid?  We've had
> better luck with that in softer than steel metals.
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
>
> On 9/11/2022 7:00 PM, Michael Morningstar via RE-wrenches wrote:
> > We've gotten around needing UL listings for one-off in house
> > fabrication by running things through a licensed engineer. Right now
> > we are building a gutter bus which has two 1/2" x 4" x 20' copper bars
> > in a 10" x 10" gutter. We are using 2" x 9" x 9" UDPM plates with
> > slots routed out for the bars as insulators. This is for 24 Discover
> > AES and 8 Sol-Ark's. It usually costs about 1K to have an engineer
> > sign off on our designs.
> >
> > I'd be interested in learning tricks for tapping 3/8" in thick copper.
> > I've never been able to get consistent results and resort to
> > thru-bolting.
>
>
> --
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
>
> --
>
> Michael Morningstar
>
>
>
> Morningstar Electric
>
> PO Box 1494
>
> Mount Shasta, CA 96067
>
> 530-921-0560
>
> mjmornings...@gmail.com
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
&

Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-12-02 Thread Glenn Burt via RE-wrenches
I recently found that Victron makes DC bus bars for battery work with studs 
already on them. Up to 600A models are available.-GlennSent from my 
'smart'phone, so please excuse typos and spelling errors.-- Original 
message--From: William Miller via RE-wrenchesDate: Fri, Dec 2, 2022 3:42 
PMTo: RE-wrenches;Cc: William Miller;Subject:Re: [RE-wrenches] Large current 
battery combiners, UL ListingColleagues: I am gearing up to tap some more 
copper.  I assume this is a pertinent subject since bus bars are going to be 
needed frequently for any storage work. I bought the fancy drill press with the 
tapping function and I am setting it up.  I ran a few tests and the 
functionality of the tool is pretty amazing.  I still need to work on 
programming it to reverse when needed.  I am close.  I also ordered a cross 
vise for part holding. I found this tutorial on line that has provided me with 
some valuable insight on different styles of taps.   William Miller Solar17395 
Oak Road, Ata
 scadero, CA
 93422805-438-5600www.millersolar.comCA Lic. 773985  From: RE-wrenches 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Michael 
Morningstar via RE-wrenchesSent: Monday, September 12, 2022 7:39 PMTo: 
RE-wrenchesCc: Michael MorningstarSubject: Re: [RE-wrenches] Large current 
battery combiners, UL Listing No, I haven't. I'll do some testing tomorrow as 
we have 60 holes/taps to do in the above mentioned bussing On Mon, Sep 12, 2022 
at 7:54 AM frenergy via RE-wrenches  
wrote:Michael,         Are you using kerosene as a cutting fluid?  We've 
had better luck with that in softer than steel metals.BillFeather River Solar 
ElectricBill Battagin, Owner4291 Nelson St.Taylorsville, CA 95983530.284.7849CA 
Lic 874049On 9/11/2022 7:00 PM, Michael Morningstar via RE-wrenches wrote:> 
We've gotten around needing UL listings for one-off in house > fabrication by 
running things through a licensed engineer. Right now > we are building a g
 utter bus which
 has two 1/2" x 4" x 20' copper bars > in a 10" x 10" gutter. We are using 2" x 
9" x 9" UDPM plates with > slots routed out for the bars as insulators. This is 
for 24 Discover > AES and 8 Sol-Ark's. It usually costs about 1K to have an 
engineer > sign off on our designs.>> I'd be interested in learning tricks for 
tapping 3/8" in thick copper. > I've never been able to get consistent results 
and resort to > thru-bolting.-- This email has been checked for viruses by 
Avast antivirus 
software.www.avast.com___List 
sponsored by Redwood AlliancePay optional member dues here: 
http://re-wrenches.orgList Address: re-wrenc...@lists.re-wrenches.orgChange 
listserver email address & 
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere
 are two list archives for searching. When one doesn't work, try the
 
other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList
 rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update 
participant bios:http://www.members.re-wrenches.org -- Michael Morningstar 
Morningstar ElectricPO Box 1494Mount Shasta, CA 
96067530-921-0560mjmornings...@gmail.com___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-12-02 Thread William Miller via RE-wrenches
Colleagues:



I am gearing up to tap some more copper.  I assume this is a pertinent
subject since bus bars are going to be needed frequently for any storage
work.



I bought the fancy drill press with the tapping function and I am setting
it up.  I ran a few tests and the functionality of the tool is pretty
amazing.  I still need to work on programming it to reverse when needed.  I
am close.  I also ordered a cross vise for part holding.



I found this tutorial
<https://www.youtube.com/watch?v=bkrUzGooA9k_channel=HaasAutomation%2CInc.>
on line that has provided me with some valuable insight on different styles
of taps.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Michael Morningstar via RE-wrenches
*Sent:* Monday, September 12, 2022 7:39 PM
*To:* RE-wrenches
*Cc:* Michael Morningstar
*Subject:* Re: [RE-wrenches] Large current battery combiners, UL Listing



No, I haven't. I'll do some testing tomorrow as we have 60 holes/taps to do
in the above mentioned bussing



On Mon, Sep 12, 2022 at 7:54 AM frenergy via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

Michael,

 Are you using kerosene as a cutting fluid?  We've had
better luck with that in softer than steel metals.

Bill

Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049

On 9/11/2022 7:00 PM, Michael Morningstar via RE-wrenches wrote:
> We've gotten around needing UL listings for one-off in house
> fabrication by running things through a licensed engineer. Right now
> we are building a gutter bus which has two 1/2" x 4" x 20' copper bars
> in a 10" x 10" gutter. We are using 2" x 9" x 9" UDPM plates with
> slots routed out for the bars as insulators. This is for 24 Discover
> AES and 8 Sol-Ark's. It usually costs about 1K to have an engineer
> sign off on our designs.
>
> I'd be interested in learning tricks for tapping 3/8" in thick copper.
> I've never been able to get consistent results and resort to
> thru-bolting.


-- 
This email has been checked for viruses by Avast antivirus software.
www.avast.com
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org




-- 

Michael Morningstar



Morningstar Electric

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

mjmornings...@gmail.com
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-09-12 Thread Michael Morningstar via RE-wrenches
No, I haven't. I'll do some testing tomorrow as we have 60 holes/taps to do
in the above mentioned bussing

On Mon, Sep 12, 2022 at 7:54 AM frenergy via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Michael,
>
>  Are you using kerosene as a cutting fluid?  We've had
> better luck with that in softer than steel metals.
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
>
> On 9/11/2022 7:00 PM, Michael Morningstar via RE-wrenches wrote:
> > We've gotten around needing UL listings for one-off in house
> > fabrication by running things through a licensed engineer. Right now
> > we are building a gutter bus which has two 1/2" x 4" x 20' copper bars
> > in a 10" x 10" gutter. We are using 2" x 9" x 9" UDPM plates with
> > slots routed out for the bars as insulators. This is for 24 Discover
> > AES and 8 Sol-Ark's. It usually costs about 1K to have an engineer
> > sign off on our designs.
> >
> > I'd be interested in learning tricks for tapping 3/8" in thick copper.
> > I've never been able to get consistent results and resort to
> > thru-bolting.
>
>
> --
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

Michael Morningstar


Morningstar Electric

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

mjmornings...@gmail.com
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-09-12 Thread frenergy via RE-wrenches

Michael,

            Are you using kerosene as a cutting fluid?  We've had 
better luck with that in softer than steel metals.


Bill

Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049

On 9/11/2022 7:00 PM, Michael Morningstar via RE-wrenches wrote:
We've gotten around needing UL listings for one-off in house 
fabrication by running things through a licensed engineer. Right now 
we are building a gutter bus which has two 1/2" x 4" x 20' copper bars 
in a 10" x 10" gutter. We are using 2" x 9" x 9" UDPM plates with 
slots routed out for the bars as insulators. This is for 24 Discover 
AES and 8 Sol-Ark's. It usually costs about 1K to have an engineer 
sign off on our designs.


I'd be interested in learning tricks for tapping 3/8" in thick copper. 
I've never been able to get consistent results and resort to 
thru-bolting.



--
This email has been checked for viruses by Avast antivirus software.
www.avast.com
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-09-11 Thread Michael Morningstar via RE-wrenches
We've gotten around needing UL listings for one-off in house fabrication by
running things through a licensed engineer. Right now we are building a
gutter bus which has two 1/2" x 4" x 20' copper bars in a 10" x 10" gutter.
We are using 2" x 9" x 9" UDPM plates with slots routed out for the bars as
insulators. This is for 24 Discover AES and 8 Sol-Ark's. It usually costs
about 1K to have an engineer sign off on our designs.

I'd be interested in learning tricks for tapping 3/8" in thick copper. I've
never been able to get consistent results and resort to thru-bolting.

On Sun, Sep 11, 2022 at 4:49 AM Dana Orzel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> You might possibly check with Northwest energy storage all of their hup
> solar one batteries come with solid copper bars lead plated I don’t know
> what the ampacities are but Rob might be able to assist you there
>
> Dana Orzel
> C: 208.721.7003
> E- d...@solarwork.com
>
> On Sep 10, 2022, at 7:17 PM, Kirk Herander via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> 
> SolarBOS can possibly make one custom for you, it will be listed, and it
> will not be cheap. I was going to order a 2000A w/ multiple OCPDs on both
> inputs and outputs from them, but then Midnite came out with a 2000A
> combiner, and I don't need it listed for my application.
>
> On Sat, Sep 10, 2022 at 6:15 PM William Miller via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Mac:
>>
>>
>>
>> Getting listing on something as specialized as you are talking about may
>> be difficult.  I would turn to the telecom industry for solutions.  Here is
>> one link
>> <https://bertholdelectric.com/dc-telecom-products/battery-termination-bars/>
>> I found.  Their product line is pretty sexy and it is listed.
>>
>>
>>
>> If you are rolling your own, you can find ampacities for standard copper
>> bar thicknesses someplace like here
>> <https://www.copper.org/applications/electrical/busbar/busbar_ampacities.html>.
>> You might fabricate something that looks like one of these
>> <https://millersolar.com/MillerSolar/Portfolio/Inverters/battery_iinverters/JP_Radian/Images/Battery_busses_open.jpg>
>> but bigger.  Threading is desirable so you can avoid wrangling nuts on the
>> back sides, but tapping copper at a reasonable bolt size (likely 3/8-16)
>> can be tricky.  I am looking for any excuse to buy one of these drill
>> presses
>> <https://www.grizzly.com/products/teknatool-18-nova-voyager-dvr-variable-speed-drill-press/t30589>
>> which can automatically chip-clear.  Basically at this point in my life my
>> only reason for working is to support my tool addiction.
>>
>>
>>
>> Good luck.
>>
>>
>>
>> William Miller
>>
>>
>>
>> Miller Solar
>>
>> 17395 Oak Road, Atascadero, CA 93422
>>
>> 805-438-5600
>>
>> www.millersolar.com
>>
>> CA Lic. 773985
>>
>>
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
>> Behalf Of *Mac Lewis via RE-wrenches
>> *Sent:* Thursday, September 8, 2022 8:46 PM
>> *To:* RE-wrenches
>> *Cc:* Mac Lewis
>> *Subject:* [RE-wrenches] Large current battery combiners, UL Listing
>>
>>
>>
>> Hello Wrenches,
>>
>>
>>
>> Is anyone aware of a high current, (~3000A DC rated, 48Vdc nominal)
>> battery combiner panel that would allow for ~36-48 x 4/0 cables to connect?
>>
>>
>>
>> Seems like nothing will be close to UL listed on this.  How do you go
>> about building a 60 kW off-grid system on the battery side of things?  Do I
>> need to increase battery voltage design?
>>
>>
>>
>> I have gotten a custom busbar fabricated by Storm Power rated for about
>> 2kA before, but I'd love to have a UL Listed solution for large battery
>> combining.  Any suggestions are appreciated.
>>
>>
>>
>> Thanks!
>>
>>
>>
>> --
>>
>>
>>
>>
>>
>>
>>
>> Mac Lewis
>>
>> "Yo solo sé que no sé nada." *-Sócrates*
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archiv

Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-09-11 Thread Dana Orzel via RE-wrenches
You might possibly check with Northwest energy storage all of their hup solar 
one batteries come with solid copper bars lead plated I don’t know what the 
ampacities are but Rob might be able to assist you there

Dana Orzel
C: 208.721.7003
E- d...@solarwork.com

> On Sep 10, 2022, at 7:17 PM, Kirk Herander via RE-wrenches 
>  wrote:
> 
> 
> SolarBOS can possibly make one custom for you, it will be listed, and it will 
> not be cheap. I was going to order a 2000A w/ multiple OCPDs on both inputs 
> and outputs from them, but then Midnite came out with a 2000A combiner, and I 
> don't need it listed for my application.
> 
>> On Sat, Sep 10, 2022 at 6:15 PM William Miller via RE-wrenches 
>>  wrote:
>> Mac:
>> 
>>  
>> 
>> Getting listing on something as specialized as you are talking about may be 
>> difficult.  I would turn to the telecom industry for solutions.  Here is one 
>> link I found.  Their product line is pretty sexy and it is listed.
>> 
>>  
>> 
>> If you are rolling your own, you can find ampacities for standard copper bar 
>> thicknesses someplace like here.  You might fabricate something that looks 
>> like one of these but bigger.  Threading is desirable so you can avoid 
>> wrangling nuts on the back sides, but tapping copper at a reasonable bolt 
>> size (likely 3/8-16) can be tricky.  I am looking for any excuse to buy one 
>> of these drill presses which can automatically chip-clear.  Basically at 
>> this point in my life my only reason for working is to support my tool 
>> addiction.
>> 
>>  
>> 
>> Good luck.
>> 
>>  
>> 
>> William Miller
>> 
>>  
>> 
>> Miller Solar
>> 
>> 17395 Oak Road, Atascadero, CA 93422
>> 
>> 805-438-5600
>> 
>> www.millersolar.com
>> 
>> CA Lic. 773985
>> 
>>  
>> 
>>  
>> 
>> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On 
>> Behalf Of Mac Lewis via RE-wrenches
>> Sent: Thursday, September 8, 2022 8:46 PM
>> To: RE-wrenches
>> Cc: Mac Lewis
>> Subject: [RE-wrenches] Large current battery combiners, UL Listing
>> 
>>  
>> 
>> Hello Wrenches,
>> 
>>  
>> 
>> Is anyone aware of a high current, (~3000A DC rated, 48Vdc nominal) battery 
>> combiner panel that would allow for ~36-48 x 4/0 cables to connect?
>> 
>>  
>> 
>> Seems like nothing will be close to UL listed on this.  How do you go about 
>> building a 60 kW off-grid system on the battery side of things?  Do I need 
>> to increase battery voltage design?
>> 
>>  
>> 
>> I have gotten a custom busbar fabricated by Storm Power rated for about 2kA 
>> before, but I'd love to have a UL Listed solution for large battery 
>> combining.  Any suggestions are appreciated.
>> 
>>  
>> 
>> Thanks!
>> 
>>  
>> 
>> --
>> 
>>  
>> 
>>  
>> 
>>  
>> 
>> Mac Lewis
>> 
>> "Yo solo sé que no sé nada." -Sócrates
>> 
>> ___
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> 
> 
> -- 
> Kirk Herander / kirkh@vermont.solar
> Owner|Principal, VT Solar, LLC
> Celebrating our 31st Anniversary 1991-2022!!
> www.vermont.solar
> dba Vermont Solar Engineering
> 802.863.1202
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pip

Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-09-10 Thread Kirk Herander via RE-wrenches
SolarBOS can possibly make one custom for you, it will be listed, and it
will not be cheap. I was going to order a 2000A w/ multiple OCPDs on both
inputs and outputs from them, but then Midnite came out with a 2000A
combiner, and I don't need it listed for my application.

On Sat, Sep 10, 2022 at 6:15 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Mac:
>
>
>
> Getting listing on something as specialized as you are talking about may
> be difficult.  I would turn to the telecom industry for solutions.  Here is
> one link
> <https://bertholdelectric.com/dc-telecom-products/battery-termination-bars/>
> I found.  Their product line is pretty sexy and it is listed.
>
>
>
> If you are rolling your own, you can find ampacities for standard copper
> bar thicknesses someplace like here
> <https://www.copper.org/applications/electrical/busbar/busbar_ampacities.html>.
> You might fabricate something that looks like one of these
> <https://millersolar.com/MillerSolar/Portfolio/Inverters/battery_iinverters/JP_Radian/Images/Battery_busses_open.jpg>
> but bigger.  Threading is desirable so you can avoid wrangling nuts on the
> back sides, but tapping copper at a reasonable bolt size (likely 3/8-16)
> can be tricky.  I am looking for any excuse to buy one of these drill
> presses
> <https://www.grizzly.com/products/teknatool-18-nova-voyager-dvr-variable-speed-drill-press/t30589>
> which can automatically chip-clear.  Basically at this point in my life my
> only reason for working is to support my tool addiction.
>
>
>
> Good luck.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Mac Lewis via RE-wrenches
> *Sent:* Thursday, September 8, 2022 8:46 PM
> *To:* RE-wrenches
> *Cc:* Mac Lewis
> *Subject:* [RE-wrenches] Large current battery combiners, UL Listing
>
>
>
> Hello Wrenches,
>
>
>
> Is anyone aware of a high current, (~3000A DC rated, 48Vdc nominal)
> battery combiner panel that would allow for ~36-48 x 4/0 cables to connect?
>
>
>
> Seems like nothing will be close to UL listed on this.  How do you go
> about building a 60 kW off-grid system on the battery side of things?  Do I
> need to increase battery voltage design?
>
>
>
> I have gotten a custom busbar fabricated by Storm Power rated for about
> 2kA before, but I'd love to have a UL Listed solution for large battery
> combining.  Any suggestions are appreciated.
>
>
>
> Thanks!
>
>
>
> --
>
>
>
>
>
>
>
> Mac Lewis
>
> "Yo solo sé que no sé nada." *-Sócrates*
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

*Kirk Herander / **kirkh@vermont.solar *

*Owner|Principal, VT Solar, LLC*

*Celebrating our 31st Anniversary 1991-2022!!*

*www.vermont.solar*
<https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435%7C1%7C0%7C636842843233477645=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D=0>

dba Vermont Solar Engineering

802.863.1202
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-09-10 Thread Jerry Shafer via RE-wrenches
Wrenches
We have used the midnight box, both with and without OCP breakers, I dont
think they are large enough for what you want,  we have up to 80 kWhrs
connected going to 5 Radians.
Fun times

On Thu, Sep 8, 2022, 8:47 PM Mac Lewis via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hello Wrenches,
>
> Is anyone aware of a high current, (~3000A DC rated, 48Vdc nominal)
> battery combiner panel that would allow for ~36-48 x 4/0 cables to connect?
>
> Seems like nothing will be close to UL listed on this.  How do you go
> about building a 60 kW off-grid system on the battery side of things?  Do I
> need to increase battery voltage design?
>
> I have gotten a custom busbar fabricated by Storm Power rated for about
> 2kA before, but I'd love to have a UL Listed solution for large battery
> combining.  Any suggestions are appreciated.
>
> Thanks!
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Large current battery combiners, UL Listing

2022-09-10 Thread William Miller via RE-wrenches
Mac:



Getting listing on something as specialized as you are talking about may be
difficult.  I would turn to the telecom industry for solutions.  Here is
one link
<https://bertholdelectric.com/dc-telecom-products/battery-termination-bars/>
I found.  Their product line is pretty sexy and it is listed.



If you are rolling your own, you can find ampacities for standard copper
bar thicknesses someplace like here
<https://www.copper.org/applications/electrical/busbar/busbar_ampacities.html>.
You might fabricate something that looks like one of these
<https://millersolar.com/MillerSolar/Portfolio/Inverters/battery_iinverters/JP_Radian/Images/Battery_busses_open.jpg>
but bigger.  Threading is desirable so you can avoid wrangling nuts on the
back sides, but tapping copper at a reasonable bolt size (likely 3/8-16)
can be tricky.  I am looking for any excuse to buy one of these drill
presses
<https://www.grizzly.com/products/teknatool-18-nova-voyager-dvr-variable-speed-drill-press/t30589>
which can automatically chip-clear.  Basically at this point in my life my
only reason for working is to support my tool addiction.



Good luck.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Mac Lewis via RE-wrenches
*Sent:* Thursday, September 8, 2022 8:46 PM
*To:* RE-wrenches
*Cc:* Mac Lewis
*Subject:* [RE-wrenches] Large current battery combiners, UL Listing



Hello Wrenches,



Is anyone aware of a high current, (~3000A DC rated, 48Vdc nominal) battery
combiner panel that would allow for ~36-48 x 4/0 cables to connect?



Seems like nothing will be close to UL listed on this.  How do you go about
building a 60 kW off-grid system on the battery side of things?  Do I need
to increase battery voltage design?



I have gotten a custom busbar fabricated by Storm Power rated for about 2kA
before, but I'd love to have a UL Listed solution for large battery
combining.  Any suggestions are appreciated.



Thanks!



-- 







Mac Lewis

"Yo solo sé que no sé nada." *-Sócrates*
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Large current battery combiners, UL Listing

2022-09-08 Thread Mac Lewis via RE-wrenches
Hello Wrenches,

Is anyone aware of a high current, (~3000A DC rated, 48Vdc nominal) battery
combiner panel that would allow for ~36-48 x 4/0 cables to connect?

Seems like nothing will be close to UL listed on this.  How do you go about
building a 60 kW off-grid system on the battery side of things?  Do I need
to increase battery voltage design?

I have gotten a custom busbar fabricated by Storm Power rated for about 2kA
before, but I'd love to have a UL Listed solution for large battery
combining.  Any suggestions are appreciated.

Thanks!

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org