Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Dave Angelini Offgrid Solar via RE-wrenches



Another reason as Bradley suggests to avoid all of these problems and 
only install a closed loop battery power system.  Zero problems since 
Discover
came out with the AES in 2018 or so.  A 25% gain in charge time that 
genset users will love by closing the loop. Lot's more also!


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

On 2022-11-19 10:28 am, Bradley Bassett via RE-wrenches wrote:

On some LFP batteries the cell balancing only happens at full charge, 
so you do need to get to full every so often. Discover AES is one that 
needs this.


Brad

On Sat, Nov 19, 2022 at 10:10 AM Dana Orzel via RE-wrenches 
 wrote:
Another issue is what charge controller are you using? I know for me 
with Outback products I've had to switch from an FM 80 to the OB - FM 
100 in order to have a more accurate high-voltage cut out voltage.
The FM 100 has a much more accurate micro processor in it then the FM 
60 or 80 per Brad Bassett with AEE.


Dana Orzel
C: 208.721.7003
E- d...@solarwork.com

On Nov 19, 2022, at 7:15 AM, Jeff Clearwater via RE-wrenches 
 wrote:


Hi Kris

What voltage do you have your charge settings at?

I recommend that bulk or absorb voltage for lithium iron phosphate not 
be set above 56 V  - there is no reason for it even though many 
manufactures suggest higher settings.  In cases where total storage 
is sized generously enough I  often use 55.6 or even 55.4 in order to 
target 95% as full instead of 100% in order to extend cycle life.   and 
for float there's no reason to ever go over 54 V and better maybe even 
to be in the mid-53s.


See if that helps assuming you had it higher.

The other thought is you have one bms that is perhaps not protecting 
overcharge  and allowing a temporary spike when the others do limit.


Hope that helps!

Best Jeff C.
Village Power Design

Sent from my iPhone

On Nov 19, 2022, at 6:32 AM, Kristopher Schmid via RE-wrenches 
 wrote:


Greetings all,

I have seen an issue on two different systems that I am hoping someone 
can shed some light on for me.  One was a 48 volt pack of 12 volt 
Battle Bornes and the other was a 24 volt pack of SOKs.  What happens 
is when reaching the end of the bulk charging stage, the battery 
voltage spikes and sends the inverter into an overvoltage error.  Can 
anyone explain what is happening and a solution?


Thanks,
Kris

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com [1]
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE ___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

 ___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:


Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread John Blittersdorf via RE-wrenches
Great timely topic.  I Have a new installation with 3 eFlex and radian
system.  Setting were per Outback and Fortress and we had a series of
mid day hi voltage shut downs when our November sun returned.  Luckily
it has Optics and the unattended house is now happy with lowered top
voltages.  Ray, nice comment that we don't have any reason to charge
full now.

John Blittersdorf

On Sat, Nov 19, 2022 at 1:10 PM Dana Orzel via RE-wrenches
 wrote:
>
> Another issue is what charge controller are you using? I know for me with 
> Outback products I’ve had to switch from an FM 80 to the OB - FM 100 in order 
> to have a more accurate high-voltage cut out voltage.
> The FM 100 has a much more accurate micro processor in it then the FM 60 or 
> 80 per Brad Bassett with AEE.
>
> Dana Orzel
> C: 208.721.7003
> E- d...@solarwork.com
>
> On Nov 19, 2022, at 7:15 AM, Jeff Clearwater via RE-wrenches 
>  wrote:
>
> Hi Kris
>
> What voltage do you have your charge settings at?
>
> I recommend that bulk or absorb voltage for lithium iron phosphate not be set 
> above 56 V  - there is no reason for it even though many manufactures suggest 
> higher settings.  In cases where total storage is sized generously enough 
> I  often use 55.6 or even 55.4 in order to target 95% as full instead of 100% 
> in order to extend cycle life.   and for float there’s no reason to ever go 
> over 54 V and better maybe even to be in the mid-53s.
>
> See if that helps assuming you had it higher.
>
> The other thought is you have one bms that is perhaps not protecting 
> overcharge  and allowing a temporary spike when the others do limit.
>
> Hope that helps!
>
> Best Jeff C.
> Village Power Design
>
>
>
> Sent from my iPhone
>
> On Nov 19, 2022, at 6:32 AM, Kristopher Schmid via RE-wrenches 
>  wrote:
>
> 
> Greetings all,
>
> I have seen an issue on two different systems that I am hoping someone can 
> shed some light on for me.  One was a 48 volt pack of 12 volt Battle Bornes 
> and the other was a 24 volt pack of SOKs.  What happens is when reaching the 
> end of the bulk charging stage, the battery voltage spikes and sends the 
> inverter into an overvoltage error.  Can anyone explain what is happening and 
> a solution?
>
> Thanks,
> Kris
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/

Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Bradley Bassett via RE-wrenches
On some LFP batteries the cell balancing only happens at full charge, so
you do need to get to full every so often. Discover AES is one that needs
this.

Brad

On Sat, Nov 19, 2022 at 10:10 AM Dana Orzel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Another issue is what charge controller are you using? I know for me with
> Outback products I’ve had to switch from an FM 80 to the OB - FM 100 in
> order to have a more accurate high-voltage cut out voltage.
> The FM 100 has a much more accurate micro processor in it then the FM 60
> or 80 per Brad Bassett with AEE.
>
> Dana Orzel
> C: 208.721.7003
> E- d...@solarwork.com
>
> On Nov 19, 2022, at 7:15 AM, Jeff Clearwater via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Hi Kris
>
> What voltage do you have your charge settings at?
>
> I recommend that bulk or absorb voltage for lithium iron phosphate not be
> set above 56 V  - there is no reason for it even though many manufactures
> suggest higher settings.  In cases where total storage is sized
> generously enough I  often use 55.6 or even 55.4 in order to target 95% as
> full instead of 100% in order to extend cycle life.   and for float there’s
> no reason to ever go over 54 V and better maybe even to be in the mid-53s.
>
> See if that helps assuming you had it higher.
>
> The other thought is you have one bms that is perhaps not protecting
> overcharge  and allowing a temporary spike when the others do limit.
>
> Hope that helps!
>
> Best Jeff C.
> Village Power Design
>
>
>
> Sent from my iPhone
>
> On Nov 19, 2022, at 6:32 AM, Kristopher Schmid via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> 
> Greetings all,
>
> I have seen an issue on two different systems that I am hoping someone can
> shed some light on for me.  One was a 48 volt pack of 12 volt Battle Bornes
> and the other was a 24 volt pack of SOKs.  What happens is when reaching
> the end of the bulk charging stage, the battery voltage spikes and sends
> the inverter into an overvoltage error.  Can anyone explain what is
> happening and a solution?
>
> Thanks,
> Kris
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm


Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Dana Orzel via RE-wrenches
Another issue is what charge controller are you using? I know for me with 
Outback products I’ve had to switch from an FM 80 to the OB - FM 100 in order 
to have a more accurate high-voltage cut out voltage.
The FM 100 has a much more accurate micro processor in it then the FM 60 or 80 
per Brad Bassett with AEE.

Dana Orzel
C: 208.721.7003
E- d...@solarwork.com

> On Nov 19, 2022, at 7:15 AM, Jeff Clearwater via RE-wrenches 
>  wrote:
> 
> Hi Kris
> 
> What voltage do you have your charge settings at?  
> 
> I recommend that bulk or absorb voltage for lithium iron phosphate not be set 
> above 56 V  - there is no reason for it even though many manufactures suggest 
> higher settings.  In cases where total storage is sized generously enough 
> I  often use 55.6 or even 55.4 in order to target 95% as full instead of 100% 
> in order to extend cycle life.   and for float there’s no reason to ever go 
> over 54 V and better maybe even to be in the mid-53s. 
> 
> See if that helps assuming you had it higher. 
> 
> The other thought is you have one bms that is perhaps not protecting 
> overcharge  and allowing a temporary spike when the others do limit. 
> 
> Hope that helps!  
> 
> Best Jeff C. 
> Village Power Design
> 
> 
> 
> Sent from my iPhone
> 
>>> On Nov 19, 2022, at 6:32 AM, Kristopher Schmid via RE-wrenches 
>>>  wrote:
>>> 
>> 
>> Greetings all,
>> 
>> I have seen an issue on two different systems that I am hoping someone can 
>> shed some light on for me.  One was a 48 volt pack of 12 volt Battle Bornes 
>> and the other was a 24 volt pack of SOKs.  What happens is when reaching the 
>> end of the bulk charging stage, the battery voltage spikes and sends the 
>> inverter into an overvoltage error.  Can anyone explain what is happening 
>> and a solution?
>> 
>> Thanks,
>> Kris
>> 
>> Shine On!
>> 
>> Kris Schmid
>> Legacy Solar, LLC
>> 137 West 1st Avenue
>> Luck, WI 54853
>> www.legacysolar.com
>> 715-653-4295
>> NABCEP Certified PV Installation Professional
>> Licensed Wisconsin Master Electrician
>> BSEE
>> ___
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Ray Walters via RE-wrenches
To add to Jeff's suggestion of targeting 95%, many Li+ batteries have a 
spike in voltage as they reach 100%.  We just don't have to worry 
anymore about sulfate damage from under charging.


Ray Walters
Remote Solar

On 11/19/2022 7:14 AM, Jeff Clearwater via RE-wrenches wrote:

Hi Kris

What voltage do you have your charge settings at?

I recommend that bulk or absorb voltage for lithium iron phosphate not 
be set above 56 V  - there is no reason for it even though many 
manufactures suggest higher settings.      In cases where total 
storage is sized generously enough I  often use 55.6 or even 55.4 in 
order to target 95% as full instead of 100% in order to extend cycle 
life.   and for float there’s no reason to ever go over 54 V and 
better maybe even to be in the mid-53s.


See if that helps assuming you had it higher.

The other thought is you have one bms that is perhaps not protecting 
overcharge  and allowing a temporary spike when the others do limit.


Hope that helps!

Best Jeff C.
Village Power Design



Sent from my iPhone

On Nov 19, 2022, at 6:32 AM, Kristopher Schmid via RE-wrenches 
 wrote:



Greetings all,

I have seen an issue on two different systems that I am hoping 
someone can shed some light on for me.  One was a 48 volt pack of 12 
volt Battle Bornes and the other was a 24 volt pack of SOKs.  What 
happens is when reaching the end of the bulk charging stage, the 
battery voltage spikes and sends the inverter into an overvoltage 
error.  Can anyone explain what is happening and a solution?


Thanks,
Kris

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com 
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Jeff Clearwater via RE-wrenches
Hi Kris

What voltage do you have your charge settings at?  

I recommend that bulk or absorb voltage for lithium iron phosphate not be set 
above 56 V  - there is no reason for it even though many manufactures suggest 
higher settings.  In cases where total storage is sized generously enough I 
 often use 55.6 or even 55.4 in order to target 95% as full instead of 100% in 
order to extend cycle life.   and for float there’s no reason to ever go over 
54 V and better maybe even to be in the mid-53s. 

See if that helps assuming you had it higher. 

The other thought is you have one bms that is perhaps not protecting overcharge 
 and allowing a temporary spike when the others do limit. 

Hope that helps!  

Best Jeff C. 
Village Power Design



Sent from my iPhone

> On Nov 19, 2022, at 6:32 AM, Kristopher Schmid via RE-wrenches 
>  wrote:
> 
> 
> Greetings all,
> 
> I have seen an issue on two different systems that I am hoping someone can 
> shed some light on for me.  One was a 48 volt pack of 12 volt Battle Bornes 
> and the other was a 24 volt pack of SOKs.  What happens is when reaching the 
> end of the bulk charging stage, the battery voltage spikes and sends the 
> inverter into an overvoltage error.  Can anyone explain what is happening and 
> a solution?
> 
> Thanks,
> Kris
> 
> Shine On!
> 
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Jay via RE-wrenches
Hi KrisCan you share what equipment is being used, watts of solar etc. ThxJayOn Nov 19, 2022, at 5:32 AM, Kristopher Schmid via RE-wrenches  wrote:Greetings all,I have seen an issue on two different systems that I am hoping someone can shed some light on for me.  One was a 48 volt pack of 12 volt Battle Bornes and the other was a 24 volt pack of SOKs.  What happens is when reaching the end of the bulk charging stage, the battery voltage spikes and sends the inverter into an overvoltage error.  Can anyone explain what is happening and a solution?Thanks,KrisShine On!Kris SchmidLegacy Solar, LLC137 West 1st AvenueLuck, WI 54853www.legacysolar.com715-653-4295NABCEP Certified PV Installation ProfessionalLicensed Wisconsin Master ElectricianBSEE
___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Mac Lewis via RE-wrenches
Hi Kris,

When the BMS suddenly blocks charge, the voltage will spike up if the
charger can't respond quickly enough.

You may try to decrease charge voltage slightly.  This same affect can cook
an alternator in a vehicle as well.  Higher end BMS systems can shunt
current to mediate this.

Good luck!

On Sat, Nov 19, 2022, 5:32 AM Kristopher Schmid via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Greetings all,
>
> I have seen an issue on two different systems that I am hoping someone can
> shed some light on for me.  One was a 48 volt pack of 12 volt Battle Bornes
> and the other was a 24 volt pack of SOKs.  What happens is when reaching
> the end of the bulk charging stage, the battery voltage spikes and sends
> the inverter into an overvoltage error.  Can anyone explain what is
> happening and a solution?
>
> Thanks,
> Kris
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Low voltage lithiums

2022-11-19 Thread Kristopher Schmid via RE-wrenches
Greetings all,

I have seen an issue on two different systems that I am hoping someone can
shed some light on for me.  One was a 48 volt pack of 12 volt Battle Bornes
and the other was a 24 volt pack of SOKs.  What happens is when reaching
the end of the bulk charging stage, the battery voltage spikes and sends
the inverter into an overvoltage error.  Can anyone explain what is
happening and a solution?

Thanks,
Kris

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org