Hi John, I have been vexed about the settings on the 4448 PAE in off grid 
scenarios too, but am trying to figure out how to make these work as intended? 
That being said there's a couple of settings that might be messing with this 
that you can check out. I am  also open to any suggestions here, thanks. 
Recently I was programming a pair of these using the RTR, check in 02  Control 
Charger that you're using Multi-Stage. This is also in the Setup 03F Final 
Charge Stage menu. In Setup 03A AC Input Amps, 60 to 70 Amps max with 1 
inverter and 1/2 that with 2. You have probably already set 03E Max Charge Rate 
up to 100% I reckon. If not give it a shot and see if it will approach the 60 
Amps DC per inverter rating. Anyway these RTR menus are from 2014 +/- so I 
don't know if you have the same menus. Hope this helps. Chris Worcester 
chris@solarwindworks.com530-448-9692Sent from my Samsung Galaxy s9.
 Original message From: John Blittersdorf via RE-wrenches 
 Date: 12/6/23  6:08 PM  (GMT-08:00) To: 
RE-wrenches  Cc: John Blittersdorf 
 Subject: [RE-wrenches] Magnum 4448 PAE whimpy 
charge rate. I have noticed on several Magnum Installations that the charge 
rate is low compared to the inverter rated output.  Typically I would assume 
the charge rate should be up to about 70 to 80 % of the inverter capacity, but 
I am getting only about 1400 watts (26 amps DC) from it with a 14kw generator.  
Is there some setting I am missing that would limit it other than the charge %. 
 I know of one system where they added a 2nd Magnum inverter and then had 
problems with them working together consistently.  I have used the 8 kilowatt 
Radians for any off grid with significant loads and battery capacity and easily 
get 6000 charging watts from a large generator. I also needed remote control of 
the generator (Generac EcoGen 15 kw so a quick inexpensive but clunky solution 
I came up with was to add an old (2003 vintage) used MX-60 to the system purely 
to use the Aux relay with a used HUB and old but good Mate3.  Works perfectly 
giving us AGS start and stop voltage settings and basic battery voltage graph. 
I would be interested in other ways to remote control generators with non 
Outback inverters. FlexNet DC?John Blittersdorf
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Magnum 4448 PAE whimpy charge rate.

2023-12-07 Thread Kevin Pegg via RE-wrenches
Hi John,

Are these made in Mexico units? We have had a few issues with quality control 
since the relocation, not specific issue you have, but charger-related.

There are two settings – Under the Shore menu make sure Amps are set properly, 
and then there is the battery charge rate in the setup menu. That inverter 
should give a 63A charge @ 48VDC, and generally doesn’t really care about power 
quality even with very cheap generators the charge rate is good.

Kevin

From: RE-wrenches  On Behalf Of John 
Blittersdorf via RE-wrenches
Sent: Wednesday, December 6, 2023 6:08 PM
To: RE-wrenches 
Cc: John Blittersdorf 
Subject: [RE-wrenches] Magnum 4448 PAE whimpy charge rate.

I have noticed on several Magnum Installations that the charge rate is low 
compared to the inverter rated output.  Typically I would assume the charge 
rate should be up to about 70 to 80 % of the inverter capacity, but I am 
getting only about 1400 watts (26 amps DC) from it with a 14kw generator.  Is 
there some setting I am missing that would limit it other than the charge %.  I 
know of one system where they added a 2nd Magnum inverter and then had problems 
with them working together consistently.  I have used the 8 kilowatt Radians 
for any off grid with significant loads and battery capacity and easily get 
6000 charging watts from a large generator. I also needed remote control of the 
generator (Generac EcoGen 15 kw so a quick inexpensive but clunky solution I 
came up with was to add an old (2003 vintage) used MX-60 to the system purely 
to use the Aux relay with a used HUB and old but good Mate3.  Works perfectly 
giving us AGS start and stop voltage settings and basic battery voltage graph. 
I would be interested in other ways to remote control generators with non 
Outback inverters. FlexNet DC?

John Blittersdorf
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Magnum 4448 PAE whimpy charge rate.

2023-12-06 Thread Maverick Brown via RE-wrenches
John

I would try the Victron Cerbo GX for remote control of stuff. It has plethora 
of ports (I/O and temperature) and they can connect to lots of different 
devices, especially other Victron items like inverters and charge controllers 
and smart shunts (that one I’d also add to the Cerbo right away for SOC). 


1. Cerbo GX
2. SmartShunt 500 amp Battery Monitor (Bluetooth)
3. Temperature sensor BMV-702/712 for the shunt. 
4. VE.direct cable of correct length to go from Cerbo to SmartShunt


Cerbo GX connects to the internet via wired or wireless internet ports 
provided.  
They have a cellular modem add on as well. 

Victron offers a VRM virtual remote monitoring via the web. 




Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
 • Solar Commander Remote Power
 • SunFlow Systems Cathodic Protection 
maver...@mavericksolar.com
512-460-9825


> On Dec 6, 2023, at 8:08 PM, John Blittersdorf via RE-wrenches 
>  wrote:
> 
> 
> I have noticed on several Magnum Installations that the charge rate is low 
> compared to the inverter rated output.  Typically I would assume the charge 
> rate should be up to about 70 to 80 % of the inverter capacity, but I am 
> getting only about 1400 watts (26 amps DC) from it with a 14kw generator.  Is 
> there some setting I am missing that would limit it other than the charge %.  
> I know of one system where they added a 2nd Magnum inverter and then had 
> problems with them working together consistently.  I have used the 8 kilowatt 
> Radians for any off grid with significant loads and battery capacity and 
> easily get 6000 charging watts from a large generator. I also needed remote 
> control of the generator (Generac EcoGen 15 kw so a quick inexpensive but 
> clunky solution I came up with was to add an old (2003 vintage) used MX-60 to 
> the system purely to use the Aux relay with a used HUB and old but good 
> Mate3.  Works perfectly giving us AGS start and stop voltage settings and 
> basic battery voltage graph. I would be interested in other ways to remote 
> control generators with non Outback inverters. FlexNet DC?
> 
> John Blittersdorf
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Magnum 4448 PAE whimpy charge rate.

2023-12-06 Thread John Blittersdorf via RE-wrenches
I have noticed on several Magnum Installations that the charge rate is low
compared to the inverter rated output.  Typically I would assume the charge
rate should be up to about 70 to 80 % of the inverter capacity, but I am
getting only about 1400 watts (26 amps DC) from it with a 14kw generator.
Is there some setting I am missing that would limit it other than the
charge %.  I know of one system where they added a 2nd Magnum inverter and
then had problems with them working together consistently.  I have used the
8 kilowatt Radians for any off grid with significant loads and battery
capacity and easily get 6000 charging watts from a large generator. I also
needed remote control of the generator (Generac EcoGen 15 kw so a quick
inexpensive but clunky solution I came up with was to add an old (2003
vintage) used MX-60 to the system purely to use the Aux relay with a used
HUB and old but good Mate3.  Works perfectly giving us AGS start and stop
voltage settings and basic battery voltage graph. I would be interested in
other ways to remote control generators with non Outback inverters. FlexNet
DC?

John Blittersdorf
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org