Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-12 Thread robert ellison
Seems that I remember that the APC and other backups are not a sine wave but
a modified wave? But it's been a while.

Bob

On Wed, Feb 11, 2009 at 9:52 AM, Howie Michaelson ho...@suncatchervt.comwrote:

 I installed an off-grid system with identical symptoms:

 OB VFX 3648 dual stack
 Buderus GB142-24
 Kohler 12 kW propane genny

 The boiler runs fine on the inverter power, but will occasionally error
 out (6A) and shut down while the generator is running (usually after it
 has been on for hours).  The plumber installed an APC uninterruptable
 power supply/surge suppressor (not sure of the model) before the boiler,
 but when running on the internal inverter, the symptoms seemed to get
 worse.  When running on just the surge suppressor portion, the symptoms
 were the same as if the APC wasn't in-line.  We've checked the grounding
 at the genny, made sure the neutral was isolated except for the main
 panel, still the same problem.  Seems this is a Buderus issue (or at least
 not an inverter one) - see:


 http://www.buderus.net/Support/TechnicalInfoForums/tabid/132/forumid/15/threadid/4334/scope/posts/Default.aspx

 I haven't been able to make the boiler run reliably when the genny is on,
 which is a problem in our climate, when the client goes away in the
 winter...

 Howie
 --
 Howie Michaelson
 NABCEP Certified Solar PV Installer™

 Sun Catcher, LLC
 Renewable Energy Systems Sales and Service
 VT Solar  Wind Incentive Program Partner
 http://www.SunCatcherVT.com http://www.suncatchervt.com/
 (cell) 802-272-0004
 (home) 802-439-6096


 On Wed, February 11, 2009 7:47 am, Darryl Thayer wrote:
  Some of the hot surface ignitors I have seen draw a lot of current, in
 the
  order of amps.  I would expect the inverter to drop out if it were
  overloaded however.  Also does the magnum drop voltage at very low loads?
  Where the furnace controls can not function due to low voltage or poor
  wave shape.
 
  Darryl
 
 
 
  This may be true about high frequency switching interfering
  with something, but I believe the problem with this ignitor
  is that it is a very poor design. Judging by what I read on
  their company forum, it doesn't look like they have a
  clue about
  this problem. Maybe you can go inside the Buderus and
  filter something there or maybe you can fine another product
  to try ?
 
  boB



  ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-11 Thread Darryl Thayer
Some of the hot surface ignitors I have seen draw a lot of current, in the 
order of amps.  I would expect the inverter to drop out if it were overloaded 
however.  Also does the magnum drop voltage at very low loads?  Where the 
furnace controls can not function due to low voltage or poor wave shape.

Darryl


--- On Wed, 2/11/09, boB Gudgel b...@midnitesolar.com wrote:

 From: boB Gudgel b...@midnitesolar.com
 Subject: Re: [RE-wrenches] Magnum MS4448AE Compatibility Question
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Wednesday, February 11, 2009, 12:03 AM
 Peter Parrish wrote:
  
  As an old Ham Radio Operator, it would seem the
 solution is very simple. First, I assume that the voltage is
 compliant and so is the frequency. The problem is high
 frequency noise (hash from the switching circuitry) on the
 waveform that has not been filtered out. Figure out the
 switching frequency and get a low-pass filter whose cutoff
 is below the switching frequency but above 60 Hz. Make sure
 the filter is rated for the load, but since we’re taking
 about a burner control/igniter, we’re talking low-power,
 correct? LPFs are low-cost commodity items, probably in
 DigiKey or similar catalogs.
  
  - Peter
  
 
 This may be true about high frequency switching interfering
 with something, but I believe the problem with this ignitor
 is that it is a very poor design. Judging by what I read on
 their company forum, it doesn't look like they have a
 clue about
 this problem. Maybe you can go inside the Buderus and
 filter something there or maybe you can fine another product
 to try ?
 
 boB
 
 
 
 
  Peter T. Parrish, President
  California Solar Engineering, Inc.
  820 Cynthia Ave., Los Angeles, CA 90065
  Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
  CA Lic. 854779, NABCEP Cert. 031806-26
  peter.parr...@calsolareng.com
  
 
 
  
  *From:* re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
 Behalf Of *David Katz
  *Sent:* Monday, February 09, 2009 9:31 PM
  *To:* al...@positiveenergysolar.com; RE-wrenches
  *Subject:* Re: [RE-wrenches] Magnum MS4448AE
 Compatibility Question
  
  Hi Allan,
  This is not an unusual problem. i have seen it with
 conventional forced air heating systems. The burner controls
 would not run on A Xantrex or Outback sine wave inverter.
 There is something about waveforms from inverters designed
 by Trace legacy engineers. I had to put in Exeltech or
 Studer inverters to operate the heating control system. you
 can do this and still run larger pumps and fans on the
 Magnum.
  David
  
  David Katz
  
  President
  
  AEE Solar
  
  1155 Redway Drive
  
  P.O. Box 339
  
  Redway, CA 95560
  
  Tel (707) 825-1200
  
  Fax (707) 825-1202
  
  da...@aeesolar.com mailto:da...@aeesolar.com
  
  www.aeesolar.com http://www.aeesolar.com
  
  DISCLAIMER:
  This communication, along with any documents, files or
 attachments, is intended for the use of only the addressee
 and contains privileged and confidential information. If you
 are not the intended recipient, you are hereby notified that
 any dissemination, distribution or copying of any
 information contained in or attached to this communication
 is strictly prohibited. If you have received this message in
 error, please notify the sender immediately by e-mail reply
 and destroy the original communication and its attachments
 without reading, printing or saving in any manner.
  
  P Please consider the environment before printing this
 e-mail.
  
  
  
  Allan Sindelar wrote:
  
  Wrenches,
  We have an unusual problem, and I need to know if
 anyone else has had this
  or a related problem, and what to do about it.
  This concerns a new off-grid residential system, very
 conventional: 1,800W
  PV, Midnite E-Panel with Magnum MS4448-AE inverter,
 MX60, 16 S-460s,
  installed summer 2008. This existing home is being
 extensively remodeled,
  and the home is not yet occupied. A local mechanical
 contractor installed a
  new infloor radiant (gypcrete) hydronic heating system
 using a
  Netherlands-made (German company) Buderus GB142
 high-efficiency boiler. The
  problem is that the boiler won't start reliably on
 the inverter. It appears
  that the hot-surface igniter does not get full AC
 voltage (it runs on
  straight 120V AC, but is supplied through the
 boiler's control circuitry).
  We tested the igniter by disconnecting it and plugging
 it straight into
  inverter AC and it lit right up. The mechanical
 contractor has tried a replacement Buderus GB142 boiler with
  the same result. I was told that they brought out a
 generator and it also
  failed to ignite on generator AC, but not knowing the
 generator used or the
  way it was wired (I believe an extension cord to a
 portable) I don't put
  much weight on this data. They also took a Lochinvar
 Boiler to the site to
  test the theory that a different

Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-11 Thread jay peltz
I dont' know if you can power just the part this is giving problems  
and not the big load which is pumping?

but had a similar problem with an SW trace.
I installed a Exeltech inverter to power that load specifically and  
ever since has worked fine.


The guys at Exeltech make a wave form that everything likes.
Just a thought,

jay

peltz power
On Feb 11, 2009, at 6:52 AM, Howie Michaelson wrote:


I installed an off-grid system with identical symptoms:

OB VFX 3648 dual stack
Buderus GB142-24
Kohler 12 kW propane genny

The boiler runs fine on the inverter power, but will occasionally  
error
out (6A) and shut down while the generator is running (usually after  
it

has been on for hours).  The plumber installed an APC uninterruptable
power supply/surge suppressor (not sure of the model) before the  
boiler,

but when running on the internal inverter, the symptoms seemed to get
worse.  When running on just the surge suppressor portion, the  
symptoms
were the same as if the APC wasn't in-line.  We've checked the  
grounding

at the genny, made sure the neutral was isolated except for the main
panel, still the same problem.  Seems this is a Buderus issue (or at  
least

not an inverter one) - see:

http://www.buderus.net/Support/TechnicalInfoForums/tabid/132/forumid/15/threadid/4334/scope/posts/Default.aspx

I haven't been able to make the boiler run reliably when the genny  
is on,

which is a problem in our climate, when the client goes away in the
winter...

Howie
--
Howie Michaelson
NABCEP Certified Solar PV Installer™

Sun Catcher, LLC
Renewable Energy Systems Sales and Service
VT Solar  Wind Incentive Program Partner
http://www.SunCatcherVT.com
(cell) 802-272-0004
(home) 802-439-6096


On Wed, February 11, 2009 7:47 am, Darryl Thayer wrote:
Some of the hot surface ignitors I have seen draw a lot of current,  
in the

order of amps.  I would expect the inverter to drop out if it were
overloaded however.  Also does the magnum drop voltage at very low  
loads?
Where the furnace controls can not function due to low voltage or  
poor

wave shape.

Darryl




This may be true about high frequency switching interfering
with something, but I believe the problem with this ignitor
is that it is a very poor design. Judging by what I read on
their company forum, it doesn't look like they have a
clue about
this problem. Maybe you can go inside the Buderus and
filter something there or maybe you can fine another product
to try ?

boB




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-11 Thread Hans Frederickson
A few years back, we had a customer who was having similar problems. I don't
recall if it was a Buderus boiler, but the generator was a Generac. This was
a simple generator backup system. We were able to get the boiler to work
reliably after adjusting the governor on the generator so that it ran at
60Hz under load. As I recall, it would then drift above 60Hz when unloaded.

If you were to try a UPS, it would need to be a dual-conversion type to make
a difference, otherwise it would just pass the generator power straight
through. True dual-conversion UPS units are very expensive... Probably
costing more than the cheap generator in many cases.

-Hans

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Howie
Michaelson
Sent: Wednesday, February 11, 2009 6:52 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

I installed an off-grid system with identical symptoms:

OB VFX 3648 dual stack
Buderus GB142-24
Kohler 12 kW propane genny

The boiler runs fine on the inverter power, but will occasionally error out
(6A) and shut down while the generator is running (usually after it has been
on for hours).  The plumber installed an APC uninterruptable power
supply/surge suppressor (not sure of the model) before the boiler, but when
running on the internal inverter, the symptoms seemed to get worse.  When
running on just the surge suppressor portion, the symptoms were the same as
if the APC wasn't in-line.  We've checked the grounding at the genny, made
sure the neutral was isolated except for the main panel, still the same
problem.  Seems this is a Buderus issue (or at least not an inverter one) -
see:

http://www.buderus.net/Support/TechnicalInfoForums/tabid/132/forumid/15/thre
adid/4334/scope/posts/Default.aspx

I haven't been able to make the boiler run reliably when the genny is on,
which is a problem in our climate, when the client goes away in the
winter...

Howie
--
Howie Michaelson
NABCEP Certified Solar PV InstallerT

Sun Catcher, LLC
Renewable Energy Systems Sales and Service VT Solar  Wind Incentive Program
Partner http://www.SunCatcherVT.com
(cell) 802-272-0004
(home) 802-439-6096


On Wed, February 11, 2009 7:47 am, Darryl Thayer wrote:
 Some of the hot surface ignitors I have seen draw a lot of current, in 
 the order of amps.  I would expect the inverter to drop out if it were 
 overloaded however.  Also does the magnum drop voltage at very low loads?
 Where the furnace controls can not function due to low voltage or poor 
 wave shape.

 Darryl



 This may be true about high frequency switching interfering with 
 something, but I believe the problem with this ignitor is that it is 
 a very poor design. Judging by what I read on their company forum, it 
 doesn't look like they have a clue about this problem. Maybe you can 
 go inside the Buderus and filter something there or maybe you can 
 fine another product to try ?

 boB



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-11 Thread Allan Sindelar
Wrenches,
Thank you to you Wrenches who have responded. Keep them coming; I'm
collating all as part of our customer support on this. We have several ideas
to try out.

Darryl, it's not excessive draw. I had a Kill-a-Watt on the AC input during
on-site testing. I saw a momentary peak of 360W (for all, including AC
pumps). The observed draw sequence was 205W for the purge blower, followed
by 270 for the igniter for about 5 seconds, dropping to 220-230W upon
ignition. Later, the hydronic distributor's rep turned down the sidearm
circulator pump from high to low setting and reduced this pump draw by about
45-50 watts. AC voltage during testing bounced around in the range of
117-123VAC, but the fluctuation was not load-based.

At this point Magnum has stepped up to support us; we'll see where this goes
and how it (hopefully) resolves. Magnum has suggested a 50 microfarad
capacitor, per Peter's suggestion. They have also contacted the wholesale
distributor for Buderus boilers for New Mexico, and I believe the plan is to
ship the boiler to Magnum for testing. I may have further questions for the
list, and I'll eventually post how all this resolves.

Allan at Positive Energy

-Original Message-
From: re-wrenches- On Behalf Of Darryl Thayer

Some of the hot surface ignitors I have seen draw a lot of current, in the
order of amps.  I would expect the inverter to drop out if it were
overloaded however.  Also does the magnum drop voltage at very low loads?
Where the furnace controls can not function due to low voltage or poor wave
shape.

Darryl


--- On Wed, 2/11/09, boB Gudgel b...@midnitesolar.com wrote:

 Peter Parrish wrote:
  
  As an old Ham Radio Operator, it would seem the
 solution is very simple. First, I assume that the voltage is
 compliant and so is the frequency. The problem is high
 frequency noise (hash from the switching circuitry) on the
 waveform that has not been filtered out. Figure out the
 switching frequency and get a low-pass filter whose cutoff
 is below the switching frequency but above 60 Hz. Make sure
 the filter is rated for the load, but since we're taking
 about a burner control/igniter, we're talking low-power,
 correct? LPFs are low-cost commodity items, probably in
 DigiKey or similar catalogs.
  
  - Peter
  
 
 This may be true about high frequency switching interfering
 with something, but I believe the problem with this ignitor
 is that it is a very poor design. Judging by what I read on
 their company forum, it doesn't look like they have a
 clue about
 this problem. Maybe you can go inside the Buderus and
 filter something there or maybe you can fine another product
 to try ?
 
 boB

*From:* *David Katz
  
  Hi Allan,
  This is not an unusual problem. i have seen it with
 conventional forced air heating systems. The burner controls
 would not run on A Xantrex or Outback sine wave inverter.
 There is something about waveforms from inverters designed
 by Trace legacy engineers. I had to put in Exeltech or
 Studer inverters to operate the heating control system. you
 can do this and still run larger pumps and fans on the
 Magnum.
  David

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-10 Thread boB Gudgel

David Katz wrote:

Hi Allan,
This is not an unusual problem.  i have seen it with conventional 
forced air heating systems.  The burner controls would not run on A 
Xantrex or Outback sine wave inverter.  There is something about 
waveforms from inverters designed by Trace legacy engineers.  I had to 
put in Exeltech or Studer inverters to operate the heating control 
system.  you can do this and still run larger pumps and fans on the 
Magnum.

David

Try this:   Add a semi-large load to that inverter and then see if the 
ignitor works in addition to that load.  A lot of times, a SineWave
inverter will clean up its waveform some when loaded due to 
inductances...  Yes, even inverters designed by X Trace Engineering

and/or Xandroid engineers.

BTW, I checked that company's forum and this same basic question showed 
up, except it was a generator that had problems.  They couldn't
answer it either, except to say that separating (or connecting 
together?) the Neutral and Ground wires might fix it for some reason.  
Must be

something I'm missing there, but I've seen stranger things I suppose.

boB


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread Allan Sindelar
Wrenches,
We have an unusual problem, and I need to know if anyone else has had this
or a related problem, and what to do about it.
This concerns a new off-grid residential system, very conventional: 1,800W
PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16 S-460s,
installed summer 2008. This existing home is being extensively remodeled,
and the home is not yet occupied. A local mechanical contractor installed a
new infloor radiant (gypcrete) hydronic heating system using a
Netherlands-made (German company) Buderus GB142 high-efficiency boiler. The
problem is that the boiler won't start reliably on the inverter. It appears
that the hot-surface igniter does not get full AC voltage (it runs on
straight 120V AC, but is supplied through the boiler's control circuitry).
We tested the igniter by disconnecting it and plugging it straight into
inverter AC and it lit right up. 
The mechanical contractor has tried a replacement Buderus GB142 boiler with
the same result. I was told that they brought out a generator and it also
failed to ignite on generator AC, but not knowing the generator used or the
way it was wired (I believe an extension cord to a portable) I don't put
much weight on this data. They also took a Lochinvar Boiler to the site to
test the theory that a different manufacturer's boiler might work. The
Lochinvar boiler, which uses a different control and a spark ignition rather
than a hot surface igniter, worked on site without any problems.
I'm looking for solutions. Magnum tech support had not heard of this. Have
you? 
Also, if indeed we have an inverter that is incapable of running this load,
how do we make it right to the homeowner and the mechanical contractor? What
should be Magnum's obligation? What should be ours? This issue hasn't come
up here since the days when the Trace SW mod-sine series was the waveform
standard.
Thanks,
Allan Sindelar
allan_(at)_positiveenergysolar.com mailto:al...@positiveenergysolar.com 
NABCEP certified solar PV installer
Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread Dana
I have hit this one a couple of times but not with the equipment you are
listing. It turned out to be how the sine wave crossed the X axis and the
controls did not like the wave form.

 

Thanks -

 

Dana Orzel

 

Great Solar Works, Inc

www.solarwork.com

E - d...@solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

I'd put my money on solar energy. I hope we don't have to wait 'til oil and
coal run out before we tackle that.

-Thomas Edison, in conversation with Henry Ford and Harvey Firestone, March
1931

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Monday, February 09, 2009 11:16 AM
To: RE Wrenches
Subject: [RE-wrenches] Magnum MS4448AE Compatibility Question

 

Wrenches, 
We have an unusual problem, and I need to know if anyone else has had this
or a related problem, and what to do about it.

This concerns a new off-grid residential system, very conventional: 1,800W
PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16 S-460s,
installed summer 2008. This existing home is being extensively remodeled,
and the home is not yet occupied. A local mechanical contractor installed a
new infloor radiant (gypcrete) hydronic heating system using a
Netherlands-made (German company) Buderus GB142 high-efficiency boiler. The
problem is that the boiler won't start reliably on the inverter. It appears
that the hot-surface igniter does not get full AC voltage (it runs on
straight 120V AC, but is supplied through the boiler's control circuitry).
We tested the igniter by disconnecting it and plugging it straight into
inverter AC and it lit right up. 

The mechanical contractor has tried a replacement Buderus GB142 boiler with
the same result. I was told that they brought out a generator and it also
failed to ignite on generator AC, but not knowing the generator used or the
way it was wired (I believe an extension cord to a portable) I don't put
much weight on this data. They also took a Lochinvar Boiler to the site to
test the theory that a different manufacturer's boiler might work. The
Lochinvar boiler, which uses a different control and a spark ignition rather
than a hot surface igniter, worked on site without any problems.

I'm looking for solutions. Magnum tech support had not heard of this. Have
you? 
Also, if indeed we have an inverter that is incapable of running this load,
how do we make it right to the homeowner and the mechanical contractor? What
should be Magnum's obligation? What should be ours? This issue hasn't come
up here since the days when the Trace SW mod-sine series was the waveform
standard.

Thanks, 
Allan Sindelar 
 mailto:al...@positiveenergysolar.com allan_(at)_positiveenergysolar.com 
NABCEP certified solar PV installer 
Positive Energy, Inc. 
3225A Richards Lane 
Santa Fe NM 87507 
505 424-1112 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread John Raynes
I second Dana's response.  I have observed that the MS4448 waveform 
quality degenerates quite rapidly with imbalanced loading of one or 
the other of the 120 volt output legs.  I can't give a quantitative 
(% distortion/amps) number to it, but I would classify it as 
severe.  I first noticed it when doing some test measurements in the 
shop, and found large discrepancies between various current metering 
devices I was using, as some of the meters were not measuring RMS, 
and the distortion was throwing them way off.  And when using 120 
volt motors, even though their surge may be well within specified 
load limits, count on things not going well.


I'm generally satisfied with the Magnum MS4448, but this is one the 
two key shortcomings that I see with the product.  The other is the 
idle power draw when not in search.


John Raynes
RE Solar
Torrey, UT


At 11:16 AM 2/9/2009, you wrote:


Wrenches,
We have an unusual problem, and I need to know if anyone else has 
had this or a related problem, and what to do about it.


This concerns a new off-grid residential system, very conventional: 
1,800W PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16 
S-460s, installed summer 2008. This existing home is being 
extensively remodeled, and the home is not yet occupied. A local 
mechanical contractor installed a new infloor radiant (gypcrete) 
hydronic heating system using a Netherlands-made (German company) 
Buderus GB142 high-efficiency boiler. The problem is that the boiler 
won't start reliably on the inverter. It appears that the 
hot-surface igniter does not get full AC voltage (it runs on 
straight 120V AC, but is supplied through the boiler's control 
circuitry). We tested the igniter by disconnecting it and plugging 
it straight into inverter AC and it lit right up.


The mechanical contractor has tried a replacement Buderus GB142 
boiler with the same result. I was told that they brought out a 
generator and it also failed to ignite on generator AC, but not 
knowing the generator used or the way it was wired (I believe an 
extension cord to a portable) I don't put much weight on this data. 
They also took a Lochinvar Boiler to the site to test the theory 
that a different manufacturer's boiler might work. The Lochinvar 
boiler, which uses a different control and a spark ignition rather 
than a hot surface igniter, worked on site without any problems.


I'm looking for solutions. Magnum tech support had not heard of 
this. Have you?
Also, if indeed we have an inverter that is incapable of running 
this load, how do we make it right to the homeowner and the 
mechanical contractor? What should be Magnum's obligation? What 
should be ours? This issue hasn't come up here since the days when 
the Trace SW mod-sine series was the waveform standard.


Thanks,
Allan Sindelar
mailto:al...@positiveenergysolar.comallan_(at)_positiveenergysolar.com
NABCEP certified solar PV installer
Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread robert ellison
I wonder if a work around might be to run the igniter off a relay activated
by the original board and fed by the inverter direct?

I have seen things not start when the charger was drawing off the generator,
not Magnums but old Hearts.

Bob

On Mon, Feb 9, 2009 at 1:16 PM, Allan Sindelar 
al...@positiveenergysolar.com wrote:

  Wrenches,
 We have an unusual problem, and I need to know if anyone else has had this
 or a related problem, and what to do about it.

 This concerns a new off-grid residential system, very conventional: 1,800W
 PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16 S-460s,
 installed summer 2008. This existing home is being extensively remodeled,
 and the home is not yet occupied. A local mechanical contractor installed a
 new infloor radiant (gypcrete) hydronic heating system using a
 Netherlands-made (German company) Buderus GB142 high-efficiency boiler. The
 problem is that the boiler won't start reliably on the inverter. It appears
 that the hot-surface igniter does not get full AC voltage (it runs on
 straight 120V AC, but is supplied through the boiler's control circuitry).
 We tested the igniter by disconnecting it and plugging it straight into
 inverter AC and it lit right up.

 The mechanical contractor has tried a replacement Buderus GB142 boiler with
 the same result. I was told that they brought out a generator and it also
 failed to ignite on generator AC, but not knowing the generator used or the
 way it was wired (I believe an extension cord to a portable) I don't put
 much weight on this data. They also took a Lochinvar Boiler to the site to
 test the theory that a different manufacturer's boiler might work. The
 Lochinvar boiler, which uses a different control and a spark ignition rather
 than a hot surface igniter, worked on site without any problems.

 I'm looking for solutions. Magnum tech support had not heard of this. Have
 you?
 Also, if indeed we have an inverter that is incapable of running this load,
 how do we make it right to the homeowner and the mechanical contractor? What
 should be Magnum's obligation? What should be ours? This issue hasn't come
 up here since the days when the Trace SW mod-sine series was the waveform
 standard.

 Thanks,
 Allan Sindelar
 ***allan_(at)_positiveenergysolar.com* al...@positiveenergysolar.com
 NABCEP certified solar PV installer
 Positive Energy, Inc.
 3225A Richards Lane
 Santa Fe NM 87507
 505 424-1112

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread Ezra Auerbach
Have you tried a different SW inverter at the site? There is a  
difference between brands.


Also, have you tried a clean wave form gennie like the Honda  
inverter series.


Finally I don't think that most manufacturers will guarantee that  
their wave form will power a specific load.


Regards,

Ezra Auerbach



On 9-Feb-09, at 4:18 PM, robert ellison reelli...@gmail.com wrote:

I wonder if a work around might be to run the igniter off a relay  
activated by the original board and fed by the inverter direct?


I have seen things not start when the charger was drawing off the  
generator, not Magnums but old Hearts.


Bob

On Mon, Feb 9, 2009 at 1:16 PM, Allan Sindelar al...@positiveenergysolar.com 
 wrote:

Wrenches,
We have an unusual problem, and I need to know if anyone else has  
had this or a related problem, and what to do about it.


This concerns a new off-grid residential system, very conventional:  
1,800W PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16  
S-460s, installed summer 2008. This existing home is being  
extensively remodeled, and the home is not yet occupied. A local  
mechanical contractor installed a new infloor radiant (gypcrete)  
hydronic heating system using a Netherlands-made (German company)  
Buderus GB142 high-efficiency boiler. The problem is that the boiler  
won't start reliably on the inverter. It appears that the hot- 
surface igniter does not get full AC voltage (it runs on straight  
120V AC, but is supplied through the boiler's control circuitry). We  
tested the igniter by disconnecting it and plugging it straight into  
inverter AC and it lit right up.


The mechanical contractor has tried a replacement Buderus GB142  
boiler with the same result. I was told that they brought out a  
generator and it also failed to ignite on generator AC, but not  
knowing the generator used or the way it was wired (I believe an  
extension cord to a portable) I don't put much weight on this data.  
They also took a Lochinvar Boiler to the site to test the theory  
that a different manufacturer's boiler might work. The Lochinvar  
boiler, which uses a different control and a spark ignition rather  
than a hot surface igniter, worked on site without any problems.


I'm looking for solutions. Magnum tech support had not heard of  
this. Have you?
Also, if indeed we have an inverter that is incapable of running  
this load, how do we make it right to the homeowner and the  
mechanical contractor? What should be Magnum's obligation? What  
should be ours? This issue hasn't come up here since the days when  
the Trace SW mod-sine series was the waveform standard.


Thanks,
Allan Sindelar
allan_(at)_positiveenergysolar.com
NABCEP certified solar PV installer
Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread David Katz

Hi Allan,
This is not an unusual problem.  i have seen it with conventional forced 
air heating systems.  The burner controls would not run on A Xantrex or 
Outback sine wave inverter.  There is something about waveforms from 
inverters designed by Trace legacy engineers.  I had to put in Exeltech 
or Studer inverters to operate the heating control system.  you can do 
this and still run larger pumps and fans on the Magnum.

David

David Katz

President

AEE Solar

1155 Redway Drive

P.O. Box 339

Redway, CA  95560

Tel (707) 825-1200

Fax (707) 825-1202

da...@aeesolar.com mailto:da...@aeesolar.com

www.aeesolar.com http://www.aeesolar.com



DISCLAIMER:
This communication, along with any documents, files or attachments, is 
intended for the use of only the addressee and contains privileged and 
confidential information. If you are not the intended recipient, you are 
hereby notified that any dissemination, distribution or copying of any 
information contained in or attached to this communication is strictly 
prohibited.  If you have received this message in error, please notify 
the sender immediately by e-mail reply and destroy the original 
communication and its attachments without reading, printing or saving in 
any manner.


P  Please consider the environment before printing this e-mail.



Allan Sindelar wrote:

Wrenches,
We have an unusual problem, and I need to know if anyone else has had this
or a related problem, and what to do about it.
This concerns a new off-grid residential system, very conventional: 1,800W
PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16 S-460s,
installed summer 2008. This existing home is being extensively remodeled,
and the home is not yet occupied. A local mechanical contractor installed a
new infloor radiant (gypcrete) hydronic heating system using a
Netherlands-made (German company) Buderus GB142 high-efficiency boiler. The
problem is that the boiler won't start reliably on the inverter. It appears
that the hot-surface igniter does not get full AC voltage (it runs on
straight 120V AC, but is supplied through the boiler's control circuitry).
We tested the igniter by disconnecting it and plugging it straight into
inverter AC and it lit right up. 
The mechanical contractor has tried a replacement Buderus GB142 boiler with

the same result. I was told that they brought out a generator and it also
failed to ignite on generator AC, but not knowing the generator used or the
way it was wired (I believe an extension cord to a portable) I don't put
much weight on this data. They also took a Lochinvar Boiler to the site to
test the theory that a different manufacturer's boiler might work. The
Lochinvar boiler, which uses a different control and a spark ignition rather
than a hot surface igniter, worked on site without any problems.
I'm looking for solutions. Magnum tech support had not heard of this. Have
you? 
Also, if indeed we have an inverter that is incapable of running this load,

how do we make it right to the homeowner and the mechanical contractor? What
should be Magnum's obligation? What should be ours? This issue hasn't come
up here since the days when the Trace SW mod-sine series was the waveform
standard.
Thanks,
Allan Sindelar
allan_(at)_positiveenergysolar.com mailto:al...@positiveenergysolar.com 
NABCEP certified solar PV installer

Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112


  



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org