Re: [RE-wrenches] Metering a whole house Outback system

2012-08-21 Thread toddcory

i get mine through vision metering (used to be austin international).
 
refurbished, and programmed for seperate buy  sell registers they are around 
$75.00 each.
 
[https://visionmetering.3dcartstores.com/Vision-Meter-Form-12S-120V-Class-200_p_211.html]
 
https://visionmetering.3dcartstores.com/Vision-Meter-Form-12S-120V-Class-200_p_211.html
 
todd
 
 
 
 
On Monday, August 20, 2012 6:39pm, James Jarvis j...@aprsworld.com said:



Hi Todd,

 Where does one actually buy KV2C meters? We have been looking for   the 
KV2C meters to use with the Modbus option, and nobody seems to   be able to 
supply them.

 Thanks,

 -James Jarvis
 APRS World, LLC

 On 8/20/2012 8:37 PM, [mailto:toddc...@finestplanet.com] 
toddc...@finestplanet.com wrote:
you will need two kv2c 'green   tag' meters... one for each 120 volt 
leg.
 
todd
 
 
 
On Monday, August 20, 2012   9:15am, Hilton Dier III 
[mailto:hiltond...@gmail.com] hiltond...@gmail.com said:


Hello Wrenches,

 Here's a metering conundrum for you.

 I have a client with a dual stacked Outback 3648 inverter panel 
and a PV array. He has been off-grid for years, but he is now going 
on-grid. He is getting the Outbacks rebuilt at the factory to be 
grid tie compatible.

 As per our local requirements, he needs a meter to read just the 
output of the inverter. The problem is that he has the whole house 
on the inverters, not just a vital loads panel. He wants to keep it 
that way. That gives him two separate outputs, AC Out to the main 
breaker panel and AC In(teractive) to the grid connection. If he 
just puts a meter on the AC In line, he will lose track of the 
inverter output that goes to power the house, and he'll get his 
output reduced by any grid-based charging he does.

 There is a green tag method of wiring the meter to avoid this, 
but it is designed for two single-leg 120VAC outputs and the 
stacked Outbacks are putting out 240VAC on two legs.

 Aside from dropping $600 on an e-Gauge, is there any way to get 
around this?

 Many thanks,

 Hilton

-- Hilton Dier III Renewable Energy Design 
Partner, Solar Gain LLC 453 East Hill Rd. Middlesex, VT 
05602


 Sent from Finest Planet WebMail.

 

___List sponsored by Home Power 
magazineList Address: [mailto:RE-wrenches@lists.re-wrenches.org] 
re-wrenc...@lists.re-wrenches.orgOptions  
settings:[http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org] 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:
 [http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org] 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules  
etiquette:[http://www.re-wrenches.org/etiquette.htm] 
www.re-wrenches.org/etiquette.htmCheck out participant 
bios:[http://www.members.re-wrenches.org] www.members.re-wrenches.org




Sent from Finest Planet WebMail.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Metering a whole house Outback system

2012-08-20 Thread Hilton Dier III

Hello Wrenches,

Here's a metering conundrum for you.

I have a client with a dual stacked Outback 3648 inverter panel and a PV 
array. He has been off-grid for years, but he is now going on-grid. He 
is getting the Outbacks rebuilt at the factory to be grid tie compatible.


As per our local requirements, he needs a meter to read just the output 
of the inverter. The problem is that he has the whole house on the 
inverters, not just a vital loads panel. He wants to keep it that way. 
That gives him two separate outputs, AC Out to the main breaker panel 
and AC In(teractive) to the grid connection. If he just puts a meter 
on the AC In line, he will lose track of the inverter output that goes 
to power the house, and he'll get his output reduced by any grid-based 
charging he does.


There is a green tag method of wiring the meter to avoid this, but it 
is designed for two single-leg 120VAC outputs and the stacked Outbacks 
are putting out 240VAC on two legs.


Aside from dropping $600 on an e-Gauge, is there any way to get around this?

Many thanks,

Hilton

--
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Metering a whole house Outback system

2012-08-20 Thread David Katz
Hilton,
I am metering an Outback Radian in this situation.  I am using an Elkor meter 
with a pair of current transformers, but you can use and meter with CTs.  Just 
feed the two AC lines from the main panel through the CTs to the AC in of the 
inverters, then run the wires coming from the inverters output, going to the 
sub-panel back through the same CTs, keeping the L1 and L2 in phase.  This way 
the utility power cancels and you only read the inverters output.  You get the 
sum of what goes to the grid and what is used kb the subpanel.  It also 
subtracts what is used to float the batteries.
I read my Elkor meter with a SolarLog monitor.
David Katz

Sent from my HTC smartphone on the Now Network from Sprint!


- Reply message -
From: Hilton Dier III hiltond...@gmail.com
To: re-wrenches@lists.re-wrenches.org re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Metering a whole house Outback system
Date: Mon, Aug 20, 2012 9:15 am



Hello Wrenches,

Here's a metering conundrum for you.

I have a client with a dual stacked Outback 3648 inverter panel and a PV array. 
He has been off-grid for years, but he is now going on-grid. He is getting the 
Outbacks rebuilt at the factory to be grid tie compatible.

As per our local requirements, he needs a meter to read just the output of the 
inverter. The problem is that he has the whole house on the inverters, not just 
a vital loads panel. He wants to keep it that way. That gives him two separate 
outputs, AC Out to the main breaker panel and AC In(teractive) to the grid 
connection. If he just puts a meter on the AC In line, he will lose track of 
the inverter output that goes to power the house, and he'll get his output 
reduced by any grid-based charging he does.

There is a green tag method of wiring the meter to avoid this, but it is 
designed for two single-leg 120VAC outputs and the stacked Outbacks are putting 
out 240VAC on two legs.

Aside from dropping $600 on an e-Gauge, is there any way to get around this?

Many thanks,

Hilton

--
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Metering a whole house Outback system

2012-08-20 Thread Dave Palumbo
Dave,

 

Sounds like a great solution. We have an OB Radian net-metered PV with
battery back-up coming up this fall.  Where do we source an Elkor meter?

 

Thanks,

Dave

 

David Palumbo

Independent Power LLC 

462 Solar Way Drive

Hyde Park, VT 05655

www.independentpowerllc.com 

NABCEP Certified PV Installer

Vermont Solar Partner

24 Years Experience, (802) 888-7194 

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Katz
Sent: Monday, August 20, 2012 3:48 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Metering a whole house Outback system

 

Hilton,
I am metering an Outback Radian in this situation.  I am using an Elkor
meter with a pair of current transformers, but you can use and meter with
CTs.  Just feed the two AC lines from the main panel through the CTs to the
AC in of the inverters, then run the wires coming from the inverters output,
going to the sub-panel back through the same CTs, keeping the L1 and L2 in
phase.  This way the utility power cancels and you only read the inverters
output.  You get the sum of what goes to the grid and what is used kb the
subpanel.  It also subtracts what is used to float the batteries.
I read my Elkor meter with a SolarLog monitor.
David Katz

Sent from my HTC smartphone on the Now Network from Sprint!



- Reply message -
From: Hilton Dier III hiltond...@gmail.com
To: re-wrenches@lists.re-wrenches.org re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Metering a whole house Outback system
Date: Mon, Aug 20, 2012 9:15 am

 

Hello Wrenches,

Here's a metering conundrum for you.

I have a client with a dual stacked Outback 3648 inverter panel and a PV
array. He has been off-grid for years, but he is now going on-grid. He is
getting the Outbacks rebuilt at the factory to be grid tie compatible.

As per our local requirements, he needs a meter to read just the output of
the inverter. The problem is that he has the whole house on the inverters,
not just a vital loads panel. He wants to keep it that way. That gives him
two separate outputs, AC Out to the main breaker panel and AC
In(teractive) to the grid connection. If he just puts a meter on the AC In
line, he will lose track of the inverter output that goes to power the
house, and he'll get his output reduced by any grid-based charging he does.

There is a green tag method of wiring the meter to avoid this, but it is
designed for two single-leg 120VAC outputs and the stacked Outbacks are
putting out 240VAC on two legs.

Aside from dropping $600 on an e-Gauge, is there any way to get around this?

Many thanks,

Hilton



-- 
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Metering a whole house Outback system

2012-08-20 Thread David Katz
I get them from SolarLog in Connecticut.
David

Sent from my HTC smartphone on the Now Network from Sprint!


- Reply message -
From: Dave Palumbo d...@independentpowerllc.com
To: apos;RE-wrenchesapos; re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Metering a whole house Outback system
Date: Mon, Aug 20, 2012 1:06 pm



Dave,

Sounds like a great solution. We have an OB Radian net-metered PV with battery 
back-up coming up this fall.  Where do we source an “Elkor” meter?

Thanks,
Dave

David Palumbo
Independent Power LLC
462 Solar Way Drive
Hyde Park, VT 05655
www.independentpowerllc.com
NABCEP Certified PV Installer
Vermont Solar Partner
24 Years Experience, (802) 888-7194



From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Katz
Sent: Monday, August 20, 2012 3:48 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Metering a whole house Outback system

Hilton,
I am metering an Outback Radian in this situation.  I am using an Elkor meter 
with a pair of current transformers, but you can use and meter with CTs.  Just 
feed the two AC lines from the main panel through the CTs to the AC in of the 
inverters, then run the wires coming from the inverters output, going to the 
sub-panel back through the same CTs, keeping the L1 and L2 in phase.  This way 
the utility power cancels and you only read the inverters output.  You get the 
sum of what goes to the grid and what is used kb the subpanel.  It also 
subtracts what is used to float the batteries.
I read my Elkor meter with a SolarLog monitor.
David Katz

Sent from my HTC smartphone on the Now Network from Sprint!

- Reply message -
From: Hilton Dier III hiltond...@gmail.commailto:hiltond...@gmail.com
To: 
re-wrenches@lists.re-wrenches.orgmailto:re-wrenches@lists.re-wrenches.org 
re-wrenches@lists.re-wrenches.orgmailto:re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Metering a whole house Outback system
Date: Mon, Aug 20, 2012 9:15 am

Hello Wrenches,

Here's a metering conundrum for you.

I have a client with a dual stacked Outback 3648 inverter panel and a PV array. 
He has been off-grid for years, but he is now going on-grid. He is getting the 
Outbacks rebuilt at the factory to be grid tie compatible.

As per our local requirements, he needs a meter to read just the output of the 
inverter. The problem is that he has the whole house on the inverters, not just 
a vital loads panel. He wants to keep it that way. That gives him two separate 
outputs, AC Out to the main breaker panel and AC In(teractive) to the grid 
connection. If he just puts a meter on the AC In line, he will lose track of 
the inverter output that goes to power the house, and he'll get his output 
reduced by any grid-based charging he does.

There is a green tag method of wiring the meter to avoid this, but it is 
designed for two single-leg 120VAC outputs and the stacked Outbacks are putting 
out 240VAC on two legs.

Aside from dropping $600 on an e-Gauge, is there any way to get around this?

Many thanks,

Hilton


--

Hilton Dier III

Renewable Energy Design

Partner, Solar Gain LLC

453 East Hill Rd.

Middlesex, VT 05602
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Metering a whole house Outback system

2012-08-20 Thread Chris Mason
An eGuage is a REALLY good way to do this so I would not dismiss it.

On Mon, Aug 20, 2012 at 12:15 PM, Hilton Dier III hiltond...@gmail.comwrote:

  Hello Wrenches,

 Here's a metering conundrum for you.

 I have a client with a dual stacked Outback 3648 inverter panel and a PV
 array. He has been off-grid for years, but he is now going on-grid. He is
 getting the Outbacks rebuilt at the factory to be grid tie compatible.

 As per our local requirements, he needs a meter to read just the output of
 the inverter. The problem is that he has the whole house on the inverters,
 not just a vital loads panel. He wants to keep it that way. That gives him
 two separate outputs, AC Out to the main breaker panel and AC
 In(teractive) to the grid connection. If he just puts a meter on the AC In
 line, he will lose track of the inverter output that goes to power the
 house, and he'll get his output reduced by any grid-based charging he does.

 There is a green tag method of wiring the meter to avoid this, but it is
 designed for two single-leg 120VAC outputs and the stacked Outbacks are
 putting out 240VAC on two legs.

 Aside from dropping $600 on an e-Gauge, is there any way to get around
 this?

 Many thanks,

 Hilton

 --
 Hilton Dier III
 Renewable Energy Design
 Partner, Solar Gain LLC
 453 East Hill Rd.
 Middlesex, VT 05602


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Metering a whole house Outback system

2012-08-20 Thread Glenn Burt
http://www.elkor.net/

 

I have purchased the kWh meter and remote display direct from Elkor in the
past.

 

-Glenn

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Palumbo
Sent: Monday, August 20, 2012 4:07 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Metering a whole house Outback system

 

Dave,

 

Sounds like a great solution. We have an OB Radian net-metered PV with
battery back-up coming up this fall.  Where do we source an Elkor meter?

 

Thanks,

Dave

 

David Palumbo

Independent Power LLC 

462 Solar Way Drive

Hyde Park, VT 05655

www.independentpowerllc.com 

NABCEP Certified PV Installer

Vermont Solar Partner

24 Years Experience, (802) 888-7194 

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Katz
Sent: Monday, August 20, 2012 3:48 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Metering a whole house Outback system

 

Hilton,
I am metering an Outback Radian in this situation.  I am using an Elkor
meter with a pair of current transformers, but you can use and meter with
CTs.  Just feed the two AC lines from the main panel through the CTs to the
AC in of the inverters, then run the wires coming from the inverters output,
going to the sub-panel back through the same CTs, keeping the L1 and L2 in
phase.  This way the utility power cancels and you only read the inverters
output.  You get the sum of what goes to the grid and what is used kb the
subpanel.  It also subtracts what is used to float the batteries.
I read my Elkor meter with a SolarLog monitor.
David Katz

Sent from my HTC smartphone on the Now Network from Sprint!

- Reply message -
From: Hilton Dier III hiltond...@gmail.com
To: re-wrenches@lists.re-wrenches.org re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Metering a whole house Outback system
Date: Mon, Aug 20, 2012 9:15 am

 

Hello Wrenches,

Here's a metering conundrum for you.

I have a client with a dual stacked Outback 3648 inverter panel and a PV
array. He has been off-grid for years, but he is now going on-grid. He is
getting the Outbacks rebuilt at the factory to be grid tie compatible.

As per our local requirements, he needs a meter to read just the output of
the inverter. The problem is that he has the whole house on the inverters,
not just a vital loads panel. He wants to keep it that way. That gives him
two separate outputs, AC Out to the main breaker panel and AC
In(teractive) to the grid connection. If he just puts a meter on the AC In
line, he will lose track of the inverter output that goes to power the
house, and he'll get his output reduced by any grid-based charging he does.

There is a green tag method of wiring the meter to avoid this, but it is
designed for two single-leg 120VAC outputs and the stacked Outbacks are
putting out 240VAC on two legs.

Aside from dropping $600 on an e-Gauge, is there any way to get around this?

Many thanks,

Hilton

-- 
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Metering a whole house Outback system

2012-08-20 Thread toddcory

you will need two kv2c 'green tag' meters... one for each 120 volt leg.
 
todd
 
 
 
On Monday, August 20, 2012 9:15am, Hilton Dier III hiltond...@gmail.com 
said:


Hello Wrenches,

 Here's a metering conundrum for you.

 I have a client with a dual stacked Outback 3648 inverter panel   and a PV 
array. He has been off-grid for years, but he is now   going on-grid. He is 
getting the Outbacks rebuilt at the factory   to be grid tie compatible.

 As per our local requirements, he needs a meter to read just the   output 
of the inverter. The problem is that he has the whole house   on the 
inverters, not just a vital loads panel. He wants to keep   it that way. 
That gives him two separate outputs, AC Out to the   main breaker panel 
and AC In(teractive) to the grid connection.   If he just puts a meter on 
the AC In line, he will lose track of   the inverter output that goes to 
power the house, and he'll get   his output reduced by any grid-based 
charging he does.

 There is a green tag method of wiring the meter to avoid this,   but it 
is designed for two single-leg 120VAC outputs and the   stacked Outbacks 
are putting out 240VAC on two legs.

 Aside from dropping $600 on an e-Gauge, is there any way to get   around 
this?

 Many thanks,

 Hilton

-- Hilton Dier IIIRenewable Energy DesignPartner, Solar Gain LLC453 East Hill 
Rd.Middlesex, VT 05602


Sent from Finest Planet WebMail.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org