Do you think Enphase be willing to increase the VMax? That's what we do
here when we have 220V 3ph issues. As we are not US based, there is no UL
issue.
I have a project right now that Enphase is the best solution, but the
voltage would be 129v typically, so I would be unwilling to put in stock
units.


On Mon, Apr 15, 2013 at 8:03 PM, Kent Osterberg k...@coveoregon.com wrote:

  Enphase lists the standard operating range for the 208-volt 3-phase
 configuration as 183 to 229 volts. Seems like 220-volt 3-phase might work
 with a little caution about wiring losses.

 Kent Osterberg
 Blue Mountain Solar, Inc.www.bluemountainsolar.com

  On 4/15/2013 4:28 PM, Larry Crutcher, Starlight Solar Power Systems wrote:

 Interesting….Here is a reply from Enphase received on 4-11-13, Hi
 Larry, No we do not have a inverter that will work with this. Our inverter
 is for 240AC 2 Phase, 208AC 3 Phase…




 Larry Crutcher
 Starlight Solar Power Systems






  On Apr 15, 2013, at 1:54 PM, Nick Soleil nsol...@enphaseenergy.com
 wrote:

  Hi Larry,

  Enphase is supplying microinverters into Mexico and supporting the
 127/220 applications.  We have hundreds of installations installed at this
 voltage now.  Feel free to contact me off-line, and I would be happy to
 discuss the details.





 On Mon, Apr 15, 2013 at 1:25 PM, Larry Crutcher, Starlight Solar Power
 Systems la...@starlightsolar.com wrote:

 Wrenches,

   A customer in Mexico wants to start with about 10kW PV. They have
 a 225 kva transformer supplying 220/127 volt 3-phase to the property. They
 are adding buildings/roof space in several stages over the next 4 years and
 want to grow the installation to 120kW of PV solar power.

  Manufacturer data sheets are not real clear. Who makes micro-inverters
 suitable for this? I know Enphase does not.

  Thank you,

 Larry Crutcher
  Starlight Solar Power Systems










 --
 Cordially,
 *Nick Soleil*
 *Field Applications Engineer
 *
 *Enphase Energy*
 Mobile: (707) 321-2937

 **
 *Enphase Commercial Solar.* 
 *Limitless.*http://www.enphase.com/commercial?utm_source=emailutm_medium=sigutm_campaign=Comm2012
 *
 *http://www.enphase.com/commercial?utm_source=emailutm_medium=sigutm_campaign=Comm2012
 1420 North McDowell
  Petaluma, CA 94954

 www.enphase.com http://www.enphaseenergy.com/
 P: (707) 763-4784 x7267
 F: (707) 763-0784
 E: nsol...@enphaseenergy.com

  image002.jpg Certified Solar PV Installer #03262011-300

 “Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
 to fission. And it just so happens that there’s an enormous fusion reactor
 safely banked a few million miles from us. It delivers more than we could
 ever use in just about 8 minutes. And it’s wireless! .”

 - William McDonough

 This email message is for the sole use of the intended recipient(s) and may 
 contain confidential and/or privileged information. If you are not an 
 intended recipient, you may not review, use, copy, disclose or distribute 
 this message. If you received this message in error, please contact the 
 sender by reply email and destroy all copies of the original message.

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  
 settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:www.re-wrenches.org/etiquette.htm

 Check out participant bios:www.members.re-wrenches.org




 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  
 settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:www.re-wrenches.org/etiquette.htm

 Check out participant bios:www.members.re-wrenches.org



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:

Re: [RE-wrenches] Micro-inverters for 3-phase 220/127 in Mexico

2013-04-18 Thread jay peltz
Hi all

You might look at HiQ
http://www.hiqsolar.com/

Dave Katz has been using them and likes them a lot

They are a true 3 wire 3 phase. 
And have bidirectional communication. 

Jay

Peltz power

Sent from my iPad

On Apr 18, 2013, at 7:20 AM, Chris Mason cometenergysyst...@gmail.com wrote:

 Do you think Enphase be willing to increase the VMax? That's what we do here 
 when we have 220V 3ph issues. As we are not US based, there is no UL issue.
 I have a project right now that Enphase is the best solution, but the voltage 
 would be 129v typically, so I would be unwilling to put in stock units.
 
 
 On Mon, Apr 15, 2013 at 8:03 PM, Kent Osterberg k...@coveoregon.com wrote:
 Enphase lists the standard operating range for the 208-volt 3-phase 
 configuration as 183 to 229 volts. Seems like 220-volt 3-phase might work 
 with a little caution about wiring losses.
 Kent Osterberg
 Blue Mountain Solar, Inc.
 www.bluemountainsolar.com
 
 
 On 4/15/2013 4:28 PM, Larry Crutcher, Starlight Solar Power Systems wrote:
 Interesting….Here is a reply from Enphase received on 4-11-13, Hi Larry, 
 No we do not have a inverter that will work with this. Our inverter is for 
 240AC 2 Phase, 208AC 3 Phase…
 
 
 
 
 Larry Crutcher
 Starlight Solar Power Systems
 
 
 
 
 
 
 On Apr 15, 2013, at 1:54 PM, Nick Soleil nsol...@enphaseenergy.com wrote:
 
 Hi Larry,
 
 Enphase is supplying microinverters into Mexico and supporting the 127/220 
 applications.  We have hundreds of installations installed at this voltage 
 now.  Feel free to contact me off-line, and I would be happy to discuss the 
 details.
 
 
 
 
 
 On Mon, Apr 15, 2013 at 1:25 PM, Larry Crutcher, Starlight Solar Power 
 Systems la...@starlightsolar.com wrote:
 Wrenches, 
 
 A customer in Mexico wants to start with about 10kW PV. They have a 225 
 kva transformer supplying 220/127 volt 3-phase to the property. They are 
 adding buildings/roof space in several stages over the next 4 years and 
 want to grow the installation to 120kW of PV solar power.
 
 Manufacturer data sheets are not real clear. Who makes micro-inverters 
 suitable for this? I know Enphase does not.
 
 Thank you,
 
 Larry Crutcher
 Starlight Solar Power Systems
 
 
 -- 
 Cordially,
 Nick Soleil
 Field Applications Engineer
 Enphase Energy
 Mobile: (707) 321-2937
 
 Enphase Commercial Solar. Limitless.
 
 1420 North McDowell
 Petaluma, CA 94954
 www.enphase.com
 P: (707) 763-4784 x7267
 F: (707) 763-0784
 E: nsol...@enphaseenergy.com
 image002.jpg Certified Solar PV Installer #03262011-300
 
 “Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion 
 to fission. And it just so happens that there’s an enormous fusion reactor 
 safely banked a few million miles from us. It delivers more than we could 
 ever use in just about 8 minutes. And it’s wireless! .”  
 - William McDonough
 
 This email message is for the sole use of the intended recipient(s) and may 
 contain confidential and/or privileged information. If you are not an 
 intended recipient, you may not review, use, copy, disclose or distribute 
 this message. If you received this message in error, please contact the 
 sender by reply email and destroy all copies of the original message. 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 -- 
 Chris Mason
 President, Comet Systems Ltd
 www.cometenergysystems.com
 Cell: 264.235.5670
 Skype: netconcepts
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 

[RE-wrenches] Micro-inverters for 3-phase 220/127 in Mexico

2013-04-15 Thread Larry Crutcher, Starlight Solar Power Systems
Wrenches, 

A customer in Mexico wants to start with about 10kW PV. They have a 225 kva 
transformer supplying 220/127 volt 3-phase to the property. They are adding 
buildings/roof space in several stages over the next 4 years and want to grow 
the installation to 120kW of PV solar power.

Manufacturer data sheets are not real clear. Who makes micro-inverters suitable 
for this? I know Enphase does not.

Thank you,

Larry Crutcher
Starlight Solar Power Systems







___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Micro-inverters for 3-phase 220/127 in Mexico

2013-04-15 Thread Nick Soleil
Hi Larry,

Enphase is supplying microinverters into Mexico and supporting the 127/220
applications.  We have hundreds of installations installed at this voltage
now.  Feel free to contact me off-line, and I would be happy to discuss the
details.


On Mon, Apr 15, 2013 at 1:25 PM, Larry Crutcher, Starlight Solar Power
Systems la...@starlightsolar.com wrote:

 Wrenches,

A customer in Mexico wants to start with about 10kW PV. They have a
 225 kva transformer supplying 220/127 volt 3-phase to the property. They
 are adding buildings/roof space in several stages over the next 4 years and
 want to grow the installation to 120kW of PV solar power.

 Manufacturer data sheets are not real clear. Who makes micro-inverters
 suitable for this? I know Enphase does not.

 Thank you,

 Larry Crutcher
 Starlight Solar Power Systems








 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 

Cordially,

*Nick Soleil*

*Field Applications Engineer
*

*Enphase Energy*

Mobile: (707) 321-2937


**

*Enphase Commercial Solar.*
*Limitless.*http://www.enphase.com/commercial?utm_source=emailutm_medium=sigutm_campaign=Comm2012

*
*http://www.enphase.com/commercial?utm_source=emailutm_medium=sigutm_campaign=Comm2012

1420 North McDowell

Petaluma, CA 94954

www.enphase.com http://www.enphaseenergy.com/

P: (707) 763-4784 x7267

F: (707) 763-0784

E: nsol...@enphaseenergy.com

[image: nabcep logo] Certified Solar PV Installer #03262011-300

“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
to fission. And it just so happens that there’s an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it’s wireless! .”

- William McDonough



This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of the original message. 

image002.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Micro-inverters for 3-phase 220/127 in Mexico

2013-04-15 Thread Bill Hoffer
Larry

I believe that APS ( Bluefrog http://bluefrogsolar.com/aps-inverters)
micro inverters can be adjusted down to 180 VAC, so they should  work line
to line in your application. I know that their spec sheet and manual do not
indicate that, but I have installed them in adjusted for a 208 VAC and they
have been sending adjusted units to Hawaii.  You will probably have to
contact them directly to see what can be done.

Bill


On Mon, Apr 15, 2013 at 1:25 PM, Larry Crutcher, Starlight Solar Power
Systems la...@starlightsolar.com wrote:

 Wrenches,

 A customer in Mexico wants to start with about 10kW PV. They have a 225
 kva transformer supplying 220/127 volt 3-phase to the property. They are
 adding buildings/roof space in several stages over the next 4 years and
 want to grow the installation to 120kW of PV solar power.

 Manufacturer data sheets are not real clear. Who makes micro-inverters
 suitable for this? I know Enphase does not.

 Thank you,

 Larry Crutcher
 Starlight Solar Power Systems








 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Bill Hoffer
P.O. Box 1823
White Salmon, WA 98672
suneng...@gmail.com bhof...@sunergyengineeringservices.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org