Allan,

According to Wikipedia, it is not a typo. It is, however, an excellent example
of lousy technical writing / documentation. You are correct to zero in on it

What Outback seems to have done, is switch from a four line drawing on the input
side of the circuit to a one line drawing on the output. Bad. And, it was a
confusing drawing to begin with. However, I think 120VAC to Neutral was
correctly meant to mean, as measured from that point to the neutral bar. Your
proposed 120VAC output to Inverter is much better.

Allow me to digress point out, most consumers, homeowners, tradesmen, and
engineers only read the owners manuals when forced to. One reason, perhaps, the
manuals, more often than not, suck. A pet peeve of mine.
Great documentation takes time and talent. Both cost real money.

I agree. Your solution works. It really is that simple.

Dick Ratico
Solarwind Electric
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PSX-240 wiring question

2013-09-07 Thread dan

I'd just launder the tool thru the sw wid another X240 on its own switch. db

 Original Message 
Subject: [RE-wrenches] PSX-240 wiring question
From: Allan Sindelar al...@positiveenergysolar.com
Date: Sat, September 7, 2013 2:56 pm
To: RE-wrenches re-wrenches@lists.re-wrenches.org

Wrenches,
 Here's a small issue on which I need help. It concerns the best functional way 
to wire up an Outback PSX-240 balancing autotransformer for a specific purpose.
 
 I have somehow succeeded in transferring the wiring diagram on page 6 of 
Outback's PSX-240 installation manual into this message. This is for a 
step-down/generator balancing function. 
 
 The situation: 8kW 240V AC generator serving an older system with a single 
Trace SW4024. The 240V from the generator enters the PSX240 as wired according 
to the diagram. The primary role of the generator is to provide occasional 
backup charging to the batteries through the inverter. The specific issue is 
that the client also wants 240V AC from the generator to be available to a 
single shop receptacle to run a stationary woodworking tool. The generator is 
not large enough to both run the tool and charge at full (33A @120V AC / 120A 
@24V DC) AC2 amps in setting, and we don't want to reduce the charge rate, as 
it's currently ideal for the new HUP industrial flooded batteries.
 
 We initially tapped 240V off of the generator feed ahead of the 25A two-pole 
breaker in the PSX-240. We instructed the customer to turn off this 25A breaker 
when using the power tool (the tool circuit has its own separate two-pole 
breaker). What we discovered, which is obvious in hindsight, is that one of the 
generator's 120V AC legs continues to feed the inverter AC2 input with the 
breaker off. This causes the inverter to try to draw too much current from that 
AC generator leg only.
 
 My question: could I solve this by simply moving the 120VAC to Neutral 
output feed (now tapped off of L2) shown on the drawing below to the other side 
of the 25A circuit breaker; that is, to point 4 in the drawing? It seems to me 
that this would work, and would not intrinsically overload either of the two 
25A poles of the breaker. The 120V AC output to the inverter could in theory 
draw 50A; 25A from L2 and 25A through the windings of the transformer. But this 
solution seems almost too simple. What am I missing, please?
 
 
  
 
 -- 
  Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified PV Installation Professional 
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc., a Certified B CorporationTM
 3209 Richards Lane
 Santa Fe, New Mexico 87507
 505 424-1112 office 780-2738 cell
 www.positiveenergysolar.com___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PSX-240 wiring question

2013-09-07 Thread Chris Schaefer
I've got a similar situation with an old SW-4024. The house is wired
entirely for 120vac and is still an off-grid home but at some point the new
owners received grid power which they want to use as a back-up. They also
want to add a back-up 240vac genny. At first I thought of doing as Dan
suggest, using two X240's. But as I mulled over the design I decided to use
a single manual transfer switch and one X240. The transfer switch is 1/2 the
price of the 2nd PSX240. Thus on the primary of the transfer switch will be
either the grid or genny with the secondary side of the switch to be the
PSX240. I'm doing the upgrade next week.

Christopher

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
d...@foxfire-energy.com
Sent: Saturday, September 07, 2013 16:00
To: al...@positiveenergysolar.com; RE-wrenches
Subject: Re: [RE-wrenches] PSX-240 wiring question

I'd just launder the tool thru the sw wid another X240 on its own switch. db

 Original Message 
Subject: [RE-wrenches] PSX-240 wiring question
From: Allan Sindelar al...@positiveenergysolar.com
Date: Sat, September 7, 2013 2:56 pm
To: RE-wrenches re-wrenches@lists.re-wrenches.org

Wrenches,
 Here's a small issue on which I need help. It concerns the best functional
way to wire up an Outback PSX-240 balancing autotransformer for a specific
purpose.
 
 I have somehow succeeded in transferring the wiring diagram on page 6 of
Outback's PSX-240 installation manual into this message. This is for a
step-down/generator balancing function. 
 
 The situation: 8kW 240V AC generator serving an older system with a single
Trace SW4024. The 240V from the generator enters the PSX240 as wired
according to the diagram. The primary role of the generator is to provide
occasional backup charging to the batteries through the inverter. The
specific issue is that the client also wants 240V AC from the generator to
be available to a single shop receptacle to run a stationary woodworking
tool. The generator is not large enough to both run the tool and charge at
full (33A @120V AC / 120A @24V DC) AC2 amps in setting, and we don't want to
reduce the charge rate, as it's currently ideal for the new HUP industrial
flooded batteries.
 
 We initially tapped 240V off of the generator feed ahead of the 25A
two-pole breaker in the PSX-240. We instructed the customer to turn off this
25A breaker when using the power tool (the tool circuit has its own separate
two-pole breaker). What we discovered, which is obvious in hindsight, is
that one of the generator's 120V AC legs continues to feed the inverter AC2
input with the breaker off. This causes the inverter to try to draw too much
current from that AC generator leg only.
 
 My question: could I solve this by simply moving the 120VAC to Neutral
output feed (now tapped off of L2) shown on the drawing below to the other
side of the 25A circuit breaker; that is, to point 4 in the drawing? It
seems to me that this would work, and would not intrinsically overload
either of the two 25A poles of the breaker. The 120V AC output to the
inverter could in theory draw 50A; 25A from L2 and 25A through the windings
of the transformer. But this solution seems almost too simple. What am I
missing, please?
 
 
  
 
 -- 
  Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified PV Installation Professional  NABCEP Certified Technical
Sales Professional  New Mexico EE98J Journeyman Electrician  Founder and
Chief Technology Officer  Positive Energy, Inc., a Certified B CorporationTM
 3209 Richards Lane
 Santa Fe, New Mexico 87507
 505 424-1112 office 780-2738 cell
 www.positiveenergysolar.com___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Re: [RE-wrenches] PSX-240 wiring question

2013-09-07 Thread Jay Peltz
Hi Allan

I have had to address this issue before. 
My two choices are either a mechanical  disconnect or a relay ahead of the 
Tformer. 

Whether its a cool custom interlock,simple switch or relay,  you get the fun 
call on that one. 

And yes if there was room for an addition 60 amp breaker in the box it would 
really help. 

Jay
Peltz power

Sent from my iPhone

On Sep 7, 2013, at 11:56 AM, Allan Sindelar al...@positiveenergysolar.com 
wrote:

 Wrenches,
 Here's a small issue on which I need help. It concerns the best functional 
 way to wire up an Outback PSX-240 balancing autotransformer for a specific 
 purpose.
 
 I have somehow succeeded in transferring the wiring diagram on page 6 of 
 Outback's PSX-240 installation manual into this message. This is for a 
 step-down/generator balancing function. 
 
 The situation: 8kW 240V AC generator serving an older system with a single 
 Trace SW4024. The 240V from the generator enters the PSX240 as wired 
 according to the diagram. The primary role of the generator is to provide 
 occasional backup charging to the batteries through the inverter. The 
 specific issue is that the client also wants 240V AC from the generator to be 
 available to a single shop receptacle to run a stationary woodworking tool. 
 The generator is not large enough to both run the tool and charge at full 
 (33A @120V AC / 120A @24V DC) AC2 amps in setting, and we don't want to 
 reduce the charge rate, as it's currently ideal for the new HUP industrial 
 flooded batteries.
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org