We used to use ferrules on smaller conductors. Both insulated and
uninsulated are available. A quick search came up with this source:
http://www.ferrulesdirect.com/Merchant2/merchant.mvc?Screen=CTGY
http://www.ferrulesdirect.com/Merchant2/merchant.mvc?Screen=CTGYStore_Code
=FDCategory_Code=UNFERR Store_Code=FDCategory_Code=UNFERR
can't say I've used the larger sizes and you might be in the hole even more
after acquiring the correct crimping tool.
-Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Friday, March 15, 2013 6:58 PM
To: RE-wrenches
Subject: [RE-wrenches] Question re fine stranded cable with Sunny Island
inverters
Wrenches,
A small issue, drawing on the collective wisdom here:
For an upcoming quad-stack installation of Sunny Island inverters, I
foolishly ordered some fine stranded copper 1/0 Cobra X-Flex Cable because
of its flexibility. In this situation, because of NEC ampacity requirements
on our total DC cabling (this system also has a single Radian for some
dedicated loads) we are only running 125 amp DC breakers on each SI
inverter.
Our issue is that the SI installation manual specifically notes not to use
fine stranded cable into the terminal lugs. This was news to me. We can
purchase 1/0 Ilsco or Panduit copper pigtail adapters to make the connection
into the terminals of the inverters, but they are $10 to $14 each, and we
need eight of them.
Is using doubled up #4 or #2 the only solution? Are there any other
suggestions that will allow us to use the 1/0 X-Flex?
Thank you,
Allan
-
Allan Sindelar
mailto:al...@positiveenergysolar.com al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com http://www.positiveenergysolar.com/
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org