Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread August Goers
Hi Mac,

We use wireway "gutters" all the time. Our supplier mostly sends us Hoffman
brand wireways and they also sell a barrier kit:

Here is an example of a barrier and a 4"x4"x24" wireway, you'd need to spec
out the dimensions you need for your project:

https://hoffman.nvent.com/en-us/products/barrier-kit-bolt/encf44bk60

https://hoffman.nvent.com/en-us/products/straight-section-lay-flat-cover-type-1/encf44t124gvp

August
Luminalt




On Mon, Feb 1, 2021 at 4:12 PM Dave Angelini Offgrid Solar <
offgridso...@sti.net> wrote:

> Not a day for me.
>
> I do not care if it is UL listed or not. The Schneider PDP is UL also. Not
> high reliability in my opinion! Especially at 600vdc as there is not disco
> that will fit in the load center or PDP that I would trust. We all have our
> requirements and they can easily exceed UL !
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ 
> e-mail  offgridso...@sti.net 
> text 209 813 0060*
>
> On Mon, 1 Feb 2021 19:06:10 -0500, Ray  wrote:
>
> On both Outback and Midnites's AC/DC Load centers, they just have separate
> areas, but there is no partition, or anything like that. They are UL
> listed.  I don't do GT, so I don't really deal with this issue outside of
> the E panel, but if it were me, I'd just zip tie the PV wires together, put
> labeling on them so that it was clear they were PV conductors, and call it
> a day.
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 2/1/21 6:55 PM, Dave Angelini Offgrid Solar wrote:
>
> I land 600vdc PV into the Mppt/Mppt's only.  I never mix 600vdc with
> anything except SPD/disco ever!
>
> Just not that hard and for offgrid, standard practice for reliability.
> Same with 150vdc, I never get it into the PDP and disco it up stream form
> mppt.
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ 
> e-mail  offgridso...@sti.net 
> text 209 813 0060*
>
> On Mon, 1 Feb 2021 15:37:34 -0700, Mac Lewis 
>  wrote:
>
> Hello wrenches,
>
> What are folks using for raceway partitions to comply with 690.31(B) when
> running AC/DC and batteries conductors through a common gutter?  Is there a
> product or just something made by the installer?  These multiport inverters
> make it difficult not to use a gutter and have a clean installation.
>
> Thanks!
>
> --
>
>
>
> Mac Lewis
>
> "Yo solo sé que no sé nada." -Sócrates
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the 
> other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread Blake Gleason
Wire Loom/Split loom

Blake Gleason, PE
Director of Innovation
& Technical Excellence
Sun Light & Power

On Mon, Feb 1, 2021, 2:37 PM Mac Lewis  wrote:

> Hello wrenches,
>
> What are folks using for raceway partitions to comply with 690.31(B) when
> running AC/DC and batteries conductors through a common gutter?  Is there a
> product or just something made by the installer?  These multiport inverters
> make it difficult not to use a gutter and have a clean installation.
>
> Thanks!
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread Dave Angelini Offgrid Solar


Not a day for me. 

I do not care if it is UL listed or not. The
Schneider PDP is UL also. Not high reliability in my opinion! Especially at
600vdc as there is not disco that will fit in the load center or PDP that I
would trust. We all have our requirements and they can easily exceed UL ! 


Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridso...@sti.net
[2]
text 209 813 0060

On Mon, 1 Feb 2021 19:06:10 -0500, Ray  wrote:   


On both Outback and Midnites's AC/DC Load centers, they just have
separate areas, but there is no partition, or anything like that. They are
UL listed. I don't do GT, so I don't really deal with this issue outside of
the E panel, but if it were me, I'd just zip tie the PV wires together, put
labeling on them so that it was clear they were PV conductors, and call it
a day. 
Ray Walters
Remote Solar
303 505-8760
 On 2/1/21 6:55 PM, Dave
Angelini Offgrid Solar wrote:  

I land 600vdc PV into the Mppt/Mppt's
only. I never mix 600vdc with anything except SPD/disco ever! 

Just not
that hard and for offgrid, standard practice for reliability. Same with
150vdc, I never get it into the PDP and disco it up stream form mppt. 


Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [3]
e-mail offgridso...@sti.net
[4]
text 209 813 0060

On Mon, 1 Feb 2021 15:37:34 -0700, Mac Lewis  [5]
wrote:  Hello wrenches,   What are folks using for raceway partitions to
comply with 690.31(B) when running AC/DC and batteries conductors through a
common gutter? Is there a product or just something made by the installer?
These multiport inverters make it difficult not to use a gutter and have a
clean installation.Thanks!
   -- 
Mac Lewis

"Yo solo sé que no
sé nada." -Sócrates


___
List sponsored by Redwood
Alliance

List Address: RE-wrenches@lists.re-wrenches.org [6]

Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[7]

There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[8]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[9]

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
[10]

Check out or update participant
bios:
http://www.members.re-wrenches.org [11]

  

Links:
--
[1]
http://members.sti.net/offgridsolar/
[2] mailto:offgridso...@sti.net
[3]
http://members.sti.net/offgridsolar/
[4] mailto:offgridso...@sti.net
[5]
mailto:maclew...@gmail.com
[6] mailto:RE-wrenches@lists.re-wrenches.org
[7]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[8]
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[9]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[10]
http://www.re-wrenches.org/etiquette.htm
[11]
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread Ray
On both Outback and Midnites's AC/DC Load centers, they just have 
separate areas, but there is no partition, or anything like that. They 
are UL listed.  I don't do GT, so I don't really deal with this issue 
outside of the E panel, but if it were me, I'd just zip tie the PV wires 
together, put labeling on them so that it was clear they were PV 
conductors, and call it a day.


Ray Walters
Remote Solar
303 505-8760

On 2/1/21 6:55 PM, Dave Angelini Offgrid Solar wrote:


I land 600vdc PV into the Mppt/Mppt's only.  I never mix 600vdc with 
anything except SPD/disco ever!


Just not that hard and for offgrid, standard practice for reliability. 
Same with 150vdc, I never get it into the PDP and disco it up stream 
form mppt.


  
*Dave Angelini Offgrid Solar "we go where powerlines don't" 
http://members.sti.net/offgridsolar/ 
 e-mail offgridso...@sti.net 
 text 209 813 0060*


On Mon, 1 Feb 2021 15:37:34 -0700, Mac Lewis  wrote:


Hello wrenches,
What are folks using for raceway partitions to comply with 690.31(B) 
when running AC/DC and batteries conductors through a common gutter?  
Is there a product or just something made by the installer?  These 
multiport inverters make it difficult not to use a gutter and have a 
clean installation.

Thanks!
--
Mac Lewis

"Yo solo sé que no sé nada." -Sócrates



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread Dave Angelini Offgrid Solar


I land 600vdc PV into the Mppt/Mppt's only. I never mix 600vdc with
anything except SPD/disco ever! 

Just not that hard and for offgrid,
standard practice for reliability. Same with 150vdc, I never get it into
the PDP and disco it up stream form mppt.  

Dave Angelini Offgrid
Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
[1]
e-mail offgridso...@sti.net [2]
text 209 813 0060

On Mon, 1 Feb 2021
15:37:34 -0700, Mac Lewis  wrote:  Hello wrenches,   What are folks using
for raceway partitions to comply with 690.31(B) when running AC/DC and
batteries conductors through a common gutter? Is there a product or just
something made by the installer? These multiport inverters make it
difficult not to use a gutter and have a clean installation.Thanks!
  
-- 
Mac Lewis

"Yo solo sé que no sé nada." -Sócrates   


Links:
--
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridso...@sti.net
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread William Miller
Mac, Wrenches:



I hope y’all can keep a secret:  I admit I have been getting away without
partitioning due to ignorance on the part of the local inspectors.  I do
try to follow the letter of the code, but I have not seen the safety hazard
presented by not partitioning.  Does anyone know why this requirement might
make sense?



However when I am called on it, I sleeve the PV conductors in some
appropriately sized NMLT inside of the gutter. We have also run bonded EMT
inside of a gutter in the past to meet separation requirements.  The nice
thing about this plan is crossing types of conductors inside the gutter is
not the huge issue I imagine it could be.



If you desire 100% coverage you size the NMLT to slip inside of the conduit
entering the gutter for a short distance.  Alternatively, we thread a rigid
coupler on the inside of the fitting that enters your gutter and thread up
an NMLT or other appropriate conduit connector onto that coupling inside of
the gutter.



Seems one of these methods should make your inspector happy and require
minimal fabrication.



See photo below for an example:





I hope there is something here that helps you out.



William Miller

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Mac Lewis
*Sent:* Monday, February 1, 2021 2:38 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Raceway Partitions or Barrier in Gutters



Hello wrenches,



What are folks using for raceway partitions to comply with 690.31(B) when
running AC/DC and batteries conductors through a common gutter?  Is there a
product or just something made by the installer?  These multiport inverters
make it difficult not to use a gutter and have a clean installation.



Thanks!



-- 







Mac Lewis

"Yo solo sé que no sé nada." *-Sócrates*
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Raceway Partitions or Barrier in Gutters

2021-02-01 Thread Mac Lewis
Hello wrenches,

What are folks using for raceway partitions to comply with 690.31(B) when
running AC/DC and batteries conductors through a common gutter?  Is there a
product or just something made by the installer?  These multiport inverters
make it difficult not to use a gutter and have a clean installation.

Thanks!

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org