Re: [RE-wrenches] Rapid shutdown questions

2014-08-31 Thread jay peltz
HI Dan,

If you are doing 24v battery or below, you should be able to ignore the battery 
rapid shutdown part.
IE under 30v

jay

peltz power

On Aug 30, 2014, at 2:04 PM, Dan Fink wrote:

 Dave; I feel your pain as do many others.
 I feel like I've been Rick-rolled on the whole 690.12 thing. As a 
 firefighter, I thought rapid shutdown was a great idea for roof mounted 
 arrays. Shut down fast from a central location on the ground, get up on the 
 roof, do what needs to be done, fast and no worries other than the fire 
 itself.
 
 But disconnects hanging 15 feet in the air? Allowed to mount them in the 
 attic through a locked door to a disused lavatory behind a file cabinet 
 labeled beware of the leopard? - meets code.
 Rapid shutdown for ground mount arrays? Just walk over to the danged thing 
 and throw the clearly-labeled disconnects, the central signage told you where 
 they are. Problem solved.
 All just plain silly, counterproductive and expensive for the homeowner. As I 
 work exclusively with off-grid systems, most of them ranging from small to 
 tiny, I've been seeing their potential client's eyes go wide as dinner plates 
 when I inform them By the way, Colorado just adopted NEC 2014, and it'll be 
 an extra $1500 to comply, sorry that's a 33% increase in your system 
 cost..
 What's happening in the real world is folks getting the household 120/240 AC 
 wiring signed off as powered by gasoline generator and they do the solar 
 later, and change the gate combo so the inspector can't come back. Now 
 *that's* counterproductive.
 
 Robin, glad to hear clarifications are coming in 2017. 
 
 Dan Fink
 Buckville Energy
 IREC Certified Instructor™ - PV Installation Professional and Small Wind 
 Installer
 970.672.4342
 
  
 
 
 On Fri, Aug 29, 2014 at 11:08 AM, Dave Click davecl...@fsec.ucf.edu wrote:
 While I share Robin's optimism, I should also note the NEC 2017 690.12 
 committee referred to is not the code making panel. While it does have (at 
 least) one firefighter representative among a majority of PV industry 
 personnel, there's no guarantee that the Code Making Panel approves this 
 committee's proposal. There could very well be a competing proposal from 
 firefighters that requires cell-level shutdown every time a red truck drives 
 within 1/4 mile of an array, because SAFETY!
 
 DKC
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rapid shutdown questions

2014-08-31 Thread Drake

Hello Robin and boB.

Ryan’s Midnite video of the Birdhouse and rapid 
shutdown disconnects is amazing. It does look 
like you are producing a means of implementing this new code rule.


In many situations, the rapid shutdown 
requirement certainly makes sense. In a large 
system where high voltages and currents are 
present over large areas of solar array, major 
safety features need to be in place. The extra 
cost of the rapid shutdown equipment and its 
installation likely wouldn't produce much of an 
obstacle to the budget of a major commercial installation.


A very nice feature of today’s lower module 
prices is that many people who really want PV, 
but have never been able to afford it, can now 
have a system. New requirements are eroding this new found ability.


I would like to suggest the use of hazard-based 
criteria to decide if rapid shutdown is to be 
required. A small cabin system with 750 W of PV, 
a Kid charge control, and a couple of L-16 
batteries should clearly be excused from any 
rapid shutdown requirement. The system is easy to 
understand, and can be disabled quickly.


The requirement should be applied only to systems 
that have a large amount of power. The level of 
hazard could be evaluated for different 
scenarios. What is the demonstrated hazard of a 
9.6 kW system feeding a pair of Classics and a 
fused battery bank? How many problems have been 
reported with properly installed systems of this 
size? What is the arc potential?


Please keep in mind that a standard 120/240 V 
grid connection can have an open wire running 10 
feet above the yard, which can run as much as 25 
feet down the side of a house, in unprotected 
Service Entrance Cable. This wire may have a 
10,000 Amp (or greater) short circuit current at 
240 V­and this wire can't be shut 
off.  Therefore, 2,400 kW is available! Why can't 
a few kW of PV be run down the side of a house in metal conduit?



What are the statistics that demonstrate that 
small PV systems are significant safety hazards? 
Are there real statistics, rather than anecdotal 
events? There were an estimated 
http://www.thecarconnection.com/news/1090330_early-estimate-35200-traffic-deaths-in-2013-a-drop-of-3-from-201232,500 
traffic deaths in 2013.  How many people were 
killed by solar electric systems that year?


How about an exemption for residential systems 
under 12 kW? This size system has a power 
potential of 1/200th of that of the wire that 
runs 10 feet over your back yard with no protection­which you can't shut off!


Given the good safety record of PV, maybe we can 
keep existing standards for smaller systems­ones 
that won't add unnecessary expenses that keep 
these systems from ever being built.


Drake

Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
http://athens-electric.com/http://athens-electric.com/



At 03:16 PM 8/28/2014, you wrote:


[Robin chiming in, below]

Dan, The 2014 690.12 is worded poorly. That is 
why there is so much confusion. MidNite Solar is 
sitting on the NEC2017 690.12 committee. There 
are a lot of smart people in this group. The 
2017 version says ALL PV SYSTEMS, not just on or 
in buildings. The 10 foot space gets reduced to 
1 foot like it always should have been.


There will be a lot of other clarifications too. 
The systems that use shunt trip breakers [with 
Remote Trip coil] and contactors are for string 
inverters. Shunt trip breakers will be used for 
battery based systems and grid tie inverters 
with an AC outlet like the SMA TL series. Micro 
inverters do not require anything like what our 
system is. They can use the existing backfed 
breaker in the main distribution box as long as 
it is labeled accordingly.  Solar Edge has a 
system that meets the Rapid Shutdown requirement also.


The UL standard for Rapid Shutdown has been 
written. It is going to go out to a task force 
for review, comment and changes soon. MidNite 
Solar will be on that task force. The MidNite 
Birdhouse is going through UL now and is being 
evaluated to this new standard. All of our 
disconnecting combiners and SOBs are already ETL 
listed. UL is modifying the new Rapid Shutdown 
Draft standard as they come upon things in the 
Birdhouse that the standard didn't consider. One 
of the biggies that has not been sorted out is a 
requirement for feedback. Contactors, power 
supplies and a switch will meet the requirement 
for 2014. The issue with this type of system is 
that when you push the button to turn off the 
contactors, there is no way to tell that they 
actually opened up. Without feedback that 
verifies that the contactors are actually open, 
you are taking a chance with people's lives. 
600VDC contactors can weld themselves closed. If 
first responders don't trust the Rapid Shutdown 
system, they are going to let the house burn. We 
do have feedback on the birdhouse system. 
Contactors do not have feedback. It is not 
simple to add this feature to 

Re: [RE-wrenches] Rapid shutdown questions

2014-08-30 Thread Dan Fink
Dave; I feel your pain as do many others.
I feel like I've been Rick-rolled on the whole 690.12 thing. As a
firefighter, I thought rapid shutdown was a great idea for roof mounted
arrays. Shut down fast from a central location on the ground, get up on the
roof, do what needs to be done, fast and no worries other than the fire
itself.

But disconnects hanging 15 feet in the air? Allowed to mount them in the
attic through a locked door to a disused lavatory behind a file cabinet
labeled beware of the leopard? - meets code.
Rapid shutdown for ground mount arrays? Just walk over to the danged thing
and throw the clearly-labeled disconnects, the central signage told you
where they are. Problem solved.
All just plain silly, counterproductive and expensive for the homeowner. As
I work exclusively with off-grid systems, most of them ranging from small
to tiny, I've been seeing their potential client's eyes go wide as dinner
plates when I inform them By the way, Colorado just adopted NEC 2014, and
it'll be an extra $1500 to comply, sorry that's a 33% increase in your
system cost..
What's happening in the real world is folks getting the household 120/240
AC wiring signed off as powered by gasoline generator and they do the
solar later, and change the gate combo so the inspector can't come back.
Now *that's* counterproductive.

Robin, glad to hear clarifications are coming in 2017.

Dan Fink
Buckville Energy
IREC Certified Instructor™ - PV Installation Professional and Small Wind
Installer
970.672.4342




On Fri, Aug 29, 2014 at 11:08 AM, Dave Click davecl...@fsec.ucf.edu wrote:

 While I share Robin's optimism, I should also note the NEC 2017 690.12
 committee referred to is not the code making panel. While it does have (at
 least) one firefighter representative among a majority of PV industry
 personnel, there's no guarantee that the Code Making Panel approves this
 committee's proposal. There could very well be a competing proposal from
 firefighters that requires cell-level shutdown every time a red truck
 drives within 1/4 mile of an array, because SAFETY!

 DKC


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rapid shutdown questions

2014-08-29 Thread Dave Click
While I share Robin's optimism, I should also note the NEC 2017 690.12 
committee referred to is not the code making panel. While it does have 
(at least) one firefighter representative among a majority of PV 
industry personnel, there's no guarantee that the Code Making Panel 
approves this committee's proposal. There could very well be a competing 
proposal from firefighters that requires cell-level shutdown every time 
a red truck drives within 1/4 mile of an array, because SAFETY!


DKC


On 2014/8/28, 15:16, b...@midnitesolar.com wrote:


[Robin chiming in, below]

Dan, The 2014 690.12 is worded poorly. That is why there is so much 
confusion. MidNite Solar is sitting on the NEC2017 690.12 committee. 
There are a lot of smart people in this group. The 2017 version says 
ALL PV SYSTEMS, not just on or in buildings. The 10 foot space gets 
reduced to 1 foot like it always should have been.


There will be a lot of other clarifications too. The systems that use 
shunt trip breakers [with Remote Trip coil] and contactors are for 
string inverters. Shunt trip breakers will be used for battery based 
systems and grid tie inverters with an AC outlet like the SMA TL 
series. Micro inverters do not require anything like what our system 
is. They can use the existing backfed breaker in the main distribution 
box as long as it is labeled accordingly.  Solar Edge has a system 
that meets the Rapid Shutdown requirement also.


The UL standard for Rapid Shutdown has been written. It is going to go 
out to a task force for review, comment and changes soon. MidNite 
Solar will be on that task force. The MidNite Birdhouse is going 
through UL now and is being evaluated to this new standard. All of our 
disconnecting combiners and SOBs are already ETL listed. UL is 
modifying the new Rapid Shutdown Draft standard as they come upon 
things in the Birdhouse that the standard didn't consider. One of the 
biggies that has not been sorted out is a requirement for feedback. 
Contactors, power supplies and a switch will meet the requirement for 
2014. The issue with this type of system is that when you push the 
button to turn off the contactors, there is no way to tell that they 
actually opened up. Without feedback that verifies that the contactors 
are actually open, you are taking a chance with people's lives. 600VDC 
contactors can weld themselves closed. If first responders don't trust 
the Rapid Shutdown system, they are going to let the house burn. We do 
have feedback on the birdhouse system. Contactors do not have 
feedback. It is not simple to add this feature to a contactor based 
system.


Installing a switch 15 feet up on the side of a building or on the 
roof is not the intent of 690.12. This will not be allowed in 2017. 
The exact placement of the initiating device (Birdhouse) is not cast 
in concrete due to the differences in where main panel boards are 
located, but it will not allow things like mentioned here 15 feet up 
in the air or in the attic or on the roof.


Battery based systems are the most complicated to meet 690.12. The NEC 
committee is deferring a lot of this to MidNite as we are already 
doing it and have gone over all the different ways things can go 
wrong. We started designing our system right after the Bakersfield 
fire 5 years ago. The Bakersfield fire is what got the NEC to require 
disconnecting combiners. We couldn't imagine why a fire fighter would 
want to get up on the roof of a burning building to look for a 
combiner? This is why we started the birdhouse project way before 
anyone ever thought of the words Rapid Shutdown. Turns out this was a 
good thing since battery backed up systems make the issue ten times 
more complicated. We spent years working out issues and there were 
lots of them that required a start from scratch approach numerous times.


AC coupling to a battery based inverter does not automatically meet 
690.12 as someone mentioned in this thread. That battery based 
inverter must also be shut off. The micro inverters would of course 
shut off when the utility is shut down, but the battery based 
inverters job is to keep things powered up when the grid is down. So 
the battery based inverter has to be shut down also.


 It would also make sense to shut off an auto start generator with the 
Rapid Shutdown button. Some generators are designed to start up upon 
loss of grid. Once the first responders have the meter pulled, that 
could start up a generator and cause risk of shock. If the generator 
is designed to start on low battery, it could start a day later when 
the fire has been put out, but that also poses risk of electrical 
shock when unexpectedly the part of the house that is left all of a 
sudden comes live with juice.


The cost for a Rapid Shutdown system will vary a lot depending on what 
you want to shut down. You do not need to run conduit to all the boxes 
and switches. There is 600V Cat5e 90C USE-2 cable available that will 
suffice. I don't see a 

Re: [RE-wrenches] Rapid shutdown questions

2014-08-28 Thread b...@midnitesolar.com


[Robin chiming in, below]

Dan, The 2014 690.12 is worded poorly. That is why there is so much 
confusion. MidNite Solar is sitting on the NEC2017 690.12 committee. 
There are a lot of smart people in this group. The 2017 version says ALL 
PV SYSTEMS, not just on or in buildings. The 10 foot space gets reduced 
to 1 foot like it always should have been.


There will be a lot of other clarifications too. The systems that use 
shunt trip breakers [with Remote Trip coil] and contactors are for 
string inverters. Shunt trip breakers will be used for battery based 
systems and grid tie inverters with an AC outlet like the SMA TL series. 
Micro inverters do not require anything like what our system is. They 
can use the existing backfed breaker in the main distribution box as 
long as it is labeled accordingly.  Solar Edge has a system that meets 
the Rapid Shutdown requirement also.


The UL standard for Rapid Shutdown has been written. It is going to go 
out to a task force for review, comment and changes soon. MidNite Solar 
will be on that task force. The MidNite Birdhouse is going through UL 
now and is being evaluated to this new standard. All of our 
disconnecting combiners and SOBs are already ETL listed. UL is modifying 
the new Rapid Shutdown Draft standard as they come upon things in the 
Birdhouse that the standard didn't consider. One of the biggies that has 
not been sorted out is a requirement for feedback. Contactors, power 
supplies and a switch will meet the requirement for 2014. The issue with 
this type of system is that when you push the button to turn off the 
contactors, there is no way to tell that they actually opened up. 
Without feedback that verifies that the contactors are actually open, 
you are taking a chance with people's lives. 600VDC contactors can weld 
themselves closed. If first responders don't trust the Rapid Shutdown 
system, they are going to let the house burn. We do have feedback on the 
birdhouse system. Contactors do not have feedback. It is not simple to 
add this feature to a contactor based system.


Installing a switch 15 feet up on the side of a building or on the roof 
is not the intent of 690.12. This will not be allowed in 2017. The exact 
placement of the initiating device (Birdhouse) is not cast in concrete 
due to the differences in where main panel boards are located, but it 
will not allow things like mentioned here 15 feet up in the air or in 
the attic or on the roof.


Battery based systems are the most complicated to meet 690.12. The NEC 
committee is deferring a lot of this to MidNite as we are already doing 
it and have gone over all the different ways things can go wrong. We 
started designing our system right after the Bakersfield fire 5 years 
ago. The Bakersfield fire is what got the NEC to require disconnecting 
combiners. We couldn't imagine why a fire fighter would want to get up 
on the roof of a burning building to look for a combiner? This is why we 
started the birdhouse project way before anyone ever thought of the 
words Rapid Shutdown. Turns out this was a good thing since battery 
backed up systems make the issue ten times more complicated. We spent 
years working out issues and there were lots of them that required a 
start from scratch approach numerous times.


AC coupling to a battery based inverter does not automatically meet 
690.12 as someone mentioned in this thread. That battery based inverter 
must also be shut off. The micro inverters would of course shut off when 
the utility is shut down, but the battery based inverters job is to keep 
things powered up when the grid is down. So the battery based inverter 
has to be shut down also.


 It would also make sense to shut off an auto start generator with the 
Rapid Shutdown button. Some generators are designed to start up upon 
loss of grid. Once the first responders have the meter pulled, that 
could start up a generator and cause risk of shock. If the generator is 
designed to start on low battery, it could start a day later when the 
fire has been put out, but that also poses risk of electrical shock when 
unexpectedly the part of the house that is left all of a sudden comes 
live with juice.


The cost for a Rapid Shutdown system will vary a lot depending on what 
you want to shut down. You do not need to run conduit to all the boxes 
and switches. There is 600V Cat5e 90C USE-2 cable available that will 
suffice. I don't see a system being installed for less than $1500 though.


Robin Gudgels



On 8/27/2014 8:45 AM, Dan Fink wrote:

Hi Mac, all;
Since Colorado just adopted NEC2014 July 1, I have not heard any AHJ 
stories yet. But look at 690.12 (1):
Requirements for controlled conductors shall apply only to PV system 
conductors of more than 5 ft in length inside a building, OR more than 
10 ft from a PV array.

(my emphasis on OR)

I interpret this to mean that if a ground mount array is more than 10 
ft from the building, then any PV circuits that run up the 

Re: [RE-wrenches] Rapid shutdown questions

2014-08-28 Thread Ray Walters
So this would make sense that this Rapid Shut down provision would cover 
all generator backup systems too, not just solar.
Considering auto start backup generators have been around for many 
decades, I have a few questions:
1) Does NEC 2014 require Rapid shutdown for all generator systems, or is 
solar once again being singled out for additional requirements not 
applied to everyone else?
2) What is the history of fire fighting and backup generators?  It seems 
that there would be much more long term experience, than a hand full of 
incidents in the solar industry.
3) What about portable generators, and folks back feeding the grid or 
house with little to no protection at all.  Are there safety precautions 
that fire fighters take to make sure a neighbor isn't powering up lines 
down the street?  I've seen too many male to male extension cords, so I 
know this is real issue, that can't be prevented by the NEC code alone.  
Basically any idiot can go to Home depot and create a very dangerous 
situation quickly.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 8/28/2014 1:16 PM, b...@midnitesolar.com wrote:


 It would also make sense to shut off an auto start generator with the 
Rapid Shutdown button. Some generators are designed to start up upon 
loss of grid. Once the first responders have the meter pulled, that 
could start up a generator and cause risk of shock.

Robin Gudgels




___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rapid shutdown questions

2014-08-27 Thread Will White
Our experience in MA with rapid shutdown unfortunately varies with AHJ.  Some 
are letting us put an Eaton NEMA 4 disconnect on the roof next to the array.  
Some are letting us put a disconnect in an accessible attic within 5’ of the 
penetration.  Some are requiring the Midnight Birdhouse remote switch which is 
expensive.

Rapid shutdown doesn’t apply to pole or ground mounts.

Hope this helps.

Will

Will White
Operations Manager - New England
RGS Energy


64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980

RGSEnergy.comhttp://www.rgsenergy.com/ | 
william.wh...@rgsenergy.commailto:william.wh...@rgsenergy.com

Confidentiality Note: This e-mail message may contain confidential or legally 
privileged information and is intended only for the use of the intended 
recipient(s). Any unauthorized disclosure, dissemination, distribution, copying 
or the taking of any action in reliance on the information herein is 
prohibited. E-mails are not secure and cannot be guaranteed to be error free as 
they can be intercepted, amended, or contain viruses. Anyone who communicates 
with us by e-mail is deemed to have accepted these risks. RGS Energy is not 
responsible for errors or omissions in this message and denies any 
responsibility for any damage arising from the use of e-mail. Any opinion and 
other statement contained in this message and any attachment are solely those 
of the author and do not necessarily represent those of the company.






From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Mac Lewis
Sent: Wednesday, August 27, 2014 8:32 AM
To: RE-wrenches
Subject: [RE-wrenches] Rapid shutdown questions

Hello wrenches,

I am still trying to wrap my head around how to comply with rapid shutdown in 
off-grid and hybrid situations.  I've got a few questions that maybe you can 
help with.

1.  What is a (currently listed) rapid shutdown system that will accommodate 8 
strings?  I know I can do this with Midnite combiners but as I understand these 
aren't listed yet.
2.  On a remote pole mount, does rapid shutdown apply?  If the intent is to 
isolate a safe zone around an array for fire fighting, it seems as though a 
standard pole mounted DC disconnect can cover this concern.
3.  I estimate on a typical hybrid installation, rapid shutdown will cost at 
least $3000 to implement. This includes remote shunt trip battery breakers, 
contactors on PV side of charge controller and roof combiners, and running 
control cable from remote disconnect to all locations.  As of now, this would 
also require me to modify listed interconnection equipment.  Is this what 
others are finding?
4.  AC coupling with microinverters may be the easiest way to comply with most 
of these requirements.  However, this doesn't seem like a great alternative to 
the standard charge controller installation in an off-grid system.

Thanks in advance for your thoughts


--



Mac Lewis

Yo solo sé que no sé nada. -Sócrates
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rapid shutdown questions

2014-08-27 Thread Mac Lewis
Hi Will,

Yes I'm sure AHJ's will be all over the place for a while here in Colorado.
 To clarify, is this a manual disconnect in the attic?  If so, that is
really missing the whole idea of a rapid shutdown.

Thanks


On Wed, Aug 27, 2014 at 7:47 AM, Will White william.wh...@rgsenergy.com
wrote:

  Our experience in MA with rapid shutdown unfortunately varies with AHJ.
 Some are letting us put an Eaton NEMA 4 disconnect on the roof next to the
 array.  Some are letting us put a disconnect in an accessible attic within
 5’ of the penetration.  Some are requiring the Midnight Birdhouse remote
 switch which is expensive.



 Rapid shutdown doesn’t apply to pole or ground mounts.



 Hope this helps.



 Will



 *Will White*
 Operations Manager - New England

 RGS Energy

 64 Main St. |Montpelier, VT 05602
 tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980

 *RGSEnergy.com http://www.rgsenergy.com/ **|
 william.wh...@rgsenergy.com william.wh...@rgsenergy.com *

 *Confidentiality Note: *This e-mail message may contain confidential or
 legally privileged information and is intended only for the use of the
 intended recipient(s). Any unauthorized disclosure, dissemination,
 distribution, copying or the taking of any action in reliance on the
 information herein is prohibited. E-mails are not secure and cannot be
 guaranteed to be error free as they can be intercepted, amended, or contain
 viruses. Anyone who communicates with us by e-mail is deemed to have
 accepted these risks. RGS Energy is not responsible for errors or omissions
 in this message and denies any responsibility for any damage arising from
 the use of e-mail. Any opinion and other statement contained in this
 message and any attachment are solely those of the author and do not
 necessarily represent those of the company.









 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
 Behalf Of *Mac Lewis
 *Sent:* Wednesday, August 27, 2014 8:32 AM
 *To:* RE-wrenches
 *Subject:* [RE-wrenches] Rapid shutdown questions



 Hello wrenches,



 I am still trying to wrap my head around how to comply with rapid shutdown
 in off-grid and hybrid situations.  I've got a few questions that maybe you
 can help with.



 1.  What is a (currently listed) rapid shutdown system that will
 accommodate 8 strings?  I know I can do this with Midnite combiners but as
 I understand these aren't listed yet.

 2.  On a remote pole mount, does rapid shutdown apply?  If the intent is
 to isolate a safe zone around an array for fire fighting, it seems as
 though a standard pole mounted DC disconnect can cover this concern.

 3.  I estimate on a typical hybrid installation, rapid shutdown will cost
 at least $3000 to implement. This includes remote shunt trip battery
 breakers, contactors on PV side of charge controller and roof combiners,
 and running control cable from remote disconnect to all locations.  As of
 now, this would also require me to modify listed interconnection equipment.
  Is this what others are finding?

 4.  AC coupling with microinverters may be the easiest way to comply with
 most of these requirements.  However, this doesn't seem like a great
 alternative to the standard charge controller installation in an off-grid
 system.



 Thanks in advance for your thoughts





 --







 Mac Lewis

 Yo solo sé que no sé nada. *-Sócrates*

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org





-- 



Mac Lewis

*Yo solo sé que no sé nada. -Sócrates*
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rapid shutdown questions

2014-08-27 Thread Will White
That’s correct it’s a manual disconnect and I agree it totally defeats the 
purpose but some AHJ’s are accepting that it’s within 5’ of entering the 
building and nowhere in the code does it say it has to be readily accessible.

We had one AHJ make us put the disconnect on the side of the house about 15’ 
feet up.  I believe that photo was in the last issue of SolarPro.  It was the 
dumbest thing we’ve ever had to do and it looks ridiculous but that’s what the 
inspector wanted.

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Mac Lewis
Sent: Wednesday, August 27, 2014 10:02 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Rapid shutdown questions

Hi Will,

Yes I'm sure AHJ's will be all over the place for a while here in Colorado.  To 
clarify, is this a manual disconnect in the attic?  If so, that is really 
missing the whole idea of a rapid shutdown.

Thanks

On Wed, Aug 27, 2014 at 7:47 AM, Will White 
william.wh...@rgsenergy.commailto:william.wh...@rgsenergy.com wrote:
Our experience in MA with rapid shutdown unfortunately varies with AHJ.  Some 
are letting us put an Eaton NEMA 4 disconnect on the roof next to the array.  
Some are letting us put a disconnect in an accessible attic within 5’ of the 
penetration.  Some are requiring the Midnight Birdhouse remote switch which is 
expensive.

Rapid shutdown doesn’t apply to pole or ground mounts.

Hope this helps.

Will

Will White
Operations Manager - New England
RGS Energy


64 Main St. |Montpelier, VT 05602
tel 802.223.7804tel:802.223.7804 | mobile 802.234.3167tel:802.234.3167 | 
fax 802.223.8980tel:802.223.8980

RGSEnergy.comhttp://www.rgsenergy.com/ | 
william.wh...@rgsenergy.commailto:william.wh...@rgsenergy.com

Confidentiality Note: This e-mail message may contain confidential or legally 
privileged information and is intended only for the use of the intended 
recipient(s). Any unauthorized disclosure, dissemination, distribution, copying 
or the taking of any action in reliance on the information herein is 
prohibited. E-mails are not secure and cannot be guaranteed to be error free as 
they can be intercepted, amended, or contain viruses. Anyone who communicates 
with us by e-mail is deemed to have accepted these risks. RGS Energy is not 
responsible for errors or omissions in this message and denies any 
responsibility for any damage arising from the use of e-mail. Any opinion and 
other statement contained in this message and any attachment are solely those 
of the author and do not necessarily represent those of the company.





From: RE-wrenches 
[mailto:re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org]
 On Behalf Of Mac Lewis
Sent: Wednesday, August 27, 2014 8:32 AM
To: RE-wrenches
Subject: [RE-wrenches] Rapid shutdown questions

Hello wrenches,

I am still trying to wrap my head around how to comply with rapid shutdown in 
off-grid and hybrid situations.  I've got a few questions that maybe you can 
help with.

1.  What is a (currently listed) rapid shutdown system that will accommodate 8 
strings?  I know I can do this with Midnite combiners but as I understand these 
aren't listed yet.
2.  On a remote pole mount, does rapid shutdown apply?  If the intent is to 
isolate a safe zone around an array for fire fighting, it seems as though a 
standard pole mounted DC disconnect can cover this concern.
3.  I estimate on a typical hybrid installation, rapid shutdown will cost at 
least $3000 to implement. This includes remote shunt trip battery breakers, 
contactors on PV side of charge controller and roof combiners, and running 
control cable from remote disconnect to all locations.  As of now, this would 
also require me to modify listed interconnection equipment.  Is this what 
others are finding?
4.  AC coupling with microinverters may be the easiest way to comply with most 
of these requirements.  However, this doesn't seem like a great alternative to 
the standard charge controller installation in an off-grid system.

Thanks in advance for your thoughts


--



Mac Lewis

Yo solo sé que no sé nada. -Sócrates

___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.orgmailto:RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htmhttp://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.orghttp://www.members.re-wrenches.org




--



Mac Lewis

Yo solo sé que no sé nada. -Sócrates
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re

Re: [RE-wrenches] Rapid shutdown questions

2014-08-27 Thread Brian Mehalic
-wrenches] Rapid shutdown questions



 Hello wrenches,



 I am still trying to wrap my head around how to comply with rapid
 shutdown in off-grid and hybrid situations.  I've got a few questions that
 maybe you can help with.



 1.  What is a (currently listed) rapid shutdown system that will
 accommodate 8 strings?  I know I can do this with Midnite combiners but as
 I understand these aren't listed yet.

 2.  On a remote pole mount, does rapid shutdown apply?  If the intent is
 to isolate a safe zone around an array for fire fighting, it seems as
 though a standard pole mounted DC disconnect can cover this concern.

 3.  I estimate on a typical hybrid installation, rapid shutdown will cost
 at least $3000 to implement. This includes remote shunt trip battery
 breakers, contactors on PV side of charge controller and roof combiners,
 and running control cable from remote disconnect to all locations.  As of
 now, this would also require me to modify listed interconnection equipment.
  Is this what others are finding?

 4.  AC coupling with microinverters may be the easiest way to comply with
 most of these requirements.  However, this doesn't seem like a great
 alternative to the standard charge controller installation in an off-grid
 system.



 Thanks in advance for your thoughts





 --







 Mac Lewis

 Yo solo sé que no sé nada. *-Sócrates*

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org





 --



 Mac Lewis

 * Yo solo sé que no sé nada. -Sócrates *

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rapid shutdown questions

2014-08-27 Thread Dan Fink
Hi Mac, all;
Since Colorado just adopted NEC2014 July 1, I have not heard any AHJ
stories yet. But look at 690.12 (1):
Requirements for controlled conductors shall apply only to PV system
conductors of more than 5 ft in length inside a building, OR more than 10
ft from a PV array.
(my emphasis on OR)

I interpret this to mean that if a ground mount array is more than 10 ft
from the building, then any PV circuits that run up the outside of the
building from their trench  (for example to penetrate the wall to the power
center on the inside) must be controlled because they are on the
building. And even if you penetrated right from the trench into the crawl
space, then up to the power center on the inside wall, with less than 5 ft
distance, still needs to be controlled if the array is more than 10 feet
from the building because of that OR

The logic and safety advantage of this for firefighters is another topic
entirely. As a first-arriving firefighter, I would spot the PV racks on the
ground, walk over to them, and throw the disconnects on the nicely-labeled
combiner boxes located within 10 feet of the array.

All thoughts appreciated, still puzzling this out.

Dan Fink
Buckville Energy
Otherpower
NABCEP / IREC / ISPQ accredited Continuing Education Providers
970.672.4342
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org