Re: [RE-wrenches] SDHW and High Mains Pressure

2008-12-10 Thread jay peltz

Hi Peter,

There are some hi end units that are really nice.

Takagi, Rennai  are the two that come to mind that are really  
amazing.  They have digital remote controlls and are are designed to  
mounted outside, which saves a lot of

interior space, cost of reworking the flue etc.

Jay

Peltz power
On Dec 7, 2008, at 3:22 PM, Peter Parrish wrote:

We are getting ready to install a SDHW system for a customer and we  
looked at a number of things regarding his current set up. I just  
posted a question about tankless heaters but I wanted this query to  
be a separate one. The customer’s mains water pressure is 88 psi on  
a Saturday afternoon and some time over the next 18 hours, the  
pressure went as high as 96 psi. I understand that 80 psi is the  
high end of the safe range in general and that 96 psi on a regular  
basis can/will damage valves and possibly trigger T&P valves on  
water heaters.


At the recommendation of a plumber I know I looked into pressure  
reducers, specifically the Wilkins/Zurn line. All the Wilkins  
regulators produce zero pressure drop at zero flow. What good are  
these products in protecting plumbing systems from high mains  
pressures at night when pressures tend to be the highest and usage  
is at a minimum or even zero?


Are there products that will prevent system pressures from exceeding  
a set point (e.g. 60 psi) under any flow condition including zero?


- Peter
Peter T. Parrish, President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED]

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SDHW and High Mains Pressure

2008-12-08 Thread Peter Parrish
Great! I was looking at their Model 70 Spec sheet. I will go back and read
the specs on the Model 70 as well as the Model 500 more carefully. 

 

- Peter

 

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

  _  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Christopher
Freitas
Sent: Monday, December 08, 2008 10:42 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] SDHW and High Mains Pressure

 

All of the pressure reducers I have seen work at no pressure - I think you
are misreading the specification sheet - the zero drop at zero flow is
referring to pressure drop due to flow - not due to the function of the
regulator - its sort of like zero voltage drop at zero amps.

 

The spec sheet on the Wilkins model 500 does say "The assembly shall be of
the balanced piston design and shall reduce

pressure in both flow and no-flow conditions."  

 

I don't think they would sell many if they didn't reduce the pressure under
no-flow conditions.  

 

 

Christopher

 

 

Christopher Freitas

Director of Research and Development 

OutBack Power Systems, Inc.

 <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]

Tel 360 435 6030

Cell 360 202 4239

19009 62nd Ave NE 

Arlington WA 98223 USA

 <http://www.outbackpower.com/> www.outbackpower.com

  _  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Peter
Parrish
Sent: Sunday, December 07, 2008 3:22 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] SDHW and High Mains Pressure

 

We are getting ready to install a SDHW system for a customer and we looked
at a number of things regarding his current set up. I just posted a question
about tankless heaters but I wanted this query to be a separate one. The
customer's mains water pressure is 88 psi on a Saturday afternoon and some
time over the next 18 hours, the pressure went as high as 96 psi. I
understand that 80 psi is the high end of the safe range in general and that
96 psi on a regular basis can/will damage valves and possibly trigger T&P
valves on water heaters.

 

At the recommendation of a plumber I know I looked into pressure reducers,
specifically the Wilkins/Zurn line. All the Wilkins regulators produce zero
pressure drop at zero flow. What good are these products in protecting
plumbing systems from high mains pressures at night when pressures tend to
be the highest and usage is at a minimum or even zero?

 

Are there products that will prevent system pressures from exceeding a set
point (e.g. 60 psi) under any flow condition including zero?   

 

- Peter

Peter T. Parrish, President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

MESSAGE CONFIDENTIALITY NOTICE:

This message (including attachments) is covered by the Electronic
Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential,
and may also be protected by attorney-client or other privilege. If you
believe that it has been sent to you in error, please do not read it. If you
are not the intended recipient,you are hereby notified that any retention,
dissemination, distribution, or copying of this communication is strictly
prohibited.  Please reply to the sender that you have received the message
in error, then delete it. Thank you.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SDHW and High Mains Pressure

2008-12-08 Thread Christopher Freitas
All of the pressure reducers I have seen work at no pressure - I think
you are misreading the specification sheet - the zero drop at zero flow
is referring to pressure drop due to flow - not due to the function of
the regulator - its sort of like zero voltage drop at zero amps...

 

The spec sheet on the Wilkins model 500 does say "The assembly shall be
of the balanced piston design and shall reduce

pressure in both flow and no-flow conditions."  

 

I don't think they would sell many if they didn't reduce the pressure
under no-flow conditions.  

 

 

Christopher

 

 

Christopher Freitas

Director of Research and Development 

OutBack Power Systems, Inc.

[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> 

Tel 360 435 6030

Cell 360 202 4239

19009 62nd Ave NE 

Arlington WA 98223 USA

www.outbackpower.com <http://www.outbackpower.com/> 



From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Peter
Parrish
Sent: Sunday, December 07, 2008 3:22 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] SDHW and High Mains Pressure

 

We are getting ready to install a SDHW system for a customer and we
looked at a number of things regarding his current set up. I just posted
a question about tankless heaters but I wanted this query to be a
separate one. The customer's mains water pressure is 88 psi on a
Saturday afternoon and some time over the next 18 hours, the pressure
went as high as 96 psi. I understand that 80 psi is the high end of the
safe range in general and that 96 psi on a regular basis can/will damage
valves and possibly trigger T&P valves on water heaters.

 

At the recommendation of a plumber I know I looked into pressure
reducers, specifically the Wilkins/Zurn line. All the Wilkins regulators
produce zero pressure drop at zero flow. What good are these products in
protecting plumbing systems from high mains pressures at night when
pressures tend to be the highest and usage is at a minimum or even zero?

 

Are there products that will prevent system pressures from exceeding a
set point (e.g. 60 psi) under any flow condition including zero?   

 

- Peter

Peter T. Parrish, President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 


MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication 
Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be 
protected by attorney-client or other privilege. If you believe that it has 
been sent to you in error, please do not read it. If you are not the intended 
recipient,you are hereby notified that any retention, dissemination, 
distribution, or copying of this communication is strictly prohibited.  Please 
reply to the sender that you have received the message in error, then delete 
it. Thank you.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SDHW and High Mains Pressure

2008-12-08 Thread Peter Parrish
Dean,

 

Thanks for the info on the tankless water heater. However, when I looked up
the specs on the Watts regulator, I found the same behavior: zero pressure
drop at zero flow. So the Watts regulator will not solve the problem of high
water pressure at night (when there is zero or very little flow). 

 

Anyone else know of a control unit that can limit the water pressure (to say
60 psi) on the customer side under all flow conditions (including zero)?

 

- Peter

 

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

  _  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dean T.
Newberry
Sent: Sunday, December 07, 2008 4:18 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SDHW and High Mains Pressure

 

Hello Peter,
You want a Watts Regulator.

Here's the link: http://www.watts.com/pro/_products_sub.asp?catId=64
<http://www.watts.com/pro/_products_sub.asp?catId=64&parCat=285> &parCat=285


Good Luck

Peter Parrish wrote: 

We are getting ready to install a SDHW system for a customer and we looked
at a number of things regarding his current set up. I just posted a question
about tankless heaters but I wanted this query to be a separate one. The
customer's mains water pressure is 88 psi on a Saturday afternoon and some
time over the next 18 hours, the pressure went as high as 96 psi. I
understand that 80 psi is the high end of the safe range in general and that
96 psi on a regular basis can/will damage valves and possibly trigger T&P
valves on water heaters.

 

At the recommendation of a plumber I know I looked into pressure reducers,
specifically the Wilkins/Zurn line. All the Wilkins regulators produce zero
pressure drop at zero flow. What good are these products in protecting
plumbing systems from high mains pressures at night when pressures tend to
be the highest and usage is at a minimum or even zero?

 

Are there products that will prevent system pressures from exceeding a set
point (e.g. 60 psi) under any flow condition including zero?   

 

- Peter

Peter T. Parrish, President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

 





  _  



 
___
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 
  





-- 
Dean T. Newberry
Talbott Solar & Radiant Homes Inc.
430 D Street
Davis, CA 95616
 
T: 530 219-3606
F: 530 758-8187
E: [EMAIL PROTECTED]
W: http://www.TalbottSolar.com/
   http://www.TalbottRadiant.com/
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SDHW and High Mains Pressure

2008-12-07 Thread Dean T. Newberry




Hello Peter,
You want a Watts Regulator.

Here's the link: http://www.watts.com/pro/_products_sub.asp?catId=64&parCat=285


Good Luck

Peter Parrish wrote:

  
  
  
  
  We are getting
ready to install a SDHW
system for a customer and we looked at a number of things regarding his
current
set up. I just posted a question about tankless heaters but I wanted
this query
to be a separate one. The customer’s mains water pressure is 88 psi on
a
Saturday afternoon and some time over the next 18 hours, the pressure
went as
high as 96 psi. I understand that 80 psi is the high end of the safe
range in
general and that 96 psi on a regular basis can/will damage valves and
possibly
trigger T&P valves on water heaters.
   
  At the
recommendation of a plumber I know
I looked into pressure reducers, specifically the Wilkins/Zurn line.
All the
Wilkins regulators produce zero pressure drop at zero flow. What good
are these
products in protecting plumbing systems from high mains pressures at
night when
pressures tend to be the highest and usage is at a minimum or even zero?
   
  Are there
products that will prevent system
pressures from exceeding a set point (e.g. 60 psi) under any flow
condition including
zero?   
   
  - Peter
  
  Peter T.
Parrish, President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 
  
  
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  


-- 
Dean T. Newberry
Talbott Solar & Radiant Homes Inc.
430 D Street
Davis, CA 95616

T: 530 219-3606
F: 530 758-8187
E: [EMAIL PROTECTED]
W: http://www.TalbottSolar.com/
   http://www.TalbottRadiant.com/




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] SDHW and High Mains Pressure

2008-12-07 Thread Peter Parrish
We are getting ready to install a SDHW system for a customer and we looked
at a number of things regarding his current set up. I just posted a question
about tankless heaters but I wanted this query to be a separate one. The
customer's mains water pressure is 88 psi on a Saturday afternoon and some
time over the next 18 hours, the pressure went as high as 96 psi. I
understand that 80 psi is the high end of the safe range in general and that
96 psi on a regular basis can/will damage valves and possibly trigger T&P
valves on water heaters.

 

At the recommendation of a plumber I know I looked into pressure reducers,
specifically the Wilkins/Zurn line. All the Wilkins regulators produce zero
pressure drop at zero flow. What good are these products in protecting
plumbing systems from high mains pressures at night when pressures tend to
be the highest and usage is at a minimum or even zero?

 

Are there products that will prevent system pressures from exceeding a set
point (e.g. 60 psi) under any flow condition including zero?   

 

- Peter

Peter T. Parrish, President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org