   I used to use the 6kw ecogen but it has been disco'd and I can't
   justify the 15 kw. Checking out the HD Kohler 8kw and Onan QG3600.

   Thanks!

   Bruce



    Original Message 
   Subject: Re: [RE-wrenches] Small genset 2 wire start?
   From: Darryl Thayer <[1]darylsol...@gmail.com>
   Date: Thu, October 12, 2017 10:15 am
   To: RE-wrenches <[2]re-wrenches@lists.re-wrenches.org>
   Maybe the Home Depot 8 kW Kohler would meet the ticket. It has 2 wire
   start, propane version, can be configured for 120 volt OR 120-240 volt
   output, has an optional "carb heater" run synthetic oil for cold
   weather
   starting. It is not rated Prime power, but for an off grid customer,
   with
   solar and batteries Prime power is not a consideration. It has a 12
   volt
   battery, that can be charged from a 24 to 12 converter or a 48 to 12 if
   one
   can be found. I set the 12 volt float voltage at 13.6 and the batteries
   seem to last for years. charging the battery supplies control and
   monitoring function.
   On Thu, Oct 12, 2017 at 12:01 PM, <[3]br...@willpowerelect.com> wrote:
   > Does anyone know of an electric / 2 wire start propane generator 7kw
   or
   > less? I have a LOL (little old lady) customer off grid for years on a
   > Trace 2512 and 6) T105s. We would like to give her auto start
   function
   > and use her propane supply. I haven't found anything but aftermarket
   > mods and would like to use factory equipment.
   >
   > Thanks
   >
   > Bruce Fiero
   >
   > E: [1][4]br...@willpowerelect.com
   >
   > W: [2]Willpower Electric, LLC
   >
   > Oregon Electrical Contractor C-681
   >
   > CCB 191852
   >
   > Energy Trust of Oregon Trade Ally
   >
   > Oregon Tax Credit Certified Technician Solar Electric
   >
   > NABCEP Certified PV Installer
   >
   > References
   >
   > Visible links
   > 1. [5]mailto:br...@willpowerelect.com
   > 2. [6]http://www.willpower-electric.com/
   >
   > Hidden links:
   > 4. [7]mailto:br...@willpowerelect.com
   > ___
   > List sponsored by Redwood Alliance
   >
   > List Address: [8]RE-wrenches@lists.re-wrenches.org
   >
   > Change listserver email address & settings:
   >
   [9]http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
   >
   > List-Archive:
   http:[10]//www.mail-archive.com/re-wrenches@lists.re-wrenches.
   > org/maillist.html
   >
   > List rules & etiquette:
   > [11]www.re-wrenches.org/etiquette.htm
   >
   > Check out or update participant bios:
   > [12]www.members.re-wrenches.org
   >
   >
   ___
   List sponsored by Redwood Alliance
   List Address: [13]RE-wrenches@lists.re-wrenches.org
   Change listserver email address & settings:
   [14]http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.or
   g
   List-Archive:
   [15]http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maill
   ist.html
   List rules & etiquette:
   [16]www.re-wrenches.org/etiquette.htm
   Check out or update participant bios:
   [17]www.members.re-wrenches.org

References

   1. mailto:darylsol...@gmail.com
   2. mailto:re-wrenches@lists.re-wrenches.org
   3. mailto:br...@willpowerelect.com
   4. mailto:br...@willpowerelect.com
   5. mailto:br...@willpowerelect.com
   6. http://www.willpower-electric.com/
   7. mailto:br...@willpowerelect.com
   8. mailto:RE-wrenches@lists.re-wrenches.org
   9. http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  10. mailto://www.mail-archive.com/re-wrenches@lists.re
  11. http://www.re-wrenches.org/etiquette.htm
  12. http://www.members.re-wrenches.org/
  13. mailto:RE-wrenches@lists.re-wrenches.org
  14. http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  15. 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
  16. http://www.re-wrenches.org/etiquette.htm
  17. http://www.members.re-wrenches.org/
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Small genset 2 wire start?

2017-10-13 Thread Gary Willett
Generac has a 6kw and 15kw EcoGen line  that was specifically designed for 
2-wire start and off-grid battery backup applications. It is dual fuel capable 
(LP and natural gas). I upgraded my 6kw EcoGen to the 15kw model a couple of 
years ago. 

Regards,
Gary Willett
Icarus Engineering & Solar LLC

Sent from my iPhone 5s

> On Oct 12, 2017, at 12:01 PM,  
>  wrote:
> 
>   Does anyone know of an electric / 2 wire start propane generator 7kw or
>   less?  I have a LOL (little old lady) customer off grid for years on a
>   Trace 2512 and 6) T105s. We would like to give her auto start function
>   and use her propane supply. I haven't found anything but aftermarket
>   mods and would like to use factory equipment.
> 
>   Thanks
> 
>   Bruce Fiero
> 
>   E: [1]br...@willpowerelect.com
> 
>   W: [2]Willpower Electric, LLC
> 
>   Oregon Electrical Contractor C-681
> 
>   CCB 191852
> 
>   Energy Trust of Oregon Trade Ally
> 
>   Oregon Tax Credit Certified Technician Solar Electric
> 
>   NABCEP Certified PV Installer
> 
> References
> 
>   Visible links
>   1. mailto:br...@willpowerelect.com
>   2. http://www.willpower-electric.com/
> 
>   Hidden links:
>   4. mailto:br...@willpowerelect.com
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Small genset 2 wire start?

2017-10-12 Thread Darryl Thayer
Maybe the Home Depot 8 kW Kohler would meet the ticket.  It has 2 wire
start, propane version, can be configured for 120 volt OR 120-240 volt
output, has an optional "carb heater" run synthetic oil for cold weather
starting.  It is not rated Prime power, but for an off grid customer, with
solar and batteries Prime power is not a consideration.  It has a 12 volt
battery, that can be charged from a 24 to 12 converter or a 48 to 12 if one
can be found.  I set the 12 volt float voltage at 13.6 and the batteries
seem to last for years. charging the battery supplies control and
monitoring function.

On Thu, Oct 12, 2017 at 12:01 PM,  wrote:

>Does anyone know of an electric / 2 wire start propane generator 7kw or
>less?  I have a LOL (little old lady) customer off grid for years on a
>Trace 2512 and 6) T105s. We would like to give her auto start function
>and use her propane supply. I haven't found anything but aftermarket
>mods and would like to use factory equipment.
>
>Thanks
>
>Bruce Fiero
>
>E: [1]br...@willpowerelect.com
>
>W: [2]Willpower Electric, LLC
>
>Oregon Electrical Contractor C-681
>
>CCB 191852
>
>Energy Trust of Oregon Trade Ally
>
>Oregon Tax Credit Certified Technician Solar Electric
>
>NABCEP Certified PV Installer
>
> References
>
>Visible links
>1. mailto:br...@willpowerelect.com
>2. http://www.willpower-electric.com/
>
>Hidden links:
>4. mailto:br...@willpowerelect.com
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Small genset 2 wire start?

2017-10-12 Thread Chris Mason
You can hack a Generac Ecogen to do it
http://www.outbackpower.com/forum/viewtopic.php?f=17&t=8382


On Thu, Oct 12, 2017 at 1:01 PM,  wrote:

>Does anyone know of an electric / 2 wire start propane generator 7kw or
>less?  I have a LOL (little old lady) customer off grid for years on a
>Trace 2512 and 6) T105s. We would like to give her auto start function
>and use her propane supply. I haven't found anything but aftermarket
>mods and would like to use factory equipment.
>
>Thanks
>
>Bruce Fiero
>
>E: [1]br...@willpowerelect.com
>
>W: [2]Willpower Electric, LLC
>
>Oregon Electrical Contractor C-681
>
>CCB 191852
>
>Energy Trust of Oregon Trade Ally
>
>Oregon Tax Credit Certified Technician Solar Electric
>
>NABCEP Certified PV Installer
>
> References
>
>Visible links
>1. mailto:br...@willpowerelect.com
>2. http://www.willpower-electric.com/
>
>Hidden links:
>4. mailto:br...@willpowerelect.com
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installerâ„¢
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com 
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Small genset 2 wire start?

2017-10-12 Thread bruce
   Does anyone know of an electric / 2 wire start propane generator 7kw or
   less?  I have a LOL (little old lady) customer off grid for years on a
   Trace 2512 and 6) T105s. We would like to give her auto start function
   and use her propane supply. I haven't found anything but aftermarket
   mods and would like to use factory equipment.

   Thanks

   Bruce Fiero

   E: [1]br...@willpowerelect.com

   W: [2]Willpower Electric, LLC

   Oregon Electrical Contractor C-681

   CCB 191852

   Energy Trust of Oregon Trade Ally

   Oregon Tax Credit Certified Technician Solar Electric

   NABCEP Certified PV Installer

References

   Visible links
   1. mailto:br...@willpowerelect.com
   2. http://www.willpower-electric.com/

   Hidden links:
   4. mailto:br...@willpowerelect.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org