Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-17 Thread Chris Mason
Yes, correct on both. The generator support is there, I did not use it.

On Fri, Jun 17, 2016 at 3:07 PM, Carl Adams  wrote:

> Chris,
>
> Nice finish on the Sonnen install.  It looks fabulous.  My understanding
> is the Eco 2-8 integrate the 4kW radian, and the 10-16 incorporates the 8kW
> radian.  I assume generator support is fully supported
>
> On Fri, Jun 17, 2016 at 8:35 AM, Chris Mason  > wrote:
>
>> I promised a picture of the Sonnen installation. As these units are
>> getting close to being appliances in the same vein as home audio, we wanted
>> to have a clean finish so we made some mill work to complete the top of the
>> unit to the ceiling and hide the ugly conduits.
>> https://www.dropbox.com/s/vlh0uumlgf5549g/2016-06-15%2011.00.44-1.jpg?dl=0
>>
>> On Thu, Jun 16, 2016 at 3:47 PM, Marco Mangelsdorf 
>> wrote:
>>
>>> Dunno exactly, Carl.
>>>
>>>
>>>
>>> Twas not I who installed it.
>>>
>>>
>>>
>>> marco
>>>
>>>
>>>
>>> Marco,
>>>
>>>
>>>
>>> Are the two switch gear boxes integral to the installation.  If so can
>>> you give me an idea of what their function/purpose is?
>>>
>>>
>>>
>>> On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf 
>>> wrote:
>>>
>>> Provides an idea of size and scale.
>>>
>>> [image: Tesla Battery system Aalto residence2. 6 may 2016]
>>>
>>> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear,
>>> two Tesla Powerwalls.
>>>
>>>
>>>
>>>
>>>
>>>
>>> --
>>>
>>>
>>> 
>>>
>>> This email has been checked for viruses by Avast antivirus software.
>>> www.avast.com
>>> 
>>>
>>>
>>>
>>>
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>>>
>>> --
>>>
>>> 
>>>
>>> This email has been checked for viruses by Avast antivirus software.
>>> www.avast.com
>>> 
>>>
>>>
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>>
>>
>> --
>> Chris Mason
>> NABCEP Certified Solar PV Installer™
>> Solar Design Engineer
>> Generac Generators Industrial technician
>>
>> www.cometsolar.com 
>> 264.235.5670
>> 869.662.5670
>> Skype: netconcepts
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com 
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:

Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-17 Thread Carl Adams
Chris,

Nice finish on the Sonnen install.  It looks fabulous.  My understanding is
the Eco 2-8 integrate the 4kW radian, and the 10-16 incorporates the 8kW
radian.  I assume generator support is fully supported

On Fri, Jun 17, 2016 at 8:35 AM, Chris Mason 
wrote:

> I promised a picture of the Sonnen installation. As these units are
> getting close to being appliances in the same vein as home audio, we wanted
> to have a clean finish so we made some mill work to complete the top of the
> unit to the ceiling and hide the ugly conduits.
> https://www.dropbox.com/s/vlh0uumlgf5549g/2016-06-15%2011.00.44-1.jpg?dl=0
>
> On Thu, Jun 16, 2016 at 3:47 PM, Marco Mangelsdorf 
> wrote:
>
>> Dunno exactly, Carl.
>>
>>
>>
>> Twas not I who installed it.
>>
>>
>>
>> marco
>>
>>
>>
>> Marco,
>>
>>
>>
>> Are the two switch gear boxes integral to the installation.  If so can
>> you give me an idea of what their function/purpose is?
>>
>>
>>
>> On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf 
>> wrote:
>>
>> Provides an idea of size and scale.
>>
>> [image: Tesla Battery system Aalto residence2. 6 may 2016]
>>
>> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear,
>> two Tesla Powerwalls.
>>
>>
>>
>>
>>
>>
>> --
>>
>>
>> 
>>
>> This email has been checked for viruses by Avast antivirus software.
>> www.avast.com
>> 
>>
>>
>>
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>>
>> --
>>
>> 
>>
>> This email has been checked for viruses by Avast antivirus software.
>> www.avast.com
>> 
>>
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
> --
> Chris Mason
> NABCEP Certified Solar PV Installer™
> Solar Design Engineer
> Generac Generators Industrial technician
>
> www.cometsolar.com 
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-17 Thread Chris Mason
I promised a picture of the Sonnen installation. As these units are getting
close to being appliances in the same vein as home audio, we wanted to have
a clean finish so we made some mill work to complete the top of the unit to
the ceiling and hide the ugly conduits.
https://www.dropbox.com/s/vlh0uumlgf5549g/2016-06-15%2011.00.44-1.jpg?dl=0

On Thu, Jun 16, 2016 at 3:47 PM, Marco Mangelsdorf 
wrote:

> Dunno exactly, Carl.
>
>
>
> Twas not I who installed it.
>
>
>
> marco
>
>
>
> Marco,
>
>
>
> Are the two switch gear boxes integral to the installation.  If so can you
> give me an idea of what their function/purpose is?
>
>
>
> On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf 
> wrote:
>
> Provides an idea of size and scale.
>
> [image: Tesla Battery system Aalto residence2. 6 may 2016]
>
> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear, two
> Tesla Powerwalls.
>
>
>
>
>
>
> --
>
>
> 
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com
> 
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
>
> --
>
> 
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com
> 
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com 
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-16 Thread Marco Mangelsdorf
Dunno exactly, Carl.



Twas not I who installed it.



marco



Marco,



Are the two switch gear boxes integral to the installation.  If so can you give 
me an idea of what their function/purpose is?



On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf  wrote:

Provides an idea of size and scale.

Tesla Battery system Aalto residence2. 6 may 2016

>From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear, two 
>Tesla Powerwalls.







  _


 


This email has been checked for viruses by Avast antivirus software.
www.avast.com 





___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org







---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-16 Thread Carl Adams
Marco,

Are the two switch gear boxes integral to the installation.  If so can you
give me an idea of what their function/purpose is?

On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf 
wrote:

> Provides an idea of size and scale.
>
> [image: Tesla Battery system Aalto residence2. 6 may 2016]
>
> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear, two
> Tesla Powerwalls.
>
>
>
>
>
>
> --
>
> 
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com
> 
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Chris Mason
Howie,

The Sonnen Eco16 we installed is very nice equipment. I have previously
used the Radian 8048A inverter but the Sonnen adds a really nice battery
system, nice interface, and a Z-wave energy management system.
The battery system is by Sony and the stats are incredible. !0 year
warranty, 10,000 cycles, discharge to zero without damage, very good
battery management system.
The install was easy enough, connecting the mains cabling is a challenge as
there is very little room, I would definitely have a trough or some kind of
cable management device above the unit. It takes two people, one to guide
the cables into place and one to push them.
The batteries are so light it is surprising, one person can easily carry
them. This alone is enough reason to go Lithium.
I set the minimum battery reserve to 10%, this client wants to use as much
solar as possible.

Setting up the system is simple, there's a few parameters but they are
easily understood and the manual is very complete.
The client already had an 8KW PV system using a Sunny Boy 8000TL. That was
already connected to the load panel so we didn't have to do any solar
installation.
The Sonnen Eco uses frequency shift to turn off the inverter. This does not
work when it is grid tied, so it can't stop the inverter backfeeding the
grid, which is a problem for us. There's going to be a fix for that shortly
that will allow us to use a contactor to disable the inverter.

If you have clients looking for Lithium batteries, this is a very clean,
very easy to install and configure system.
I will post pictures after I finish the clean up, we are making a wooden
shroud to hide the conduits.



On Tue, Jun 14, 2016 at 12:15 PM, Howie Michaelson <ho...@suncatchervt.com>
wrote:

> I would love to hear more about that install. Design, sense of equipment
> quality and development (is programming and function well thought out and
> implemented), availability, pictures, etc. are all significant questions.
> Thanks for the offer!
>
> Howie
> Howie Michaelson
> NABCEP Certified Solar PV Installer™
>
> Sun Catcher
> Renewable Energy Systems Sales and Service
> VT Solar Electric Incentive Partner
> 802-272-0004
> On Jun 14, 2016 11:45 AM, "Chris Mason" <cometenergysyst...@gmail.com>
> wrote:
>
>> I just completed a 14KWh Sonnen system for one of our clients if anyone
>> wants to know about that system.
>> On Jun 14, 2016 8:59 AM, "Lloyd Hoffstatter" <
>> lhoffstat...@sunstruckconsulting.com> wrote:
>>
>>> Marco,
>>>
>>>
>>>
>>> Thank you, your timing is perfect.  I am working with a utility to get
>>> approval of a StorEdge  / Solar Edge combination with Tesla batteries and
>>> potentially export limitation.
>>>
>>> The utility has been asking for examples, and this is the first I can
>>> bring them back.  HECO territory?  Sorry the system isn’t yours, but thanks
>>> for helping  pave the way for others!
>>>
>>>
>>>
>>> Any other examples of StorEdge with batteries or SolarEdge or StorEdge
>>> using export limitation would be most helpful, meeting with them on Friday,
>>>
>>>
>>>
>>> Best regards,
>>>
>>> Lloyd
>>>
>>>
>>>
>>> Lloyd Hoffstatter
>>>
>>> M.S. in Applied Solar Energy
>>>
>>> NABCEP Solar PV Installer #102503-23
>>>
>>>
>>>
>>> Director
>>>
>>> Sunstruck Consulting
>>>
>>> ll...@sunstruckconsulting.com
>>>
>>> 845-657-8132
>>>
>>>
>>>
>>>
>>>
>>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
>>> Behalf Of *Marco Mangelsdorf
>>> *Sent:* Monday, June 13, 2016 11:43 PM
>>> *To:* 'RE-wrenches' <re-wrenches@lists.re-wrenches.org>
>>> *Subject:* Re: [RE-wrenches] SolarEdge 7600 and the Powerwall
>>>
>>>
>>>
>>> Yes, Howie…their SE StorEdge.
>>>
>>>
>>>
>>> Not my install.  Sunrun did it on Oahu.  Did a big press whoopdeedo and
>>> even got the governor of Hawaii and mayor of Honolulu to attend.
>>>
>>>
>>>
>>> marco
>>>
>>>
>>>
>>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
>>> <re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of *Howie
>>> Michaelson
>>> *Sent:* Monday, June 13, 2016 4:55 PM
>>> *To:* RE-wrenches
>>> *Subject:* Re: [RE-wrenches] SolarEdge 7600 and the Powerwall
>>>
>>>
>>>
>>> Hi Marco,
>

[RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Marco Mangelsdorf
Yes, this install was on Oahu in HECO territory.

 

HECO, HELCO and MECO have an interconnect agreement known as Customer 
Self-Supply (CSS) where the customer-generator is not supposed to export more 
than an “inadvertent” amount of surplus power to the grid.  For these CSS 
systems, battery storage is needed.

 

Note that there’s been a whopping one CSS system installed to-date by Sunrun.

 

marco

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Lloyd Hoffstatter
Sent: Tuesday, June 14, 2016 2:59 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

 

Marco,

 

Thank you, your timing is perfect.  I am working with a utility to get approval 
of a StorEdge  / Solar Edge combination with Tesla batteries and potentially 
export limitation.

The utility has been asking for examples, and this is the first I can bring 
them back.  HECO territory?  Sorry the system isn’t yours, but thanks for 
helping  pave the way for others!

 

Any other examples of StorEdge with batteries or SolarEdge or StorEdge using 
export limitation would be most helpful, meeting with them on Friday,

 

Best regards,

Lloyd

 

Lloyd Hoffstatter

M.S. in Applied Solar Energy

NABCEP Solar PV Installer #102503-23

 

Director

Sunstruck Consulting

 <mailto:ll...@sunstruckconsulting.com> ll...@sunstruckconsulting.com

845-657-8132

  

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Marco Mangelsdorf
Sent: Monday, June 13, 2016 11:43 PM
To: 'RE-wrenches' <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

 

Yes, Howie…their SE StorEdge.  

 

Not my install.  Sunrun did it on Oahu.  Did a big press whoopdeedo and even 
got the governor of Hawaii and mayor of Honolulu to attend.

 

marco

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Howie Michaelson
Sent: Monday, June 13, 2016 4:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

 

Hi Marco,
I assume that is the StorEdge 7600? Is this your install? What was your access 
to the StorEdge?

Thanks for the photo,
Howie
Howie Michaelson
NABCEP Certified Solar PV Installer™

Sun Catcher
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004
On Jun 13, 2016 9:29 PM, "Marco Mangelsdorf" <ma...@pvthawaii.com> wrote:
>
> Provides an idea of size and scale.
>
> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear, two 
> Tesla Powerwalls.
>
>  

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Lloyd Hoffstatter
That would be great!

Lloyd

Lloyd Hoffstatter
Sunstruck Consulting
ll...@sunstruckconsulting.com<mailto:ll...@sunstruckconsulting.com>




From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Howie Michaelson
Sent: Tuesday, June 14, 2016 12:16 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall


I would love to hear more about that install. Design, sense of equipment 
quality and development (is programming and function well thought out and 
implemented), availability, pictures, etc. are all significant questions. 
Thanks for the offer!

Howie
Howie Michaelson
NABCEP Certified Solar PV Installer™

Sun Catcher
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004
On Jun 14, 2016 11:45 AM, "Chris Mason" 
<cometenergysyst...@gmail.com<mailto:cometenergysyst...@gmail.com>> wrote:

I just completed a 14KWh Sonnen system for one of our clients if anyone wants 
to know about that system.
On Jun 14, 2016 8:59 AM, "Lloyd Hoffstatter" 
<lhoffstat...@sunstruckconsulting.com<mailto:lhoffstat...@sunstruckconsulting.com>>
 wrote:
Marco,

Thank you, your timing is perfect.  I am working with a utility to get approval 
of a StorEdge  / Solar Edge combination with Tesla batteries and potentially 
export limitation.
The utility has been asking for examples, and this is the first I can bring 
them back.  HECO territory?  Sorry the system isn’t yours, but thanks for 
helping  pave the way for others!

Any other examples of StorEdge with batteries or SolarEdge or StorEdge using 
export limitation would be most helpful, meeting with them on Friday,

Best regards,
Lloyd

Lloyd Hoffstatter
M.S. in Applied Solar Energy
NABCEP Solar PV Installer #102503-23

Director
Sunstruck Consulting
ll...@sunstruckconsulting.com<mailto:ll...@sunstruckconsulting.com>
845-657-8132


From: RE-wrenches 
[mailto:re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>]
 On Behalf Of Marco Mangelsdorf
Sent: Monday, June 13, 2016 11:43 PM
To: 'RE-wrenches' 
<re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>>
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

Yes, Howie…their SE StorEdge.

Not my install.  Sunrun did it on Oahu.  Did a big press whoopdeedo and even 
got the governor of Hawaii and mayor of Honolulu to attend.

marco

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Howie Michaelson
Sent: Monday, June 13, 2016 4:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall


Hi Marco,
I assume that is the StorEdge 7600? Is this your install? What was your access 
to the StorEdge?

Thanks for the photo,
Howie
Howie Michaelson
NABCEP Certified Solar PV Installer™

Sun Catcher
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004
On Jun 13, 2016 9:29 PM, "Marco Mangelsdorf" 
<ma...@pvthawaii.com<mailto:ma...@pvthawaii.com>> wrote:
>
> Provides an idea of size and scale.
>
> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear, two 
> Tesla Powerwalls.
>
>

___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Howie Michaelson
I would love to hear more about that install. Design, sense of equipment
quality and development (is programming and function well thought out and
implemented), availability, pictures, etc. are all significant questions.
Thanks for the offer!

Howie
Howie Michaelson
NABCEP Certified Solar PV Installer™

Sun Catcher
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004
On Jun 14, 2016 11:45 AM, "Chris Mason" <cometenergysyst...@gmail.com>
wrote:

> I just completed a 14KWh Sonnen system for one of our clients if anyone
> wants to know about that system.
> On Jun 14, 2016 8:59 AM, "Lloyd Hoffstatter" <
> lhoffstat...@sunstruckconsulting.com> wrote:
>
>> Marco,
>>
>>
>>
>> Thank you, your timing is perfect.  I am working with a utility to get
>> approval of a StorEdge  / Solar Edge combination with Tesla batteries and
>> potentially export limitation.
>>
>> The utility has been asking for examples, and this is the first I can
>> bring them back.  HECO territory?  Sorry the system isn’t yours, but thanks
>> for helping  pave the way for others!
>>
>>
>>
>> Any other examples of StorEdge with batteries or SolarEdge or StorEdge
>> using export limitation would be most helpful, meeting with them on Friday,
>>
>>
>>
>> Best regards,
>>
>> Lloyd
>>
>>
>>
>> Lloyd Hoffstatter
>>
>> M.S. in Applied Solar Energy
>>
>> NABCEP Solar PV Installer #102503-23
>>
>>
>>
>> Director
>>
>> Sunstruck Consulting
>>
>> ll...@sunstruckconsulting.com
>>
>> 845-657-8132
>>
>>
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
>> Behalf Of *Marco Mangelsdorf
>> *Sent:* Monday, June 13, 2016 11:43 PM
>> *To:* 'RE-wrenches' <re-wrenches@lists.re-wrenches.org>
>> *Subject:* Re: [RE-wrenches] SolarEdge 7600 and the Powerwall
>>
>>
>>
>> Yes, Howie…their SE StorEdge.
>>
>>
>>
>> Not my install.  Sunrun did it on Oahu.  Did a big press whoopdeedo and
>> even got the governor of Hawaii and mayor of Honolulu to attend.
>>
>>
>>
>> marco
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
>> <re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of *Howie
>> Michaelson
>> *Sent:* Monday, June 13, 2016 4:55 PM
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] SolarEdge 7600 and the Powerwall
>>
>>
>>
>> Hi Marco,
>> I assume that is the StorEdge 7600? Is this your install? What was your
>> access to the StorEdge?
>>
>> Thanks for the photo,
>> Howie
>> Howie Michaelson
>> NABCEP Certified Solar PV Installer™
>>
>> Sun Catcher
>> Renewable Energy Systems Sales and Service
>> VT Solar Electric Incentive Partner
>> 802-272-0004
>> On Jun 13, 2016 9:29 PM, "Marco Mangelsdorf" <ma...@pvthawaii.com> wrote:
>> >
>> > Provides an idea of size and scale.
>> >
>> > From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear,
>> two Tesla Powerwalls.
>> >
>> >
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Chris Mason
I just completed a 14KWh Sonnen system for one of our clients if anyone
wants to know about that system.
On Jun 14, 2016 8:59 AM, "Lloyd Hoffstatter" <
lhoffstat...@sunstruckconsulting.com> wrote:

> Marco,
>
>
>
> Thank you, your timing is perfect.  I am working with a utility to get
> approval of a StorEdge  / Solar Edge combination with Tesla batteries and
> potentially export limitation.
>
> The utility has been asking for examples, and this is the first I can
> bring them back.  HECO territory?  Sorry the system isn’t yours, but thanks
> for helping  pave the way for others!
>
>
>
> Any other examples of StorEdge with batteries or SolarEdge or StorEdge
> using export limitation would be most helpful, meeting with them on Friday,
>
>
>
> Best regards,
>
> Lloyd
>
>
>
> Lloyd Hoffstatter
>
> M.S. in Applied Solar Energy
>
> NABCEP Solar PV Installer #102503-23
>
>
>
> Director
>
> Sunstruck Consulting
>
> ll...@sunstruckconsulting.com
>
> 845-657-8132
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Marco Mangelsdorf
> *Sent:* Monday, June 13, 2016 11:43 PM
> *To:* 'RE-wrenches' <re-wrenches@lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] SolarEdge 7600 and the Powerwall
>
>
>
> Yes, Howie…their SE StorEdge.
>
>
>
> Not my install.  Sunrun did it on Oahu.  Did a big press whoopdeedo and
> even got the governor of Hawaii and mayor of Honolulu to attend.
>
>
>
> marco
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
> <re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of *Howie
> Michaelson
> *Sent:* Monday, June 13, 2016 4:55 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] SolarEdge 7600 and the Powerwall
>
>
>
> Hi Marco,
> I assume that is the StorEdge 7600? Is this your install? What was your
> access to the StorEdge?
>
> Thanks for the photo,
> Howie
> Howie Michaelson
> NABCEP Certified Solar PV Installer™
>
> Sun Catcher
> Renewable Energy Systems Sales and Service
> VT Solar Electric Incentive Partner
> 802-272-0004
> On Jun 13, 2016 9:29 PM, "Marco Mangelsdorf" <ma...@pvthawaii.com> wrote:
> >
> > Provides an idea of size and scale.
> >
> > From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear,
> two Tesla Powerwalls.
> >
> >
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Lloyd Hoffstatter
Marco,

Thank you, your timing is perfect.  I am working with a utility to get approval 
of a StorEdge  / Solar Edge combination with Tesla batteries and potentially 
export limitation.
The utility has been asking for examples, and this is the first I can bring 
them back.  HECO territory?  Sorry the system isn’t yours, but thanks for 
helping  pave the way for others!

Any other examples of StorEdge with batteries or SolarEdge or StorEdge using 
export limitation would be most helpful, meeting with them on Friday,

Best regards,
Lloyd

Lloyd Hoffstatter
M.S. in Applied Solar Energy
NABCEP Solar PV Installer #102503-23

Director
Sunstruck Consulting
ll...@sunstruckconsulting.com<mailto:ll...@sunstruckconsulting.com>
845-657-8132


From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Marco Mangelsdorf
Sent: Monday, June 13, 2016 11:43 PM
To: 'RE-wrenches' <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

Yes, Howie…their SE StorEdge.

Not my install.  Sunrun did it on Oahu.  Did a big press whoopdeedo and even 
got the governor of Hawaii and mayor of Honolulu to attend.

marco

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Howie Michaelson
Sent: Monday, June 13, 2016 4:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall


Hi Marco,
I assume that is the StorEdge 7600? Is this your install? What was your access 
to the StorEdge?

Thanks for the photo,
Howie
Howie Michaelson
NABCEP Certified Solar PV Installer™

Sun Catcher
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004
On Jun 13, 2016 9:29 PM, "Marco Mangelsdorf" 
<ma...@pvthawaii.com<mailto:ma...@pvthawaii.com>> wrote:
>
> Provides an idea of size and scale.
>
> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear, two 
> Tesla Powerwalls.
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-14 Thread Marco Mangelsdorf
Yes, Howie…their SE StorEdge.  

 

Not my install.  Sunrun did it on Oahu.  Did a big press whoopdeedo and even 
got the governor of Hawaii and mayor of Honolulu to attend.

 

marco

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Howie Michaelson
Sent: Monday, June 13, 2016 4:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

 

Hi Marco,
I assume that is the StorEdge 7600? Is this your install? What was your access 
to the StorEdge?

Thanks for the photo,
Howie
Howie Michaelson
NABCEP Certified Solar PV Installer™

Sun Catcher
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004
On Jun 13, 2016 9:29 PM, "Marco Mangelsdorf" <ma...@pvthawaii.com> wrote:
>
> Provides an idea of size and scale.
>
> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear, two 
> Tesla Powerwalls.
>
>  

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-13 Thread Howie Michaelson
Hi Marco,
I assume that is the StorEdge 7600? Is this your install? What was your
access to the StorEdge?

Thanks for the photo,
Howie
Howie Michaelson
NABCEP Certified Solar PV Installer™

Sun Catcher
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004
On Jun 13, 2016 9:29 PM, "Marco Mangelsdorf"  wrote:
>
> Provides an idea of size and scale.
>
> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear,
two Tesla Powerwalls.
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-13 Thread Marco Mangelsdorf
Provides an idea of size and scale.

Tesla Battery system Aalto residence2. 6 may 2016

>From left to right-disconnect, kWh meter, SolarEdge 7600, switch gear, two
Tesla Powerwalls.

 

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org