[RE-wrenches] Sourcing 600 Volt CAT 5 cable

2017-04-29 Thread Dana
Thanks, All. I have located & ordered the distance I needed. 

BTW – Midnite only sells to direct dealers that are purchasing in the $100- +/ 
year range. This is disappointing as the 600-V CAT5 is not a very common cable. 
Midnite did redirect me to ALT-E and shipping from NY was $77 for the  cable, 
50% of the cost of the cable itself.

I tried 3 wholesalers & they were not even aware of this type of cable till 
they researched it. All were able to source it only as a 1000’ reel order. AEE 
had stopped carrying the 600 V CAT5. 

Sigh………

 



Dana Orzel   Great Solar Works, Inc. 

208.721.7003   d...@solarwork.com

Idaho Contractor - # 028765  Idaho PV # 028374

NABCEP # 051112-136   www.solarwork.biz

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Tump
Sent: Friday, April 28, 2017 8:42 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Sourcing 600 Volt CAT 5 cable

 

Midnite has this and can sell it to you directly if you wish.

On Apr 28, 2017, at 7:36 AM, Dana <d...@solarwork.com 
<mailto:d...@solarwork.com> > wrote:

 

Thanks I will look into this option. This is my first go around with the rapid 
shut down & was going with the Midnite manual recommendation. So far sourcing 
this has not been easy.

 



Dana Orzel   Great Solar Works, Inc. 

208.721.7003<mailto:d...@solarwork.com> 
d...@solarwork.com

Idaho Contractor - # 028765  Idaho PV # 028374

NABCEP # 051112-136<http://www.solarwork.biz/> 
www.solarwork.biz

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: RE-wrenches [ <mailto:re-wrenches-boun...@lists.re-wrenches.org> 
mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Thursday, April 27, 2017 9:20 PM
To: RE-wrenches < <mailto:re-wrenches@lists.re-wrenches.org> 
re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Sourcing 600 Volt CAT 5 cable

 

Dana:

 

The garden variety Cat5 we have been using is rated at 300 volts. Unless your 
off-grid system is using 600 volt controllers, standard Cat5 should be code 
compliant. 

 

We did source a Belden 600 V Cat5 and used it when we did not really need to. 
It was expensive and very hard to terminate.  (I damaged an Outback Hub 10. 
Expensive mistake). 

 

600 volt Cat5 can be had, but I recommend you avoid using it if possible. 

 

William Miller 


On Apr 27, 2017, at 6:04 PM, Dana < <mailto:d...@solarwork.com> 
d...@solarwork.com> wrote:

Hey All’yall.

 

I am looking for 185’ of 600 volt CAT 5 cable for my off grid MidNite Solar 
rapid shut down system.

I am not looking for the USE version.

 

Please contact me off list. 

 

Thankyou!  

 



Dana Orzel   Great Solar Works, Inc. 

208.721.7003<mailto:d...@solarwork.com> 
d...@solarwork.com

Idaho Contractor - # 028765  Idaho PV # 028374

NABCEP # 051112-136<http://www.solarwork.biz/> 
www.solarwork.biz

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

___
List sponsored by Redwood Alliance

List Address:  <mailto:RE-wrenches@lists.re-wrenches.org> 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:  
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm> www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
 <http://www.members.re-wrenches.org/> www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address:  <mailto:RE-wrenches@lists.re-wrenches.org> 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:  
<http:/

Re: [RE-wrenches] Sourcing 600 Volt CAT 5 cable

2017-04-28 Thread Howie Michaelson
Turns out I have a 400' roll of the Midnite wire which I do not need
(client changed mind, and I cannot get my supplier to take back - very
annoying!) and am willing to sell cheap,but you'd probably do better
sourcing from Midnite since shipping from VT will probably be prohibitive.

Howie

*Howie Michaelson*
*NABCEP Certified Solar PV Installer™*
Sun Catcher, LLC
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004

On Fri, Apr 28, 2017 at 7:36 AM, Dana <d...@solarwork.com> wrote:

> Thanks I will look into this option. This is my first go around with the
> rapid shut down & was going with the Midnite manual recommendation. So far
> sourcing this has not been easy.
>
>
>
> 
> 
>
> Dana Orzel   Great Solar Works, Inc.
>
> *208.721.7003 <%28208%29%20721-7003>
> d...@solarwork.com <d...@solarwork.com>*
>
> Idaho Contractor - # 028765  Idaho PV # 028374
>
> NABCEP # 051112-136   www.solarwork.biz
>
> *"Responsible Technologies for Responsible People since 1988"  *
>
> *P* Please consider the environment before printing this email.
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *William Miller
> *Sent:* Thursday, April 27, 2017 9:20 PM
> *To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] Sourcing 600 Volt CAT 5 cable
>
>
>
> Dana:
>
>
>
> The garden variety Cat5 we have been using is rated at 300 volts. Unless
> your off-grid system is using 600 volt controllers, standard Cat5 should be
> code compliant.
>
>
>
> We did source a Belden 600 V Cat5 and used it when we did not really need
> to. It was expensive and very hard to terminate.  (I damaged an Outback Hub
> 10. Expensive mistake).
>
>
>
> 600 volt Cat5 can be had, but I recommend you avoid using it if possible.
>
>
>
> William Miller
>
>
> On Apr 27, 2017, at 6:04 PM, Dana <d...@solarwork.com> wrote:
>
> Hey All’yall.
>
>
>
> I am looking for 185’ of 600 volt CAT 5 cable for my off grid MidNite
> Solar rapid shut down system.
>
> I am not looking for the USE version.
>
>
>
> Please contact me off list.
>
>
>
> Thankyou!
>
>
>
> 
> 
>
> Dana Orzel   Great Solar Works, Inc.
>
> *208.721.7003 <%28208%29%20721-7003>
> d...@solarwork.com <d...@solarwork.com>*
>
> Idaho Contractor - # 028765  Idaho PV # 028374
>
> NABCEP # 051112-136   www.solarwork.biz
>
> *"Responsible Technologies for Responsible People since 1988"  *
>
> *P* Please consider the environment before printing this email.
>
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Sourcing 600 Volt CAT 5 cable

2017-04-28 Thread Chris Mason
Or you can sleeve it in innerduct.

On Fri, Apr 28, 2017 at 10:41 AM, Tump <t...@swnl.net> wrote:

> Midnite has this and can sell it to you directly if you wish.
>
> On Apr 28, 2017, at 7:36 AM, Dana <d...@solarwork.com> wrote:
>
> Thanks I will look into this option. This is my first go around with the
> rapid shut down & was going with the Midnite manual recommendation. So far
> sourcing this has not been easy.
>
> 
> 
> Dana Orzel   Great Solar Works, Inc.
> *208.721.7003 <(208)%20721-7003>   d...@solarwork.com
> <d...@solarwork.com>*
> Idaho Contractor - # 028765  Idaho PV # 028374
> NABCEP # 051112-136   www.solarwork.biz
> *"Responsible Technologies for Responsible People since 1988"  *
> *P* Please consider the environment before printing this email.
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
> <re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of *William Miller
> *Sent:* Thursday, April 27, 2017 9:20 PM
> *To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] Sourcing 600 Volt CAT 5 cable
>
> Dana:
>
> The garden variety Cat5 we have been using is rated at 300 volts. Unless
> your off-grid system is using 600 volt controllers, standard Cat5 should be
> code compliant.
>
> We did source a Belden 600 V Cat5 and used it when we did not really need
> to. It was expensive and very hard to terminate.  (I damaged an Outback Hub
> 10. Expensive mistake).
>
> 600 volt Cat5 can be had, but I recommend you avoid using it if possible.
>
> William Miller
>
>
> On Apr 27, 2017, at 6:04 PM, Dana <d...@solarwork.com> wrote:
>
> Hey All’yall.
>
> I am looking for 185’ of 600 volt CAT 5 cable for my off grid MidNite
> Solar rapid shut down system.
> I am not looking for the USE version.
>
> Please contact me off list.
>
> Thankyou!
>
> 
> 
> Dana Orzel   Great Solar Works, Inc.
> *208.721.7003 <(208)%20721-7003>   d...@solarwork.com
> <d...@solarwork.com>*
> Idaho Contractor - # 028765  Idaho PV # 028374
> NABCEP # 051112-136   www.solarwork.biz
> *"Responsible Technologies for Responsible People since 1988"  *
> *P* Please consider the environment before printing this email.
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.
> re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.
> re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> *t...@swnl.net*   *www.SWNL.net*
> Solarwinds Northernlights
> *   Serving Mid Coast Maine & Northern California*
> * 207-832-7574 <(207)%20832-7574>   Cl.
> 610-517-8401 <(610)%20517-8401>  *
>   *Blair "TUMP" May*
>
>
> *     MAINE'S CHARTER  *   *
> NABCEP"Certified PV Installer"*
>
>
> *   MAINE'S CHARTER   **
> Trace Xantrex "Certified" Dealer / Installer"*
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>

Re: [RE-wrenches] Sourcing 600 Volt CAT 5 cable

2017-04-28 Thread Tump
Midnite has this and can sell it to you directly if you wish.
> On Apr 28, 2017, at 7:36 AM, Dana <d...@solarwork.com> wrote:
> 
> Thanks I will look into this option. This is my first go around with the 
> rapid shut down & was going with the Midnite manual recommendation. So far 
> sourcing this has not been easy.
>  
> 
> Dana Orzel   Great Solar Works, Inc. 
> 208.721.7003   d...@solarwork.com 
> <mailto:d...@solarwork.com>
> Idaho Contractor - # 028765  Idaho PV # 028374
> NABCEP # 051112-136   www.solarwork.biz 
> <http://www.solarwork.biz/>
> "Responsible Technologies for Responsible People since 1988"  
> P Please consider the environment before printing this email.
>  
>  
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org 
> <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of William 
> Miller
> Sent: Thursday, April 27, 2017 9:20 PM
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org 
> <mailto:re-wrenches@lists.re-wrenches.org>>
> Subject: Re: [RE-wrenches] Sourcing 600 Volt CAT 5 cable
>  
> Dana:
>  
> The garden variety Cat5 we have been using is rated at 300 volts. Unless your 
> off-grid system is using 600 volt controllers, standard Cat5 should be code 
> compliant. 
>  
> We did source a Belden 600 V Cat5 and used it when we did not really need to. 
> It was expensive and very hard to terminate.  (I damaged an Outback Hub 10. 
> Expensive mistake). 
>  
> 600 volt Cat5 can be had, but I recommend you avoid using it if possible. 
>  
> William Miller 
> 
> On Apr 27, 2017, at 6:04 PM, Dana <d...@solarwork.com 
> <mailto:d...@solarwork.com>> wrote:
> 
>> Hey All’yall.
>>  
>> I am looking for 185’ of 600 volt CAT 5 cable for my off grid MidNite Solar 
>> rapid shut down system.
>> I am not looking for the USE version.
>>  
>> Please contact me off list. 
>>  
>> Thankyou!  
>>  
>> 
>> Dana Orzel   Great Solar Works, Inc. 
>> 208.721.7003   d...@solarwork.com 
>> <mailto:d...@solarwork.com>
>> Idaho Contractor - # 028765  Idaho PV # 028374
>> NABCEP # 051112-136   www.solarwork.biz 
>> <http://www.solarwork.biz/>
>> "Responsible Technologies for Responsible People since 1988"  
>> P Please consider the environment before printing this email.
>>  
>>  
>> ___
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org 
>> <mailto:RE-wrenches@lists.re-wrenches.org>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org 
>> <http://www.members.re-wrenches.org/>___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> t...@swnl.net 
> <blocked::mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>  
>  www.SWNL.net 
> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
> Solarwinds Northernlights   
>Ser

Re: [RE-wrenches] Sourcing 600 Volt CAT 5 cable

2017-04-28 Thread Dana
Thanks I will look into this option. This is my first go around with the rapid 
shut down & was going with the Midnite manual recommendation. So far sourcing 
this has not been easy.

 



Dana Orzel   Great Solar Works, Inc. 

208.721.7003   d...@solarwork.com

Idaho Contractor - # 028765  Idaho PV # 028374

NABCEP # 051112-136   www.solarwork.biz

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of William Miller
Sent: Thursday, April 27, 2017 9:20 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Sourcing 600 Volt CAT 5 cable

 

Dana:

 

The garden variety Cat5 we have been using is rated at 300 volts. Unless your 
off-grid system is using 600 volt controllers, standard Cat5 should be code 
compliant. 

 

We did source a Belden 600 V Cat5 and used it when we did not really need to. 
It was expensive and very hard to terminate.  (I damaged an Outback Hub 10. 
Expensive mistake). 

 

600 volt Cat5 can be had, but I recommend you avoid using it if possible. 

 

William Miller 


On Apr 27, 2017, at 6:04 PM, Dana <d...@solarwork.com 
<mailto:d...@solarwork.com> > wrote:

Hey All’yall.

 

I am looking for 185’ of 600 volt CAT 5 cable for my off grid MidNite Solar 
rapid shut down system.

I am not looking for the USE version.

 

Please contact me off list. 

 

Thankyou!  

 



Dana Orzel   Great Solar Works, Inc. 

208.721.7003   d...@solarwork.com 
<mailto:d...@solarwork.com> 

Idaho Contractor - # 028765  Idaho PV # 028374

NABCEP # 051112-136   www.solarwork.biz 
<http://www.solarwork.biz> 

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Sourcing 600 Volt CAT 5 cable

2017-04-27 Thread William Miller
Dana:

The garden variety Cat5 we have been using is rated at 300 volts. Unless your 
off-grid system is using 600 volt controllers, standard Cat5 should be code 
compliant. 

We did source a Belden 600 V Cat5 and used it when we did not really need to. 
It was expensive and very hard to terminate.  (I damaged an Outback Hub 10. 
Expensive mistake). 

600 volt Cat5 can be had, but I recommend you avoid using it if possible. 

William Miller 

> On Apr 27, 2017, at 6:04 PM, Dana  wrote:
> 
> Hey All’yall.
>  
> I am looking for 185’ of 600 volt CAT 5 cable for my off grid MidNite Solar 
> rapid shut down system.
> I am not looking for the USE version.
>  
> Please contact me off list.
>  
> Thankyou!  
>  
> 
> Dana Orzel   Great Solar Works, Inc.
> 208.721.7003   d...@solarwork.com
> Idaho Contractor - # 028765  Idaho PV # 028374
> NABCEP # 051112-136   www.solarwork.biz
> "Responsible Technologies for Responsible People since 1988"  
> P Please consider the environment before printing this email.
>  
>  
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Sourcing 600 Volt CAT 5 cable

2017-04-27 Thread Dana
Hey All'yall.

 

I am looking for 185' of 600 volt CAT 5 cable for my off grid MidNite Solar
rapid shut down system.

I am not looking for the USE version.

 

Please contact me off list. 

 

Thankyou!  

 



Dana Orzel   Great Solar Works, Inc. 

208.721.7003   d...@solarwork.com

Idaho Contractor - # 028765  Idaho PV # 028374

NABCEP # 051112-136   www.solarwork.biz

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org