Re: [RE-wrenches] Testing new batteries

2011-03-27 Thread benn kilburn

Wrenches,Follow up from the mfgr (Surrette) for new batteries, SG and 
electrolyte levels should level out after a few cycles and do not add water 
until after an initial charge.  The "rise" of the low electrolyte levels can be 
'surprising'.No comment on adding acid, or not.
Had a great Saturday installing that 48V, 2400Ah bank.  Thanks for all comments.
cheers,benn
DayStar Renewable Energy Inc. benn@daystarsolar.ca780-906-7807 HAVE A SUNNY DAY


  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Testing new batteries

2011-03-25 Thread Starlight Solar, Larry Crutcher
Hello Rob,

I agree. I did not read where he said the electrolyte was spilled out, simply 
that he was "considering" adding acid. Let me extend my statement... There is 
never a reason to add acid unless the electrolyte has been spilled. 

Thanks,

Larry
  - Original Message - 
  From: Rob Shappell 
  To: 'RE-wrenches' 
  Sent: Friday, March 25, 2011 6:35 AM
  Subject: Re: [RE-wrenches] Testing new batteries


  With all due respect Larry, you must add acid, not water, if you know acid 
has been lost. Otherwise you can charge, charge, charge and never reach full SG.

   

  Rob Shappell

  Northwest Energy Storage

  Solar-One Batteries

   

  From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Starlight 
Solar, Larry Crutcher
  Sent: Thursday, March 24, 2011 8:12 PM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] Testing new batteries

   

  Benn,

   

  First off, there is never a reason to add acid. The acid/water mixture is 
very specific and should not be changed.

   

  From the moment a battery has been activated (electrolyte added), it is in a 
discharge mode. The sulfuric acid in the electrolyte starts to be absorbed into 
the plates (electrochemical process) creating lead sulfate. All new batteries 
need to be initially charged to reverse this. Only then can you get an accurate 
SG base reading to record in the log book.

   

  New flooded battery charging process:

  Start by charging the new battery at a relatively high voltage, about 2.47vpc 
@ 77 degrees, until the current drops to about 0.5 amps per 100AH capacity. As 
long as the plates are covered, you do not need to add any water during this 
process. Turn the voltage up to about 2.6 volts per cell for at least a couple 
hours. You will notice heavy gassing so make sure they are vented well. Let 
batteries rest a while and take your SG reading. Only if necessary, add water 
to the proper level. Long battery life note: Do not discharge new batteries 
very deep until they have been cycled about 10 to 15 times.

   

  About battery manufacture dates: 

  Too often we have received batteries that have set for many months after 
manufacturing. We return these because the amorphous lead sulfate ions may have 
formed bonds to the plate that are (or may be) irreversible. This same effect 
is caused by undercharging a battery for long periods and it usually leads to 
premature failure. Any flooded battery setting for over 30 days should be fully 
recharged.

   

  To answer your question about liquid volume, the plates are absorbent. They 
absorb acid while discharging and the acid is recombined with water when 
charging. So the level is in constant flux. That is why you should not add 
water to a discharged battery except to cover the plates; charge it first.

   

  Much more than 2 cents but that's just me.

   

  Larry Crutcher
  Starlight Solar Power Systems
  www.starlightsolar.com
  928-342-9103

   

- Original Message - 

From: benn kilburn 

To: Wrenches 

Sent: Thursday, March 24, 2011 11:12 AM

Subject: Re: [RE-wrenches] Testing new batteries

 

Mick n' Nick, 

Thanks guys.  I shoulda mentioned that the date code says they were mfgrd 
the 7th week of 2011 and the one exception, the 8th week.  So they haven't been 
sitting too long.

 

I have been in contact with the mfgr, and of course i will take their 
advice over anyone else's (gotta keep the warranty valid), but you cannot deny 
the value of the hands-on experience and insight from this list.  They said to 
add distilled water after the initial charge, which is why i was only 
"considering" adding acid.  I have asked about adding acid rather than water.  
Waiting for reply.

 

Mick, you mentioned that the electrolyte levels may level once all 
batteries are at equal SOC.  Can you elaborate?  Do the plates become more or 
less 'absorbent' or does the chemical reaction change the volume of the liquid. 
 I will watch this closely.

 

cheers,

benn

DayStar Renewable Energy Inc.  

b...@daystarsolar.ca

780-906-7807 

HAVE A SUNNY DAY 



--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi

Re: [RE-wrenches] Testing new batteries

2011-03-25 Thread Rob Shappell
With all due respect Larry, you must add acid, not water, if you know acid
has been lost. Otherwise you can charge, charge, charge and never reach full
SG.

 

Rob Shappell

Northwest Energy Storage

Solar-One Batteries

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Starlight
Solar, Larry Crutcher
Sent: Thursday, March 24, 2011 8:12 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Testing new batteries

 

Benn,

 

First off, there is never a reason to add acid. The acid/water mixture is
very specific and should not be changed.

 

>From the moment a battery has been activated (electrolyte added), it is in a
discharge mode. The sulfuric acid in the electrolyte starts to be absorbed
into the plates (electrochemical process) creating lead sulfate. All new
batteries need to be initially charged to reverse this. Only then can you
get an accurate SG base reading to record in the log book.

 

New flooded battery charging process:

Start by charging the new battery at a relatively high voltage, about
2.47vpc @ 77 degrees, until the current drops to about 0.5 amps per 100AH
capacity. As long as the plates are covered, you do not need to add any
water during this process. Turn the voltage up to about 2.6 volts per cell
for at least a couple hours. You will notice heavy gassing so make sure they
are vented well. Let batteries rest a while and take your SG reading. Only
if necessary, add water to the proper level. Long battery life note: Do not
discharge new batteries very deep until they have been cycled about 10 to 15
times.

 

About battery manufacture dates: 

Too often we have received batteries that have set for many months after
manufacturing. We return these because the amorphous lead sulfate ions may
have formed bonds to the plate that are (or may be) irreversible. This same
effect is caused by undercharging a battery for long periods and it usually
leads to premature failure. Any flooded battery setting for over 30 days
should be fully recharged.

 

To answer your question about liquid volume, the plates are absorbent. They
absorb acid while discharging and the acid is recombined with water when
charging. So the level is in constant flux. That is why you should not add
water to a discharged battery except to cover the plates; charge it first.

 

Much more than 2 cents but that's just me.

 

Larry Crutcher
Starlight Solar Power Systems
www.starlightsolar.com
928-342-9103

 

- Original Message - 

From: benn kilburn <mailto:b...@daystarsolar.ca>  

To: Wrenches <mailto:re-wrenches@lists.re-wrenches.org>  

Sent: Thursday, March 24, 2011 11:12 AM

Subject: Re: [RE-wrenches] Testing new batteries

 

Mick n' Nick, 

Thanks guys.  I shoulda mentioned that the date code says they were mfgrd
the 7th week of 2011 and the one exception, the 8th week.  So they haven't
been sitting too long.

 

I have been in contact with the mfgr, and of course i will take their advice
over anyone else's (gotta keep the warranty valid), but you cannot deny the
value of the hands-on experience and insight from this list.  They said to
add distilled water after the initial charge, which is why i was only
"considering" adding acid.  I have asked about adding acid rather than
water.  Waiting for reply.

 

Mick, you mentioned that the electrolyte levels may level once all batteries
are at equal SOC.  Can you elaborate?  Do the plates become more or less
'absorbent' or does the chemical reaction change the volume of the liquid.
I will watch this closely.

 

cheers,

benn

DayStar Renewable Energy Inc.  

b...@daystarsolar.ca

780-906-7807 

HAVE A SUNNY DAY 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Testing new batteries

2011-03-24 Thread Starlight Solar, Larry Crutcher
Benn,

First off, there is never a reason to add acid. The acid/water mixture is very 
specific and should not be changed.

>From the moment a battery has been activated (electrolyte added), it is in a 
>discharge mode. The sulfuric acid in the electrolyte starts to be absorbed 
>into the plates (electrochemical process) creating lead sulfate. All new 
>batteries need to be initially charged to reverse this. Only then can you get 
>an accurate SG base reading to record in the log book.

New flooded battery charging process:
Start by charging the new battery at a relatively high voltage, about 2.47vpc @ 
77 degrees, until the current drops to about 0.5 amps per 100AH capacity. As 
long as the plates are covered, you do not need to add any water during this 
process. Turn the voltage up to about 2.6 volts per cell for at least a couple 
hours. You will notice heavy gassing so make sure they are vented well. Let 
batteries rest a while and take your SG reading. Only if necessary, add water 
to the proper level. Long battery life note: Do not discharge new batteries 
very deep until they have been cycled about 10 to 15 times.

About battery manufacture dates: 
Too often we have received batteries that have set for many months after 
manufacturing. We return these because the amorphous lead sulfate ions may have 
formed bonds to the plate that are (or may be) irreversible. This same effect 
is caused by undercharging a battery for long periods and it usually leads to 
premature failure. Any flooded battery setting for over 30 days should be fully 
recharged.

To answer your question about liquid volume, the plates are absorbent. They 
absorb acid while discharging and the acid is recombined with water when 
charging. So the level is in constant flux. That is why you should not add 
water to a discharged battery except to cover the plates; charge it first.

Much more than 2 cents but that's just me.

Larry Crutcher
Starlight Solar Power Systems
www.starlightsolar.com
928-342-9103

  - Original Message - 
  From: benn kilburn 
  To: Wrenches 
  Sent: Thursday, March 24, 2011 11:12 AM
  Subject: Re: [RE-wrenches] Testing new batteries


  Mick n' Nick,
  Thanks guys.  I shoulda mentioned that the date code says they were mfgrd the 
7th week of 2011 and the one exception, the 8th week.  So they haven't been 
sitting too long.


  I have been in contact with the mfgr, and of course i will take their advice 
over anyone else's (gotta keep the warranty valid), but you cannot deny the 
value of the hands-on experience and insight from this list.  They said to add 
distilled water after the initial charge, which is why i was only "considering" 
adding acid.  I have asked about adding acid rather than water.  Waiting for 
reply.


  Mick, you mentioned that the electrolyte levels may level once all batteries 
are at equal SOC.  Can you elaborate?  Do the plates become more or less 
'absorbent' or does the chemical reaction change the volume of the liquid.  I 
will watch this closely.


  cheers,
  benn

  DayStar Renewable Energy Inc. 
  b...@daystarsolar.ca
  780-906-7807 
  HAVE A SUNNY DAY ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Testing new batteries

2011-03-24 Thread dan
We got one shipment of thick plate 2V that apparently had been mistakenly shipped with the wrong electrolyte mix.. the Battery folks were pretty good about ponying up.. they sent me everything I needed to get things straightened out.. (Including $$ for the hassle).. Basically they had me set the Charge Controllers a Little Hot to burn off Water, then charge the snot out of them (like on EQ all week end). after the return amps dropped below like 3-5% of the normal charge rate, we'd let things rest for a while and then check SG (temp compensated).. My take away was the notion that the batteries were designed to be "fully charged" when the regulated charge rate dropped below 3-5% and the SG averaged 1.28.. The Tech guy also told me that they used a constant current of like 80A for days for their commissioning charge... The biggest problem I've been having is getting folks head around the scale of the difference between thick plate technology and their old UL16s.. They sure can take a whole lot more to charge when they're down... Good Luck.. dbDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44


 Original Message ----
Subject: [RE-wrenches] Testing new batteries
From: "Dana" <d...@solarwork.com>
Date: Thu, March 24, 2011 1:34 pm
To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org>

HUP Solar One batteries recommend topping off the electrolyte and doing an initial EQ cycle prior to use. We always check SG and voltage/cell on arrival and to date never had any discrepancy on either. Additionally we unbolt all connections, polish with a copper pipe wire brush all connecting surfaces [with a respirator on] re-bolt, check voltage & SG, then coat with Vaseline all connecting surfaces. So, total we check volt per cell and SG twice. Considering that this bank will be in place for 16-20 years it is a good place to start. Do it once and do it correctly. This serves as a good baseline.  I have mentioned this before but we only use a refractometer for checking specific gravity anymore the accuracy is dead on and not subject to sticking floats and curvature of the electrolyte in the hydrometer.  Refractometers are $85-$100 each from a good plumbing wholesale house. Dana OrzelGreat Solar Works, IncE - d...@solarwork.comV - 970.626.5253F - 970.626.4140C - 970.209.4076web - www.solarwork.com "Responsible Technologies for Responsible People since 1988"Do not ever believe anything, but seriously trust through action. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick SoleilSent: Thursday, March 24, 2011 11:20 AMTo: RE-wrenchesSubject: Re: [RE-wrenches] Testing new batteries Hi Benn:    Perhaps those batteries have just been sitting a little while, and need a recharge.  Generally speaking, if you find that the batteries test reading are a little low, they are probably just a little discharged.  After recharging the batteries, test them again.  If those readings are low, then contact the manufacturer with the data.  I have had great luck with battery manufacturers warranting their defective batteries in warranty. Nick SoleilProject ManagerAdvanced Alternative Energy Solutions, LLCPO Box 657Petaluma, CA 94953Cell: 707-321-2937Office: 707-789-9537Fax: 707-769-9037  From: benn kilburn <b...@daystarsolar.ca>To: Wrenches <re-wrenches@lists.re-wrenches.org>Sent: Thu, March 24, 2011 9:43:20 AMSubject: [RE-wrenches] Testing new batteriesI'm curious of others experiences with testing "new" batteries right from the mfgr, before putting them into service.  I'm not talking about load testing, i mean just basics...voltage, specific gravity and electrolyte level. I recently received some batteries (24 x 2V) and before putting them to work i tested all the voltages, SG's and levels.  Voltages were all with-in 0.016 V (2.1-2.084).  The SG's were within 0.037 (1.281-1.244).  Yes, the one with the lowest SG also had the lowest V.   What concerns me a bit more than the few cells with lower SG is the consistent low levels of electrolyte.  All cells were between 3/4" and 1-1/2" below full, which is 1/4" below the bottom of the vent well tube with one exception that was bang-on full.  Interestingly, the one full battery was the only one with a different date code than the rest.  Should the various levels of electrolyte mentioned be acceptable when a battery is brand new, straight from the mfgr?  How bout the SG's? I'm considering adding electrolyte from a local battery shop instead of distilled water to top up all the batteries.  Comments? Very thankful for the wealth of knowledge and experience on this list,bennDayStar Renewable Energy Inc. b...@daystarsolar.ca780-906-7807 HAVE A SUNNY DAY    ___
List sponsored 

Re: [RE-wrenches] Testing new batteries

2011-03-24 Thread Rob Shappell
Hey Dana, it's EQ then top off.

 

Rob

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dana
Sent: Thursday, March 24, 2011 1:35 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Testing new batteries

 

HUP Solar One batteries recommend topping off the electrolyte and doing an
initial EQ cycle prior to use. We always check SG and voltage/cell on
arrival and to date never had any discrepancy on either.

 

Additionally we unbolt all connections, polish with a copper pipe wire brush
all connecting surfaces [with a respirator on] re-bolt, check voltage & SG,
then coat with Vaseline all connecting surfaces.

 

So, total we check volt per cell and SG twice. Considering that this bank
will be in place for 16-20 years it is a good place to start. Do it once and
do it correctly. This serves as a good baseline. 

 

I have mentioned this before but we only use a refractometer for checking
specific gravity anymore the accuracy is dead on and not subject to sticking
floats and curvature of the electrolyte in the hydrometer.  Refractometers
are $85-$100 each from a good plumbing wholesale house.

 

Dana Orzel

Great Solar Works, Inc

E - d...@solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

 

"Responsible Technologies for Responsible People since 1988"

Do not ever believe anything, but seriously trust through action.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick Soleil
Sent: Thursday, March 24, 2011 11:20 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Testing new batteries

 

Hi Benn:
Perhaps those batteries have just been sitting a little while, and need
a recharge.  Generally speaking, if you find that the batteries test reading
are a little low, they are probably just a little discharged.  After
recharging the batteries, test them again.  If those readings are low, then
contact the manufacturer with the data.  I have had great luck with battery
manufacturers warranting their defective batteries in warranty.

 

Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037

 

 

  _  

From: benn kilburn 
To: Wrenches 
Sent: Thu, March 24, 2011 9:43:20 AM
Subject: [RE-wrenches] Testing new batteries

I'm curious of others experiences with testing "new" batteries right from
the mfgr, before putting them into service.  I'm not talking about load
testing, i mean just basics...voltage, specific gravity and electrolyte
level.

 

I recently received some batteries (24 x 2V) and before putting them to work
i tested all the voltages, SG's and levels.  Voltages were all with-in 0.016
V (2.1-2.084).  The SG's were within 0.037 (1.281-1.244).  Yes, the one with
the lowest SG also had the lowest V.  

 

What concerns me a bit more than the few cells with lower SG is the
consistent low levels of electrolyte.  All cells were between 3/4" and
1-1/2" below full, which is 1/4" below the bottom of the vent well tube
with one exception that was bang-on full.  Interestingly, the one full
battery was the only one with a different date code than the rest. 

 

Should the various levels of electrolyte mentioned be acceptable when a
battery is brand new, straight from the mfgr?  How bout the SG's?

 

I'm considering adding electrolyte from a local battery shop instead of
distilled water to top up all the batteries.  Comments?

 

Very thankful for the wealth of knowledge and experience on this list,

benn

DayStar Renewable Energy Inc. 

b...@daystarsolar.ca

780-906-7807 

HAVE A SUNNY DAY 

 

 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Testing new batteries

2011-03-24 Thread Dana
HUP Solar One batteries recommend topping off the
electrolyte and doing an initial EQ cycle prior to use. We
always check SG and voltage/cell on arrival and to date
never had any discrepancy on either.

 

Additionally we unbolt all connections, polish with a copper
pipe wire brush all connecting surfaces [with a respirator
on] re-bolt, check voltage & SG, then coat with Vaseline all
connecting surfaces.

 

So, total we check volt per cell and SG twice. Considering
that this bank will be in place for 16-20 years it is a good
place to start. Do it once and do it correctly. This serves
as a good baseline. 

 

I have mentioned this before but we only use a refractometer
for checking specific gravity anymore the accuracy is dead
on and not subject to sticking floats and curvature of the
electrolyte in the hydrometer.  Refractometers are $85-$100
each from a good plumbing wholesale house.

 

Dana Orzel

Great Solar Works, Inc

E - d...@solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

 

"Responsible Technologies for Responsible People since 1988"

Do not ever believe anything, but seriously trust through
action.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Nick Soleil
Sent: Thursday, March 24, 2011 11:20 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Testing new batteries

 

Hi Benn:
Perhaps those batteries have just been sitting a little
while, and need a recharge.  Generally speaking, if you find
that the batteries test reading are a little low, they are
probably just a little discharged.  After recharging the
batteries, test them again.  If those readings are low, then
contact the manufacturer with the data.  I have had great
luck with battery manufacturers warranting their defective
batteries in warranty.

 

Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037

 

 

  _  

From: benn kilburn 
To: Wrenches 
Sent: Thu, March 24, 2011 9:43:20 AM
Subject: [RE-wrenches] Testing new batteries

I'm curious of others experiences with testing "new"
batteries right from the mfgr, before putting them into
service.  I'm not talking about load testing, i mean just
basics...voltage, specific gravity and electrolyte level.

 

I recently received some batteries (24 x 2V) and before
putting them to work i tested all the voltages, SG's and
levels.  Voltages were all with-in 0.016 V (2.1-2.084).  The
SG's were within 0.037 (1.281-1.244).  Yes, the one with the
lowest SG also had the lowest V.  

 

What concerns me a bit more than the few cells with lower SG
is the consistent low levels of electrolyte.  All cells were
between 3/4" and 1-1/2" below full, which is 1/4" below the
bottom of the vent well tube with one exception that was
bang-on full.  Interestingly, the one full battery was the
only one with a different date code than the rest. 

 

Should the various levels of electrolyte mentioned be
acceptable when a battery is brand new, straight from the
mfgr?  How bout the SG's?

 

I'm considering adding electrolyte from a local battery shop
instead of distilled water to top up all the batteries.
Comments?

 

Very thankful for the wealth of knowledge and experience on
this list,

benn

DayStar Renewable Energy Inc. 

b...@daystarsolar.ca

780-906-7807 

HAVE A SUNNY DAY 

 

 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Testing new batteries

2011-03-24 Thread Allan Sindelar


  
  
I just spoke with Derek at IBE, having just taken delivery of two
sets of 2V industrial cells, one for a customer and the other for my
own home. On the customer's set, installed yesterday, I measured one
cell as .01V lower and .022 SG lower, before hooking up to any
charging source, and asked him whether to be concerned. His advice:

Before any testing and comparing of cells, EQ the bank to conteract
self-discharge. Ignore differences until this has been done.

Don't add acid, as doing so will upset the concentration. After
initial EQ charge, test SG again. Adjust SG to even out the cells by
transferring modest amounts of electrolyte from the cells with the
highest SG to those with lower SG. This will tend to even out acid
concentration. Acid concentration thus takes priority over
electrolyte level in each cell. Later addition of distilled water
will tend to dilute the cells with stronger SG from which
electrolyte was removed.


  
  
  Allan Sindelar
  al...@positiveenergysolar.com
NABCEP Certified Photovoltaic
  Installer
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Positive Energy, Inc.
  3201 Calle Marie
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com
  
  
  
   

On 3/24/2011 12:12 PM, benn kilburn wrote:

  
  Mick n' Nick,
  Thanks guys.  I shoulda mentioned that the date code says
they were mfgrd the 7th week of 2011 and the one exception, the
8th week.  So they haven't been sitting too long.
  
  
  I have been in contact with the mfgr, and of course i will
take their advice over anyone else's (gotta keep the warranty
valid), but you cannot deny the value of the hands-on experience
and insight from this list.  They said to add distilled water
after the initial charge, which is why i was only "considering"
adding acid.  I have asked about adding acid rather than water.
 Waiting for reply.
  
  
  Mick, you mentioned that the electrolyte levels may level
once all batteries are at equal SOC.  Can you elaborate?  Do the
plates become more or less 'absorbent' or does the chemical
reaction change the volume of the liquid.  I will watch this
closely.
  
  
  cheers,
  benn

DayStar Renewable Energy
Inc. 

  b...@daystarsolar.ca
  780-906-7807 
  HAVE A SUNNY DAY

  
  





From: m...@abrahamsolar.com
Date: Thu, 24 Mar 2011 11:27:36 -0600
To: re-wrenches@lists.re-wrenches.org
    Subject: Re: [RE-wrenches] Testing new batteries

Benn~ If the company that built those batteries is a major brand
name, I advise that you add neither water nor acid to the new
cells. Check with the mfr, but most of the serious mfrs are
using robotic fill equipment that is very precise. 

If some of the cells are older stock they may have self
discharged a bit and the electrolyte level rises & falls
like the tide based on state of charge. I'll bet if you can EQ
the batts to reach equal state of charge, you also will find the
electrolyte level to equalize. 

Jolliness, 

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675


On Thu, Mar 24, 2011 at 11:20 AM,
  Nick Soleil <nicksoleilso...@yahoo.com>
  wrote:
  

  Hi Benn:
    Perhaps those batteries have just been sitting a
little while, and need a recharge.  Generally speaking,
if you find that the batteries test reading are a little
low, they are probably just a little discharged.  After
recharging the batteries, test them again.  If those
readings are low, then contact the manufacturer with the
data.  I have had great luck with battery manufacturers
warranting their defective batteries in warranty.
 
Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037



  
  
  From:
  benn kilburn <b...@daystarsolar.ca>

Re: [RE-wrenches] Testing new batteries

2011-03-24 Thread Mick Abraham
Hi, Benn~

When the batteries are chemically discharged, the plates absorb some of the
volume of the electrolyte...and that "lowers the tide". Upon recharge the
chemicals that had been absorbed into the plates are driven back into
solution...and that "raises the tide".

This is why one should never top up the levels on a battery which is
electrically discharged. The problem with that is if/when the battery
receives a good charge, the electrolyte level will rise, maybe enough to
overflow through the cell caps.

Jolliness,

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675


On Thu, Mar 24, 2011 at 12:12 PM, benn kilburn  wrote:

>  Mick n' Nick,
> Thanks guys.  I shoulda mentioned that the date code says they were mfgrd
> the 7th week of 2011 and the one exception, the 8th week.  So they haven't
> been sitting too long.
>
> I have been in contact with the mfgr, and of course i will take their
> advice over anyone else's (gotta keep the warranty valid), but you cannot
> deny the value of the hands-on experience and insight from this list.  They
> said to add distilled water after the initial charge, which is why i was
> only "considering" adding acid.  I have asked about adding acid rather than
> water.  Waiting for reply.
>
> Mick, you mentioned that the electrolyte levels may level once all
> batteries are at equal SOC.  Can you elaborate?  Do the plates become more
> or less 'absorbent' or does the chemical reaction change the volume of the
> liquid.  I will watch this closely.
>
> cheers,
> benn
>
> DayStar Renewable Energy Inc.
> b...@daystarsolar.ca
> 780-906-7807
> HAVE A SUNNY DAY
>
>
>
>
>
> ------
> From: m...@abrahamsolar.com
> Date: Thu, 24 Mar 2011 11:27:36 -0600
> To: re-wrenches@lists.re-wrenches.org
> Subject: Re: [RE-wrenches] Testing new batteries
>
>
> Benn~ If the company that built those batteries is a major brand name, I
> advise that you add neither water nor acid to the new cells. Check with the
> mfr, but most of the serious mfrs are using robotic fill equipment that is
> very precise.
>
> If some of the cells are older stock they may have self discharged a bit
> and the electrolyte level rises & falls like the tide based on state of
> charge. I'll bet if you can EQ the batts to reach equal state of charge, you
> also will find the electrolyte level to equalize.
>
> Jolliness,
>
> Mick Abraham, Proprietor
> www.abrahamsolar.com
>
> Voice: 970-731-4675
>
>
> On Thu, Mar 24, 2011 at 11:20 AM, Nick Soleil 
> wrote:
>
> Hi Benn:
> Perhaps those batteries have just been sitting a little while, and need
> a recharge.  Generally speaking, if you find that the batteries test reading
> are a little low, they are probably just a little discharged.  After
> recharging the batteries, test them again.  If those readings are low, then
> contact the manufacturer with the data.  I have had great luck with battery
> manufacturers warranting their defective batteries in warranty.
>
> Nick Soleil
> Project Manager
> Advanced Alternative Energy Solutions, LLC
> PO Box 657
> Petaluma, CA 94953
> Cell: 707-321-2937
> Office: 707-789-9537
> Fax: 707-769-9037
>
>
> --
> *From:* benn kilburn 
> *To:* Wrenches 
> *Sent:* Thu, March 24, 2011 9:43:20 AM
> *Subject:* [RE-wrenches] Testing new batteries
>
> I'm curious of others experiences with testing "new" batteries right from
> the mfgr, before putting them into service.  I'm not talking about load
> testing, i mean just basics...voltage, specific gravity and electrolyte
> level.
>
> I recently received some batteries (24 x 2V) and before putting them to
> work i tested all the voltages, SG's and levels.  Voltages were all with-in
> 0.016 V (2.1-2.084).  The SG's were within 0.037 (1.281-1.244).  Yes, the
> one with the lowest SG also had the lowest V.
>
> What concerns me a bit more than the few cells with lower SG is the
> consistent low levels of electrolyte.  All cells were between 3/4" and
> 1-1/2" below full, which is 1/4" below the bottom of the vent well tube
> with one exception that was bang-on full.  Interestingly, the one full
> battery was the only one with a different date code than the rest.
>
> Should the various levels of electrolyte mentioned be acceptable when a
> battery is brand new, straight from the mfgr?  How bout the SG's?
>
> I'm considering adding electrolyte from a local battery shop instead of
> distilled water to top up all the batteries.  Comments?
>
> Very thankful for the wealth of knowledge and experience on this list,

Re: [RE-wrenches] Testing new batteries

2011-03-24 Thread benn kilburn

Mick n' Nick,Thanks guys.  I shoulda mentioned that the date code says they 
were mfgrd the 7th week of 2011 and the one exception, the 8th week.  So they 
haven't been sitting too long.
I have been in contact with the mfgr, and of course i will take their advice 
over anyone else's (gotta keep the warranty valid), but you cannot deny the 
value of the hands-on experience and insight from this list.  They said to add 
distilled water after the initial charge, which is why i was only "considering" 
adding acid.  I have asked about adding acid rather than water.  Waiting for 
reply.
Mick, you mentioned that the electrolyte levels may level once all batteries 
are at equal SOC.  Can you elaborate?  Do the plates become more or less 
'absorbent' or does the chemical reaction change the volume of the liquid.  I 
will watch this closely.
cheers,benn

DayStar Renewable Energy Inc. benn@daystarsolar.ca780-906-7807 HAVE A SUNNY DAY







From: m...@abrahamsolar.com
Date: Thu, 24 Mar 2011 11:27:36 -0600
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Testing new batteries

Benn~ If the company that built those batteries is a major brand name, I advise 
that you add neither water nor acid to the new cells. Check with the mfr, but 
most of the serious mfrs are using robotic fill equipment that is very precise. 



If some of the cells are older stock they may have self discharged a bit and 
the electrolyte level rises & falls like the tide based on state of charge. 
I'll bet if you can EQ the batts to reach equal state of charge, you also will 
find the electrolyte level to equalize. 



Jolliness, 
Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675



On Thu, Mar 24, 2011 at 11:20 AM, Nick Soleil  wrote:


Hi Benn:
Perhaps those batteries have just been sitting a little while, and need a 
recharge.  Generally speaking, if you find that the batteries test reading are 
a little low, they are probably just a little discharged.  After recharging the 
batteries, test them again.  If those readings are low, then contact the 
manufacturer with the data.  I have had great luck with battery manufacturers 
warranting their defective batteries in warranty.


 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037



From: benn kilburn 


To: Wrenches 
Sent: Thu, March 24, 2011 9:43:20 AM


Subject: [RE-wrenches] Testing new batteries





I'm curious of others experiences with testing "new" batteries right from the 
mfgr, before putting them into service.  I'm not talking about load testing, i 
mean just basics...voltage, specific gravity and electrolyte level.


I recently received some batteries (24 x 2V) and before putting them to work i 
tested all the voltages, SG's and levels.  Voltages were all with-in 0.016 V 
(2.1-2.084).  The SG's were within 0.037 (1.281-1.244).  Yes, the one with the 
lowest SG also had the lowest V.  


What concerns me a bit more than the few cells with lower SG is the consistent 
low levels of electrolyte.  All cells were between 3/4" and 1-1/2" below full, 
which is 1/4" below the bottom of the vent well tube with one exception 
that was bang-on full.  Interestingly, the one full battery was the only one 
with a different date code than the rest. 


Should the
 various levels of electrolyte mentioned be acceptable when a battery is brand 
new, straight from the mfgr?  How bout the SG's?
I'm considering adding electrolyte from a local battery shop instead of 
distilled water to top up all the batteries.  Comments?


Very thankful for the wealth of knowledge and experience on this list,benn

DayStar Renewable Energy Inc. 

benn@daystarsolar.ca780-906-7807 

HAVE A SUNNY DAY





  









  
___

List sponsored by Home Power magazine



List Address: RE-wrenches@lists.re-wrenches.org



Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm



Check out participant bios:

www.members.re-wrenches.org







___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org   ___
List sponsored by Home Power magazine

List Addr

Re: [RE-wrenches] Testing new batteries

2011-03-24 Thread Mick Abraham
Benn~ If the company that built those batteries is a major brand name, I
advise that you add neither water nor acid to the new cells. Check with the
mfr, but most of the serious mfrs are using robotic fill equipment that is
very precise.

If some of the cells are older stock they may have self discharged a bit and
the electrolyte level rises & falls like the tide based on state of charge.
I'll bet if you can EQ the batts to reach equal state of charge, you also
will find the electrolyte level to equalize.

Jolliness,

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675


On Thu, Mar 24, 2011 at 11:20 AM, Nick Soleil wrote:

> Hi Benn:
> Perhaps those batteries have just been sitting a little while, and need
> a recharge.  Generally speaking, if you find that the batteries test reading
> are a little low, they are probably just a little discharged.  After
> recharging the batteries, test them again.  If those readings are low, then
> contact the manufacturer with the data.  I have had great luck with battery
> manufacturers warranting their defective batteries in warranty.
>
> Nick Soleil
> Project Manager
> Advanced Alternative Energy Solutions, LLC
> PO Box 657
> Petaluma, CA 94953
> Cell: 707-321-2937
> Office: 707-789-9537
> Fax: 707-769-9037
>
>
> --
> *From:* benn kilburn 
> *To:* Wrenches 
> *Sent:* Thu, March 24, 2011 9:43:20 AM
> *Subject:* [RE-wrenches] Testing new batteries
>
> I'm curious of others experiences with testing "new" batteries right from
> the mfgr, before putting them into service.  I'm not talking about load
> testing, i mean just basics...voltage, specific gravity and electrolyte
> level.
>
> I recently received some batteries (24 x 2V) and before putting them to
> work i tested all the voltages, SG's and levels.  Voltages were all with-in
> 0.016 V (2.1-2.084).  The SG's were within 0.037 (1.281-1.244).  Yes, the
> one with the lowest SG also had the lowest V.
>
> What concerns me a bit more than the few cells with lower SG is the
> consistent low levels of electrolyte.  All cells were between 3/4" and
> 1-1/2" below full, which is 1/4" below the bottom of the vent well tube
> with one exception that was bang-on full.  Interestingly, the one full
> battery was the only one with a different date code than the rest.
>
> Should the various levels of electrolyte mentioned be acceptable when a
> battery is brand new, straight from the mfgr?  How bout the SG's?
>
> I'm considering adding electrolyte from a local battery shop instead of
> distilled water to top up all the batteries.  Comments?
>
> Very thankful for the wealth of knowledge and experience on this list,
> benn
>
> DayStar Renewable Energy Inc.
> b...@daystarsolar.ca
> 780-906-7807
> HAVE A SUNNY DAY
>
>
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Testing new batteries

2011-03-24 Thread Nick Soleil
Hi Benn:
Perhaps those batteries have just been sitting a little while, and need a 
recharge.  Generally speaking, if you find that the batteries test reading are 
a 
little low, they are probably just a little discharged.  After recharging the 
batteries, test them again.  If those readings are low, then contact the 
manufacturer with the data.  I have had great luck with battery manufacturers 
warranting their defective batteries in warranty.

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037





From: benn kilburn 
To: Wrenches 
Sent: Thu, March 24, 2011 9:43:20 AM
Subject: [RE-wrenches] Testing new batteries

  I'm curious of others experiences with testing "new" batteries right from the 
mfgr, before putting them into service.  I'm not talking about load testing, i 
mean just basics...voltage, specific gravity and electrolyte level.

I recently received some batteries (24 x 2V) and before putting them to work i 
tested all the voltages, SG's and levels.  Voltages were all with-in 0.016 V 
(2.1-2.084).  The SG's were within 0.037 (1.281-1.244).  Yes, the one with the 
lowest SG also had the lowest V.  

What concerns me a bit more than the few cells with lower SG is the consistent 
low levels of electrolyte.  All cells were between 3/4" and 1-1/2" below full, 
which is 1/4" below the bottom of the vent well tube with one exception 
that 
was bang-on full.  Interestingly, the one full battery was the only one with a 
different date code than the rest. 

Should the various levels of electrolyte mentioned be acceptable when a battery 
is brand new, straight from the mfgr?  How bout the SG's?

I'm considering adding electrolyte from a local battery shop instead of 
distilled water to top up all the batteries.  Comments?

Very thankful for the wealth of knowledge and experience on this list,
benn

DayStar Renewable Energy Inc. 
b...@daystarsolar.ca
780-906-7807 
HAVE A SUNNY DAY 


  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Testing new batteries

2011-03-24 Thread benn kilburn

I'm curious of others experiences with testing "new" batteries right from the 
mfgr, before putting them into service.  I'm not talking about load testing, i 
mean just basics...voltage, specific gravity and electrolyte level.
I recently received some batteries (24 x 2V) and before putting them to work i 
tested all the voltages, SG's and levels.  Voltages were all with-in 0.016 V 
(2.1-2.084).  The SG's were within 0.037 (1.281-1.244).  Yes, the one with the 
lowest SG also had the lowest V.  
What concerns me a bit more than the few cells with lower SG is the consistent 
low levels of electrolyte.  All cells were between 3/4" and 1-1/2" below full, 
which is 1/4" below the bottom of the vent well tube with one exception 
that was bang-on full.  Interestingly, the one full battery was the only one 
with a different date code than the rest. 
Should the various levels of electrolyte mentioned be acceptable when a battery 
is brand new, straight from the mfgr?  How bout the SG's?
I'm considering adding electrolyte from a local battery shop instead of 
distilled water to top up all the batteries.  Comments?
Very thankful for the wealth of knowledge and experience on this list,benn

DayStar Renewable Energy Inc. benn@daystarsolar.ca780-906-7807 HAVE A SUNNY DAY





  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org