Re: [RE-wrenches] Voltage Rise

2023-03-09 Thread Dave Tedeyan via RE-wrenches
Hi All,
Just thought I'd follow up here. Turns out the transformer was rated at
10kva. (remember, this system has three 7.7kw inverters...) We were able to
get the utility to come out and put in a 25kVa transformer, and the voltage
rise is now way more in line with what we would expect.
Cheers,
Dave

On Thu, Feb 23, 2023 at 1:36 PM Dave Tedeyan 
wrote:

> The customer has already had the utility come out to take a look. He says
> they had him turn off the solar, and then they measured 246V at the
> transformer and then said it's not their problem. He was going to try to
> get them back out to check the connections at the transformer and the
> meter.
> Also, that's a good suggestion to check each leg separately to see if
> maybe there is only one line that has a bad connection.
> Cheers,
> Dave
>
> On Thu, Feb 23, 2023 at 1:33 PM Jerry Shafer via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Wrenches, Dave
>> I have had this issue, first turn off everything, check static voltage,
>> this will drive everything else. If the static is 240 L-L look at the
>> utility side you might have small conductors, you might also have a
>> transformer size issue bottlenecking the current.  Next turn loads more the
>> better watch if there is a drop and how much. Now turn off everything and
>> power up the solar again watch the voltage at the meter if it climbs up and
>> close to limit it might be the feeders. It's all process of elimination.
>> Lots of fun
>>
>>
>> On Thu, Feb 23, 2023, 9:03 AM Dave Tedeyan via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> Hi All,
>>>
>>> I've got a customer who is having issues with high voltage at their
>>> house. This first became an issue after installing 23.1kw of AC solar
>>> output. They have some GREE heat pumps which have been having some
>>> failures. The heat pump people are saying that the problem is that the
>>> voltage is above 252V.
>>>
>>> The grid voltage was measured at 246V with the solar off, and 260V with
>>> the solar cranking. The inverters are within 10' of the MSP where there is
>>> a line side connection. Then there is 4/0 AL cable which has to go roughly
>>> 175' before it reaches the transformer. At 246V and 92A, there should only
>>> be about a 3.6V rise, or maybe 4V including the wire from the inverters to
>>> the combiner to the MSP. Yet somehow there is about 14V of rise.
>>>
>>> The service entrance cable is buried. It is in conduit where it goes
>>> into and out of the ground, but I have no idea whether there is conduit for
>>> most of the run underground. Maybe there is a nick in the cable underground
>>> which has caused corrosion? Does anyone have any ideas of how to find the
>>> cause of the increased resistance? I should go back out there with an IR
>>> camera to check the connections that I can at least get to in the house.
>>>
>>> I have suggested that they install a buck/boost transformer on the heat
>>> pump circuits to bring down the voltage a little bit. But they are also
>>> concerned about the high voltage causing issues with other electrical
>>> appliances in the house. Does anyone have any anecdata to show whether
>>> there are other hidden issues if the house is at 260V during times of high
>>> solar production?
>>>
>>> Thanks!
>>> -Dave
>>>
>>> --
>>> [image: Logo] 
>>> Dave Tedeyan, P.E.
>>> Owner | Sungineer Solar
>>> p: he | him | his
>>> a: 1653 Slaterville Rd. | Ithaca, NY 14850
>>> w: www.sungineersolar.com 
>>> c: (607) 288-2898
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> 

Re: [RE-wrenches] Voltage Rise

2023-02-23 Thread Dave Tedeyan via RE-wrenches
The customer has already had the utility come out to take a look. He says
they had him turn off the solar, and then they measured 246V at the
transformer and then said it's not their problem. He was going to try to
get them back out to check the connections at the transformer and the
meter.
Also, that's a good suggestion to check each leg separately to see if maybe
there is only one line that has a bad connection.
Cheers,
Dave

On Thu, Feb 23, 2023 at 1:33 PM Jerry Shafer via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Wrenches, Dave
> I have had this issue, first turn off everything, check static voltage,
> this will drive everything else. If the static is 240 L-L look at the
> utility side you might have small conductors, you might also have a
> transformer size issue bottlenecking the current.  Next turn loads more the
> better watch if there is a drop and how much. Now turn off everything and
> power up the solar again watch the voltage at the meter if it climbs up and
> close to limit it might be the feeders. It's all process of elimination.
> Lots of fun
>
>
> On Thu, Feb 23, 2023, 9:03 AM Dave Tedeyan via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Hi All,
>>
>> I've got a customer who is having issues with high voltage at their
>> house. This first became an issue after installing 23.1kw of AC solar
>> output. They have some GREE heat pumps which have been having some
>> failures. The heat pump people are saying that the problem is that the
>> voltage is above 252V.
>>
>> The grid voltage was measured at 246V with the solar off, and 260V with
>> the solar cranking. The inverters are within 10' of the MSP where there is
>> a line side connection. Then there is 4/0 AL cable which has to go roughly
>> 175' before it reaches the transformer. At 246V and 92A, there should only
>> be about a 3.6V rise, or maybe 4V including the wire from the inverters to
>> the combiner to the MSP. Yet somehow there is about 14V of rise.
>>
>> The service entrance cable is buried. It is in conduit where it goes into
>> and out of the ground, but I have no idea whether there is conduit for most
>> of the run underground. Maybe there is a nick in the cable underground
>> which has caused corrosion? Does anyone have any ideas of how to find the
>> cause of the increased resistance? I should go back out there with an IR
>> camera to check the connections that I can at least get to in the house.
>>
>> I have suggested that they install a buck/boost transformer on the heat
>> pump circuits to bring down the voltage a little bit. But they are also
>> concerned about the high voltage causing issues with other electrical
>> appliances in the house. Does anyone have any anecdata to show whether
>> there are other hidden issues if the house is at 260V during times of high
>> solar production?
>>
>> Thanks!
>> -Dave
>>
>> --
>> [image: Logo] 
>> Dave Tedeyan, P.E.
>> Owner | Sungineer Solar
>> p: he | him | his
>> a: 1653 Slaterville Rd. | Ithaca, NY 14850
>> w: www.sungineersolar.com 
>> c: (607) 288-2898
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 
[image: Logo] 
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com 
c: (607) 288-2898
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & 

Re: [RE-wrenches] Voltage Rise

2023-02-23 Thread Jerry Shafer via RE-wrenches
Wrenches, Dave
I have had this issue, first turn off everything, check static voltage,
this will drive everything else. If the static is 240 L-L look at the
utility side you might have small conductors, you might also have a
transformer size issue bottlenecking the current.  Next turn loads more the
better watch if there is a drop and how much. Now turn off everything and
power up the solar again watch the voltage at the meter if it climbs up and
close to limit it might be the feeders. It's all process of elimination.
Lots of fun


On Thu, Feb 23, 2023, 9:03 AM Dave Tedeyan via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi All,
>
> I've got a customer who is having issues with high voltage at their house.
> This first became an issue after installing 23.1kw of AC solar output. They
> have some GREE heat pumps which have been having some failures. The heat
> pump people are saying that the problem is that the voltage is above 252V.
>
> The grid voltage was measured at 246V with the solar off, and 260V with
> the solar cranking. The inverters are within 10' of the MSP where there is
> a line side connection. Then there is 4/0 AL cable which has to go roughly
> 175' before it reaches the transformer. At 246V and 92A, there should only
> be about a 3.6V rise, or maybe 4V including the wire from the inverters to
> the combiner to the MSP. Yet somehow there is about 14V of rise.
>
> The service entrance cable is buried. It is in conduit where it goes into
> and out of the ground, but I have no idea whether there is conduit for most
> of the run underground. Maybe there is a nick in the cable underground
> which has caused corrosion? Does anyone have any ideas of how to find the
> cause of the increased resistance? I should go back out there with an IR
> camera to check the connections that I can at least get to in the house.
>
> I have suggested that they install a buck/boost transformer on the heat
> pump circuits to bring down the voltage a little bit. But they are also
> concerned about the high voltage causing issues with other electrical
> appliances in the house. Does anyone have any anecdata to show whether
> there are other hidden issues if the house is at 260V during times of high
> solar production?
>
> Thanks!
> -Dave
>
> --
> [image: Logo] 
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> p: he | him | his
> a: 1653 Slaterville Rd. | Ithaca, NY 14850
> w: www.sungineersolar.com 
> c: (607) 288-2898
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Voltage Rise

2023-02-23 Thread Mac Lewis via RE-wrenches
Hi Dave,

Where is the utility voltage being measured?

I might suggest doing point to point voltage calculations based on the true
wire size and then verifying with measurement. It's great to use an IR
camera to look for hot spots.  Do this when the problem is the worst.  Is
it symmetric with L1 to Neutral and L2 to Neutral? Sounds like a utility
issue to me, perhaps an undersized transformer.

Good luck and please let us know what you find.

Thanks

On Thu, Feb 23, 2023 at 10:18 AM Jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi Dave
> It might be that the utility transformer is where the extra voltage rise
> is coming from?
>
> Jay
>
>
>
> On Feb 23, 2023, at 10:03 AM, Dave Tedeyan via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> 
> Hi All,
>
> I've got a customer who is having issues with high voltage at their house.
> This first became an issue after installing 23.1kw of AC solar output. They
> have some GREE heat pumps which have been having some failures. The heat
> pump people are saying that the problem is that the voltage is above 252V.
>
> The grid voltage was measured at 246V with the solar off, and 260V with
> the solar cranking. The inverters are within 10' of the MSP where there is
> a line side connection. Then there is 4/0 AL cable which has to go roughly
> 175' before it reaches the transformer. At 246V and 92A, there should only
> be about a 3.6V rise, or maybe 4V including the wire from the inverters to
> the combiner to the MSP. Yet somehow there is about 14V of rise.
>
> The service entrance cable is buried. It is in conduit where it goes into
> and out of the ground, but I have no idea whether there is conduit for most
> of the run underground. Maybe there is a nick in the cable underground
> which has caused corrosion? Does anyone have any ideas of how to find the
> cause of the increased resistance? I should go back out there with an IR
> camera to check the connections that I can at least get to in the house.
>
> I have suggested that they install a buck/boost transformer on the heat
> pump circuits to bring down the voltage a little bit. But they are also
> concerned about the high voltage causing issues with other electrical
> appliances in the house. Does anyone have any anecdata to show whether
> there are other hidden issues if the house is at 260V during times of high
> solar production?
>
> Thanks!
> -Dave
>
> --
> [image: Logo] 
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> p: he | him | his
> a: 1653 Slaterville Rd. | Ithaca, NY 14850
> w: www.sungineersolar.com 
> c: (607) 288-2898
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Voltage Rise

2023-02-23 Thread Jay via RE-wrenches
Hi DaveIt might be that the utility transformer is where the extra voltage rise is coming from?JayOn Feb 23, 2023, at 10:03 AM, Dave Tedeyan via RE-wrenches  wrote:Hi All,I've got a customer who is having issues with high voltage at their house. This first became an issue after installing 23.1kw of AC solar output. They have some GREE heat pumps which have been having some failures. The heat pump people are saying that the problem is that the voltage is above 252V. The grid voltage was measured at 246V with the solar off, and 260V with the solar cranking. The inverters are within 10' of the MSP where there is a line side connection. Then there is 4/0 AL cable which has to go roughly 175' before it reaches the transformer. At 246V and 92A, there should only be about a 3.6V rise, or maybe 4V including the wire from the inverters to the combiner to the MSP. Yet somehow there is about 14V of rise. The service entrance cable is buried. It is in conduit where it goes into and out of the ground, but I have no idea whether there is conduit for most of the run underground. Maybe there is a nick in the cable underground which has caused corrosion? Does anyone have any ideas of how to find the cause of the increased resistance? I should go back out there with an IR camera to check the connections that I can at least get to in the house. I have suggested that they install a buck/boost transformer on the heat pump circuits to bring down the voltage a little bit. But they are also concerned about the high voltage causing issues with other electrical appliances in the house. Does anyone have any anecdata to show whether there are other hidden issues if the house is at 260V during times of high solar production?Thanks!-Dave-- Dave Tedeyan, P.E.Owner | Sungineer Solarp: he | him | hisa: 1653 Slaterville Rd. | Ithaca, NY 14850w: www.sungineersolar.comc: (607) 288-2898
___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Voltage Rise

2023-02-23 Thread Dave Tedeyan via RE-wrenches
Hi All,

I've got a customer who is having issues with high voltage at their house.
This first became an issue after installing 23.1kw of AC solar output. They
have some GREE heat pumps which have been having some failures. The heat
pump people are saying that the problem is that the voltage is above 252V.

The grid voltage was measured at 246V with the solar off, and 260V with the
solar cranking. The inverters are within 10' of the MSP where there is a
line side connection. Then there is 4/0 AL cable which has to go roughly
175' before it reaches the transformer. At 246V and 92A, there should only
be about a 3.6V rise, or maybe 4V including the wire from the inverters to
the combiner to the MSP. Yet somehow there is about 14V of rise.

The service entrance cable is buried. It is in conduit where it goes into
and out of the ground, but I have no idea whether there is conduit for most
of the run underground. Maybe there is a nick in the cable underground
which has caused corrosion? Does anyone have any ideas of how to find the
cause of the increased resistance? I should go back out there with an IR
camera to check the connections that I can at least get to in the house.

I have suggested that they install a buck/boost transformer on the heat
pump circuits to bring down the voltage a little bit. But they are also
concerned about the high voltage causing issues with other electrical
appliances in the house. Does anyone have any anecdata to show whether
there are other hidden issues if the house is at 260V during times of high
solar production?

Thanks!
-Dave

-- 
[image: Logo] 
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com 
c: (607) 288-2898
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org