[RE-wrenches] WOW Something Gone Very Wrong

2012-03-29 Thread Mark Frye

*



Rooftop solar installation sparks fires in Trenton, New Jersey* 
28.03.2012: According to local news portal NJ.com, a rooftop solar 
system has triggered several small fires at a recycling center in 
Trenton, New Jersey. The article reports that a major malfunction in 
the rooftop solar panel...caused small fires and surges of electricity 
producing arcs of current to break out. According to Fire Battalion 
Chief Rich Seeds, There definitely was a problem with the installation, 
the equipment. Firefighters on the scene said that an inverter was 
sparking and unusable. The firefighters, with the help of 
electricians, had to manually disconnect the 100-panel system from the 
electrical grid before they could safely put out the fire. The fire 
started while electricians were hooking up junction boxes on the system. 
Earlier this month, a New Jersey General Assembly committee approved a 
bill (A266) that would require buildings to clearly label with an 
exterior emblem whether they have solar panels installed on the 
premises. The measure, recommended by the National Fire Protection 
Association, is aimed at protecting firefighters from dangers posed by 
solar panels. The greater Assembly has yet to discuss the bill, but the 
New Jersey Senate version of the bill (S507) was introduced in the 
Senate on Jan. 10, 2012 and is currently being reviewed by the Senate 
Environment and Energy Committee. ... Source: NJ.com, New Jersey 
Assembly Republicans, eLobbyist; Summary: PHOTON


*http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle
_ro.html* 
http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle_ro.html


*http://www.njassemblyrepublicans.com/?p=2862*

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] WOW Something Gone Very Wrong

2012-03-29 Thread David Brearley
Perfect example of why it¹s a good idea to start designing and deploying
systems now that meet the fuse servicing requirements found in NEC 2011‹even
if these are not required by your AHJ yet.

People on this list are probably ahead of that curve. If not, you might want
to check out these articles:

http://solarprofessional.com/article/?file=SP4_3_pg14_QA_2search=  (Bill
Brooks article on Fuse Servicing disconnect requirements)

http://solarprofessional.com/article/?file=SP4_3_pg64_Hrensearch=  (Changes
to Code in 2011; See content under ³690.6, Fuses² subheading)

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer 

On 3/29/12 9:36 AM, Mark Frye ma...@berkeleysolar.com wrote:


  
  
  
  Rooftop solar installation sparks fires in Trenton, New Jersey 28.03.2012:
 According to local news portal NJ.com, a rooftop solar system has triggered
 several small fires at a recycling center in Trenton, New Jersey. The article
 reports that ³a major malfunction in the rooftop solar panelŠcaused small
 fires and surges of electricity producing arcs of current to break out.²
 According to Fire Battalion Chief Rich Seeds, ³There definitely was a problem
 with the installation, the equipment.² Firefighters on the scene said that an
 inverter was ³sparking and unusable.² The firefighters, with the help of
 electricians, had to manually disconnect the 100-panel system from the
 electrical grid before they could safely put out the fire. The fire started
 while electricians were hooking up junction boxes on the system. Earlier this
 month, a New Jersey General Assembly committee approved a bill (A266) that
 would require buildings to clearly label with an exterior emblem whether they
 have solar panels installed on the premises. The measure, recommended by the
 National Fire Protection Association, is aimed at protecting firefighters from
 dangers posed by solar panels. The greater Assembly has yet to discuss the
 bill, but the New Jersey Senate version of the bill (S507) was introduced in
 the Senate on Jan. 10, 2012 and is currently being reviewed by the Senate
 Environment and Energy Committee. Š Source: NJ.com, New Jersey Assembly
 Republicans, eLobbyist; Summary: PHOTON
 
 http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle
  _ro.html 
 http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle_ro.htm
 l 
  
 
 http://www.njassemblyrepublicans.com/?p=2862
 http://www.njassemblyrepublicans.com/?p=2862
  
 



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] WOW Something Gone Very Wrong

2012-03-29 Thread Bill Brooks
All,

 

It is very likely that the something gone very wrong was a wiring mistake by
the installing contractor. Many installers are clueless about the danger and
consequences of getting the polarity wrong in strings or combiner box
circuits. It is very likely that the contractor mixed up their combiner box
circuits causing the combiner boxes and conductors to catch on fire as soon
as the fuses were installed.

 

Polarity should be checked and verified on all circuits a total of 2 or 3
times during the course of installation and commissioning. It is the single
most important test from a safety point of view.

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David
Brearley
Sent: Thursday, March 29, 2012 8:25 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] WOW Something Gone Very Wrong

 

Perfect example of why it's a good idea to start designing and deploying
systems now that meet the fuse servicing requirements found in NEC 2011-even
if these are not required by your AHJ yet. 

People on this list are probably ahead of that curve. If not, you might want
to check out these articles:

http://solarprofessional.com/article/?file=SP4_3_pg14_QA_2
http://solarprofessional.com/article/?file=SP4_3_pg14_QA_2search=
search=  (Bill Brooks article on Fuse Servicing disconnect requirements)

http://solarprofessional.com/article/?file=SP4_3_pg64_Hren
http://solarprofessional.com/article/?file=SP4_3_pg64_Hrensearch=
search=  (Changes to Code in 2011; See content under 690.6, Fuses
subheading)

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer T

On 3/29/12 9:36 AM, Mark Frye ma...@berkeleysolar.com wrote:

  

 
 
 Rooftop solar installation sparks fires in Trenton, New Jersey 28.03.2012:
According to local news portal NJ.com, a rooftop solar system has triggered
several small fires at a recycling center in Trenton, New Jersey. The
article reports that a major malfunction in the rooftop solar panel.caused
small fires and surges of electricity producing arcs of current to break
out. According to Fire Battalion Chief Rich Seeds, There definitely was a
problem with the installation, the equipment. Firefighters on the scene
said that an inverter was sparking and unusable. The firefighters, with
the help of electricians, had to manually disconnect the 100-panel system
from the electrical grid before they could safely put out the fire. The fire
started while electricians were hooking up junction boxes on the system.
Earlier this month, a New Jersey General Assembly committee approved a bill
(A266) that would require buildings to clearly label with an exterior emblem
whether they have solar panels installed on the premises. The measure,
recommended by the National Fire Protection Association, is aimed at
protecting firefighters from dangers posed by solar panels. The greater
Assembly has yet to discuss the bill, but the New Jersey Senate version of
the bill (S507) was introduced in the Senate on Jan. 10, 2012 and is
currently being reviewed by the Senate Environment and Energy Committee. .
Source: NJ.com, New Jersey Assembly Republicans, eLobbyist; Summary: PHOTON 

http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle
 _ro.html
http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle_ro.h
tml 
 

http://www.njassemblyrepublicans.com/?p=2862
http://www.njassemblyrepublicans.com/?p=2862 
 

  _  

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] WOW Something Gone Very Wrong

2012-03-29 Thread David Brearley
That was my suspicion as well. Simple wiring mistake. Inadequate
commissioning protocol.


On 3/29/12 2:02 PM, Bill Brooks billbroo...@yahoo.com wrote:

 All,
  
 It is very likely that the something gone very wrong was a wiring mistake by
 the installing contractor. Many installers are clueless about the danger and
 consequences of getting the polarity wrong in strings or combiner box
 circuits. It is very likely that the contractor mixed up their combiner box
 circuits causing the combiner boxes and conductors to catch on fire as soon as
 the fuses were installed.
  
 Polarity should be checked and verified on all circuits a total of 2 or 3
 times during the course of installation and commissioning. It is the single
 most important test from a safety point of view.
  
 Bill.
  
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Brearley
 Sent: Thursday, March 29, 2012 8:25 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] WOW Something Gone Very Wrong
  
 Perfect example of why it¹s a good idea to start designing and deploying
 systems now that meet the fuse servicing requirements found in NEC 2011‹even
 if these are not required by your AHJ yet.
 
 People on this list are probably ahead of that curve. If not, you might want
 to check out these articles:
 
 http://solarprofessional.com/article/?file=SP4_3_pg14_QA_2search=  (Bill
 Brooks article on Fuse Servicing disconnect requirements)
 
 http://solarprofessional.com/article/?file=SP4_3_pg64_Hrensearch=  (Changes
 to Code in 2011; See content under ³690.6, Fuses² subheading)
 
 David Brearley, Senior Technical Editor
 SolarPro magazine
 NABCEP Certified PV Installer 
 
 On 3/29/12 9:36 AM, Mark Frye ma...@berkeleysolar.com wrote:
   
 
  
  
  Rooftop solar installation sparks fires in Trenton, New Jersey 28.03.2012:
 According to local news portal NJ.com, a rooftop solar system has triggered
 several small fires at a recycling center in Trenton, New Jersey. The article
 reports that ³a major malfunction in the rooftop solar panelŠcaused small
 fires and surges of electricity producing arcs of current to break out.²
 According to Fire Battalion Chief Rich Seeds, ³There definitely was a problem
 with the installation, the equipment.² Firefighters on the scene said that an
 inverter was ³sparking and unusable.² The firefighters, with the help of
 electricians, had to manually disconnect the 100-panel system from the
 electrical grid before they could safely put out the fire. The fire started
 while electricians were hooking up junction boxes on the system. Earlier this
 month, a New Jersey General Assembly committee approved a bill (A266) that
 would require buildings to clearly label with an exterior emblem whether they
 have solar panels installed on the premises. The measure, recommended by the
 National Fire Protection Association, is aimed at protecting firefighters from
 dangers posed by solar panels. The greater Assembly has yet to discuss the
 bill, but the New Jersey Senate version of the bill (S507) was introduced in
 the Senate on Jan. 10, 2012 and is currently being reviewed by the Senate
 Environment and Energy Committee. Š Source: NJ.com, New Jersey Assembly
 Republicans, eLobbyist; Summary: PHOTON
 
 http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle
  _ro.html 
 http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle_ro.htm
 l 
  
 
 http://www.njassemblyrepublicans.com/?p=2862
 http://www.njassemblyrepublicans.com/?p=2862
  
 
 
  
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 David Brearley, Senior Technical Editor
 SolarPro magazine
 NABCEP Certified PV Installer 
 david.brear...@solarprofessional.com
 Direct: 541.261.6545
 Fax:  541.512.0343
 
 Visit our Web site at solarprofessional.com
 
 (Sample copy available for download at: solarprofessional.com/sample)
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] WOW Something Gone Very Wrong

2012-03-29 Thread Brian Mehalic
Hmm...no voltage...must've left the fuse out of this holder...lemme just
open it up a take a quick looksie

On Thu, Mar 29, 2012 at 3:41 PM, David Brearley 
david.brear...@solarprofessional.com wrote:

  That was my suspicion as well. Simple wiring mistake. Inadequate
 commissioning protocol.



 On 3/29/12 2:02 PM, Bill Brooks billbroo...@yahoo.com wrote:

 All,

 It is very likely that the something gone very wrong was a wiring mistake
 by the installing contractor. Many installers are clueless about the danger
 and consequences of getting the polarity wrong in strings or combiner box
 circuits. It is very likely that the contractor mixed up their combiner box
 circuits causing the combiner boxes and conductors to catch on fire as soon
 as the fuses were installed.

 Polarity should be checked and verified on all circuits a total of 2 or 3
 times during the course of installation and commissioning. It is the single
 most important test from a safety point of view.

 Bill.


 *From:* re-wrenches-boun...@lists.re-wrenches.org [
 mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org]
 *On Behalf Of *David Brearley
 *Sent:* Thursday, March 29, 2012 8:25 AM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] WOW Something Gone Very Wrong

 Perfect example of why it’s a good idea to start designing and deploying
 systems now that meet the fuse servicing requirements found in NEC
 2011—even if these are not required by your AHJ yet.

 People on this list are probably ahead of that curve. If not, you might
 want to check out these articles:

 http://solarprofessional.com/article/?file=SP4_3_pg14_QA_2search=  (Bill
 Brooks article on Fuse Servicing disconnect requirements)

 http://solarprofessional.com/article/?file=SP4_3_pg64_Hrensearch= (Changes 
 to Code in 2011; See content under “690.6, Fuses” subheading)

 David Brearley, Senior Technical Editor
 *SolarPro* magazine
 NABCEP Certified PV Installer ™

 On 3/29/12 9:36 AM, Mark Frye ma...@berkeleysolar.com wrote:

 *


  Rooftop solar installation sparks fires in Trenton, New Jersey* 28.03.2012:
 According to local news portal NJ.com, a rooftop solar system has triggered
 several small fires at a recycling center in Trenton, New Jersey. The
 article reports that “a major malfunction in the rooftop solar panel…caused
 small fires and surges of electricity producing arcs of current to break
 out.” According to Fire Battalion Chief Rich Seeds, “There definitely was a
 problem with the installation, the equipment.” Firefighters on the scene
 said that an inverter was “sparking and unusable.” The firefighters, with
 the help of electricians, had to manually disconnect the 100-panel system
 from the electrical grid before they could safely put out the fire. The
 fire started while electricians were hooking up junction boxes on the
 system. Earlier this month, a New Jersey General Assembly committee
 approved a bill (A266) that would require buildings to clearly label with
 an exterior emblem whether they have solar panels installed on the
 premises. The measure, recommended by the National Fire Protection
 Association, is aimed at protecting firefighters from dangers posed by
 solar panels. The greater Assembly has yet to discuss the bill, but the New
 Jersey Senate version of the bill (S507) was introduced in the Senate on
 Jan. 10, 2012 and is currently being reviewed by the Senate Environment and
 Energy Committee. … Source: NJ.com, New Jersey Assembly Republicans,
 eLobbyist; Summary: PHOTON

 *http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle
  _ro.html* 
 http://www.nj.com/mercer/index.ssf/2012/03/trenton_firefighters_battle_ro.html



 *http://www.njassemblyrepublicans.com/?p=2862* 
 http://www.njassemblyrepublicans.com/?p=2862


 --




 --
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


 David Brearley, Senior Technical Editor
 *SolarPro* magazine
 NABCEP Certified PV Installer ™
 david.brear...@solarprofessional.com
 Direct: 541.261.6545
 Fax:  541.512.0343
 *
 *Visit our Web site at solarprofessional.com

 (Sample copy available for download at: solarprofessional.com/sample)



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out