At an SMA training last year they recommended the following temperature 
adders:


Open field: +22°C
Rooftop, lots of ventilation: +28°C
Rooftop, some ventilation: +29°C
Rooftop, little ventilation: +32°C
Rooftop BIPV, no ventilation: +43°C
Façade, some ventilation: +35°C
Façade, little ventilation: +39°C
Façade BIPV, no ventilation: +55°C

For your Sanyo project, I'd agree that the pole mount would be a good 
fit and +25C would seem to be OK. As you know, the 301VDC VMP on an 
inverter with a 300V+ tracking window wouldn't work very well during the 
summers for very long. My own rooftop system has a design VMP of around 
294 at 70C module temperature and I've seen it a bit lower than that on 
a sunny day-- I think it's because in irradiances below 1000Wm/2, the 
modules can still get plenty hot but the lower irradiance doesn't bring 
the VMP up to 100%. So all told, maybe plan for an array minimum of:


Inverter Tracking Minimum
/0.85 (degradation and voltage tolerance)
/0.95 (effect I just described)
/0.825 (60C operating temp)
= minimum string VMP at STC

(similar to what Bill said)

On 2011/11/30 11:04, Kirk Herander wrote:

Thanks for all the good response. Speaking of monkey wrenches, these are
Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet  above the
roof surface. They will absorb reflected light on the backside, so I
assume the cells will operate at a higher temp. But they are elevated
enough to simulate a pole-mount, thus lowering operating cell temp. So
what operating temp to use? If I use 25 C as the operating temp, the low
voltage calc comes out to 301 vdc (inverter min is 300 – using SMA
US8000). If I use 15 C the calc is 308 vdc. This is for a 6 panel
string. Unfortunately I really don’t want to use 7 panel strings due to
the layout. If I used a US7000 it would work since min vdc in is 250.
However the inverters are part of a SunnyTower and I can’t swap a 7000
for an 8000 without voiding the Tower UL listing.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

*From:*re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*b...@midnitesolar.com
*Sent:* Wednesday, November 30, 2011 1:03 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] calculating low string voltage



If you really want to throw a monkey wrench into the mix, bring up
partial shading...

Or, maybe that's just not allowed in that debate ?? Just a thought.

boB







On 11/29/2011 8:39 PM, Kent Osterberg wrote:

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to add
a little more. Most module datasheets show a normal operating cell
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
temperature, 800 W/sq m, and calm wind and nothing blocking the airflow
on the back of the module. That 27.5°C temperature rise should be pretty
close to the temperature rise that occurs for a pole-top mount. It's
common to see people use 25°C for modules on a pole and 30°C or 35°C on
a roof and there are data that support these typical values. With 1000
W/sq irradiance, the temperature rise can obviously be more too. Between
the intensity of the sun, the direction of the sun, the color of the
roof, the spacing off the roof, and the wind speed there is a lot that
is different from one system to the next or even one day to the next.

Most PV module spec sheets don't give you a temperature coefficient for
Vmp. I've seen people use the the Voc coefficient, usually expressed as
a percentage, for both Voc and Vmp. Big mistake. Data from NREL
indicates as Bill said, the temperature coefficient for Vmp is higher
than that the temperature coefficient for Voc. That's particularly true
when the coefficient is expressed as a percentage per °C. Since there
are very few manufacturer's that give both temperature coefficients,
I'll use a value from an old Evergreen module for an example. The
Evergreen ES-195 datasheet shows Voc = 30.5 volts with a coefficient of
-0.34%/°C and Vmp = 27.1 volts with a coefficient of -0.47%/°C. Since
one shouldn't add volts and percents, I'll put the temperature
coefficients in volts/°C: Voc = 30.5 V - 0.10 V/°C and Vmp = 27.1 V -
0.13V/°C. So Vmp is moving faster than Voc, but not a lot faster. That's
generically true for c-Si or poly-Si.

Kent Osterberg

Blue Mountain Solar, Inc.

www.bluemountainsolar.com  http://www.bluemountainsolar.com

t: 541-568-4882


On 11/29/2011 11:48 AM, Kirk Herander wrote:

I am in debate with a PE over calculation of low voltage of a series
string on a hot day. He insists that an arbitrary high cell temp is
factored in, not just ambient temperature. Could someone please give an
accepted formula for this calculation? Thanks. I cannot find a clear
reference to low voltage calculation on a hot day (but every reference
material is clear on how to calculate high voltage on a cold day

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Ray Walters
That's more detailed info, but I still am wondering what ambient temp to 
apply (which AHSRAE #) with the temp adder.  Daryl suggested using a 2% 
high temp.  Also, where are you all getting your weather data?  I found 
the NEC suggested ASHRAE manual to be close to $200.  That's a bit much 
just to get a couple of numbers for our design.
It seems this calculation of low voltage is far from being entirely 
codified, and I'm trying to standardize it somewhat for my PV class. Non 
of the design manuals I have currently are even close to this level of 
complexity, yet this is obviously an important calculation.  Should I 
suggest that my students just use the inverter manufacturers' online 
tools, and forget about trying to run this voltage calc themselves?


Thanks,

Ray

On 12/1/2011 6:30 AM, Dave Click wrote:
At an SMA training last year they recommended the following 
temperature adders:


Open field: +22°C
Rooftop, lots of ventilation: +28°C
Rooftop, some ventilation: +29°C
Rooftop, little ventilation: +32°C
Rooftop BIPV, no ventilation: +43°C
Façade, some ventilation: +35°C
Façade, little ventilation: +39°C
Façade BIPV, no ventilation: +55°C

For your Sanyo project, I'd agree that the pole mount would be a good 
fit and +25C would seem to be OK. As you know, the 301VDC VMP on an 
inverter with a 300V+ tracking window wouldn't work very well during 
the summers for very long. My own rooftop system has a design VMP of 
around 294 at 70C module temperature and I've seen it a bit lower than 
that on a sunny day-- I think it's because in irradiances below 
1000Wm/2, the modules can still get plenty hot but the lower 
irradiance doesn't bring the VMP up to 100%. So all told, maybe plan 
for an array minimum of:


Inverter Tracking Minimum
/0.85 (degradation and voltage tolerance)
/0.95 (effect I just described)
/0.825 (60C operating temp)
= minimum string VMP at STC

(similar to what Bill said)

On 2011/11/30 11:04, Kirk Herander wrote:

Thanks for all the good response. Speaking of monkey wrenches, these are
Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet  above the
roof surface. They will absorb reflected light on the backside, so I
assume the cells will operate at a higher temp. But they are elevated
enough to simulate a pole-mount, thus lowering operating cell temp. So
what operating temp to use? If I use 25 C as the operating temp, the low
voltage calc comes out to 301 vdc (inverter min is 300 – using SMA
US8000). If I use 15 C the calc is 308 vdc. This is for a 6 panel
string. Unfortunately I really don’t want to use 7 panel strings due to
the layout. If I used a US7000 it would work since min vdc in is 250.
However the inverters are part of a SunnyTower and I can’t swap a 7000
for an 8000 without voiding the Tower UL listing.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

*From:*re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*b...@midnitesolar.com
*Sent:* Wednesday, November 30, 2011 1:03 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] calculating low string voltage



If you really want to throw a monkey wrench into the mix, bring up
partial shading...

Or, maybe that's just not allowed in that debate ?? Just a thought.

boB







On 11/29/2011 8:39 PM, Kent Osterberg wrote:

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to add
a little more. Most module datasheets show a normal operating cell
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
temperature, 800 W/sq m, and calm wind and nothing blocking the airflow
on the back of the module. That 27.5°C temperature rise should be pretty
close to the temperature rise that occurs for a pole-top mount. It's
common to see people use 25°C for modules on a pole and 30°C or 35°C on
a roof and there are data that support these typical values. With 1000
W/sq irradiance, the temperature rise can obviously be more too. Between
the intensity of the sun, the direction of the sun, the color of the
roof, the spacing off the roof, and the wind speed there is a lot that
is different from one system to the next or even one day to the next.

Most PV module spec sheets don't give you a temperature coefficient for
Vmp. I've seen people use the the Voc coefficient, usually expressed as
a percentage, for both Voc and Vmp. Big mistake. Data from NREL
indicates as Bill said, the temperature coefficient for Vmp is higher
than that the temperature coefficient for Voc. That's particularly true
when the coefficient is expressed as a percentage per °C. Since there
are very few manufacturer's that give both temperature coefficients,
I'll use a value from an old Evergreen module for an example. The
Evergreen ES-195 datasheet shows Voc = 30.5 volts with a coefficient of
-0.34%/°C and Vmp = 27.1 volts with a coefficient of -0.47%/°C. Since
one

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Gary Willett

Ray:

Look at Appendix F in the Expedited Permit Process for PV Systems - A 
Standardized Process for the Review of Small-Scale PV Systems Prepared 
by Bill Brooks, P.E. Brooks Engineering


This document provides the ASHRE temperatures for a lot of locations 
around the USA.


http://www.solarabcs.org/about/publications/reports/expedited-permit/pdfs/Expermitprocess.pdf


Regards,


Gary Willett, PE


On 12/1/2011 14:48, Ray Walters wrote:
That's more detailed info, but I still am wondering what ambient temp 
to apply (which AHSRAE #) with the temp adder.  Daryl suggested using 
a 2% high temp.  Also, where are you all getting your weather data?  I 
found the NEC suggested ASHRAE manual to be close to $200.  That's a 
bit much just to get a couple of numbers for our design.
It seems this calculation of low voltage is far from being entirely 
codified, and I'm trying to standardize it somewhat for my PV class. 
Non of the design manuals I have currently are even close to this 
level of complexity, yet this is obviously an important calculation.  
Should I suggest that my students just use the inverter manufacturers' 
online tools, and forget about trying to run this voltage calc 
themselves?


Thanks,

Ray

On 12/1/2011 6:30 AM, Dave Click wrote:
At an SMA training last year they recommended the following 
temperature adders:


Open field: +22°C
Rooftop, lots of ventilation: +28°C
Rooftop, some ventilation: +29°C
Rooftop, little ventilation: +32°C
Rooftop BIPV, no ventilation: +43°C
Façade, some ventilation: +35°C
Façade, little ventilation: +39°C
Façade BIPV, no ventilation: +55°C

For your Sanyo project, I'd agree that the pole mount would be a good 
fit and +25C would seem to be OK. As you know, the 301VDC VMP on an 
inverter with a 300V+ tracking window wouldn't work very well during 
the summers for very long. My own rooftop system has a design VMP of 
around 294 at 70C module temperature and I've seen it a bit lower 
than that on a sunny day-- I think it's because in irradiances below 
1000Wm/2, the modules can still get plenty hot but the lower 
irradiance doesn't bring the VMP up to 100%. So all told, maybe plan 
for an array minimum of:


Inverter Tracking Minimum
/0.85 (degradation and voltage tolerance)
/0.95 (effect I just described)
/0.825 (60C operating temp)
= minimum string VMP at STC

(similar to what Bill said)

On 2011/11/30 11:04, Kirk Herander wrote:
Thanks for all the good response. Speaking of monkey wrenches, these 
are

Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet  above the
roof surface. They will absorb reflected light on the backside, so I
assume the cells will operate at a higher temp. But they are elevated
enough to simulate a pole-mount, thus lowering operating cell temp. So
what operating temp to use? If I use 25 C as the operating temp, the 
low

voltage calc comes out to 301 vdc (inverter min is 300 – using SMA
US8000). If I use 15 C the calc is 308 vdc. This is for a 6 panel
string. Unfortunately I really don’t want to use 7 panel strings due to
the layout. If I used a US7000 it would work since min vdc in is 250.
However the inverters are part of a SunnyTower and I can’t swap a 7000
for an 8000 without voiding the Tower UL listing.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

*From:*re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*b...@midnitesolar.com
*Sent:* Wednesday, November 30, 2011 1:03 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] calculating low string voltage



If you really want to throw a monkey wrench into the mix, bring up
partial shading...

Or, maybe that's just not allowed in that debate ?? Just a thought.

boB







On 11/29/2011 8:39 PM, Kent Osterberg wrote:

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to 
add

a little more. Most module datasheets show a normal operating cell
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
temperature, 800 W/sq m, and calm wind and nothing blocking the airflow
on the back of the module. That 27.5°C temperature rise should be 
pretty

close to the temperature rise that occurs for a pole-top mount. It's
common to see people use 25°C for modules on a pole and 30°C or 35°C on
a roof and there are data that support these typical values. With 
1000
W/sq irradiance, the temperature rise can obviously be more too. 
Between

the intensity of the sun, the direction of the sun, the color of the
roof, the spacing off the roof, and the wind speed there is a lot that
is different from one system to the next or even one day to the next.

Most PV module spec sheets don't give you a temperature coefficient for
Vmp. I've seen people use the the Voc coefficient, usually expressed as
a percentage, for both Voc and Vmp. Big mistake. Data from NREL
indicates as Bill said

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Glenn Burt
ASHRAE temp data as applicable to PV can be found (with some digging) on the
Solar ABCs website.
http://solarabcs.org/about/publications/reports/expedited-permit/map/map_int
ro.html

-Glenn

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Thursday, December 01, 2011 3:49 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] calculating low string voltage

That's more detailed info, but I still am wondering what ambient temp to
apply (which AHSRAE #) with the temp adder.  Daryl suggested using a 2% high
temp.  Also, where are you all getting your weather data?  I found the NEC
suggested ASHRAE manual to be close to $200.  That's a bit much just to get
a couple of numbers for our design.
It seems this calculation of low voltage is far from being entirely
codified, and I'm trying to standardize it somewhat for my PV class. Non of
the design manuals I have currently are even close to this level of
complexity, yet this is obviously an important calculation.  Should I
suggest that my students just use the inverter manufacturers' online tools,
and forget about trying to run this voltage calc themselves?

Thanks,

Ray

On 12/1/2011 6:30 AM, Dave Click wrote:
 At an SMA training last year they recommended the following 
 temperature adders:

 Open field: +22°C
 Rooftop, lots of ventilation: +28°C
 Rooftop, some ventilation: +29°C
 Rooftop, little ventilation: +32°C
 Rooftop BIPV, no ventilation: +43°C
 Façade, some ventilation: +35°C
 Façade, little ventilation: +39°C
 Façade BIPV, no ventilation: +55°C

 For your Sanyo project, I'd agree that the pole mount would be a good 
 fit and +25C would seem to be OK. As you know, the 301VDC VMP on an 
 inverter with a 300V+ tracking window wouldn't work very well during 
 the summers for very long. My own rooftop system has a design VMP of 
 around 294 at 70C module temperature and I've seen it a bit lower than 
 that on a sunny day-- I think it's because in irradiances below 
 1000Wm/2, the modules can still get plenty hot but the lower 
 irradiance doesn't bring the VMP up to 100%. So all told, maybe plan 
 for an array minimum of:

 Inverter Tracking Minimum
 /0.85 (degradation and voltage tolerance)
 /0.95 (effect I just described)
 /0.825 (60C operating temp)
 = minimum string VMP at STC

 (similar to what Bill said)

 On 2011/11/30 11:04, Kirk Herander wrote:
 Thanks for all the good response. Speaking of monkey wrenches, these 
 are Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet  
 above the roof surface. They will absorb reflected light on the 
 backside, so I assume the cells will operate at a higher temp. But 
 they are elevated enough to simulate a pole-mount, thus lowering 
 operating cell temp. So what operating temp to use? If I use 25 C as 
 the operating temp, the low voltage calc comes out to 301 vdc 
 (inverter min is 300 – using SMA US8000). If I use 15 C the calc is 
 308 vdc. This is for a 6 panel string. Unfortunately I really don’t 
 want to use 7 panel strings due to the layout. If I used a US7000 it
would work since min vdc in is 250.
 However the inverters are part of a SunnyTower and I can’t swap a 
 7000 for an 8000 without voiding the Tower UL listing.

 Kirk Herander

 VT Solar, LLC

 dba Vermont Solar Engineering

 NABCEP^TM Certified installer Charter Member

 NYSERDA-eligible Installer

 VT RE Incentive Program Partner

 *From:*re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
 *b...@midnitesolar.com
 *Sent:* Wednesday, November 30, 2011 1:03 AM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] calculating low string voltage



 If you really want to throw a monkey wrench into the mix, bring up 
 partial shading...

 Or, maybe that's just not allowed in that debate ?? Just a thought.

 boB







 On 11/29/2011 8:39 PM, Kent Osterberg wrote:

 Kirk,

 You've got some good feedback on this from Ray and Bill. I'll try to 
 add a little more. Most module datasheets show a normal operating 
 cell temperature, NOCT, value that's typically 47.5°C. That's 20°C 
 ambient temperature, 800 W/sq m, and calm wind and nothing blocking 
 the airflow on the back of the module. That 27.5°C temperature rise 
 should be pretty close to the temperature rise that occurs for a 
 pole-top mount. It's common to see people use 25°C for modules on a 
 pole and 30°C or 35°C on a roof and there are data that support these 
 typical values. With 1000 W/sq irradiance, the temperature rise can 
 obviously be more too. Between the intensity of the sun, the 
 direction of the sun, the color of the roof, the spacing off the 
 roof, and the wind speed there is a lot that is different from one system
to the next or even one day to the next.

 Most PV module spec sheets don't give you a temperature coefficient 
 for Vmp. I've seen people use the the Voc coefficient, usually 
 expressed as a percentage

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Dave Click
Ray, I'd use the 2% high temp. The 0.4% high temp would only be reached 
a few hours out of the year. However, the 0.4% high is only a few degC 
warmer than the 2% high, so that would change my fudge factor below by a 
max of 1.8-2.0%.


On 2011/12/1 15:48, Ray Walters wrote:

That's more detailed info, but I still am wondering what ambient temp to
apply (which AHSRAE #) with the temp adder. Daryl suggested using a 2%
high temp. Also, where are you all getting your weather data? I found
the NEC suggested ASHRAE manual to be close to $200. That's a bit much
just to get a couple of numbers for our design.
It seems this calculation of low voltage is far from being entirely
codified, and I'm trying to standardize it somewhat for my PV class. Non
of the design manuals I have currently are even close to this level of
complexity, yet this is obviously an important calculation. Should I
suggest that my students just use the inverter manufacturers' online
tools, and forget about trying to run this voltage calc themselves?

Thanks,

Ray

On 12/1/2011 6:30 AM, Dave Click wrote:

At an SMA training last year they recommended the following
temperature adders:

Open field: +22°C
Rooftop, lots of ventilation: +28°C
Rooftop, some ventilation: +29°C
Rooftop, little ventilation: +32°C
Rooftop BIPV, no ventilation: +43°C
Façade, some ventilation: +35°C
Façade, little ventilation: +39°C
Façade BIPV, no ventilation: +55°C

For your Sanyo project, I'd agree that the pole mount would be a good
fit and +25C would seem to be OK. As you know, the 301VDC VMP on an
inverter with a 300V+ tracking window wouldn't work very well during
the summers for very long. My own rooftop system has a design VMP of
around 294 at 70C module temperature and I've seen it a bit lower than
that on a sunny day-- I think it's because in irradiances below
1000Wm/2, the modules can still get plenty hot but the lower
irradiance doesn't bring the VMP up to 100%. So all told, maybe plan
for an array minimum of:

Inverter Tracking Minimum
/0.85 (degradation and voltage tolerance)
/0.95 (effect I just described)
/0.825 (60C operating temp)
= minimum string VMP at STC

(similar to what Bill said)

On 2011/11/30 11:04, Kirk Herander wrote:

Thanks for all the good response. Speaking of monkey wrenches, these are
Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet above the
roof surface. They will absorb reflected light on the backside, so I
assume the cells will operate at a higher temp. But they are elevated
enough to simulate a pole-mount, thus lowering operating cell temp. So
what operating temp to use? If I use 25 C as the operating temp, the low
voltage calc comes out to 301 vdc (inverter min is 300 – using SMA
US8000). If I use 15 C the calc is 308 vdc. This is for a 6 panel
string. Unfortunately I really don’t want to use 7 panel strings due to
the layout. If I used a US7000 it would work since min vdc in is 250.
However the inverters are part of a SunnyTower and I can’t swap a 7000
for an 8000 without voiding the Tower UL listing.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

*From:*re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*b...@midnitesolar.com
*Sent:* Wednesday, November 30, 2011 1:03 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] calculating low string voltage



If you really want to throw a monkey wrench into the mix, bring up
partial shading...

Or, maybe that's just not allowed in that debate ?? Just a thought.

boB







On 11/29/2011 8:39 PM, Kent Osterberg wrote:

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to add
a little more. Most module datasheets show a normal operating cell
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
temperature, 800 W/sq m, and calm wind and nothing blocking the airflow
on the back of the module. That 27.5°C temperature rise should be pretty
close to the temperature rise that occurs for a pole-top mount. It's
common to see people use 25°C for modules on a pole and 30°C or 35°C on
a roof and there are data that support these typical values. With 1000
W/sq irradiance, the temperature rise can obviously be more too. Between
the intensity of the sun, the direction of the sun, the color of the
roof, the spacing off the roof, and the wind speed there is a lot that
is different from one system to the next or even one day to the next.

Most PV module spec sheets don't give you a temperature coefficient for
Vmp. I've seen people use the the Voc coefficient, usually expressed as
a percentage, for both Voc and Vmp. Big mistake. Data from NREL
indicates as Bill said, the temperature coefficient for Vmp is higher
than that the temperature coefficient for Voc. That's particularly true
when the coefficient is expressed as a percentage per °C. Since there
are very few manufacturer's

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Bill Brooks
Ray,

There is an explanation on the www.solarabcs.org/permitting webpage for the
interactive solar map. The 2% ASHRAE data represents 14 hours in a
month-meaning temperature will be at or above that value for 14 hours in a
typical month. This is likely to correspond to at least one 3-hour timeframe
which is considered continuous in the NEC. The Copper Development
Association has chosen this number for ambient temperature calculations in
the NEC. The NEC Handbook (not the NEC) uses this number in their example
problems. 

The 0.4% ASHRAE date represents 3 hours in a month. It is much more
conservative number. I put it in the data to provide a context for the 2%
number and it allows engineers to consider a more conservative number.

Of course, the mean extreme minimum drybulb temperature is also on that
website for 690.7 max system voltage calculations. Enjoy-its free thanks to
SolarABCs.

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Thursday, December 01, 2011 3:58 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] calculating low string voltage

 

Fantastic Info everyone, I think I've got a full grasp on this topic now,
from using the correct coefficient to the correct weather data, to the
adders for installation type, and a nice link to the applicable data without
spending $180 for the ASHRAE book.  

I'm guessing the 2% number is 2%  of the time year round 24/7, not 2% of the
time the sun is shining, so losses could be higher than 2% of production?
Sorry to keep asking questions, but I know my class will probably ask the
same thing.

Ray

On 12/1/2011 2:57 PM, Gary Willett wrote: 

RAY:

This Solar Reference Guide Map web site is also linked to on the SolarABCs
site and provides the ASHRAE 0.4%   2% high temperatures, as well as the PV
module max temp based on distance above the roof (0.5, 3.5, and 12).

http://www.solarabcs.org/about/publications/reports/expedited-permit/map/ind
ex.html

Regards,

Gary Willett, PE


On 12/1/2011 14:56, Gary Willett wrote: 

Ray:  

Look at Appendix F in the Expedited Permit Process for PV Systems - A
Standardized Process for the Review of Small-Scale PV Systems Prepared by
Bill Brooks, P.E. Brooks Engineering

This document provides the ASHRE temperatures for a lot of locations around
the USA.

http://www.solarabcs.org/about/publications/reports/expedited-permit/pdfs/Ex
permitprocess.pdf



Regards,


Gary Willett, PE

 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread David Brearley
 swap a 7000
  for an 8000 without voiding the Tower UL listing.
  
  Kirk Herander
  
  VT Solar, LLC
  
  dba Vermont Solar Engineering
  
  NABCEP^TM Certified installer Charter Member
  
  NYSERDA-eligible Installer
  
  VT RE Incentive Program Partner
  
  *From:*re-wrenches-boun...@lists.re-wrenches.org
  [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
  *b...@midnitesolar.com
  *Sent:* Wednesday, November 30, 2011 1:03 AM
  *To:* RE-wrenches
  *Subject:* Re: [RE-wrenches] calculating low string voltage
  
  
  
  If you really want to throw a monkey wrench into the mix, bring up
  partial shading...
  
  Or, maybe that's just not allowed in that debate ?? Just a thought.
  
  boB 
  
  
  
  
  
  
  
  On 11/29/2011 8:39 PM, Kent Osterberg wrote:
  
  Kirk, 
  
  You've got some good feedback on this from Ray and Bill. I'll try to add
  a little more. Most module datasheets show a normal operating cell
  temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
  temperature, 800 W/sq m, and calm wind and nothing blocking the airflow
  on the back of the module. That 27.5°C temperature rise should be pretty
  close to the temperature rise that occurs for a pole-top mount. It's
  common to see people use 25°C for modules on a pole and 30°C or 35°C on
  a roof and there are data that support these typical values. With 1000
  W/sq irradiance, the temperature rise can obviously be more too. Between
  the intensity of the sun, the direction of the sun, the color of the
  roof, the spacing off the roof, and the wind speed there is a lot that
  is different from one system to the next or even one day to the next.
  
  Most PV module spec sheets don't give you a temperature coefficient for
  Vmp. I've seen people use the the Voc coefficient, usually expressed as
  a percentage, for both Voc and Vmp. Big mistake. Data from NREL
  indicates as Bill said, the temperature coefficient for Vmp is higher
  than that the temperature coefficient for Voc. That's particularly true
  when the coefficient is expressed as a percentage per °C. Since there
  are very few manufacturer's that give both temperature coefficients,
  I'll use a value from an old Evergreen module for an example. The
  Evergreen ES-195 datasheet shows Voc = 30.5 volts with a coefficient of
  -0.34%/°C and Vmp = 27.1 volts with a coefficient of -0.47%/°C. Since
  one shouldn't add volts and percents, I'll put the temperature
  coefficients in volts/°C: Voc = 30.5 V - 0.10 V/°C and Vmp = 27.1 V -
  0.13V/°C. So Vmp is moving faster than Voc, but not a lot faster. That's
  generically true for c-Si or poly-Si.
  
  Kent Osterberg
  
  Blue Mountain Solar, Inc.
  
  www.bluemountainsolar.com http://www.bluemountainsolar.com
 http://www.bluemountainsolar.com
  
  t: 541-568-4882
  
  
  On 11/29/2011 11:48 AM, Kirk Herander wrote:
  
  I am in debate with a PE over calculation of low voltage of a series
  string on a hot day. He insists that an arbitrary high cell temp is
  factored in, not just ambient temperature. Could someone please give an
  accepted formula for this calculation? Thanks. I cannot find a clear
  reference to low voltage calculation on a hot day (but every reference
  material is clear on how to calculate high voltage on a cold day).
  
  Kirk Herander
  
  VT Solar, LLC
  
  dba Vermont Solar Engineering
  
  NABCEP^TM Certified installer Charter Member
  
  NYSERDA-eligible Installer
  
  VT RE Incentive Program Partner
  
  
  
  
  
  
  ___
  
  List sponsored by Home Power magazine
  
  
  
  List Address:RE-wrenches@lists.re-wrenches.org
 mailto:RE-wrenches@lists.re-wrenches.org
  
  
  
  Options  settings:
  
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  
  
  
  
 List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrench
 es.org 
  
  
  
  List rules  etiquette:
  
  www.re-wrenches.org/etiquette.htm
 http://www.re-wrenches.org/etiquette.htm
 http://www.re-wrenches.org/etiquette.htm
  
  
  
  Check out participant bios:
  
  www.members.re-wrenches.org http://www.members.re-wrenches.org
 http://www.members.re-wrenches.org
  
  
  
  
  
  ___
  List sponsored by Home Power magazine
  
  List Address: RE-wrenches@lists.re-wrenches.org
  
  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  
  List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
  
  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm
 http://www.re-wrenches.org/etiquette.htm
  
  Check out participant bios:
  www.members.re-wrenches.org http://www.members.re-wrenches.org
  
  
  ___
  List sponsored by Home Power magazine
  
  List Address: RE-wrenches@lists.re-wrenches.org
  
  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  
  List

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Ray Walters

Again Thanks Bill and David;

Continued excellent information.
I just jumped on Solectria'a string sizing online tool, and what are 
they using for the Vmpp coefficent? just a tiny bit higher than the Voc 
coefficient.  SMAs new design tool just lists the Voc coeff.   I think 
some manus might need to be following this thread as well, and tweak 
their sizing tools appropriately.


Ray

On 12/1/2011 5:54 PM, Bill Brooks wrote:


Ray,

There is an explanation on the www.solarabcs.org/permitting 
http://www.solarabcs.org/permitting webpage for the interactive 
solar map. The 2% ASHRAE data represents 14 hours in a month---meaning 
temperature will be at or above that value for 14 hours in a typical 
month. This is likely to correspond to at least one 3-hour timeframe 
which is considered continuous in the NEC. The Copper Development 
Association has chosen this number for ambient temperature 
calculations in the NEC. The NEC Handbook (not the NEC) uses this 
number in their example problems.


The 0.4% ASHRAE date represents 3 hours in a month. It is much more 
conservative number. I put it in the data to provide a context for the 
2% number and it allows engineers to consider a more conservative number.


Of course, the mean extreme minimum drybulb temperature is also on 
that website for 690.7 max system voltage calculations. Enjoy---its 
free thanks to SolarABCs.


Bill.

*From:*re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Ray 
Walters

*Sent:* Thursday, December 01, 2011 3:58 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] calculating low string voltage

Fantastic Info everyone, I think I've got a full grasp on this topic 
now, from using the correct coefficient to the correct weather data, 
to the adders for installation type, and a nice link to the applicable 
data without spending $180 for the ASHRAE book.


I'm guessing the 2% number is 2%  of the time year round 24/7, not 2% 
of the time the sun is shining, so losses could be higher than 2% of 
production?  Sorry to keep asking questions, but I know my class will 
probably ask the same thing.


Ray

On 12/1/2011 2:57 PM, Gary Willett wrote:

RAY:

This Solar Reference Guide Map web site is also linked to on the 
SolarABCs site and provides the ASHRAE 0.4%  2% high temperatures, as 
well as the PV module max temp based on distance above the roof (0.5, 
3.5, and 12).


http://www.solarabcs.org/about/publications/reports/expedited-permit/map/index.html

Regards,

Gary Willett, PE


On 12/1/2011 14:56, Gary Willett wrote:

Ray:

Look at Appendix F in the Expedited Permit Process for PV Systems - A 
Standardized Process for the Review of Small-Scale PV Systems Prepared 
by Bill Brooks, P.E. Brooks Engineering


This document provides the ASHRE temperatures for a lot of locations 
around the USA.


http://www.solarabcs.org/about/publications/reports/expedited-permit/pdfs/Expermitprocess.pdf

Regards,


Gary Willett, PE

  



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-30 Thread David Brearley
Here¹s a link to an Excel version of our c-Si PV module specifications
table:

https://solarprofessional.com/webexclusive/

It includes coefficients for Voc, Pmp and Isc. For Vmp calculations, use the
coefficient of Pmp, which is primarily voltage driven. (Temperature
coefficients of current are VERY small, as seem in the Isc values.)

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer 
david.brear...@solarprofessional.com
Direct: 541.261.6545


On 11/30/11 12:18 AM, Ray Walters r...@solarray.com wrote:

I pulled the voltage temp coefficient off of an article from Solar Pro
 Magazine. It is indeed listed for Voc.  I have never seen a separate
 coefficient for Vmpp. Maybe we should use the Power mpp coefficient and then
 factor the slight rise in current by temp (which would make Vmpp even worse).
 My Solar world example shows a Pmpp coeff. of -0.47, while the current coeff.
 (short circuit though) is positive 0.04
  so correcting just for voltage, that would be at or slightly worse than
 Bill's suggested  -0.5 coefficient for Vmpp.  Which would pull the Vmpp from
 35 to 28 in my example, not 30.4 v. The degradation and mismatch Bill points
 out make sense, but is it really another 15% combined?   Would it be fair to
 say different modules and manufacturers would degrade at different rates?
 Finally, the ambient temp I picked was the opposite of the NEC suggested
 ASHRAE low temp. Is that really the best number for calculating this? Or is
 that too extreme a temperature, that wouldn't occur most of the time?
  
  Now I have to correct that coefficient for my next class..but that's why
 I asked for everybody to look it over.
  
  Thanks Everyone,
  
  Ray
  
  
  On 11/29/2011 8:08 PM, Doug Wells wrote:
 Ray, 
 
  
  
 I agree with what you have calculated, but the temp. coef. listed is for a
 Voc.  For voltage sag, the temp. value would be a Vmp value and I don't know
 how much of a difference that makes.   I have seen some manufacturers offer a
 temp. coefficient for Vmp as well as Voc.  Not sure what the difference would
 be, but if it gets down to a few volts with the PE, it is would be worth
 checking.  
  
 
  
   
  
  
 Doug Wells
  
 The Solar Specialists
  
 Morrisville, VT 05661
  
 (p) 802-223-7014
  
 (c) 802-498-5856
  
 www.thesolarspecialists.com http://www.thesolarspecialists.com
  
  
   
  
  
  
 On Nov 29, 2011, at 5:55 PM, Ray Walters wrote:
  
   
  I'm prepping for a class on this very subject tonight, so I'll just wrap up
 everybody's good points:
  V min = Vmpp x (1- temp diff x Temp coefficient)
  
  So first, I'd take your ambient temp from ASHRAE Extreme Annual Mean
 Maximum, then add Scott's adder (ie roof mount off 6  = +30C) so let's say
 the ASHRAE # is 35C, then you have 30 + 35 = 65C cell temp
  then, 65C - 25C(STC) = a differential of 40 deg C from standard test
 conditions
  
  The Aug/ Sept 2010 edition of Solar Pro shows the coefficients for numerous
 modules, 
  Solar world for example is -0.33 %/degC
  
  With a 40 degC differential then, the voltage would change by 40 x .33, or
 13.2%
  
  So just assuming Vmpp =  35v, the adjustment would be 35v x (100%-13.2%), or
 86.8% of 35v, 
  which gives a Volt min of 30.4 v
  
  Somebody please correct my math if I got that wrong.
  Also probably more interesting is the actual Power coefficient, which shows
 the total power losses from higher temperatures, not just voltage. The
 calculation would be similar.
  
  Ray
  
  On 11/29/2011 2:07 PM, Darryl Thayer wrote:
  
  
 I am on road so I have no texts with me, but the same formula applies about
 0.4% per degree (less voltage) or use the module label  voltage coefficent.
 However you must use the MPPT voltage and the temperature = (temperature
 ambient (2% high) plus roof temperature warming)  The roof temperature is
 hard to find good values because it depends upon spacing between roof and
 module.  I add 15 deg C for most situations.
  
  
  
 Best I can do from memory.
  
 DT
  
 
  
  
  
   From: Kirk Herander k...@vtsolar.com mailto:k...@vtsolar.com
  To: RE-wrenches re-wrenches@lists.re-wrenches.org
 mailto:re-wrenches@lists.re-wrenches.org
  Sent: Tuesday, November 29, 2011 1:48 PM
  Subject: [RE-wrenches] calculating low string voltage
   
  
   
  
  
 I am in debate with a PE over calculation of low voltage of a series string
 on a hot day. He insists that an arbitrary high cell temp is factored in,
 not just ambient temperature. Could someone please give an accepted formula
 for this calculation? Thanks. I cannot find a clear reference to low voltage
 calculation on a hot day (but every reference material is clear on how to
 calculate high voltage on a cold day).
  
   
  
 Kirk Herander
  
 VT Solar, LLC
  
 dba Vermont Solar Engineering
  
 NABCEPTM Certified installer Charter Member
  
 NYSERDA-eligible  Installer
  
 VT RE Incentive Program Partner

Re: [RE-wrenches] calculating low string voltage

2011-11-30 Thread Kirk Herander
Thanks for all the good response. Speaking of monkey wrenches, these are
Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet  above the roof
surface. They will absorb reflected light on the backside, so I assume the
cells will operate at a higher temp. But they are elevated enough to
simulate a pole-mount, thus lowering operating cell temp. So what operating
temp to use? If I use 25 C as the operating temp, the low voltage calc comes
out to 301 vdc (inverter min is 300 – using SMA US8000). If I use 15 C the
calc is 308 vdc. This is for a 6 panel string. Unfortunately I really don’t
want to use 7 panel strings due to the layout. If I used a US7000 it would
work since min vdc in is 250. However the inverters are part of a SunnyTower
and I can’t swap a 7000 for an 8000 without voiding the Tower UL listing.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
b...@midnitesolar.com
Sent: Wednesday, November 30, 2011 1:03 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] calculating low string voltage

 



If you really want to throw a monkey wrench into the mix, bring up partial
shading...

Or, maybe that's just not allowed in that debate ??Just a thought.

boB







On 11/29/2011 8:39 PM, Kent Osterberg wrote: 

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to add a
little more. Most module datasheets show a normal operating cell
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
temperature, 800 W/sq m, and calm wind and nothing blocking the airflow on
the back of the module. That 27.5°C temperature rise should be pretty close
to the temperature rise that occurs for a pole-top mount. It's common to see
people use 25°C for modules on a pole and 30°C or 35°C on a roof and there
are data that support these typical values. With 1000 W/sq irradiance, the
temperature rise can obviously be more too. Between the intensity of the
sun, the direction of the sun, the color of the roof, the spacing off the
roof, and the wind speed there is a lot that is different from one system to
the next or even one day to the next.

Most PV module spec sheets don't give you a temperature coefficient for Vmp.
I've seen people use the the Voc coefficient, usually expressed as a
percentage, for both Voc and Vmp. Big mistake. Data from NREL indicates as
Bill said, the temperature coefficient for Vmp is higher than that the
temperature coefficient for Voc. That's particularly true when the
coefficient is expressed as a percentage per °C. Since there are very few
manufacturer's that give both temperature coefficients, I'll use a value
from an old Evergreen module for an example. The Evergreen ES-195 datasheet
shows Voc = 30.5 volts with a coefficient of -0.34%/°C and Vmp = 27.1 volts
with a coefficient of -0.47%/°C. Since one shouldn't add volts and percents,
I'll put the temperature coefficients in volts/°C: Voc = 30.5 V - 0.10 V/°C
and Vmp = 27.1 V - 0.13V/°C. So Vmp is moving faster than Voc, but not a lot
faster. That's generically true for c-Si or poly-Si.



Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882


On 11/29/2011 11:48 AM, Kirk Herander wrote: 

I am in debate with a PE over calculation of low voltage of a series string
on a hot day. He insists that an arbitrary high cell temp is factored in,
not just ambient temperature. Could someone please give an accepted formula
for this calculation? Thanks. I cannot find a clear reference to low voltage
calculation on a hot day (but every reference material is clear on how to
calculate high voltage on a cold day).

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

 










___
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules  etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] calculating low string voltage

2011-11-29 Thread Kirk Herander
I am in debate with a PE over calculation of low voltage of a series string
on a hot day. He insists that an arbitrary high cell temp is factored in,
not just ambient temperature. Could someone please give an accepted formula
for this calculation? Thanks. I cannot find a clear reference to low voltage
calculation on a hot day (but every reference material is clear on how to
calculate high voltage on a cold day).

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Scott McCalmont
Usually you increase the temperature above ambient by an amount which depends 
on the mounting method. Close to the roof is +35 degrees C, more than 6 inches 
above the roof is +30 degrees C, and pole or ground mount is +25 degrees C.

Scott

On Nov 29, 2011, at 11:48 AM, Kirk Herander wrote:

 I am in debate with a PE over calculation of low voltage of a series string 
 on a hot day. He insists that an arbitrary high cell temp is factored in, not 
 just ambient temperature. Could someone please give an accepted formula for 
 this calculation? Thanks. I cannot find a clear reference to low voltage 
 calculation on a hot day (but every reference material is clear on how to 
 calculate high voltage on a cold day).
  
 Kirk Herander
 VT Solar, LLC
 dba Vermont Solar Engineering
 NABCEPTM Certified installer Charter Member
 NYSERDA-eligible Installer
 VT RE Incentive Program Partner
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Comet Systems
As far as I know, the temperature coefficient holds true whether you are
increasing or decreasing the temperature around the STC temperature of 25C.
Of course, there is going to be a point at which it goes non-linear, but
that is not stated.

On Tue, Nov 29, 2011 at 3:58 PM, Scott McCalmont 
re-wrenc...@scottmccalmont.com wrote:

 Usually you increase the temperature above ambient by an amount which
 depends on the mounting method. Close to the roof is +35 degrees C, more
 than 6 inches above the roof is +30 degrees C, and pole or ground mount is
 +25 degrees C.

 Scott

 On Nov 29, 2011, at 11:48 AM, Kirk Herander wrote:

 I am in debate with a PE over calculation of low voltage of a series
 string on a hot day. He insists that an arbitrary high cell temp is
 factored in, not just ambient temperature. Could someone please give an
 accepted formula for this calculation? Thanks. I cannot find a clear
 reference to low voltage calculation on a hot day (but every reference
 material is clear on how to calculate high voltage on a cold day).
 ** **
 Kirk Herander
 VT Solar, LLC
 dba Vermont Solar Engineering
 NABCEPTM Certified installer Charter Member
 NYSERDA-eligible Installer
 VT RE Incentive Program Partner
 ** **
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Chris Mason
President, Comet Systems Ltd
mas...@cometsystems.co
www.cometsystems.co
Cell: 264.235.5670
Int: +1305.767.2094
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Darryl Thayer
I am on road so I have no texts with me, but the same formula applies about 
0.4% per degree (less voltage) or use the module label  voltage coefficent.  
However you must use the MPPT voltage and the temperature = (temperature 
ambient (2% high) plus roof temperature warming)  The roof temperature is hard 
to find good values because it depends upon spacing between roof and module.  I 
add 15 deg C for most situations.  
 
Best I can do from memory.
DT
 


 From: Kirk Herander k...@vtsolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org 
Sent: Tuesday, November 29, 2011 1:48 PM
Subject: [RE-wrenches] calculating low string voltage
 

I am in debate with a PE over calculation of low voltage of a series string on 
a hot day. He insists that an arbitrary high cell temp is factored in, not just 
ambient temperature. Could someone please give an accepted formula for this 
calculation? Thanks. I cannot find a clear reference to low voltage calculation 
on a hot day (but every reference material is clear on how to calculate high 
voltage on a cold day).
 
Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Ray Walters
I'm prepping for a class on this very subject tonight, so I'll just wrap 
up everybody's good points:

V min = Vmpp x (1- temp diff x Temp coefficient)

So first, I'd take your ambient temp from ASHRAE Extreme Annual Mean 
Maximum, then add Scott's adder (ie roof mount off 6  = +30C) so let's 
say the ASHRAE # is 35C, then you have 30 + 35 = 65C cell temp
then, 65C - 25C(STC) = a differential of 40 deg C from standard test 
conditions


The Aug/ Sept 2010 edition of Solar Pro shows the coefficients for 
numerous modules,

Solar world for example is -0.33 %/degC

With a 40 degC differential then, the voltage would change by 40 x .33, 
or 13.2%


So just assuming Vmpp =  35v, the adjustment would be 35v x 
(100%-13.2%), or 86.8% of 35v,

which gives a Volt min of 30.4 v

Somebody please correct my math if I got that wrong.
Also probably more interesting is the actual Power coefficient, which 
shows the total power losses from higher temperatures, not just voltage. 
The calculation would be similar.


Ray

On 11/29/2011 2:07 PM, Darryl Thayer wrote:
I am on road so I have no texts with me, but the same formula applies 
about 0.4% per degree (less voltage) or use the module label  voltage 
coefficent.  However you must use the MPPT voltage and the temperature 
= (temperature ambient (2% high) plus roof temperature warming)  The 
roof temperature is hard to find good values because it depends upon 
spacing between roof and module.  I add 15 deg C for most situations.

Best I can do from memory.
DT

*From:* Kirk Herander k...@vtsolar.com
*To:* RE-wrenches re-wrenches@lists.re-wrenches.org
*Sent:* Tuesday, November 29, 2011 1:48 PM
*Subject:* [RE-wrenches] calculating low string voltage

I am in debate with a PE over calculation of low voltage of a series 
string on a hot day. He insists that an arbitrary high cell temp is 
factored in, not just ambient temperature. Could someone please give 
an accepted formula for this calculation? Thanks. I cannot find a 
clear reference to low voltage calculation on a hot day (but every 
reference material is clear on how to calculate high voltage on a cold 
day).

Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEP^TM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
mailto:RE-wrenches@lists.re-wrenches.org


Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Exeltech
This reply from Scott actually answered the original question.  To that end, I
would like to include my vote for the accuracy of his information.

Measurements conducted here at Exeltech affirm the ~30C temperature delta
directly behind any cell near the center of the PV for an array with sufficient
area to allow convective cooling.

We have also found a few other variables impact cell temperature *slightly*,
but not enough to worry about.

The figures given by Scott below are as accurate a value as can be utilized.


Dan
Sr. Engineer
Exeltech










--- On Tue, 11/29/11, Scott McCalmont re-wrenc...@scottmccalmont.com wrote:

From: Scott McCalmont re-wrenc...@scottmccalmont.com
Subject: Re: [RE-wrenches] calculating low string voltage
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Tuesday, November 29, 2011, 1:58 PM

Usually you increase the temperature above ambient by an amount which depends 
on the mounting method. Close to the roof is +35 degrees C, more than 6 inches 
above the roof is +30 degrees C, and pole or ground mount is +25 degrees C.
Scott

On Nov 29, 2011, at 11:48 AM, Kirk Herander wrote:
I am in debate with a PE over calculation of low voltage of a series string on 
a hot day. He insists that an arbitrary high cell temp is factored in, not just 
ambient temperature. Could someone please give an accepted formula for this 
calculation? Thanks. I cannot find a clear reference to low voltage calculation 
on a hot day (but every reference material is clear on how to calculate high 
voltage on a cold day).  Kirk HeranderVT Solar, LLCdba Vermont Solar 
EngineeringNABCEPTM Certified installer Charter MemberNYSERDA-eligible 
InstallerVT RE Incentive Program Partner   
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



-Inline Attachment Follows-

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Bill Brooks
Folks,

 

One factor often overlooked when calculating minimum system voltage is
degradation of the array and rating variations of the modules.

 

If you assume 0.5% loss in voltage per year, you need to factor a 10% higher
voltage at year one.

 

Manufacturers tolerance on voltage and current can be 5-10% (rare in real
life). It is healthy to add another 5% for voltage tolerance. Voltage
tolerance can be much larger than power tolerance that may only be +/- 3%.

 

The voltage tolerance numbers used by Ray are for Voc not Vmp. Vmp numbers
are closer to 0.45% to 0.5%. This why the power loss due to temperature is
about 0.5%/C-all of it is in voltage, not current. Therefore, for a 40C rise
in temperature, there will be a 20% loss in voltage. Factoring another 15%
loss for degradation and module tolerance, the total loss in voltage would
be:

 

Vmin = 35V x 0.8 x 0.9 x 0.95 = 23.94V = 24 Volts, not 30 Volts. It is
always lower than you think unless you are Eeyore. This is one reason why
the most common string sizing mistake is not enough modules in series.

 

Bill.

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Tuesday, November 29, 2011 2:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] calculating low string voltage

 

I'm prepping for a class on this very subject tonight, so I'll just wrap up
everybody's good points:
V min = Vmpp x (1- temp diff x Temp coefficient)

So first, I'd take your ambient temp from ASHRAE Extreme Annual Mean
Maximum, then add Scott's adder (ie roof mount off 6  = +30C) so let's say
the ASHRAE # is 35C, then you have 30 + 35 = 65C cell temp
then, 65C - 25C(STC) = a differential of 40 deg C from standard test
conditions

The Aug/ Sept 2010 edition of Solar Pro shows the coefficients for numerous
modules, 
Solar world for example is -0.33 %/degC

With a 40 degC differential then, the voltage would change by 40 x .33, or
13.2%

So just assuming Vmpp =  35v, the adjustment would be 35v x (100%-13.2%), or
86.8% of 35v, 
which gives a Volt min of 30.4 v

Somebody please correct my math if I got that wrong.
Also probably more interesting is the actual Power coefficient, which shows
the total power losses from higher temperatures, not just voltage. The
calculation would be similar.

Ray

On 11/29/2011 2:07 PM, Darryl Thayer wrote: 

I am on road so I have no texts with me, but the same formula applies about
0.4% per degree (less voltage) or use the module label  voltage coefficent.
However you must use the MPPT voltage and the temperature = (temperature
ambient (2% high) plus roof temperature warming)  The roof temperature is
hard to find good values because it depends upon spacing between roof and
module.  I add 15 deg C for most situations.  

 

Best I can do from memory.

DT

 

From: Kirk Herander  mailto:k...@vtsolar.com k...@vtsolar.com
To: RE-wrenches  mailto:re-wrenches@lists.re-wrenches.org
re-wrenches@lists.re-wrenches.org 
Sent: Tuesday, November 29, 2011 1:48 PM
Subject: [RE-wrenches] calculating low string voltage

I am in debate with a PE over calculation of low voltage of a series string
on a hot day. He insists that an arbitrary high cell temp is factored in,
not just ambient temperature. Could someone please give an accepted formula
for this calculation? Thanks. I cannot find a clear reference to low voltage
calculation on a hot day (but every reference material is clear on how to
calculate high voltage on a cold day).

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org









___
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules  etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Doug Wells
Ray,

I agree with what you have calculated, but the temp. coef. listed is for a Voc. 
 For voltage sag, the temp. value would be a Vmp value and I don't know how 
much of a difference that makes.   I have seen some manufacturers offer a temp. 
coefficient for Vmp as well as Voc.  Not sure what the difference would be, but 
if it gets down to a few volts with the PE, it is would be worth checking.  

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

On Nov 29, 2011, at 5:55 PM, Ray Walters wrote:

I'm prepping for a class on this very subject tonight, so I'll just wrap up 
everybody's good points:
V min = Vmpp x (1- temp diff x Temp coefficient)

So first, I'd take your ambient temp from ASHRAE Extreme Annual Mean Maximum, 
then add Scott's adder (ie roof mount off 6  = +30C) so let's say the ASHRAE # 
is 35C, then you have 30 + 35 = 65C cell temp
then, 65C - 25C(STC) = a differential of 40 deg C from standard test conditions

The Aug/ Sept 2010 edition of Solar Pro shows the coefficients for numerous 
modules, 
Solar world for example is -0.33 %/degC

With a 40 degC differential then, the voltage would change by 40 x .33, or 13.2%

So just assuming Vmpp =  35v, the adjustment would be 35v x (100%-13.2%), or 
86.8% of 35v, 
which gives a Volt min of 30.4 v

Somebody please correct my math if I got that wrong.
Also probably more interesting is the actual Power coefficient, which shows the 
total power losses from higher temperatures, not just voltage. The calculation 
would be similar.

Ray

On 11/29/2011 2:07 PM, Darryl Thayer wrote:
 
 I am on road so I have no texts with me, but the same formula applies about 
 0.4% per degree (less voltage) or use the module label  voltage coefficent.  
 However you must use the MPPT voltage and the temperature = (temperature 
 ambient (2% high) plus roof temperature warming)  The roof temperature is 
 hard to find good values because it depends upon spacing between roof and 
 module.  I add 15 deg C for most situations.  
  
 Best I can do from memory.
 DT
 
 From: Kirk Herander k...@vtsolar.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org 
 Sent: Tuesday, November 29, 2011 1:48 PM
 Subject: [RE-wrenches] calculating low string voltage
 
 I am in debate with a PE over calculation of low voltage of a series string 
 on a hot day. He insists that an arbitrary high cell temp is factored in, not 
 just ambient temperature. Could someone please give an accepted formula for 
 this calculation? Thanks. I cannot find a clear reference to low voltage 
 calculation on a hot day (but every reference material is clear on how to 
 calculate high voltage on a cold day).
  
 Kirk Herander
 VT Solar, LLC
 dba Vermont Solar Engineering
 NABCEPTM Certified installer Charter Member
 NYSERDA-eligible Installer
 VT RE Incentive Program Partner
  
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Kent Osterberg

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to add 
a little more. Most module datasheets show a normal operating cell 
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient 
temperature, 800 W/sq m, and calm wind and nothing blocking the airflow 
on the back of the module. That 27.5°C temperature rise should be pretty 
close to the temperature rise that occurs for a pole-top mount. It's 
common to see people use 25°C for modules on a pole and 30°C or 35°C on 
a roof and there are data that support these typical values. With 1000 
W/sq irradiance, the temperature rise can obviously be more too. Between 
the intensity of the sun, the direction of the sun, the color of the 
roof, the spacing off the roof, and the wind speed there is a lot that 
is different from one system to the next or even one day to the next.


Most PV module spec sheets don't give you a temperature coefficient for 
Vmp. I've seen people use the the Voc coefficient, usually expressed as 
a percentage, for both Voc and Vmp. Big mistake. Data from NREL 
indicates as Bill said, the temperature coefficient for Vmp is higher 
than that the temperature coefficient for Voc. That's particularly true 
when the coefficient is expressed as a percentage per °C. Since there 
are very few manufacturer's that give both temperature coefficients, 
I'll use a value from an old Evergreen module for an example. The 
Evergreen ES-195 datasheet shows Voc = 30.5 volts with a coefficient of 
-0.34%/°C and Vmp = 27.1 volts with a coefficient of -0.47%/°C. Since 
one shouldn't add volts and percents, I'll put the temperature 
coefficients in volts/°C: Voc = 30.5 V - 0.10 V/°C and Vmp = 27.1 V - 
0.13V/°C. So Vmp is moving faster than Voc, but not a lot faster. That's 
generically true for c-Si or poly-Si.


Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882


On 11/29/2011 11:48 AM, Kirk Herander wrote:


I am in debate with a PE over calculation of low voltage of a series 
string on a hot day. He insists that an arbitrary high cell temp is 
factored in, not just ambient temperature. Could someone please give 
an accepted formula for this calculation? Thanks. I cannot find a 
clear reference to low voltage calculation on a hot day (but every 
reference material is clear on how to calculate high voltage on a cold 
day).


Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread b...@midnitesolar.com



If you really want to throw a monkey wrench into the mix, bring up 
partial shading...


Or, maybe that's just not allowed in that debate ??Just a thought.

boB







On 11/29/2011 8:39 PM, Kent Osterberg wrote:

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to 
add a little more. Most module datasheets show a normal operating cell 
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient 
temperature, 800 W/sq m, and calm wind and nothing blocking the 
airflow on the back of the module. That 27.5°C temperature rise should 
be pretty close to the temperature rise that occurs for a pole-top 
mount. It's common to see people use 25°C for modules on a pole and 
30°C or 35°C on a roof and there are data that support these typical 
values. With 1000 W/sq irradiance, the temperature rise can obviously 
be more too. Between the intensity of the sun, the direction of the 
sun, the color of the roof, the spacing off the roof, and the wind 
speed there is a lot that is different from one system to the next or 
even one day to the next.


Most PV module spec sheets don't give you a temperature coefficient 
for Vmp. I've seen people use the the Voc coefficient, usually 
expressed as a percentage, for both Voc and Vmp. Big mistake. Data 
from NREL indicates as Bill said, the temperature coefficient for Vmp 
is higher than that the temperature coefficient for Voc. That's 
particularly true when the coefficient is expressed as a percentage 
per °C. Since there are very few manufacturer's that give both 
temperature coefficients, I'll use a value from an old Evergreen 
module for an example. The Evergreen ES-195 datasheet shows Voc = 30.5 
volts with a coefficient of -0.34%/°C and Vmp = 27.1 volts with a 
coefficient of -0.47%/°C. Since one shouldn't add volts and percents, 
I'll put the temperature coefficients in volts/°C: Voc = 30.5 V - 0.10 
V/°C and Vmp = 27.1 V - 0.13V/°C. So Vmp is moving faster than Voc, 
but not a lot faster. That's generically true for c-Si or poly-Si.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882

On 11/29/2011 11:48 AM, Kirk Herander wrote:


I am in debate with a PE over calculation of low voltage of a series 
string on a hot day. He insists that an arbitrary high cell temp is 
factored in, not just ambient temperature. Could someone please give 
an accepted formula for this calculation? Thanks. I cannot find a 
clear reference to low voltage calculation on a hot day (but every 
reference material is clear on how to calculate high voltage on a 
cold day).


Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-11-29 Thread Ray Walters
I pulled the voltage temp coefficient off of an article from Solar Pro 
Magazine. It is indeed listed for Voc.  I have never seen a separate 
coefficient for Vmpp. Maybe we should use the Power mpp coefficient and 
then factor the slight rise in current by temp (which would make Vmpp 
even worse). My Solar world example shows a Pmpp coeff. of -0.47, while 
the current coeff. (short circuit though) is positive 0.04
so correcting just for voltage, that would be at or slightly worse than 
Bill's suggested  -0.5 coefficient for Vmpp.  Which would pull the Vmpp 
from 35 to 28 in my example, not 30.4 v. The degradation and mismatch 
Bill points out make sense, but is it really another 15% combined?   
Would it be fair to say different modules and manufacturers would 
degrade at different rates? Finally, the ambient temp I picked was the 
opposite of the NEC suggested ASHRAE low temp. Is that really the best 
number for calculating this? Or is that too extreme a temperature, that 
wouldn't occur most of the time?


Now I have to correct that coefficient for my next class..but that's 
why I asked for everybody to look it over.


Thanks Everyone,

Ray


On 11/29/2011 8:08 PM, Doug Wells wrote:

Ray,

I agree with what you have calculated, but the temp. coef. listed is 
for a Voc.  For voltage sag, the temp. value would be a Vmp value and 
I don't know how much of a difference that makes.   I have seen some 
manufacturers offer a temp. coefficient for Vmp as well as Voc.  Not 
sure what the difference would be, but if it gets down to a few volts 
with the PE, it is would be worth checking.


Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com http://www.thesolarspecialists.com

On Nov 29, 2011, at 5:55 PM, Ray Walters wrote:

I'm prepping for a class on this very subject tonight, so I'll just 
wrap up everybody's good points:

V min = Vmpp x (1- temp diff x Temp coefficient)

So first, I'd take your ambient temp from ASHRAE Extreme Annual Mean 
Maximum, then add Scott's adder (ie roof mount off 6  = +30C) so 
let's say the ASHRAE # is 35C, then you have 30 + 35 = 65C cell temp
then, 65C - 25C(STC) = a differential of 40 deg C from standard test 
conditions


The Aug/ Sept 2010 edition of Solar Pro shows the coefficients for 
numerous modules,

Solar world for example is -0.33 %/degC

With a 40 degC differential then, the voltage would change by 40 x 
.33, or 13.2%


So just assuming Vmpp =  35v, the adjustment would be 35v x 
(100%-13.2%), or 86.8% of 35v,

which gives a Volt min of 30.4 v

Somebody please correct my math if I got that wrong.
Also probably more interesting is the actual Power coefficient, which 
shows the total power losses from higher temperatures, not just 
voltage. The calculation would be similar.


Ray

On 11/29/2011 2:07 PM, Darryl Thayer wrote:
I am on road so I have no texts with me, but the same formula applies 
about 0.4% per degree (less voltage) or use the module label  voltage 
coefficent.  However you must use the MPPT voltage and the 
temperature = (temperature ambient (2% high) plus roof temperature 
warming)  The roof temperature is hard to find good values because it 
depends upon spacing between roof and module.  I add 15 deg C for 
most situations.

Best I can do from memory.
DT

*From:* Kirk Herander k...@vtsolar.com
*To:* RE-wrenches re-wrenches@lists.re-wrenches.org
*Sent:* Tuesday, November 29, 2011 1:48 PM
*Subject:* [RE-wrenches] calculating low string voltage

I am in debate with a PE over calculation of low voltage of a series 
string on a hot day. He insists that an arbitrary high cell temp is 
factored in, not just ambient temperature. Could someone please give 
an accepted formula for this calculation? Thanks. I cannot find a 
clear reference to low voltage calculation on a hot day (but every 
reference material is clear on how to calculate high voltage on a 
cold day).

Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEP^TM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
mailto:RE-wrenches@lists.re-wrenches.org


Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address:RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re