Re: [RE-wrenches] conductors and the 120% rule

2014-03-06 Thread Kirk Herander
Changes to
<http://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=3&cad=rja&uact
=8&ved=0CEoQFjAC&url=http%3A%2F%2Fwww.slideshare.net%2Fsolpowerpeople%2Finte
rconnection-rule&ei=FZcYU5e_LsSi0QH5yICQCQ&usg=AFQjCNGypW0SbS6-POHt4d82Sxc--
kZ0ig&sig2=Kz2661LzDghXtx9GwuhOfw&bvm=bv.62577051,d.dmQ> 2014 NEC
Interconnection Rule 705.12

Here's a link to a powerpoint (slideshare.net) by Richard Stovall which
clarifies 705.12 using some excellent illustrations. Maybe some have seen it
already. Works for me.

Contact me off-list if you'd like a pdf version.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Brian
Mehalic
Sent: Wednesday, March 05, 2014 10:02 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

A very clarifying change is what I'd call it! 

 

First off, rather than being based on the actual breaker size on the
inverter output circuit, calcs are instead based on 125% of the inverter
rated output current.

 

705.12(D)(2)(1) addresses "Feeders" - but only applies when the inverter
output circuit connection is made somewhere other than the opposite end of
the feeder from the utility supply.  This addresses concerns about whether
the feeder conductor needs to be larger due to the presence of the
additional source of supply, and so long as the inverter isn't connected to
the feeder in the middle of it then the existing conductor size should be
okay (because if it is at the opposite end of the feeder than there is
nowhere where the utility and inverter current will be additive).

 

705.12(D)(2)(3) addresses "Busbars" and allows several options, including
the familiar "120% rule" as you stated in your original post.  Also check
out 705.12(D)(2)(3)(c) - depending on the load breakers in the subpanel, the
120% rule may not even need to be used (if the sum of the inverter and load
breakers is less than or equal to the busbar rating).

 

And remember, even if your AHJ hasn't adopted 2014 yet it is worth having a
conversation with them to see if they'll allow you to design the system
based on the new Code - after all, in a certain sense, the 2014 NEC is what
"they" meant the 2011 NEC to say!

 

Cheers,




 

Brian Mehalic 
NABCEP Certified Solar PV Installation ProfessionalT R031508-59

IREC ISPQ Certified Affiliated Instructor/PV US-0132

 

PV Curriculum Developer and Instructor

Solar Energy International
http://www.solarenergy.org

 

On Tue, Mar 4, 2014 at 5:21 PM, Kirk  wrote:

Is this a code change in 2014 vs 2011 or merely a clarification? Vt has not
adopted 2014 yet. What was the original rationale for the 120% rule to apply
to conductors in addition to a panel bus? 

Kirk Herander

VSE


On Mar 4, 2014, at 6:20 PM, Brian Mehalic  wrote:

If the subpanel is at the end if the feeder, and there are no taps in
between the main and the sub then I don't see any reason that the conductors
need to be any larger than 200 A as there is no where on the feeder
conductors where grid and PV current will be additive. 

 

The changes in 705.12 in 2014 address this in large part. 

Brian


On Mar 4, 2014, at 2:41 PM, "Kirk Herander"  wrote:

Solaredge 20 kw, 480 3-phase. Good point, but that may be irrelevant. The
feed-in subpanel is also powering unrelated loads, which use the neutral as
a conductor from the main panel. So 4 conductors from the main.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allen
Frishman
Sent: Tuesday, March 04, 2014 4:32 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

what inverter(s) are you using?In many cases the Neutral is not
considered a Current Carying Conductor by the Manufacturer and therefore you
only have 3 CCC.

Al Frishman
AeonSolar

(917) 699-6641   - cell
(888) 460-2867  
www.aeonsolar.com <http://www.aeonsolar.com/> 

 

On Mar 4, 2014, at 4:20 PM, Kirk Herander wrote:

 

Approx.. 50 - 60ft.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Tuesday, March 04, 2014 4:05 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

What is the length of the conduit to the subpanel? That will

Re: [RE-wrenches] conductors and the 120% rule

2014-03-05 Thread William Korthof
Even in a feeder with line-neutral loads, the neutral still only carries the 
imbalance between the phase loads: the case of maximum possible neutral current 
is the hypothetical situation of the phase with largest line-neutral load 
current, with all those loads on, and both other phases having all line-neutral 
loads off---in order to get neutral current, you have to reduce the phase 
current in two legs--- 
So normally in 4-wire star feeders, you only need to rate for 3 current 
carrying conductors. 

If the neutral conductor connects to a solar inverter, the neutral load is 
either zero (3 phase inverter) or non-additive if you have a bank of 1 phase 
line/neutral (120 or 277 volt) inverters 

/wk

William Korthof
714.875.3576
Sustainable Solutions
#956904

On Mar 4, 2014, at 1:31 PM, Allen Frishman  wrote:

what inverter(s) are you using?In many cases the Neutral is not considered 
a Current Carying Conductor by the Manufacturer and therefore you only have 3 
CCC.
Al Frishman
AeonSolar

(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com


On Mar 4, 2014, at 4:20 PM, Kirk Herander wrote:

> Approx.. 50 – 60ft.
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
> Sent: Tuesday, March 04, 2014 4:05 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] conductors and the 120% rule
>  
> What is the length of the conduit to the subpanel? That will determine 
> whether to apply the derates.
> 
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer, 
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> On 3/4/2014 1:34 PM, Kirk Herander wrote:
> Whether or not a further derate has to be applied is the killer here, as I am 
> working with existing panels and conductors. In an old Code Corner(HP140) J. 
> Wiles goes through a similar scenario and calls out the allowable current 
> rating and conductor in 310.15, but makes no mention of applying additional 
> derate factors. The .8 derate for 4-6 conductors(l1,l2,l3, & n) will put the 
> existing 4/0 cable between feed-in and main panel at 208 amps, less than the 
> allowable 217. I’d hate to need to upsize the wire to 250 mcm.
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason 
> Szumlanski
> Sent: Tuesday, March 04, 2014 2:57 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] conductors and the 120% rule
>  
> Both the bus and conductors need to be rated for 217 amps minimum. As you 
> mentioned, the bus is not a problem. The way I interpret it, the conductor 
> size required would be after derate factors are applied. The rating of the 
> conductor is ultimately dependent on the derate factors.
>  
> If you can locate your subpanel adjacent to the main distribution panel, you 
> may be able to use Exception #3 to 310.15(B)(2) by connecting the panels with 
> a short nipple. I assume you are just looking at a number of conductor derate 
> and not an ambient temperature derate.
>  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] conductors and the 120% rule

2014-03-05 Thread Jason Szumlanski
00 A as there is no where on the
>> feeder conductors where grid and PV current will be additive.
>>
>>  The changes in 705.12 in 2014 address this in large part.
>>
>> Brian
>>
>> On Mar 4, 2014, at 2:41 PM, "Kirk Herander"  wrote:
>>
>>   Solaredge 20 kw, 480 3-phase. Good point, but that may be irrelevant.
>> The feed-in subpanel is also powering unrelated loads, which use the
>> neutral as a conductor from the main panel. So 4 conductors from the main.
>>
>>
>>
>> Kirk Herander
>>
>> VT Solar, LLC
>>
>> dba Vermont Solar Engineering
>>
>> NABCEPTM Certified Inaugural Certificant
>>
>> NYSERDA-eligible Installer
>>
>> VT RE Incentive Program Partner
>>
>> 802.863.1202
>>
>>
>>
>> *From:* re-wrenches-boun...@lists.re-wrenches.org [
>> mailto:re-wrenches-boun...@lists.re-wrenches.org]
>> *On Behalf Of *Allen Frishman
>> *Sent:* Tuesday, March 04, 2014 4:32 PM
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] conductors and the 120% rule
>>
>>
>>
>> what inverter(s) are you using?In many cases the Neutral is not
>> considered a Current Carying Conductor by the Manufacturer and therefore
>> you only have 3 CCC.
>>
>> *Al Frishman*
>> AeonSolar
>>
>> *(917) 699-6641 <%28917%29%20699-6641> - cell*
>> *(888) 460-2867 <%2%29%20460-2867>*
>> *www.aeonsolar.com <http://www.aeonsolar.com/>*
>>
>>
>>
>> On Mar 4, 2014, at 4:20 PM, Kirk Herander wrote:
>>
>>
>>
>>   Approx.. 50 - 60ft.
>>
>>
>>
>> Kirk Herander
>>
>> VT Solar, LLC
>>
>> dba Vermont Solar Engineering
>>
>> NABCEPTM Certified Inaugural Certificant
>>
>> NYSERDA-eligible Installer
>>
>> VT RE Incentive Program Partner
>>
>> 802.863.1202
>>
>>
>>
>> *From:* re-wrenches-boun...@lists.re-wrenches.org
>> [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Ray
>> Walters
>> *Sent:* Tuesday, March 04, 2014 4:05 PM
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] conductors and the 120% rule
>>
>>
>>
>> What is the length of the conduit to the subpanel? That will determine
>> whether to apply the derates.
>>
>>
>>  R.Ray Walters
>>
>> CTO, Solarray, Inc
>>
>> Nabcep Certified PV Installer,
>>
>> Licensed Master Electrician
>>
>> Solar Design Engineer
>>
>> 303 505-8760
>>
>>  On 3/4/2014 1:34 PM, Kirk Herander wrote:
>>
>>  Whether or not a further derate has to be applied is the killer here,
>> as I am working with existing panels and conductors. In an old Code
>> Corner(HP140) J. Wiles goes through a similar scenario and calls out the
>> allowable current rating and conductor in 310.15, but makes no mention of
>> applying additional derate factors. The .8 derate for 4-6
>> conductors(l1,l2,l3, & n) will put the existing 4/0 cable between feed-in
>> and main panel at 208 amps, less than the allowable 217. I'd hate to need
>> to upsize the wire to 250 mcm.
>>
>>
>>
>> Kirk Herander
>>
>> VT Solar, LLC
>>
>> dba Vermont Solar Engineering
>>
>> NABCEPTM Certified Inaugural Certificant
>>
>> NYSERDA-eligible Installer
>>
>> VT RE Incentive Program Partner
>>
>> 802.863.1202
>>
>>
>>
>> *From:* re-wrenches-boun...@lists.re-wrenches.org [
>> mailto:re-wrenches-boun...@lists.re-wrenches.org
>> ] *On Behalf Of *Jason Szumlanski
>> *Sent:* Tuesday, March 04, 2014 2:57 PM
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] conductors and the 120% rule
>>
>>
>>
>> Both the bus and conductors need to be rated for 217 amps minimum. As you
>> mentioned, the bus is not a problem. The way I interpret it, the conductor
>> size required would be after derate factors are applied. The rating of the
>> conductor is ultimately dependent on the derate factors.
>>
>>
>>
>> If you can locate your subpanel adjacent to the main distribution panel,
>> you may be able to use Exception #3 to 310.15(B)(2) by connecting the
>> panels with a short nipple. I assume you are just looking at a number of
>> conductor derate and not an ambient temperature derate.
>>
>>
>>
>> Jason Szumlanski
>>
>> Fafco Solar
>>
>>
>>
>>
>>
>>
>> On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander  wrote:
>>
>> Hello,
>>
>> I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp
>> breaker. My inverter breaker feeding the sub panel is 60 amps. So 225 a bus
>> x 1.2 = 270 amps. That's less than the sum of the two breakers of 260 amps,
>> so no issue there. The conductors between sub and main panel have to be
>> rated for at least 260/1.2 = 217 amps, correct? Is this 217 amps before or
>> after derating the conductor?
>>
>>
>>
>>
>>
>> Kirk Herander
>>
>> VT Solar, LLC
>>
>> dba Vermont Solar Engineering
>>
>> NABCEPTM Certified Inaugural Certificant
>>
>> NYSERDA-eligible Installer
>>
>> VT RE Incentive Program Partner
>>
>> 802.863.1202
>>
>>
>>
>>
>>
>>
>>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] conductors and the 120% rule

2014-03-05 Thread Brian Mehalic
A very clarifying change is what I'd call it!

First off, rather than being based on the actual breaker size on the
inverter output circuit, calcs are instead based on 125% of the inverter
rated output current.

705.12(D)(2)(1) addresses "Feeders" - but only applies when the inverter
output circuit connection is made somewhere other than the opposite end of
the feeder from the utility supply.  This addresses concerns about whether
the feeder conductor needs to be larger due to the presence of the
additional source of supply, and so long as the inverter isn't connected to
the feeder in the middle of it then the existing conductor size should be
okay (because if it is at the opposite end of the feeder than there is
nowhere where the utility and inverter current will be additive).

705.12(D)(2)(3) addresses "Busbars" and allows several options, including
the familiar "120% rule" as you stated in your original post.  Also check
out 705.12(D)(2)(3)(c) - depending on the load breakers in the subpanel,
the 120% rule may not even need to be used (if the sum of the inverter and
load breakers is less than or equal to the busbar rating).

And remember, even if your AHJ hasn't adopted 2014 yet it is worth having a
conversation with them to see if they'll allow you to design the system
based on the new Code - after all, in a certain sense, the 2014 NEC is what
"they" meant the 2011 NEC to say!

Cheers,


Brian Mehalic
NABCEP Certified Solar PV Installation Professional(tm) R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132

PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org


On Tue, Mar 4, 2014 at 5:21 PM, Kirk  wrote:

> Is this a code change in 2014 vs 2011 or merely a clarification? Vt has
> not adopted 2014 yet. What was the original rationale for the 120% rule to
> apply to conductors in addition to a panel bus?
>
> Kirk Herander
> VSE
>
> On Mar 4, 2014, at 6:20 PM, Brian Mehalic  wrote:
>
> If the subpanel is at the end if the feeder, and there are no taps in
> between the main and the sub then I don't see any reason that the
> conductors need to be any larger than 200 A as there is no where on the
> feeder conductors where grid and PV current will be additive.
>
> The changes in 705.12 in 2014 address this in large part.
>
> Brian
>
> On Mar 4, 2014, at 2:41 PM, "Kirk Herander"  wrote:
>
> Solaredge 20 kw, 480 3-phase. Good point, but that may be irrelevant. The
> feed-in subpanel is also powering unrelated loads, which use the neutral as
> a conductor from the main panel. So 4 conductors from the main.
>
>
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEPTM Certified Inaugural Certificant
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [
> mailto:re-wrenches-boun...@lists.re-wrenches.org]
> *On Behalf Of *Allen Frishman
> *Sent:* Tuesday, March 04, 2014 4:32 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] conductors and the 120% rule
>
>
>
> what inverter(s) are you using?In many cases the Neutral is not
> considered a Current Carying Conductor by the Manufacturer and therefore
> you only have 3 CCC.
>
> *Al Frishman*
> AeonSolar
>
> *(917) 699-6641 <%28917%29%20699-6641> - cell*
> *(888) 460-2867 <%2%29%20460-2867>*
> *www.aeonsolar.com <http://www.aeonsolar.com/>*
>
>
>
> On Mar 4, 2014, at 4:20 PM, Kirk Herander wrote:
>
>
>
> Approx.. 50 - 60ft.
>
>
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEPTM Certified Inaugural Certificant
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Ray
> Walters
> *Sent:* Tuesday, March 04, 2014 4:05 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] conductors and the 120% rule
>
>
>
> What is the length of the conduit to the subpanel? That will determine
> whether to apply the derates.
>
>
> R.Ray Walters
>
> CTO, Solarray, Inc
>
> Nabcep Certified PV Installer,
>
> Licensed Master Electrician
>
> Solar Design Engineer
>
> 303 505-8760
>
> On 3/4/2014 1:34 PM, Kirk Herander wrote:
>
> Whether or not a further derate has to be applied is the killer here, as I
> am working with existing panels and conductors. In an old Code
> Corner(HP140) J. Wiles goes through a similar scenario and calls out the
> allowable current rating and conductor in 310.

Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Kirk
Is this a code change in 2014 vs 2011 or merely a clarification? Vt has not 
adopted 2014 yet. What was the original rationale for the 120% rule to apply to 
conductors in addition to a panel bus? 

Kirk Herander
VSE

> On Mar 4, 2014, at 6:20 PM, Brian Mehalic  wrote:
> 
> If the subpanel is at the end if the feeder, and there are no taps in between 
> the main and the sub then I don't see any reason that the conductors need to 
> be any larger than 200 A as there is no where on the feeder conductors where 
> grid and PV current will be additive. 
> 
> The changes in 705.12 in 2014 address this in large part. 
> 
> Brian
> 
>> On Mar 4, 2014, at 2:41 PM, "Kirk Herander"  wrote:
>> 
>> Solaredge 20 kw, 480 3-phase. Good point, but that may be irrelevant. The 
>> feed-in subpanel is also powering unrelated loads, which use the neutral as 
>> a conductor from the main panel. So 4 conductors from the main.
>>  
>> Kirk Herander
>> VT Solar, LLC
>> dba Vermont Solar Engineering
>> NABCEPTM Certified Inaugural Certificant
>> NYSERDA-eligible Installer
>> VT RE Incentive Program Partner
>> 802.863.1202
>>  
>> From: re-wrenches-boun...@lists.re-wrenches.org 
>> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allen 
>> Frishman
>> Sent: Tuesday, March 04, 2014 4:32 PM
>> To: RE-wrenches
>> Subject: Re: [RE-wrenches] conductors and the 120% rule
>>  
>> what inverter(s) are you using?In many cases the Neutral is not 
>> considered a Current Carying Conductor by the Manufacturer and therefore you 
>> only have 3 CCC.
>> Al Frishman
>> AeonSolar
>> (917) 699-6641 - cell
>> (888) 460-2867
>> www.aeonsolar.com
>>  
>> On Mar 4, 2014, at 4:20 PM, Kirk Herander wrote:
>> 
>> 
>> Approx.. 50 – 60ft.
>>  
>> Kirk Herander
>> VT Solar, LLC
>> dba Vermont Solar Engineering
>> NABCEPTM Certified Inaugural Certificant
>> NYSERDA-eligible Installer
>> VT RE Incentive Program Partner
>> 802.863.1202
>>  
>> From: re-wrenches-boun...@lists.re-wrenches.org 
>> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
>> Sent: Tuesday, March 04, 2014 4:05 PM
>> To: RE-wrenches
>> Subject: Re: [RE-wrenches] conductors and the 120% rule
>>  
>> What is the length of the conduit to the subpanel? That will determine 
>> whether to apply the derates.
>> 
>> 
>> R.Ray Walters
>> CTO, Solarray, Inc
>> Nabcep Certified PV Installer, 
>> Licensed Master Electrician
>> Solar Design Engineer
>> 303 505-8760
>> On 3/4/2014 1:34 PM, Kirk Herander wrote:
>> Whether or not a further derate has to be applied is the killer here, as I 
>> am working with existing panels and conductors. In an old Code Corner(HP140) 
>> J. Wiles goes through a similar scenario and calls out the allowable current 
>> rating and conductor in 310.15, but makes no mention of applying additional 
>> derate factors. The .8 derate for 4-6 conductors(l1,l2,l3, & n) will put the 
>> existing 4/0 cable between feed-in and main panel at 208 amps, less than the 
>> allowable 217. I’d hate to need to upsize the wire to 250 mcm.
>>  
>> Kirk Herander
>> VT Solar, LLC
>> dba Vermont Solar Engineering
>> NABCEPTM Certified Inaugural Certificant
>> NYSERDA-eligible Installer
>> VT RE Incentive Program Partner
>> 802.863.1202
>>  
>> From: re-wrenches-boun...@lists.re-wrenches.org 
>> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason 
>> Szumlanski
>> Sent: Tuesday, March 04, 2014 2:57 PM
>> To: RE-wrenches
>> Subject: Re: [RE-wrenches] conductors and the 120% rule
>>  
>> Both the bus and conductors need to be rated for 217 amps minimum. As you 
>> mentioned, the bus is not a problem. The way I interpret it, the conductor 
>> size required would be after derate factors are applied. The rating of the 
>> conductor is ultimately dependent on the derate factors.
>>  
>> If you can locate your subpanel adjacent to the main distribution panel, you 
>> may be able to use Exception #3 to 310.15(B)(2) by connecting the panels 
>> with a short nipple. I assume you are just looking at a number of conductor 
>> derate and not an ambient temperature derate.
>>  
>> Jason Szumlanski
>> Fafco Solar
>> 
>>  
>> 
>>  
>> 
>> On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander  wrote:
>> Hello,
>> I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker. 
>> My i

Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Brian Mehalic
If the subpanel is at the end if the feeder, and there are no taps in between 
the main and the sub then I don't see any reason that the conductors need to be 
any larger than 200 A as there is no where on the feeder conductors where grid 
and PV current will be additive. 

The changes in 705.12 in 2014 address this in large part. 

Brian

> On Mar 4, 2014, at 2:41 PM, "Kirk Herander"  wrote:
> 
> Solaredge 20 kw, 480 3-phase. Good point, but that may be irrelevant. The 
> feed-in subpanel is also powering unrelated loads, which use the neutral as a 
> conductor from the main panel. So 4 conductors from the main.
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allen Frishman
> Sent: Tuesday, March 04, 2014 4:32 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] conductors and the 120% rule
>  
> what inverter(s) are you using?In many cases the Neutral is not 
> considered a Current Carying Conductor by the Manufacturer and therefore you 
> only have 3 CCC.
> Al Frishman
> AeonSolar
> (917) 699-6641 - cell
> (888) 460-2867
> www.aeonsolar.com
>  
> On Mar 4, 2014, at 4:20 PM, Kirk Herander wrote:
> 
> 
> Approx.. 50 – 60ft.
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
> Sent: Tuesday, March 04, 2014 4:05 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] conductors and the 120% rule
>  
> What is the length of the conduit to the subpanel? That will determine 
> whether to apply the derates.
> 
> 
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer, 
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> On 3/4/2014 1:34 PM, Kirk Herander wrote:
> Whether or not a further derate has to be applied is the killer here, as I am 
> working with existing panels and conductors. In an old Code Corner(HP140) J. 
> Wiles goes through a similar scenario and calls out the allowable current 
> rating and conductor in 310.15, but makes no mention of applying additional 
> derate factors. The .8 derate for 4-6 conductors(l1,l2,l3, & n) will put the 
> existing 4/0 cable between feed-in and main panel at 208 amps, less than the 
> allowable 217. I’d hate to need to upsize the wire to 250 mcm.
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason 
> Szumlanski
> Sent: Tuesday, March 04, 2014 2:57 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] conductors and the 120% rule
>  
> Both the bus and conductors need to be rated for 217 amps minimum. As you 
> mentioned, the bus is not a problem. The way I interpret it, the conductor 
> size required would be after derate factors are applied. The rating of the 
> conductor is ultimately dependent on the derate factors.
>  
> If you can locate your subpanel adjacent to the main distribution panel, you 
> may be able to use Exception #3 to 310.15(B)(2) by connecting the panels with 
> a short nipple. I assume you are just looking at a number of conductor derate 
> and not an ambient temperature derate.
>  
> Jason Szumlanski
> Fafco Solar
> 
>  
> 
>  
> 
> On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander  wrote:
> Hello,
> I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker. 
> My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 = 
> 270 amps. That’s less than the sum of the two breakers of 260 amps, so no 
> issue there. The conductors between sub and main panel have to be rated for 
> at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after 
> derating the conductor?
>  
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
>  
> 
> 
> 
> 
> ___
> List sponsored by Home Power m

Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Kirk Herander
Solaredge 20 kw, 480 3-phase. Good point, but that may be irrelevant. The
feed-in subpanel is also powering unrelated loads, which use the neutral as
a conductor from the main panel. So 4 conductors from the main.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allen
Frishman
Sent: Tuesday, March 04, 2014 4:32 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

what inverter(s) are you using?In many cases the Neutral is not
considered a Current Carying Conductor by the Manufacturer and therefore you
only have 3 CCC.

Al Frishman
AeonSolar

(917) 699-6641   - cell
(888) 460-2867  
www.aeonsolar.com <http://www.aeonsolar.com/> 

 

On Mar 4, 2014, at 4:20 PM, Kirk Herander wrote:





Approx.. 50 - 60ft.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Tuesday, March 04, 2014 4:05 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

What is the length of the conduit to the subpanel? That will determine
whether to apply the derates.




R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/4/2014 1:34 PM, Kirk Herander wrote:

Whether or not a further derate has to be applied is the killer here, as I
am working with existing panels and conductors. In an old Code Corner(HP140)
J. Wiles goes through a similar scenario and calls out the allowable current
rating and conductor in 310.15, but makes no mention of applying additional
derate factors. The .8 derate for 4-6 conductors(l1,l2,l3, & n) will put the
existing 4/0 cable between feed-in and main panel at 208 amps, less than the
allowable 217. I'd hate to need to upsize the wire to 250 mcm.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Tuesday, March 04, 2014 2:57 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

Both the bus and conductors need to be rated for 217 amps minimum. As you
mentioned, the bus is not a problem. The way I interpret it, the conductor
size required would be after derate factors are applied. The rating of the
conductor is ultimately dependent on the derate factors.

 

If you can locate your subpanel adjacent to the main distribution panel, you
may be able to use Exception #3 to 310.15(B)(2) by connecting the panels
with a short nipple. I assume you are just looking at a number of conductor
derate and not an ambient temperature derate.

 

Jason Szumlanski

Fafco Solar


 



 

On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander  wrote:

Hello,

I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker.
My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 =
270 amps. That's less than the sum of the two breakers of 260 amps, so no
issue there. The conductors between sub and main panel have to be rated for
at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after
derating the conductor?

 

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

 







___
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:

Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Kirk Herander
The other thing I could do is downsize the main to 190 amps or less. 190 +
60(pv) = 250 / 1.2 = 208 amps, exactly the 4/0 derate amperage.

Unfortunately I can't get away with downsizing the 60 amp pv breaker, unless
I could find a breaker rated to operate continuously at greater than 80% of
its trip rating. I guess they do exist. Then you don't have to apply the
1.25 multiplier when sizing the breaker. This is a SQD industrial panel the
inverter is feeding into. Any SQD gurus out there who know of these types of
breakers? 

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Tuesday, March 04, 2014 4:06 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

Yeah, I assumed you meant the four conductors. The exception would solve
your problem if it's physically possible.

 

How long of a run are we talking about? The cost difference shouldn't be bad
for a short distance.

 

Jason Szumlansk

i

Fafco Solar

Description: Image removed by sender.

 

On Tue, Mar 4, 2014 at 3:34 PM, Kirk Herander  wrote:

Whether or not a further derate has to be applied is the killer here, as I
am working with existing panels and conductors. In an old Code Corner(HP140)
J. Wiles goes through a similar scenario and calls out the allowable current
rating and conductor in 310.15, but makes no mention of applying additional
derate factors. The .8 derate for 4-6 conductors(l1,l2,l3, & n) will put the
existing 4/0 cable between feed-in and main panel at 208 amps, less than the
allowable 217. I'd hate to need to upsize the wire to 250 mcm.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Tuesday, March 04, 2014 2:57 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

Both the bus and conductors need to be rated for 217 amps minimum. As you
mentioned, the bus is not a problem. The way I interpret it, the conductor
size required would be after derate factors are applied. The rating of the
conductor is ultimately dependent on the derate factors.

 

If you can locate your subpanel adjacent to the main distribution panel, you
may be able to use Exception #3 to 310.15(B)(2) by connecting the panels
with a short nipple. I assume you are just looking at a number of conductor
derate and not an ambient temperature derate.

 

Jason Szumlanski

Fafco Solar


 

Description: Description: Image removed by sender.

 

On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander  wrote:

Hello,

I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker.
My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 =
270 amps. That's less than the sum of the two breakers of 260 amps, so no
issue there. The conductors between sub and main panel have to be rated for
at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after
derating the conductor?

 

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



 

<><>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Allen Frishman
what inverter(s) are you using?In many cases the Neutral is not considered 
a Current Carying Conductor by the Manufacturer and therefore you only have 3 
CCC.
Al Frishman
AeonSolar

(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com


On Mar 4, 2014, at 4:20 PM, Kirk Herander wrote:

> Approx.. 50 – 60ft.
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
> Sent: Tuesday, March 04, 2014 4:05 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] conductors and the 120% rule
>  
> What is the length of the conduit to the subpanel? That will determine 
> whether to apply the derates.
> 
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer, 
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> On 3/4/2014 1:34 PM, Kirk Herander wrote:
> Whether or not a further derate has to be applied is the killer here, as I am 
> working with existing panels and conductors. In an old Code Corner(HP140) J. 
> Wiles goes through a similar scenario and calls out the allowable current 
> rating and conductor in 310.15, but makes no mention of applying additional 
> derate factors. The .8 derate for 4-6 conductors(l1,l2,l3, & n) will put the 
> existing 4/0 cable between feed-in and main panel at 208 amps, less than the 
> allowable 217. I’d hate to need to upsize the wire to 250 mcm.
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason 
> Szumlanski
> Sent: Tuesday, March 04, 2014 2:57 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] conductors and the 120% rule
>  
> Both the bus and conductors need to be rated for 217 amps minimum. As you 
> mentioned, the bus is not a problem. The way I interpret it, the conductor 
> size required would be after derate factors are applied. The rating of the 
> conductor is ultimately dependent on the derate factors.
>  
> If you can locate your subpanel adjacent to the main distribution panel, you 
> may be able to use Exception #3 to 310.15(B)(2) by connecting the panels with 
> a short nipple. I assume you are just looking at a number of conductor derate 
> and not an ambient temperature derate.
>  
> Jason Szumlanski
> Fafco Solar
> 
>  
> 
>  
> 
> On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander  wrote:
> Hello,
> I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker. 
> My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 = 
> 270 amps. That’s less than the sum of the two breakers of 260 amps, so no 
> issue there. The conductors between sub and main panel have to be rated for 
> at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after 
> derating the conductor?
>  
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
>  
> 
> 
> 
> ___
> List sponsored by Home Power magazine
>  
> List Address: RE-wrenches@lists.re-wrenches.org
>  
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>  
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>  
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>  
> Check out participant bios:
> www.members.re-wrenches.org
>  
>  
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Kirk Herander
Approx.. 50 - 60ft.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Tuesday, March 04, 2014 4:05 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

What is the length of the conduit to the subpanel? That will determine
whether to apply the derates.



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/4/2014 1:34 PM, Kirk Herander wrote:

Whether or not a further derate has to be applied is the killer here, as I
am working with existing panels and conductors. In an old Code Corner(HP140)
J. Wiles goes through a similar scenario and calls out the allowable current
rating and conductor in 310.15, but makes no mention of applying additional
derate factors. The .8 derate for 4-6 conductors(l1,l2,l3, & n) will put the
existing 4/0 cable between feed-in and main panel at 208 amps, less than the
allowable 217. I'd hate to need to upsize the wire to 250 mcm.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Tuesday, March 04, 2014 2:57 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

Both the bus and conductors need to be rated for 217 amps minimum. As you
mentioned, the bus is not a problem. The way I interpret it, the conductor
size required would be after derate factors are applied. The rating of the
conductor is ultimately dependent on the derate factors.

 

If you can locate your subpanel adjacent to the main distribution panel, you
may be able to use Exception #3 to 310.15(B)(2) by connecting the panels
with a short nipple. I assume you are just looking at a number of conductor
derate and not an ambient temperature derate.

 

Jason Szumlanski

Fafco Solar


 

Description: Image removed by sender.

 

On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander  wrote:

Hello,

I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker.
My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 =
270 amps. That's less than the sum of the two breakers of 260 amps, so no
issue there. The conductors between sub and main panel have to be rated for
at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after
derating the conductor?

 

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

 






___
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 

 

<>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Jason Szumlanski
Yeah, I assumed you meant the four conductors. The exception would solve
your problem if it's physically possible.

How long of a run are we talking about? The cost difference shouldn't be
bad for a short distance.


Jason Szumlansk
i

Fafco Solar



On Tue, Mar 4, 2014 at 3:34 PM, Kirk Herander  wrote:

> Whether or not a further derate has to be applied is the killer here, as I
> am working with existing panels and conductors. In an old Code
> Corner(HP140) J. Wiles goes through a similar scenario and calls out the
> allowable current rating and conductor in 310.15, but makes no mention of
> applying additional derate factors. The .8 derate for 4-6
> conductors(l1,l2,l3, & n) will put the existing 4/0 cable between feed-in
> and main panel at 208 amps, less than the allowable 217. I'd hate to need
> to upsize the wire to 250 mcm.
>
>
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEPTM Certified Inaugural Certificant
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
> re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jason Szumlanski
> *Sent:* Tuesday, March 04, 2014 2:57 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] conductors and the 120% rule
>
>
>
> Both the bus and conductors need to be rated for 217 amps minimum. As you
> mentioned, the bus is not a problem. The way I interpret it, the conductor
> size required would be after derate factors are applied. The rating of the
> conductor is ultimately dependent on the derate factors.
>
>
>
> If you can locate your subpanel adjacent to the main distribution panel,
> you may be able to use Exception #3 to 310.15(B)(2) by connecting the
> panels with a short nipple. I assume you are just looking at a number of
> conductor derate and not an ambient temperature derate.
>
>
>
> Jason Szumlanski
>
> Fafco Solar
>
>
>
>
> [image: Description: Image removed by sender.]
>
>
>
> On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander  wrote:
>
> Hello,
>
> I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp
> breaker. My inverter breaker feeding the sub panel is 60 amps. So 225 a bus
> x 1.2 = 270 amps. That's less than the sum of the two breakers of 260 amps,
> so no issue there. The conductors between sub and main panel have to be
> rated for at least 260/1.2 = 217 amps, correct? Is this 217 amps before or
> after derating the conductor?
>
>
>
>
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEPTM Certified Inaugural Certificant
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
>
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
<>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Ray Walters

  
  
What is the length of the conduit to
  the subpanel? That will determine whether to apply the derates.
  R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760
  On 3/4/2014 1:34 PM, Kirk Herander wrote:


  
  
  
  
  
Whether
or not a further derate has to be applied is the killer
here, as I am working with existing panels and conductors.
In an old Code Corner(HP140) J. Wiles goes through a similar
scenario and calls out the allowable current rating and
conductor in 310.15, but makes no mention of applying
additional derate factors. The .8 derate for 4-6
conductors(l1,l2,l3, & n) will put the existing 4/0
cable between feed-in and main panel at 208 amps, less than
the allowable 217. I’d hate to need to upsize the wire to
250 mcm.
 
Kirk
Herander
VT
Solar, LLC
dba
Vermont Solar Engineering
NABCEPTM
Certified Inaugural Certificant
NYSERDA-eligible
Installer
VT
RE Incentive Program Partner
802.863.1202
 
From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On
  Behalf Of Jason Szumlanski
Sent: Tuesday, March 04, 2014 2:57 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120%
rule
 

  
Both
the bus and conductors need to be rated for 217 amps
minimum. As you mentioned, the bus is not a problem. The
way I interpret it, the conductor size required would be
after derate factors are applied. The rating of the
conductor is ultimately dependent on the derate factors.
  
  
 
  
  
If
you can locate your subpanel adjacent to the main
distribution panel, you may be able to use Exception #3
to 310.15(B)(2) by connecting the panels with a short
nipple. I assume you are just looking at a number of
conductor derate and not an ambient temperature derate.
  
   
  

  
Jason
Szumlanski

  Fafco
  Solar


 
  
  

  
  
 

  On Tue, Mar 4, 2014 at 12:05 PM, Kirk
Herander <k...@vtsolar.com>
wrote:
  

  Hello,
  I have a 225 amp 3-phase
  main lug sub-panel protected by a 200 amp breaker.
  My inverter breaker feeding the sub panel is 60
  amps. So 225 a bus x 1.2 = 270 amps. That’s less
  than the sum of the two breakers of 260 amps, so
  no issue there. The conductors between sub and
  main panel have to be rated for at least 260/1.2 =
  217 amps, correct? Is this 217 amps before or
  after derating the conductor?
   
   
  Kirk Herander
  VT Solar, LLC
  dba Vermont Solar
  Engineering
  NABCEPTM Certified
  Inaugural Certificant
  NYSERDA-eligible
  Installer
  VT RE Incentive Program
  Partner
  802.863.1202
   

  

 
  

  
  
  
  
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm


Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Kirk Herander
Whether or not a further derate has to be applied is the killer here, as I
am working with existing panels and conductors. In an old Code Corner(HP140)
J. Wiles goes through a similar scenario and calls out the allowable current
rating and conductor in 310.15, but makes no mention of applying additional
derate factors. The .8 derate for 4-6 conductors(l1,l2,l3, & n) will put the
existing 4/0 cable between feed-in and main panel at 208 amps, less than the
allowable 217. I'd hate to need to upsize the wire to 250 mcm.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Tuesday, March 04, 2014 2:57 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] conductors and the 120% rule

 

Both the bus and conductors need to be rated for 217 amps minimum. As you
mentioned, the bus is not a problem. The way I interpret it, the conductor
size required would be after derate factors are applied. The rating of the
conductor is ultimately dependent on the derate factors.

 

If you can locate your subpanel adjacent to the main distribution panel, you
may be able to use Exception #3 to 310.15(B)(2) by connecting the panels
with a short nipple. I assume you are just looking at a number of conductor
derate and not an ambient temperature derate.

 

Jason Szumlanski

Fafco Solar


 

Description: Image removed by sender.

 

On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander  wrote:

Hello,

I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker.
My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 =
270 amps. That's less than the sum of the two breakers of 260 amps, so no
issue there. The conductors between sub and main panel have to be rated for
at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after
derating the conductor?

 

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

 

<>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Jason Szumlanski
Both the bus and conductors need to be rated for 217 amps minimum. As you
mentioned, the bus is not a problem. The way I interpret it, the conductor
size required would be after derate factors are applied. The rating of the
conductor is ultimately dependent on the derate factors.

If you can locate your subpanel adjacent to the main distribution panel,
you may be able to use Exception #3 to 310.15(B)(2) by connecting the
panels with a short nipple. I assume you are just looking at a number of
conductor derate and not an ambient temperature derate.

Jason Szumlanski

Fafco Solar





On Tue, Mar 4, 2014 at 12:05 PM, Kirk Herander  wrote:

> Hello,
>
> I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp
> breaker. My inverter breaker feeding the sub panel is 60 amps. So 225 a bus
> x 1.2 = 270 amps. That's less than the sum of the two breakers of 260 amps,
> so no issue there. The conductors between sub and main panel have to be
> rated for at least 260/1.2 = 217 amps, correct? Is this 217 amps before or
> after derating the conductor?
>
>
>
>
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEPTM Certified Inaugural Certificant
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Chris Mason
The conductors have to be rated for 200A as normal. Fault current can only
come from the grid.
While the total available current on the bus of a panel is the total of the
source breakers, in the conductors, grid and solar power cancel out and the
total is not the sum of the two.


On Tue, Mar 4, 2014 at 1:05 PM, Kirk Herander  wrote:

> Hello,
>
> I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp
> breaker. My inverter breaker feeding the sub panel is 60 amps. So 225 a bus
> x 1.2 = 270 amps. That's less than the sum of the two breakers of 260 amps,
> so no issue there. The conductors between sub and main panel have to be
> rated for at least 260/1.2 = 217 amps, correct? Is this 217 amps before or
> after derating the conductor?
>
>
>
>
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEPTM Certified Inaugural Certificant
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Kirk Herander
Hello,

I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker.
My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 =
270 amps. That's less than the sum of the two breakers of 260 amps, so no
issue there. The conductors between sub and main panel have to be rated for
at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after
derating the conductor?

 

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org