Re: [RE-wrenches] metering an outback system

2010-08-11 Thread Alex Cozine
Yes, you are correct.  The Solar pro diagram and article is great for
understanding each mode the meter can be in.



On Tue, Aug 10, 2010 at 5:57 AM, Drake Chamberlin 
drake.chamber...@redwoodalliance.org wrote:

  Hi Alex,

 The one meter hook up always seems confusing to me.  I'm still confused.
 Do we have the AC IN at both the bottom left and top right?   To me it seems
 that the AC OUT from the inverter would go to the upper left and the
 protected loads panel would be fed from the bottom left.

 I've never used this method, but would like to use it instead of the two
 meter method.

 Thanks,

 Drake


 At 12:19 AM 8/10/2010, you wrote:

 When metering for production here in Washington State, we use both sides in
 a 12s 120volt meterbase with fifth jaw. * top right inverter ac in*,
 bottom right ac from grid.  top left from battery back up, *bottom left
 from inverter ac in*, fifth jaw neutral.

 this set up allows grid tied selling and battery saved energy selling to be
 metered while subtracting energy used to charge batteries and subtracting
 any power needed to run the inverter.

 hope this helps.

 contact me off list if you need the diagram (in office)



 --
 Alex Cozine
 NABCEP Certified Solar PV Installer
 Brothers Electric  Solar
 brotherselectricsolar.com
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

 Check out participant bios:
  www.members.re-wrenches.org

  Drake Chamberlin
 Athens Electric
 OH License 44810
 CO License 3773
 NABCEP TM  Certified PV Installer
 Office - 740-448-7328
 Mobile - 740-856-9648

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Alex Cozine
NABCEP Certified Solar PV Installer
Brothers Electric  Solar
brotherselectricsolar.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] metering an outback system

2010-08-10 Thread Drake Chamberlin

Hi Alex,

The one meter hook up always seems confusing to me.  I'm still 
confused.  Do we have the AC IN at both the bottom left and top 
right?   To me it seems that the AC OUT from the inverter would go to 
the upper left and the protected loads panel would be fed from the 
bottom left.


I've never used this method, but would like to use it instead of the 
two meter method.


Thanks,

Drake


At 12:19 AM 8/10/2010, you wrote:
When metering for production here in Washington State, we use both 
sides in a 12s 120volt meterbase with fifth jaw.  top right inverter 
ac in, bottom right ac from grid.  top left from battery back up, 
bottom left from inverter ac in, fifth jaw neutral.


this set up allows grid tied selling and battery saved energy 
selling to be metered while subtracting energy used to charge 
batteries and subtracting any power needed to run the inverter.


hope this helps.

contact me off list if you need the diagram (in office)



--
Alex Cozine
NABCEP Certified Solar PV Installer
Brothers Electric  Solar
http://brotherselectricsolar.combrotherselectricsolar.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] metering an outback system

2010-08-10 Thread David Brearley
Drake,

Chris Freitas wrote an article on this topic in SP1.1, ³Form 12S Metering
for Grid-Tied Systems w/ Battery Backup.² Here¹s a link to the article and a
wiring diagram:


http://solarprofessional.com/article/?file=SP1_1_pg16_QandA_3search=

David Brearley, Senior Technical Editor
SolarPro magazine 

On 8/10/10 7:57 AM, Drake Chamberlin
drake.chamber...@redwoodalliance.org wrote:

 Hi Alex,
 
 The one meter hook up always seems confusing to me.  I'm still confused.  Do
 we have the AC IN at both the bottom left and top right?   To me it seems that
 the AC OUT from the inverter would go to the upper left and the protected
 loads panel would be fed from the bottom left.
 
 I've never used this method, but would like to use it instead of the two meter
 method.
 
 Thanks,
 
 Drake 
 
 
 At 12:19 AM 8/10/2010, you wrote:
 When metering for production here in Washington State, we use both sides in a
 12s 120volt meterbase with fifth jaw.  top right inverter ac in, bottom right
 ac from grid.  top left from battery back up, bottom left from inverter ac
 in, fifth jaw neutral.
 
 this set up allows grid tied selling and battery saved energy selling to be
 metered while subtracting energy used to charge batteries and subtracting any
 power needed to run the inverter.
 
 hope this helps.
 
 contact me off list if you need the diagram (in office)
 
 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] metering an outback system

2010-08-09 Thread Gary Easton
Hello,
I am having trouble metering  a system with an Outback 3648 serving a
protected loads panel. I need a way to accurately measure the production.
I have a dual stator 12s meter installed with the AC in coming in the
bottom and out the top and the AC from the inverter going in the top and
out the bottom with a neutral from the E-panel connected to the fifth leg.
The meter is not reading anything close to the Outback. Any ideas would be
greatly appreciated.
Gary Easton
Appalachian Renewable Power Systems
NABCEP Certified Solar PV
NABCEP Certified Solar Thermal
740-277-8498

 Kelly,

 When I came across language like this in an RFP, my assumption was that we
 needed to work with a specialty lightning protection subcontractor, a firm
 listed by UL. I would call them up, give them a project description and
 request a quote, which I would build into our cost estimate for the
 project.
 Included in their scope of work is providing a ³UL Listed Lightning
 Protection Certificate.² You can include that scope of work as a line item
 in our proposal. If the proposal requires that you include resumes for key
 team members, you might also include the lightning company¹s bio as it
 shows
 you¹ve done your due diligence.

 On the projects that I managed in this fashion, the lightning protection
 company always came in after our construction was substantially complete.
 There may be cases where you want to coordinate the that scope of work
 differently and get them on site earlier. They should be able to tell you
 what will work best, based on the general project description and your
 specific equipment grounding scheme.

 David Brearley, Senior Technical Editor
 SolarPro magazine
 NABCEP Certified PV Installer 
 david.brear...@solarprofessional.com


 On 7/31/10 3:28 PM, Kelly Keilwitz, Whidbey Sun  Wind
 ke...@whidbeysunwind.com wrote:

 Hi All,
 I'm  working on the design for a PV  Wind power system for a military
 installation. The specs call for Lightning Protection as follows:

 Provide a complete lightning protection system with  a UL Lightning
 Protection Inspection Certificate.
 including, but not necessarily limited to, strike termination devices,
 conductors, ground terminals,
 interconnecting conductors, surge suppression devices, and other
 connectors
 and fittings required for
 a complete and usable system. 

 Anyone have an idea of what qualifies? Is there a package product that
 has the
 UL Lightning Protection Inspection Certificate?

 Thanks,
 -Kelly


 Kelly Keilwitz, P.E.
 Whidbey Sun  Wind
 Renewable Energy Systems
 NABCEP Certified PV Installer
 ke...@whidbeysunwind.com
 360.678.7131







 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] metering an outback system

2010-08-09 Thread Kent Osterberg




Gary,

If this is a new digital meter, it may be accumulating all energy
without regard to direction. That is the way the utilities purchase
them, to prevent energy theft, so that is the default configuration
from the meter manufacturers. When purchasing a digital kWh meter to
use for metering production per Outback's instructions, you must
specify that the meter is for net metering. Outback should warn about
that in their instructions!

It is pretty easy to wire the Outback metering scheme incorrectly. To
test for that: 
1. Disable the solar and battery charger, then confirm that the meter
disk does not spin when there is a load is turned on the protected
loads panel.
2. Disable the loads and solar, then force a bulk charge and confirm
that the meter spins backwards.

Even the digital meters show you what way power is flowing with a
simulated disk: dots progressing to the right is forward, left is
backwards.

Kent Osterberg
Blue Mountain Solar


Gary Easton wrote:

  Hello,
I am having trouble metering  a system with an Outback 3648 serving a
protected loads panel. I need a way to accurately measure the production.
I have a dual stator 12s meter installed with the "AC in" coming in the
bottom and out the top and the AC from the inverter going in the top and
out the bottom with a neutral from the E-panel connected to the fifth leg.
The meter is not reading anything close to the Outback. Any ideas would be
greatly appreciated.
Gary Easton
Appalachian Renewable Power Systems
NABCEP Certified Solar PV
NABCEP Certified Solar Thermal
740-277-8498

  
  
Kelly,

When I came across language like this in an RFP, my assumption was that we
needed to work with a specialty lightning protection subcontractor, a firm
listed by UL. I would call them up, give them a project description and
request a quote, which I would build into our cost estimate for the
project.
Included in their scope of work is providing a UL Listed Lightning
Protection Certificate. You can include that scope of work as a line item
in our proposal. If the proposal requires that you include resumes for key
team members, you might also include the lightning companys bio as it
shows
youve done your due diligence.

On the projects that I managed in this fashion, the lightning protection
company always came in after our construction was substantially complete.
There may be cases where you want to coordinate the that scope of work
differently and get them on site earlier. They should be able to tell you
what will work best, based on the general project description and your
specific equipment grounding scheme.

David Brearley, Senior Technical Editor
SolarPro magazine
NABCEP Certified PV Installer 
david.brear...@solarprofessional.com


On 7/31/10 3:28 PM, "Kelly Keilwitz, Whidbey Sun  Wind"
ke...@whidbeysunwind.com wrote:



  Hi All,
I'm  working on the design for a PV  Wind power system for a military
installation. The specs call for Lightning Protection as follows:

  
  
"Provide a complete lightning protection system with  a UL Lightning
Protection Inspection Certificate.
including, but not necessarily limited to, strike termination devices,
conductors, ground terminals,
interconnecting conductors, surge suppression devices, and other
connectors
and fittings required for
a complete and usable system. "


  
  Anyone have an idea of what qualifies? Is there a package product that
has the
"UL Lightning Protection Inspection Certificate"?

Thanks,
-Kelly


Kelly Keilwitz, P.E.
Whidbey Sun  Wind
Renewable Energy Systems
NABCEP Certified PV Installer
ke...@whidbeysunwind.com
360.678.7131


  





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



  
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
  


No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 9.0.851 / Virus Database: 271.1.1/3059 - Release Date: 08/08/10 10:57:00

  



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 

Re: [RE-wrenches] metering an outback system

2010-08-09 Thread Alex Cozine
When metering for production here in Washington State, we use both sides in
a 12s 120volt meterbase with fifth jaw.  top right inverter ac in, bottom
right ac from grid.  top left from battery back up, bottom left from
inverter ac in, fifth jaw neutral.

this set up allows grid tied selling and battery saved energy selling to be
metered while subtracting energy used to charge batteries and subtracting
any power needed to run the inverter.

hope this helps.

contact me off list if you need the diagram (in office)



-- 
Alex Cozine
NABCEP Certified Solar PV Installer
Brothers Electric  Solar
brotherselectricsolar.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org