Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

2010-04-20 Thread Dave Palumbo
Jim,

 

You have probably seen this already but it’s worth a mention here. Good article 
in SolarPro magazine April/May “Optimal PV-to-Inverter Sizing Ratio”.  

 

Dave

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jim MacDonald
Sent: Monday, April 19, 2010 7:43 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?

 

Im sorry, I meant to write “11 modules per string” below.. 

Been a long day..

 

From: Jim MacDonald 
Sent: Monday, April 19, 2010 7:41 PM
To: RE-wrenches
Cc: Jason Szrom
Subject: RE: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?

 

SB8000US only good for 480 Vac, we’re tying in at 208.

 

11 strings [11 modules per string] has been calc’d to be OK (600vdc) for 
record low -4 fahrenheit (-20 celsius).

 

I think the big concern as mentioned is getting the Voc high early in the AM to 
wake the inverter up, also maintaining the Vmp later in the day to keep it 
running for as long as possible into the late afternoon/ evening.

Will those extra kWh gleaned in the early AM/ late PM over the course of 365 
days be more than the kWh clipped during peak production times with the 9.075 
kWdc?

NYC average summer highs between 79 and 84 fahrenheit early june-late august.  
Sunlink rack @ 10° on a silver-painted built-up roof.

 

Time-of-use utility $ peak-shaving is not an issue here.

 

Thank you

 

 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

2010-04-20 Thread wes kennedy
Hi Jim,

I like using one of the design emulators for just this reason. PVSYST and 
PVSOL.  You can model each scenario and see how the numbers crunch. You import 
historical weather data for the region to get as accurate as possible. 

You mention the silver painted roof, these emulators allow you to input albedo 
affects, too.

Both packages offer free trial periods, so you could run just this case for 
free.  If you like them then you spend the money for the license. 



-Wes Kennedy
NABCEP certified PV Installer

303-653-3073

--- On Mon, 4/19/10, Jim MacDonald j...@solaresystems.com wrote:

From: Jim MacDonald j...@solaresystems.com
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Monday, April 19, 2010, 5:40 PM




 
 






SB8000US only good for 480 Vac, we’re tying in at 208. 

   

11 strings has been calc’d to be OK (600vdc) for record low -4
fahrenheit (-20 celsius). 

   

I think the big concern as mentioned is getting the Voc high
early in the AM to wake the inverter up, also maintaining the Vmp later in the
day to keep it running for as long as possible into the late afternoon/
evening. 

Will those extra kWh gleaned in the early AM/ late PM over the
course of 365 days be more than the kWh clipped during peak production times
with the 9.075 kWdc? 

NYC average summer highs between 79 and 84 fahrenheit early
june-late august.  Sunlink rack @ 10° on a silver-painted built-up
roof. 

   

Time-of-use utility $ peak-shaving is not an issue here. 

   

Thank you 

   

   

   

   



From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Darryl
Thayer

Sent: Monday, April 19, 2010 5:58 PM

To: RE-wrenches

Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod
per string? 



   


 
  
  
  The temperature correction is the concern.  I have
  heard lots of stories of inverters dieing when it gets to cold.  Look in
  the code book 690.7 at the temperature correction table.  Go to
  weather.com and find your record low temperature.  Find you Tc factor
  and will your senerios work?  I have heard from a sunny boy rep that it
  is OK to over power by 1.25%  
  
  
  darryl

  

  --- On Mon, 4/19/10, Dana d...@solarwork.com wrote: 
  
  
  

  From: Dana d...@solarwork.com

  Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per
  string?

  To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org

  Date: Monday, April 19, 2010, 4:31 PM 
  
  
  Many times we
  switch to another module manufacturer as one will not fit or another inverter
  manufacturer.  
  
  PVPowered has a
  more relaxed window and we have had fine success with them when SMA does not
  fit.  
  
  Cold is the
  dictator and the 600 VDC threshold. 
  
    
    
  
  Thanks,  Dana Orzel 
  
    
  Great Solar Works, Inc 
  web - www.solarwork.com 
  E - d...@solarwork.com 
  V - 970.626.5253 
  F - 970.626.4140 
  C - 970.209.4076 
    
  We have been slow to give up
  on the myth of the Earth's generosity. 
  Rather grandly, we have overdrawn
  our accounts. 
  Barbara Kingsolver - Water is life. 
    
  
  
  From:
  re-wrenches-boun...@lists.re-wrenches.org
  [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jim
  MacDonald

  Sent: Monday, April 19, 2010 2:37 PM

  To: RE-wrenches@lists.re-wrenches.org

  Subject: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per
  string? 
  
  
    
  For a straight grid-tie system@ 10 degree tilt, 180
  azimuth, zero/little shade, NYC avg 4.29 kWh/m²/day. 
    
  Feed an SMA7000 with (3) strings of 11 Suntech STP275’s
  [9.075 kWdc] 
  Or 
  Do strings of 10, so itd be 8.250 kWdc into the 7 kWac
  inverter. 
    
  Strings of 11= 491.7 Voc; 386 Vmp 
  Strings of 10= 447 Voc; 351 Vmp  
    
  The tradeoff would be power clipping at/around noon in the
  sunny months in the 9.075 kW scenario; 
  Inverter sleeping late every morning and retiring early in
  the evenings in the lowered voltage scenario. 
    
  Trying to figure out which would yield more kWh at the end
  of the year. 
    
  Any ideas appreciated, 
  thanks 
    
    
    
    
  Jim MacDonald 
  Solar Energy Systems, LLC 
  Brooklyn, NY 11222 
  www.solarEsystems.com 
    
  No
  virus found in this incoming message.

  Checked by AVG - www.avg.com

  Version: 9.0.801 / Virus Database: 271.1.1/2819 - Release Date: 04/19/10
  00:31:00 
  

  -Inline Attachment Follows- 
  
  ___

  List sponsored by Home Power magazine

  

  List Address: RE-wrenches@lists.re-wrenches.org

  

  Options  settings:

  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  

  List rules  etiquette:

  www.re-wrenches.org/etiquette.htm

  

  Check out participant bios

Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

2010-04-20 Thread David Brearley
In the same issue of SolarPro as the “Optimal PV-to-Inverter” Sizing Ratio”
article (April/May 2010), the lead article is “Production Modeling for
Grid-Tied PV Systems” by Tarn Yates and Bradley Hibberd at Borrego Solar:

http://solarprofessional.com/article/?file=SP3_3_pg30_Yates

While your question below can’t be answered using PVWatts, it can be
answered using the Solar Advisor Model (SAM), which was developed by NREL
and Sandia w/ DOE funding. SAM is available for free download here:

www.nrel.gov/analysis/sam/

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer ™
david.brear...@solarprofessional.com
Direct: 541.261.6545


On 4/19/10 6:40 PM, Jim MacDonald j...@solaresystems.com wrote:

 SB8000US only good for 480 Vac, we’re tying in at 208.
  
 11 strings has been calc’d to be OK (600vdc) for record low -4 fahrenheit
 (-20 celsius).
  
 I think the big concern as mentioned is getting the Voc high early in the AM
 to wake the inverter up, also maintaining the Vmp later in the day to keep it
 running for as long as possible into the late afternoon/ evening.
 Will those extra kWh gleaned in the early AM/ late PM over the course of 365
 days be more than the kWh clipped during peak production times with the 9.075
 kWdc?
 NYC average summer highs between 79 and 84 fahrenheit early june-late august.?
 Sunlink rack @ 10° on a silver-painted built-up roof.
  
 Time-of-use utility $ peak-shaving is not an issue here.
  
 Thank you
  
  
  
  
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Darryl Thayer
 Sent: Monday, April 19, 2010 5:58 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per
 string?
  
  
The temperature correction is the concern.  I have heard lots of stories of
 inverters dieing when it gets to cold.  Look in the code book 690.7 at the
 temperature correction table.  Go to weather.com and find your record low
 temperature.  Find you Tc factor and will your senerios work?  I have heard
 from a sunny boy rep that it is OK to over power by 1.25%
   darryl
  
  --- On Mon, 4/19/10, Dana d...@solarwork.com wrote:
  
  
  From: Dana d...@solarwork.com
  Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per
 string?
  To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
  Date: Monday, April 19, 2010, 4:31 PM   Many times we switch to another
 module manufacturer as one will not fit or another inverter manufacturer.
  PVPowered has a more relaxed window and we have had fine success with them
 when SMA does not fit.
  Cold is the dictator and the 600 VDC threshold.
   Thanks,  Dana Orzel
Great Solar Works, Inc web - www.solarwork.com E - d...@solarwork.com V -
 970.626.5253 F - 970.626.4140 C - 970.209.4076   We have been slow to give up
 on the myth of the Earth's generosity. Rather grandly, we have overdrawn our
 accounts. Barbara Kingsolver - Water is life. From:
 re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jim MacDonald
  Sent: Monday, April 19, 2010 2:37 PM
  To: RE-wrenches@lists.re-wrenches.org
  Subject: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per
 string? 
  
For a straight grid-tie system@ 10 degree tilt, 180 azimuth, zero/little
 shade, NYC avg 4.29 kWh/m²/day.   Feed an SMA7000 with (3) strings of 11
 Suntech STP275’s [9.075 kWdc] Or Do strings of 10, so itd be 8.250 kWdc into
 the 7 kWac inverter.   Strings of 11= 491.7 Voc; 386 Vmp Strings of 10= 447
 Voc; 351 VmpThe tradeoff would be power clipping at/around noon in the
 sunny months in the 9.075 kW scenario; Inverter sleeping late every morning
 and retiring early in the evenings in the lowered voltage scenario.   Trying
 to figure out which would yield more kWh at the end of the year.   Any ideas
 appreciated, thanks Jim MacDonald Solar Energy Systems, LLC Brooklyn,
 NY 11222 www.solarEsystems.com http://www.solaresystems.com/No virus
 found in this incoming message.
  Checked by AVG - www.avg.com
  Version: 9.0.801 / Virus Database: 271.1.1/2819 - Release Date: 04/19/10
 00:31:00 
 






___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

2010-04-19 Thread Jim MacDonald
For a straight grid-tie system@ 10 degree tilt, 180 azimuth, zero/little shade, 
NYC avg 4.29 kWh/m²/day.

Feed an SMA7000 with (3) strings of 11 Suntech STP275's [9.075 kWdc]
Or
Do strings of 10, so itd be 8.250 kWdc into the 7 kWac inverter.

Strings of 11= 491.7 Voc; 386 Vmp
Strings of 10= 447 Voc; 351 Vmp

The tradeoff would be power clipping at/around noon in the sunny months in the 
9.075 kW scenario;
Inverter sleeping late every morning and retiring early in the evenings in the 
lowered voltage scenario.

Trying to figure out which would yield more kWh at the end of the year.

Any ideas appreciated,
thanks




Jim MacDonald
Solar Energy Systems, LLC
Brooklyn, NY 11222
www.solarEsystems.comhttp://www.solaresystems.com/

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

2010-04-19 Thread David Brearley
Is using the SMA SB 8000US out of the question?

http://www.sma-america.com/en/products/solar-inverters/sunny-boy/sunny-boy-5
000us-6000us-7000us-8000us.html


On 4/19/10 3:37 PM, Jim MacDonald j...@solaresystems.com wrote:

 For a straight grid-tie system@ 10 degree tilt, 180 azimuth, zero/little
 shade, NYC avg 4.29 kWh/m²/day.
  
 Feed an SMA7000 with (3) strings of 11 Suntech STP275¹s [9.075 kWdc]
 Or
 Do strings of 10, so itd be 8.250 kWdc into the 7 kWac inverter.
  
 Strings of 11= 491.7 Voc; 386 Vmp
 Strings of 10= 447 Voc; 351 Vmp
  
 The tradeoff would be power clipping at/around noon in the sunny months in the
 9.075 kW scenario;
 Inverter sleeping late every morning and retiring early in the evenings in the
 lowered voltage scenario.
  
 Trying to figure out which would yield more kWh at the end of the year.
  
 Any ideas appreciated,
 thanks
  
  
  
  
 Jim MacDonald
 Solar Energy Systems, LLC
 Brooklyn, NY 11222
 www.solarEsystems.com http://www.solaresystems.com/
  
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer 
david.brear...@solarprofessional.com
Direct: 541.261.6545
Fax:  541.512.0343

Visit our Web site at solarprofessional.com

(Sample copy available for download at: solarprofessional.com/sample)



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

2010-04-19 Thread Dana
Many times we switch to another module manufacturer as one will not
fit or another inverter manufacturer. 

PVPowered has a more relaxed window and we have had fine success with
them when SMA does not fit. 

Cold is the dictator and the 600 VDC threshold.

 

 

Thanks,  Dana Orzel

 

Great Solar Works, Inc

web - www.solarwork.com

E - d...@solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

 

We have been slow to give up on the myth of the Earth's generosity.

Rather grandly, we have overdrawn our accounts.

Barbara Kingsolver - Water is life.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jim
MacDonald
Sent: Monday, April 19, 2010 2:37 PM
To: RE-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per
string?

 

For a straight grid-tie system@ 10 degree tilt, 180 azimuth,
zero/little shade, NYC avg 4.29 kWh/m²/day.

 

Feed an SMA7000 with (3) strings of 11 Suntech STP275’s [9.075 kWdc]

Or

Do strings of 10, so itd be 8.250 kWdc into the 7 kWac inverter.

 

Strings of 11= 491.7 Voc; 386 Vmp

Strings of 10= 447 Voc; 351 Vmp 

 

The tradeoff would be power clipping at/around noon in the sunny
months in the 9.075 kW scenario;

Inverter sleeping late every morning and retiring early in the
evenings in the lowered voltage scenario.

 

Trying to figure out which would yield more kWh at the end of the
year.

 

Any ideas appreciated,

thanks

 

 

 

 

Jim MacDonald

Solar Energy Systems, LLC

Brooklyn, NY 11222

www.solarEsystems.com http://www.solaresystems.com/ 

 

No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.801 / Virus Database: 271.1.1/2819 - Release Date:
04/19/10 00:31:00

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

2010-04-19 Thread Darryl Thayer
The temperature correction is the concern.  I have heard lots of stories of 
inverters dieing when it gets to cold.  Look in the code book 690.7 at the 
temperature correction table.  Go to weather.com and find your record low 
temperature.  Find you Tc factor and will your senerios work?  I have heard 
from a sunny boy rep that it is OK to over power by 1.25% 
darryl

--- On Mon, 4/19/10, Dana d...@solarwork.com wrote:


From: Dana d...@solarwork.com
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?
To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date: Monday, April 19, 2010, 4:31 PM








Many times we switch to another module manufacturer as one will not fit or 
another inverter manufacturer. 
PVPowered has a more relaxed window and we have had fine success with them when 
SMA does not fit. 
Cold is the dictator and the 600 VDC threshold.
 
 

Thanks,  Dana Orzel
 
Great Solar Works, Inc
web - www.solarwork.com
E - d...@solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
 
We have been slow to give up on the myth of the Earth's generosity.
Rather grandly, we have overdrawn our accounts.
Barbara Kingsolver - Water is life.
 


From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jim MacDonald
Sent: Monday, April 19, 2010 2:37 PM
To: RE-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?
 
For a straight grid-tie system@ 10 degree tilt, 180 azimuth, zero/little shade, 
NYC avg 4.29 kWh/m²/day.
 
Feed an SMA7000 with (3) strings of 11 Suntech STP275’s [9.075 kWdc]
Or
Do strings of 10, so itd be 8.250 kWdc into the 7 kWac inverter.
 
Strings of 11= 491.7 Voc; 386 Vmp
Strings of 10= 447 Voc; 351 Vmp 
 
The tradeoff would be power clipping at/around noon in the sunny months in the 
9.075 kW scenario;
Inverter sleeping late every morning and retiring early in the evenings in the 
lowered voltage scenario.
 
Trying to figure out which would yield more kWh at the end of the year.
 
Any ideas appreciated,
thanks
 
 
 
 
Jim MacDonald
Solar Energy Systems, LLC
Brooklyn, NY 11222
www.solarEsystems.com
 
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.801 / Virus Database: 271.1.1/2819 - Release Date: 04/19/10 
00:31:00
-Inline Attachment Follows-


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

2010-04-19 Thread Jim MacDonald
SB8000US only good for 480 Vac, we’re tying in at 208.

11 strings has been calc’d to be OK (600vdc) for record low -4 fahrenheit (-20 
celsius).

I think the big concern as mentioned is getting the Voc high early in the AM to 
wake the inverter up, also maintaining the Vmp later in the day to keep it 
running for as long as possible into the late afternoon/ evening.
Will those extra kWh gleaned in the early AM/ late PM over the course of 365 
days be more than the kWh clipped during peak production times with the 9.075 
kWdc?
NYC average summer highs between 79 and 84 fahrenheit early june-late august.  
Sunlink rack @ 10° on a silver-painted built-up roof.

Time-of-use utility $ peak-shaving is not an issue here.

Thank you




From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Darryl Thayer
Sent: Monday, April 19, 2010 5:58 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?

The temperature correction is the concern.  I have heard lots of stories of 
inverters dieing when it gets to cold.  Look in the code book 690.7 at the 
temperature correction table.  Go to weather.com and find your record low 
temperature.  Find you Tc factor and will your senerios work?  I have heard 
from a sunny boy rep that it is OK to over power by 1.25%
darryl

--- On Mon, 4/19/10, Dana d...@solarwork.com wrote:

From: Dana d...@solarwork.com
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?
To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date: Monday, April 19, 2010, 4:31 PM
Many times we switch to another module manufacturer as one will not fit or 
another inverter manufacturer.
PVPowered has a more relaxed window and we have had fine success with them when 
SMA does not fit.
Cold is the dictator and the 600 VDC threshold.


Thanks,  Dana Orzel

Great Solar Works, Inc
web - www.solarwork.com
E - d...@solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076

We have been slow to give up on the myth of the Earth's generosity.
Rather grandly, we have overdrawn our accounts.
Barbara Kingsolver - Water is life.

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jim MacDonald
Sent: Monday, April 19, 2010 2:37 PM
To: RE-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

For a straight grid-tie system@ 10 degree tilt, 180 azimuth, zero/little shade, 
NYC avg 4.29 kWh/m²/day.

Feed an SMA7000 with (3) strings of 11 Suntech STP275’s [9.075 kWdc]
Or
Do strings of 10, so itd be 8.250 kWdc into the 7 kWac inverter.

Strings of 11= 491.7 Voc; 386 Vmp
Strings of 10= 447 Voc; 351 Vmp

The tradeoff would be power clipping at/around noon in the sunny months in the 
9.075 kW scenario;
Inverter sleeping late every morning and retiring early in the evenings in the 
lowered voltage scenario.

Trying to figure out which would yield more kWh at the end of the year.

Any ideas appreciated,
thanks




Jim MacDonald
Solar Energy Systems, LLC
Brooklyn, NY 11222
www.solarEsystems.comhttp://www.solaresystems.com/


No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.801 / Virus Database: 271.1.1/2819 - Release Date: 04/19/10 
00:31:00

-Inline Attachment Follows-
___
List sponsored by Home Power magazine

List Address: 
RE-wrenches@lists.re-wrenches.orghttp://us.mc519.mail.yahoo.com/mc/compose?to=re-wrenc...@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

2010-04-19 Thread Jim MacDonald
Im sorry, I meant to write “11 modules per string” below..
Been a long day..

From: Jim MacDonald
Sent: Monday, April 19, 2010 7:41 PM
To: RE-wrenches
Cc: Jason Szrom
Subject: RE: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?

SB8000US only good for 480 Vac, we’re tying in at 208.

11 strings [11 modules per string] has been calc’d to be OK (600vdc) for 
record low -4 fahrenheit (-20 celsius).

I think the big concern as mentioned is getting the Voc high early in the AM to 
wake the inverter up, also maintaining the Vmp later in the day to keep it 
running for as long as possible into the late afternoon/ evening.
Will those extra kWh gleaned in the early AM/ late PM over the course of 365 
days be more than the kWh clipped during peak production times with the 9.075 
kWdc?
NYC average summer highs between 79 and 84 fahrenheit early june-late august.  
Sunlink rack @ 10° on a silver-painted built-up roof.

Time-of-use utility $ peak-shaving is not an issue here.

Thank you




From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Darryl Thayer
Sent: Monday, April 19, 2010 5:58 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?

The temperature correction is the concern.  I have heard lots of stories of 
inverters dieing when it gets to cold.  Look in the code book 690.7 at the 
temperature correction table.  Go to weather.com and find your record low 
temperature.  Find you Tc factor and will your senerios work?  I have heard 
from a sunny boy rep that it is OK to over power by 1.25%
darryl

--- On Mon, 4/19/10, Dana d...@solarwork.com wrote:

From: Dana d...@solarwork.com
Subject: Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per 
string?
To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date: Monday, April 19, 2010, 4:31 PM
Many times we switch to another module manufacturer as one will not fit or 
another inverter manufacturer.
PVPowered has a more relaxed window and we have had fine success with them when 
SMA does not fit.
Cold is the dictator and the 600 VDC threshold.


Thanks,  Dana Orzel

Great Solar Works, Inc
web - www.solarwork.com
E - d...@solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076

We have been slow to give up on the myth of the Earth's generosity.
Rather grandly, we have overdrawn our accounts.
Barbara Kingsolver - Water is life.

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jim MacDonald
Sent: Monday, April 19, 2010 2:37 PM
To: RE-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

For a straight grid-tie system@ 10 degree tilt, 180 azimuth, zero/little shade, 
NYC avg 4.29 kWh/m²/day.

Feed an SMA7000 with (3) strings of 11 Suntech STP275’s [9.075 kWdc]
Or
Do strings of 10, so itd be 8.250 kWdc into the 7 kWac inverter.

Strings of 11= 491.7 Voc; 386 Vmp
Strings of 10= 447 Voc; 351 Vmp

The tradeoff would be power clipping at/around noon in the sunny months in the 
9.075 kW scenario;
Inverter sleeping late every morning and retiring early in the evenings in the 
lowered voltage scenario.

Trying to figure out which would yield more kWh at the end of the year.

Any ideas appreciated,
thanks




Jim MacDonald
Solar Energy Systems, LLC
Brooklyn, NY 11222
www.solarEsystems.comhttp://www.solaresystems.com/


No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.801 / Virus Database: 271.1.1/2819 - Release Date: 04/19/10 
00:31:00

-Inline Attachment Follows-
___
List sponsored by Home Power magazine

List Address: 
RE-wrenches@lists.re-wrenches.orghttp://us.mc519.mail.yahoo.com/mc/compose?to=re-wrenc...@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org