2022-09-10 Thread Mac Lewis via RE-wrenches
Hi Jay,

It can process 6500W of solar per input port of the MPPT, in the case of
the 12kW, there are 2 of them. so around 13kW.  As an off-grid inverter,
it's a 9kW total if perfectly balanced, but perhaps better to think of as
37.5A per phase.

I don't believe that 37.5A increases if the solar is available or not with
the 12kW.  However, in the new 15kW, there is a little bump in the off-grid
inverter output when there is solar available.

Cheers

On Sat, Sep 10, 2022 at 11:15 AM jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> HI All
>
> I”m trying to figure out exactly how much PV/CC there is for off grid on
> the sol ark 12kw or 9kw off grid
>
>
> The manual says 6,500 and 6,500 watts but that is grid connected.
> It looks like its 6,500 max for offgrid?
>
> Is that correct?
>
> thanks in advance
> jay
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] sol ark 12kw question

2022-09-10 Thread jay via RE-wrenches
HI All

I”m trying to figure out exactly how much PV/CC there is for off grid on the 
sol ark 12kw or 9kw off grid


The manual says 6,500 and 6,500 watts but that is grid connected.  
It looks like its 6,500 max for offgrid?

Is that correct?

thanks in advance 
jay
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org