Bill Brooks posted this in 2008.  A couple of project-specific sentences
were removed to avoid confusion.

"The 6kVA value comes from the California Rule 21 that I worked on. It only
applies to split-phase 240V systems (6kVA on 120V). There is no specific
limit for imbalance on a 3-phase service.

A basic rule for single phase generation on a 3=phase service is to rotate
among the phases in a balanced manner...

...The best way to place the imbalanced single-phase generators on the service
is to test the current on all three phases and put the inverter(s) on the
most heavily loaded phase(s). This reduces the site imbalance by reducing
the imbalance on the serving transformer (lowering current on the most
heavily loaded phases). It is common for 3-phase services to have imbalances
of 10 kVA or more, so single-phase inverters can reduce the problem rather
than make it worse."




For a brighter energy future,


Andrew Truitt
NABCEP Certified PV Installerâ„¢ (ID# 032407-66)

Principal
Truitt Renewable Energy Consulting

(202) 486-7507

http://www.linkedin.com/pub/andrew-truitt/8/622/713



"Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!"

~William McDonough






On Tue, Nov 27, 2012 at 3:33 PM, Chris Mason
wrote:

> I really don't understand what your problem with this arrangement is.
> How would this be different from a house on phase A-B installing an
> inverter and the next house on Phase B-C installing an inverter? Or,
> installing two single phase 240V A/C units in a three phase building?
> Electricians have no issue with installing single phase equipment in three
> phase buildings so why should small inverters be any more a problem.
> While it is always neat to install three inverters n a three phase
> configuration, 4,500 watts of imbalance is trivial.
>
>
> On Tue, Nov 27, 2012 at 3:59 PM,  wrote:
>
>> **
>> We were asked to inspect a  GT system installed by others. Service is 208
>> 3ph with two (?) Fronius IG 4500 208v inverters. The inverter panel is 3ph
>> with two 2pole breakers - one each side of the buss bar in a A/B, B/C
>> configuration (??). Called Fronius and they said it would work, but they
>> "don't recommend it". No other information was given as to why they don't.
>> My electrician is very uncomfortable with doing work on this system as is
>> (ME TOO!), so I am wondering if I might be able get some ammo to convince
>> system owner to add a third inverter to get the system right. What problems
>> might/will be encountered in this system if not modified? BTW - inverter
>> LCD screens were crapped out, so we couldn't readily see if system was
>> functioning properlyfrom metering, we think not.
>>
>>
>> Holt E. Kelly
>> Holtek Fireplace & Solar Products
>> 500 Jewell Dr.
>> Waco TX. 76712
>> 254-751-9111
>> www.holteksolar.com
>>
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
> --
> Chris Mason
> President, Comet Systems Ltd
> www.cometenergysystems.com
>  Cell: 264.235.5670
> Skype: netconcepts
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3 Phase With 2 Inverters?

2012-11-27 Thread Chris Mason
I really don't understand what your problem with this arrangement is.
How would this be different from a house on phase A-B installing an
inverter and the next house on Phase B-C installing an inverter? Or,
installing two single phase 240V A/C units in a three phase building?
Electricians have no issue with installing single phase equipment in three
phase buildings so why should small inverters be any more a problem.
While it is always neat to install three inverters n a three phase
configuration, 4,500 watts of imbalance is trivial.


On Tue, Nov 27, 2012 at 3:59 PM,  wrote:

> **
> We were asked to inspect a  GT system installed by others. Service is 208
> 3ph with two (?) Fronius IG 4500 208v inverters. The inverter panel is 3ph
> with two 2pole breakers - one each side of the buss bar in a A/B, B/C
> configuration (??). Called Fronius and they said it would work, but they
> "don't recommend it". No other information was given as to why they don't.
> My electrician is very uncomfortable with doing work on this system as is
> (ME TOO!), so I am wondering if I might be able get some ammo to convince
> system owner to add a third inverter to get the system right. What problems
> might/will be encountered in this system if not modified? BTW - inverter
> LCD screens were crapped out, so we couldn't readily see if system was
> functioning properlyfrom metering, we think not.
>
>
> Holt E. Kelly
> Holtek Fireplace & Solar Products
> 500 Jewell Dr.
> Waco TX. 76712
> 254-751-9111
> www.holteksolar.com
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3 Phase With 2 Inverters?

2012-11-27 Thread Dave Click
I would agree that the imbalance at these power levels is not a major 
issue. If it appears that Phase A is most heavily-loaded, I'd install 
the inverters as A-B and A-C to help mitigate the existing imbalance. If 
you've got a lot of 1P loads on a 3P service-- lighting, office 
receptacles or whatever-- you could easily have a large imbalance on a 
regular basis. The 7kVA PV imbalance in your installation would happen 
extremely rarely.


If this imbalance still makes you uneasy, then install three inverters 
and then a relay system to bring all the inverters down in case any of 
them fails. The SMA Power Balancer does this for their inverters and 
maybe some third-parties offer them too for these Fronius installs. This 
seems to make the most sense for decentralized systems with many string 
inverters, to ensure that a low phase voltage doesn't turn off a 
fraction of your inverters and cause a >100kVA imbalance.


I've heard that some utilities have a max PV imbalance (calculated from 
the inverter ratings) of 6kVA. No utility to my knowledge requires an 
interconnection agreement for a 10kVA single-phase commercial water 
heater (to steal a Bill Brooks example) that would have a much stronger 
impact.


Dave


On 2012/11/27 15:14, penobscotso...@midmaine.com wrote:

Hi Holt,
We installed a commercial system a year ago for the National Park
Service that was designed by a competitor (?) and signed off on by an
engineer. It consisted of 13.2 kw of pv and two Fronius 7000 watt, 208
3 ph. inverters. It sounds a lot like what you are dealing with. I
questioned the engineer on it and he said because the facility was so
large (it was a large research and visitor "campus" for Acadia National
Park with 20+ buildings)the transformer would never see the imbalance
and therefore was not a problem. Fronius agreed, but prefaced that with
the fact that it still was "not recommended". I can say that we have
had no issues or complaints at all since the installation in August of
2011 and they monitor it continuously. It would have been a far better
design to use three Fronius 4.5 inverters at 3 ph. I drafted a letter
(CYA letter) to the powers that be about my concerns (transformer
imbalance) and they chose to go ahead with the installation. Nothing
like government work...many more stories about this installation
than anyone has time for here.

Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design




We were asked to inspect a  GT system installed by others. Service is 208
3ph with two (?) Fronius IG 4500 208v inverters. The inverter panel is 3ph
with two 2pole breakers - one each side of the buss bar in a A/B, B/C
configuration (??). Called Fronius and they said it would work, but they
"don't recommend it". No other information was given as to why they don't.
My electrician is very uncomfortable with doing work on this system as is
(ME TOO!), so I am wondering if I might be able get some ammo to convince
system owner to add a third inverter to get the system right. What
problems might/will be encountered in this system if not modified? BTW -
inverter LCD screens were crapped out, so we couldn't readily see if
system was functioning properlyfrom metering, we think not.


Holt E. Kelly
Holtek Fireplace & Solar Products
500 Jewell Dr.
Waco TX. 76712
254-751-9111
www.holteksolar.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3 Phase With 2 Inverters?

2012-11-27 Thread Larry Crutcher, Starlight Solar Power Systems
Hi holt,

Just FYI, Fronius will pay you $250 each to swap the inverters.

Larry Crutcher
Starlight Solar Power Systems





On Nov 27, 2012, at 12:59 PM,   
wrote:

We were asked to inspect a  GT system installed by others. Service is 208 3ph 
with two (?) Fronius IG 4500 208v inverters. The inverter panel is 3ph with two 
2pole breakers - one each side of the buss bar in a A/B, B/C configuration 
(??). Called Fronius and they said it would work, but they "don't recommend 
it". No other information was given as to why they don't. My electrician is 
very uncomfortable with doing work on this system as is (ME TOO!), so I am 
wondering if I might be able get some ammo to convince system owner to add a 
third inverter to get the system right. What problems might/will be encountered 
in this system if not modified? BTW - inverter LCD screens were crapped out, so 
we couldn't readily see if system was functioning properlyfrom metering, we 
think not.
 
 
Holt E. Kelly
Holtek Fireplace & Solar Products
500 Jewell Dr.
Waco TX. 76712
254-751-9111
www.holteksolar.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3 Phase With 2 Inverters?

2012-11-27 Thread penobscotsolar
Hi Holt,
   We installed a commercial system a year ago for the National Park
Service that was designed by a competitor (?) and signed off on by an
engineer. It consisted of 13.2 kw of pv and two Fronius 7000 watt, 208
3 ph. inverters. It sounds a lot like what you are dealing with. I
questioned the engineer on it and he said because the facility was so
large (it was a large research and visitor "campus" for Acadia National
Park with 20+ buildings)the transformer would never see the imbalance
and therefore was not a problem. Fronius agreed, but prefaced that with
the fact that it still was "not recommended". I can say that we have
had no issues or complaints at all since the installation in August of
2011 and they monitor it continuously. It would have been a far better
design to use three Fronius 4.5 inverters at 3 ph. I drafted a letter
(CYA letter) to the powers that be about my concerns (transformer
imbalance) and they chose to go ahead with the installation. Nothing
like government work...many more stories about this installation
than anyone has time for here.

Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design



> We were asked to inspect a  GT system installed by others. Service is 208
> 3ph with two (?) Fronius IG 4500 208v inverters. The inverter panel is 3ph
> with two 2pole breakers - one each side of the buss bar in a A/B, B/C
> configuration (??). Called Fronius and they said it would work, but they
> "don't recommend it". No other information was given as to why they don't.
> My electrician is very uncomfortable with doing work on this system as is
> (ME TOO!), so I am wondering if I might be able get some ammo to convince
> system owner to add a third inverter to get the system right. What
> problems might/will be encountered in this system if not modified? BTW -
> inverter LCD screens were crapped out, so we couldn't readily see if
> system was functioning properlyfrom metering, we think not.
>
>
> Holt E. Kelly
> Holtek Fireplace & Solar Products
> 500 Jewell Dr.
> Waco TX. 76712
> 254-751-9111
> www.holteksolar.com
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org