Re: [RE-wrenches] 48 V DC temp sensing relay
White-Rodgers-1609-101-Refrigeration-Temperature-Control- I have used this many times in various applications some close on temp rise other model closes on temp drop. Quite reliable! ___ Dana Orzel c- 2087217003 e - d...@solarwork.com --- Begin Message --- Hi Drake Try this one. I get a lot of equipment from supply house. Since you need on with temp rise it’s an AC type. This one will do 8 amps at 120v so a small amp dc fan won’t hurt the relay. Jay https://www.supplyhouse.com/White-Rodgers-1609-101-Refrigeration-Temperature-Control-30-Degrees-F-To-90-Degrees-F-Range-5-Capillary?utm_source=google_ad&utm_medium=shopping_neutral&utm_campaign=Shopping_Neutral_New_users&gad_source=1 On Dec 13, 2023, at 9:08 AM, Drake Chamberlin via RE-wrenches wrote: Hello, Does anyone know of a 48 VDC temperature sensing relay? I need to use one to control a fan in a 48 V battery bank, to bring in cold air when the bank gets too hot from the wood heating system in the house. The relay needs to operate with the 48 VDC power supply and disconnect a small current with 48 VDC contacts. Thank you, Drake Drake Chamberlin Athens Electric LLC Ohio Electrical Contractor’s License 44810 NABCEP Certified PV Installation Professional -- ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org --- End Message --- ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] 48 V DC temp sensing relay
Have you considered using a thermostat? Like the A19 series. Mechanical, non-electric. Kevin From: RE-wrenches On Behalf Of Drake Chamberlin via RE-wrenches Sent: December-13-23 8:08 AM To: RE-wrenches Cc: drake.chamber...@redwoodalliance.org Subject: [RE-wrenches] 48 V DC temp sensing relay Hello, Does anyone know of a 48 VDC temperature sensing relay? I need to use one to control a fan in a 48 V battery bank, to bring in cold air when the bank gets too hot from the wood heating system in the house. The relay needs to operate with the 48 VDC power supply and disconnect a small current with 48 VDC contacts. Thank you, Drake Drake Chamberlin Athens Electric LLC Ohio Electrical Contractor’s License 44810 NABCEP Certified PV Installation Professional -- ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] 48 V DC temp sensing relay
William, I'm planning to use a 48 V battery vent fan, turned around backwards, to blow air into the box. Thank you, Drake _Drake Chamberlin_ _Athens Electric LLC_ _Ohio Electrical Contractor's License 44810_ _NABCEP Certified PV Installation Professional_ --- On 2023-12-13 11:25, William Miller via RE-wrenches wrote: Drake: I tried running 48 VDC muffin fans on battery voltage. They failed. I switched to a Dc-Dc converter (12 or 24, can't remember) from digi-key and problem solved. Point being battery voltage ranges may be too extreme for some components. William Miller Miller Solar.com 805-438-5600 www.millersolar.com [1] On Wed, Dec 13, 2023 at 8:08 AM Drake Chamberlin via RE-wrenches wrote: Hello, Does anyone know of a 48 VDC temperature sensing relay? I need to use one to control a fan in a 48 V battery bank, to bring in cold air when the bank gets too hot from the wood heating system in the house. The relay needs to operate with the 48 VDC power supply and disconnect a small current with 48 VDC contacts. Thank you, Drake _Drake Chamberlin_ _Athens Electric LLC_ _Ohio Electrical Contractor's License 44810_ _NABCEP Certified PV Installation Professional_ -- ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org Links: -- [1] http://www.millersolar.com___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] 48 V DC temp sensing relay
Hi Drake Try this one. I get a lot of equipment from supply house. Since you need on with temp rise it’s an AC type. This one will do 8 amps at 120v so a small amp dc fan won’t hurt the relay. Jay https://www.supplyhouse.com/White-Rodgers-1609-101-Refrigeration-Temperature-Control-30-Degrees-F-To-90-Degrees-F-Range-5-Capillary?utm_source=google_ad&utm_medium=shopping_neutral&utm_campaign=Shopping_Neutral_New_users&gad_source=1 > On Dec 13, 2023, at 9:08 AM, Drake Chamberlin via RE-wrenches > wrote: > > > Hello, > > Does anyone know of a 48 VDC temperature sensing relay? I need to use one to > control a fan in a 48 V battery bank, to bring in cold air when the bank gets > too hot from the wood heating system in the house. > > The relay needs to operate with the 48 VDC power supply and disconnect a > small current with 48 VDC contacts. > > Thank you, > > Drake > > Drake Chamberlin > > Athens Electric LLC > > Ohio Electrical Contractor’s License 44810 > > NABCEP Certified PV Installation Professional > > > > -- > > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] 48 V DC temp sensing relay
Drake: I tried running 48 VDC muffin fans on battery voltage. They failed. I switched to a Dc-Dc converter (12 or 24, can’t remember) from digi-key and problem solved. Point being battery voltage ranges may be too extreme for some components. William Miller Miller Solar.com 805-438-5600 www.millersolar.com On Wed, Dec 13, 2023 at 8:08 AM Drake Chamberlin via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hello, > > Does anyone know of a 48 VDC temperature sensing relay? I need to use one > to control a fan in a 48 V battery bank, to bring in cold air when the bank > gets too hot from the wood heating system in the house. > > The relay needs to operate with the 48 VDC power supply and disconnect a > small current with 48 VDC contacts. > > Thank you, > > Drake > > > *Drake Chamberlin* > > *Athens Electric LLC* > > *Ohio Electrical Contractor’s License 44810* > > *NABCEP Certified PV Installation Professional* > > > -- > > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org