Re: [RE-wrenches] 480 single phase delta
If it's 240V single phase center tapped between two legs of a 480V delta transformer, then one of the 240V legs *is* technically a neutral. What you have is two 240V legs between two of three 480V phases. That said, if the service from the utility is this type of 480/240V "split-phase," which presumably is exclusively to run pumps, then you're probably going to have a hard time coming up with a good solution, and the utility will probably not appreciate the phase imbalance that would be introduced. On the other hand, if the load is constant and greater than the solar production, they may appreciate it, provided you can find a suitable inverter, which I don't know of for this type of service. If the service is actually 480V delta and they are providing 240V for the customer's convenience with a center tapped neutral, then obviously the 3-phase 480V is where you want to connect, but because you have 3 wires and not 4 this does not seem to be the case. See if the utility will supply the third hot 480V conductor and switch the service to 3-phase. They can leave the neutral in place to support the 240V loads. [image: Inline image 1] Jason Szumlanski Florida Solar Design Group On Fri, Apr 29, 2016 at 3:52 PM, Chris Mason wrote: > If it's delta there is no neutral. > On Apr 29, 2016 12:40, "jay" wrote: > >> HI Jerry and all, >> >> I’m sorry if I confused the issue. >> I haven’t seen this, I’m doing the research for a friend. >> It has been measured at numbers provided. 480 line to line, 240v line >> to neutral, 2 hots wires, not 3. >> >> The client has been told by 3 different installers that its impossible >> system to do. >> And as the experts here have provided, thats just not true. >> >> Thanks for the input. >> >> jay >> >> >> On Apr 28, 2016, at 6:58 PM, Jerry Shafer >> wrote: >> >> I cant say l have seen a single phase delta, open delta, use two of the >> three legs but not on pumps, can someone explain, what am l missing as the >> term delta is three points >> Jerry >> On Apr 28, 2016 3:50 PM, "Jay" wrote: >> >> Great inverter but this is single phase. >> Jay >> >> Sent from my iPhone >> >> On Apr 28, 2016, at 3:10 PM, jerrysgarage01 >> wrote: >> >> What about an SMA Tri Power inverter >> Jerry >> >> >> Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone >> >> >> Original message >> From: Chris Mason >> Date:04/28/2016 8:52 AM (GMT-10:00) >> To: RE-wrenches >> Subject: Re: [RE-wrenches] 480 single phase delta >> >> You will use a 240:480v step up transformer >> On Apr 28, 2016 14:17, "jay" wrote: >> >>> HI All, >>> >>> I have a question from a person wanting to do a intertie on a commercial >>> water pumping site with >>> >>> 480v single phase delta configuration. >>> >>> PV will be in the 10kw range. >>> >>> Anybody have an idea of what equipment will work for this? >>> >>> >>> >>> thanks >>> >>> jay >>> >>> peltz power >>> ___ >>> List sponsored by Redwood Alliance >>> >>> List Address: RE-wrenches@lists.re-wrenches.org >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> >>> List-Archive: >>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >>> >>> List rules & etiquette: >>> www.re-wrenches.org/etiquette.htm >>> >>> Check out or update participant bios: >>> www.members.re-wrenches.org >>> >>> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver
Re: [RE-wrenches] 480 single phase delta
If it's delta there is no neutral. On Apr 29, 2016 12:40, "jay" wrote: > HI Jerry and all, > > I’m sorry if I confused the issue. > I haven’t seen this, I’m doing the research for a friend. > It has been measured at numbers provided. 480 line to line, 240v line to > neutral, 2 hots wires, not 3. > > The client has been told by 3 different installers that its impossible > system to do. > And as the experts here have provided, thats just not true. > > Thanks for the input. > > jay > > > On Apr 28, 2016, at 6:58 PM, Jerry Shafer > wrote: > > I cant say l have seen a single phase delta, open delta, use two of the > three legs but not on pumps, can someone explain, what am l missing as the > term delta is three points > Jerry > On Apr 28, 2016 3:50 PM, "Jay" wrote: > > Great inverter but this is single phase. > Jay > > Sent from my iPhone > > On Apr 28, 2016, at 3:10 PM, jerrysgarage01 > wrote: > > What about an SMA Tri Power inverter > Jerry > > > Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone > > > ---- Original message > From: Chris Mason > Date:04/28/2016 8:52 AM (GMT-10:00) > To: RE-wrenches > Subject: Re: [RE-wrenches] 480 single phase delta > > You will use a 240:480v step up transformer > On Apr 28, 2016 14:17, "jay" wrote: > >> HI All, >> >> I have a question from a person wanting to do a intertie on a commercial >> water pumping site with >> >> 480v single phase delta configuration. >> >> PV will be in the 10kw range. >> >> Anybody have an idea of what equipment will work for this? >> >> >> >> thanks >> >> jay >> >> peltz power >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] 480 single phase delta
Hi Jay -Usually 408 delta will have 3 legs. See https://en.wikipedia.org/wiki/Three-phase_electric_powerUnlike Wye, the neutral is center tapped from the winding between two of the legs.The third is a hi leg or "stinger" leg that is 1.5 times the others voltage to neutral.Sounds like what you have is two of three legs with a center tapped neutral; the the hi leg is probably around somewhere on site. If you can find it then a 3-phase inverter will work. Otherwise, as mentioned you will need a transformer to get 240 across the legs you have. But 10kW of solar will unbalance the phases. Best to find that third leg and use a 3-phase inverter. I have used the Fronius IG Plus 11.4 for this with good results. Don BarchEnergy Solar Date: Fri, 29 Apr 2016 08:03:26 -0700 From: jay <jay.pe...@gmail.com> To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: Re: [RE-wrenches] 480 single phase delta Message-ID: <b75c4e4a-5eb4-49d0-a7d4-9bdee1e40...@gmail.com> Content-Type: text/plain; charset="utf-8" HI Jerry and all, I?m sorry if I confused the issue. I haven?t seen this, I?m doing the research for a friend. It has been measured at numbers provided. 480 line to line, 240v line to neutral, 2 hots wires, not 3. The client has been told by 3 different installers that its impossible system to do. And as the experts here have provided, thats just not true. Thanks for the input. jay > On Apr 28, 2016, at 6:58 PM, Jerry Shafer <jerrysgarag...@gmail.com> wrote: > > I cant say l have seen a single phase delta, open delta, use two of the three legs but not on pumps, can someone explain, what am l missing as the term delta is three points > Jerry > > On Apr 28, 2016 3:50 PM, "Jay" <jay.pe...@gmail.com ><mailto:jay.pe...@gmail.com>> wrote: > Great inverter but this is single phase. > Jay > > Sent from my iPhone > > On Apr 28, 2016, at 3:10 PM, jerrysgarage01 <jerrysgarag...@gmail.com ><mailto:jerrysgarag...@gmail.com>> wrote: > >> What about an SMA Tri Power inverter >> Jerry >> >> >> Sent via the Samsung Galaxy S? III, an AT&T 4G LTE smartphone >> >> >> Original message >> From: Chris Mason >> Date:04/28/2016 8:52 AM (GMT-10:00) >> To: RE-wrenches >> Subject: Re: [RE-wrenches] 480 single phase delta >> >> You will use a 240:480v step up transformer >> >> On Apr 28, 2016 14:17, "jay" <jay.pe...@gmail.com ><mailto:jay.pe...@gmail.com>> wrote: >> HI All, >> >> I have a question from a person wanting to do a intertie on a commercial water pumping site with >> >> 480v single phase delta configuration. >> >> PV will be in the 10kw range. >> >> Anybody have an idea of what equipment will work for this? >> >> >> >> thanks >> >> jay >> >> peltz power ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] 480 single phase delta
HI Jerry and all, I’m sorry if I confused the issue. I haven’t seen this, I’m doing the research for a friend. It has been measured at numbers provided. 480 line to line, 240v line to neutral, 2 hots wires, not 3. The client has been told by 3 different installers that its impossible system to do. And as the experts here have provided, thats just not true. Thanks for the input. jay > On Apr 28, 2016, at 6:58 PM, Jerry Shafer wrote: > > I cant say l have seen a single phase delta, open delta, use two of the three > legs but not on pumps, can someone explain, what am l missing as the term > delta is three points > Jerry > > On Apr 28, 2016 3:50 PM, "Jay" <mailto:jay.pe...@gmail.com>> wrote: > Great inverter but this is single phase. > Jay > > Sent from my iPhone > > On Apr 28, 2016, at 3:10 PM, jerrysgarage01 <mailto:jerrysgarag...@gmail.com>> wrote: > >> What about an SMA Tri Power inverter >> Jerry >> >> >> Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone >> >> >> -------- Original message ---- >> From: Chris Mason >> Date:04/28/2016 8:52 AM (GMT-10:00) >> To: RE-wrenches >> Subject: Re: [RE-wrenches] 480 single phase delta >> >> You will use a 240:480v step up transformer >> >> On Apr 28, 2016 14:17, "jay" > <mailto:jay.pe...@gmail.com>> wrote: >> HI All, >> >> I have a question from a person wanting to do a intertie on a commercial >> water pumping site with >> >> 480v single phase delta configuration. >> >> PV will be in the 10kw range. >> >> Anybody have an idea of what equipment will work for this? >> >> >> >> thanks >> >> jay >> >> peltz power >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> <mailto:RE-wrenches@lists.re-wrenches.org> >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> >> >> Check out or update participant bios: >> www.members.re-wrenches.org <http://www.members.re-wrenches.org/> >> >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> <mailto:RE-wrenches@lists.re-wrenches.org> >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> >> >> Check out or update participant bios: >> www.members.re-wrenches.org <http://www.members.re-wrenches.org/> >> > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > <mailto:RE-wrenches@lists.re-wrenches.org> > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> > > Check out or update participant bios: > www.members.re-wrenches.org <http://www.members.re-wrenches.org/> > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] 480 single phase delta
The newer Tripower STP3 can be configured for delta, but the 12000-24000 cannot. A step up transformer sounds like the way to go. Best, Garrison Garrison Riegel Solar Service Inc From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jerrysgarage01 Sent: Thursday, April 28, 2016 5:11 PM To: RE-wrenches Subject: Re: [RE-wrenches] 480 single phase delta What about an SMA Tri Power inverter Jerry Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone Original message From: Chris Mason Date:04/28/2016 8:52 AM (GMT-10:00) To: RE-wrenches Subject: Re: [RE-wrenches] 480 single phase delta You will use a 240:480v step up transformer On Apr 28, 2016 14:17, "jay" mailto:jay.pe...@gmail.com>> wrote: HI All, I have a question from a person wanting to do a intertie on a commercial water pumping site with 480v single phase delta configuration. PV will be in the 10kw range. Anybody have an idea of what equipment will work for this? thanks jay peltz power ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org> Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm> Check out or update participant bios: www.members.re-wrenches.org<http://www.members.re-wrenches.org> ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] 480 single phase delta
I cant say l have seen a single phase delta, open delta, use two of the three legs but not on pumps, can someone explain, what am l missing as the term delta is three points Jerry On Apr 28, 2016 3:50 PM, "Jay" wrote: Great inverter but this is single phase. Jay Sent from my iPhone On Apr 28, 2016, at 3:10 PM, jerrysgarage01 wrote: What about an SMA Tri Power inverter Jerry Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone Original message From: Chris Mason Date:04/28/2016 8:52 AM (GMT-10:00) To: RE-wrenches Subject: Re: [RE-wrenches] 480 single phase delta You will use a 240:480v step up transformer On Apr 28, 2016 14:17, "jay" wrote: > HI All, > > I have a question from a person wanting to do a intertie on a commercial > water pumping site with > > 480v single phase delta configuration. > > PV will be in the 10kw range. > > Anybody have an idea of what equipment will work for this? > > > > thanks > > jay > > peltz power > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] 480 single phase delta
Great inverter but this is single phase. Jay Sent from my iPhone > On Apr 28, 2016, at 3:10 PM, jerrysgarage01 wrote: > > What about an SMA Tri Power inverter > Jerry > > > Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone > > > Original message > From: Chris Mason > Date:04/28/2016 8:52 AM (GMT-10:00) > To: RE-wrenches > Subject: Re: [RE-wrenches] 480 single phase delta > > You will use a 240:480v step up transformer > >> On Apr 28, 2016 14:17, "jay" wrote: >> HI All, >> >> I have a question from a person wanting to do a intertie on a commercial >> water pumping site with >> >> 480v single phase delta configuration. >> >> PV will be in the 10kw range. >> >> Anybody have an idea of what equipment will work for this? >> >> >> >> thanks >> >> jay >> >> peltz power >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] 480 single phase delta
The Tripower is 3 phase On Apr 28, 2016 18:11, "jerrysgarage01" wrote: > What about an SMA Tri Power inverter > Jerry > > > Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone > > > Original message > From: Chris Mason > Date:04/28/2016 8:52 AM (GMT-10:00) > To: RE-wrenches > Subject: Re: [RE-wrenches] 480 single phase delta > > You will use a 240:480v step up transformer > On Apr 28, 2016 14:17, "jay" wrote: > >> HI All, >> >> I have a question from a person wanting to do a intertie on a commercial >> water pumping site with >> >> 480v single phase delta configuration. >> >> PV will be in the 10kw range. >> >> Anybody have an idea of what equipment will work for this? >> >> >> >> thanks >> >> jay >> >> peltz power >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] 480 single phase delta
What about an SMA Tri Power inverter Jerry Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone Original message From: Chris Mason Date:04/28/2016 8:52 AM (GMT-10:00) To: RE-wrenches Subject: Re: [RE-wrenches] 480 single phase delta You will use a 240:480v step up transformer On Apr 28, 2016 14:17, "jay" wrote: HI All, I have a question from a person wanting to do a intertie on a commercial water pumping site with 480v single phase delta configuration. PV will be in the 10kw range. Anybody have an idea of what equipment will work for this? thanks jay peltz power ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] 480 single phase delta
You will use a 240:480v step up transformer On Apr 28, 2016 14:17, "jay" wrote: > HI All, > > I have a question from a person wanting to do a intertie on a commercial > water pumping site with > > 480v single phase delta configuration. > > PV will be in the 10kw range. > > Anybody have an idea of what equipment will work for this? > > > > thanks > > jay > > peltz power > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org