Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-14 Thread Jarmo . Venalainen
Hi:

I came across this document related to battery venting and calculation of 
the required vent hole size which was put out by Sonnenschein, 

It's based on the EN 50272-2  standard.  Perhaps it can be used to provide 
some guidance for discussion with AHJ's

http://www.sonnenschein.org/PDF%20files/BatteryRoomVentilationInstallation.PDF

JARMO
_
 


Jarmo Venalainen  |   Schneider Electric   |  Solar Business  |   CANADA | 
  Training  Development Specialist - Senior 
Phone: +604-422-2528  |   Fax: +604-420-1591  |   Mobile: +604-505-0291 
Email: jarmo.venalai...@schneider-electric.com  |   Site: www.SEsolar.com 
|   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 


*** Please consider the environment before printing this e-mail 




From:
Allan Sindelar al...@sindelarsolar.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org, 
Date:
11/03/2014 02:36 PM
Subject:
Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)
Sent by:
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org



Drake,
No, and unless and until it comes up again, they won't. My drama with them 
in January led to a draw: I put in a vent fan and they tabled the issue 
without broader resolution and approved the final inspection so the 
clients could move in. 

Allan Sindelar
al...@sindelarsolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell

 
On 11/2/2014 10:08 AM, Drake wrote:
Allan,

Has New Mexico ever come to conclusions concerning venting sealed 
batteries to the outside, or is it still in limbo?

Thanks,

Drake

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-03 Thread Allan Sindelar

  
  
Bob,
  For what it's worth, my experience has been good. I have used
  maybe 30-40 on various systems over the years and serviced a few
  installed by homeowners and others. I have replaced perhaps half a
  dozen of the fans. But that includes ones in which rain got in, or
  a bird got in the stack, died and blocked the fan. Whoops - come
  to think of it, that also includes Sun-Mar compost toilet exhaust
  fans, which were seldom capped to keep birds out.
  
  The only moving part that could fail is the fan, and it's a
  standard 3" muffin fan, made by the millions. The rest is pretty
  much just PVC fittings. I'm not sure I'd necessarily trust Radio
  Shack to supply a better fan.
  
  In Drake's case operational longevity would be less of an issue. A
  fan that is there for safety, and seldom if ever runs, would be
  unlikely to wear out.
  Allan
  
  











  Allan Sindelar
al...@sindelarsolar.com
NABCEP Certified PV
  Installation Professional
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder (Retired), Positive Energy,
Inc.
  505 780-2738 cell
  
  
  

  
  On 11/2/2014 4:14 PM, RE Ellison wrote:


  
  
  
  
I have had
poor luck with the Zephyr fan lasting. Maybe the newer units
are improved.
Years ago I
settled on a Radio Shack 3 fan that has given me good
lifetimes and draws under the relay limit in the
controllers. I usually mount it in a PVC 6 x 6 box as high
in the battery box as I can get it. Then run the 2 as high
as I can. If backdrafts are a worry (does not seem to be an
issue with a tall pipe) use a s+d flapper valve, mounted
vertically. 

Bob Ellison

  
From:
RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On
  Behalf Of Drake
Sent: Sunday, November 02, 2014 12:08 PM
    To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Venting (WAS
    Passive Battery Venting)
  


Allan,
  
  That was my plan when he insisted on venting to the outside. 
  
  I use the Zephyr Power Vent for liquid lead acid batteries.
  When replaced the liquid electrolyte batteries in our backup
  system with AGM, we turned off the Zephyr and took the door
  off the battery box. I showed it to the client. I think when
  you use the word hydrogen to many people they think of the
  Hindenberg disaster. 
  
  Has New Mexico ever come to conclusions concerning venting
  sealed batteries to the outside, or is it still in limbo?
  
  Thanks,
  
  Drake
  
  
  
  At 11:39 AM 11/2/2014, you wrote:
  
  
Drake,
  My suggestion is that to achieve the client's wishes as well
  as your own cooling concerns, you include a Zephyr Power Vent
  in a 2" PVC vent stack to the outside. Let the charge
  controller's voltage-actuated auxiliary setting power the vent
  (it's OK to do so directly on Outback and Midnite controllers,
  and I believe all other major ones as well). As these are
  sealed batteries,they won't gas significantly under normal
  charge voltages. Set the turn-on voltage at the gassing
  voltage, or thereabouts depending on your determination. This
  will be above (or below but near) normal charge voltage, and
  will cause the Power Vent to turn on only under abnormal
  conditions. The Power Vent also has a backdraft damper built
  in (which is why it must be oriented vertically) so will
  prevent excessive convective heat loss when not running.
  
  This won't address the possibility of one cell failing and
  gassing, as the string voltage determines turn-on. However, as
  others have pointed out, that may be of benefit: if one cell
  fails you'll still be able to smell it and address the
  problem.
  Allan
  
  Allan Sindelar
  al...@sindelarsolar.com
  NABCEP Certified PV Installation Professional
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder (Retired), Positive Energy, Inc.
  505 780-2738 cell
  
  

Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-03 Thread Allan Sindelar

  
  
Drake,
  No, and unless and until it comes up again, they won't. My drama
  with them in January led to a draw: I put in a vent fan and they
  tabled the issue without broader resolution and approved the final
  inspection so the clients could move in. 
  
  











  Allan Sindelar
al...@sindelarsolar.com
NABCEP Certified PV
  Installation Professional
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder (Retired), Positive Energy,
Inc.
  505 780-2738 cell
  
  
  

  
  On 11/2/2014 10:08 AM, Drake wrote:


  Allan,
  
  Has New Mexico ever come to conclusions concerning venting sealed
  batteries to the outside, or is it still in limbo?
  
  Thanks,
  
  Drake

  

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-02 Thread Allan Sindelar

  
  
Drake,
  My suggestion is that to achieve the client's wishes as well as
  your own cooling concerns, you include a Zephyr Power Vent in a 2"
  PVC vent stack to the outside. Let the charge controller's
  voltage-actuated auxiliary setting power the vent (it's OK to do
  so directly on Outback and Midnite controllers, and I believe all
  other major ones as well). As these are sealed batteries,they
  won't gas significantly under normal charge voltages. Set the
  turn-on voltage at the gassing voltage, or thereabouts depending
  on your determination. This will be above (or below but near)
  normal charge voltage, and will cause the Power Vent to turn on
  only under abnormal conditions. The Power Vent also has a
  backdraft damper built in (which is why it must be oriented
  vertically) so will prevent excessive convective heat loss when
  not running.
  
  This won't address the possibility of one cell failing and
  gassing, as the string voltage determines turn-on. However, as
  others have pointed out, that may be of benefit: if one cell fails
  you'll still be able to smell it and address the problem.
  Allan
  
  











  Allan Sindelar
al...@sindelarsolar.com
NABCEP Certified PV
  Installation Professional
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder (Retired), Positive Energy,
Inc.
  505 780-2738 cell
  
  
  

  
  On 10/29/2014 6:19 PM, Drake wrote:

Hi Daniel,
  
  
  I typically vent them the way you do, which will allow any small
  amount of hydrogen out. The customer is absolutely adamant about
  venting these to the outside. I will cooperate so long as his
  method doesn't compromise the system through cooling the batteries
  unnecessarily in the dead of winter.
  
  
  He is a lawyer and came to the conclusion of the need for venting
  to the outside from reading the NEC which says that sealed
  batteries "require the same amount of ventilation" as liquid lead
  acid batteries. The code also says to vent appropriate to battery
  technology, so the code says two conflicting things. On the other
  hand, it doesn't say that liquid electrolyte batteries need to be
  vented to the outside. They will sure stink if you vent them to
  the inside.
  
  
  Drake
  
  
  At 09:54 AM 10/29/2014, you wrote:
  
  I just re-read the original post Drake.
These are AGM batteries. Do you have

a "belt, suspenders,...then a rocket pack" type of client here?


We typically vent our AGM boxes with small louver vents top and
bottom to

allow the batteries to ventilate for cooling purposes, not H2
concerns.


With Regards,


Daniel Young,

NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90

NABCEP Certified Solar Heating InstallerTM: Cert #SH031409-13


-Original Message-

From: RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On

Behalf Of Ray Walters

Sent: Tuesday, October 28, 2014 11:12 PM
    
To: RE-wrenches
        
Subject: Re: [RE-wrenches] Passive Battery Venting


That's why we usually have the batteries in a garage, basement,
or out

building that is not open to the living space.

I've seen some cases of very well sealed and insulated
enclosures allowing

batteries to over heat, and also build up a lot of acid damaged
connections.

Boxes I've seen with more air space and less sealing don't get
this build

up, but you're correct: they do occasionally allow H2S into the
surrounding

area.


R.Ray Walters

CTO, Solarray, Inc

Nabcep Certified PV Installer,

Licensed Master Electrician

Solar Design Engineer

303 505-8760


On 10/28/2014 8:10 PM, Jerry Shafer wrote:



 We do what we can to seal the enclosure so if or when a
battery fails

 and really gasses off the two vents on the same wall
regardless of

 wind direction will vent the gas. If it is not sealed then
the gas can

 travel through out the

Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-02 Thread Drake

Allan,

That was my plan when he insisted on venting to the outside.

I use the Zephyr Power Vent for liquid lead acid batteries. When 
replaced the liquid electrolyte batteries in our backup system with 
AGM, we turned off the Zephyr and took the door off the battery box. 
I showed it to the client. I think when you use the word hydrogen to 
many people they think of the Hindenberg disaster.


Has New Mexico ever come to conclusions concerning venting sealed 
batteries to the outside, or is it still in limbo?


Thanks,

Drake



At 11:39 AM 11/2/2014, you wrote:

Drake,
My suggestion is that to achieve the client's wishes as well as your 
own cooling concerns, you include a Zephyr Power Vent in a 2 PVC 
vent stack to the outside. Let the charge controller's 
voltage-actuated auxiliary setting power the vent (it's OK to do so 
directly on Outback and Midnite controllers, and I believe all other 
major ones as well). As these are sealed batteries,they won't gas 
significantly under normal charge voltages. Set the turn-on voltage 
at the gassing voltage, or thereabouts depending on your 
determination. This will be above (or below but near) normal charge 
voltage, and will cause the Power Vent to turn on only under 
abnormal conditions. The Power Vent also has a backdraft damper 
built in (which is why it must be oriented vertically) so will 
prevent excessive convective heat loss when not running.


This won't address the possibility of one cell failing and gassing, 
as the string voltage determines turn-on. However, as others have 
pointed out, that may be of benefit: if one cell fails you'll still 
be able to smell it and address the problem.

Allan

Allan Sindelar
mailto:al...@sindelarsolar.comal...@sindelarsolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell


On 10/29/2014 6:19 PM, Drake wrote:

Hi Daniel,

I typically vent them the way you do, which will allow any small 
amount of hydrogen out. The customer is absolutely adamant about 
venting these to the outside. I will cooperate so long as his 
method doesn't compromise the system through cooling the batteries 
unnecessarily in the dead of winter.


He is a lawyer and came to the conclusion of the need for venting 
to the outside from reading the NEC which says that sealed 
batteries require the same amount of ventilation as liquid lead 
acid batteries. The code also says to vent appropriate to battery 
technology, so the code says two conflicting things. On the other 
hand, it doesn't say that liquid electrolyte batteries need to be 
vented to the outside. They will sure stink if you vent them to the inside.


Drake

At 09:54 AM 10/29/2014, you wrote:
I just re-read the original post Drake. These are AGM batteries. 
Do you have

a belt, suspenders,...then a rocket pack type of client here?

We typically vent our AGM boxes with small louver vents top and bottom to
allow the batteries to ventilate for cooling purposes, not H2 concerns.

With Regards,

Daniel Young,
NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
NABCEP Certified Solar Heating InstallerTM: Cert #SH031409-13

-Original Message-
From: RE-wrenches 
[mailto:re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org] 
On

Behalf Of Ray Walters
Sent: Tuesday, October 28, 2014 11:12 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Passive Battery Venting

That's why we usually have the batteries in a garage, basement, or out
building that is not open to the living space.
I've seen some cases of very well sealed and insulated enclosures allowing
batteries to over heat, and also build up a lot of acid damaged 
connections.

Boxes I've seen with more air space and less sealing don't get this build
up, but you're correct: they do occasionally allow H2S into the surrounding
area.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 10/28/2014 8:10 PM, Jerry Shafer wrote:

 We do what we can to seal the enclosure so if or when a battery fails
 and really gasses off the two vents on the same wall regardless of
 wind direction will vent the gas. If it is not sealed then the gas can
 travel through out the area this is not advised.



___
List sponsored by Redwood Alliance

List Address: 
mailto:RE-wrenches@lists.re-wrenches.orgRE-wrenches@lists.re-wrenches.org


Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orghttp://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 



List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htmlhttp://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 



List rules  etiquette:
http://www.re-wrenches.org/etiquette.htmwww.re

Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-02 Thread RE Ellison
I have had poor luck with the Zephyr fan lasting. Maybe the newer units are
improved.

Years ago I settled on a Radio Shack 3 fan that has given me good lifetimes
and draws under the relay limit in the controllers. I usually mount it in a
PVC 6 x 6 box as high in the battery box as I can get it. Then run the 2 as
high as I can. If backdrafts are a worry (does not seem to be an issue with
a tall pipe) use a s+d flapper valve, mounted vertically.  

 

Bob Ellison

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Drake
Sent: Sunday, November 02, 2014 12:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

 

Allan,

That was my plan when he insisted on venting to the outside. 

I use the Zephyr Power Vent for liquid lead acid batteries. When replaced
the liquid electrolyte batteries in our backup system with AGM, we turned
off the Zephyr and took the door off the battery box. I showed it to the
client. I think when you use the word hydrogen to many people they think of
the Hindenberg disaster. 

Has New Mexico ever come to conclusions concerning venting sealed batteries
to the outside, or is it still in limbo?

Thanks,

Drake



At 11:39 AM 11/2/2014, you wrote:



Drake,
My suggestion is that to achieve the client's wishes as well as your own
cooling concerns, you include a Zephyr Power Vent in a 2 PVC vent stack to
the outside. Let the charge controller's voltage-actuated auxiliary setting
power the vent (it's OK to do so directly on Outback and Midnite
controllers, and I believe all other major ones as well). As these are
sealed batteries,they won't gas significantly under normal charge voltages.
Set the turn-on voltage at the gassing voltage, or thereabouts depending on
your determination. This will be above (or below but near) normal charge
voltage, and will cause the Power Vent to turn on only under abnormal
conditions. The Power Vent also has a backdraft damper built in (which is
why it must be oriented vertically) so will prevent excessive convective
heat loss when not running.

This won't address the possibility of one cell failing and gassing, as the
string voltage determines turn-on. However, as others have pointed out, that
may be of benefit: if one cell fails you'll still be able to smell it and
address the problem.
Allan

Allan Sindelar
al...@sindelarsolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell

 
On 10/29/2014 6:19 PM, Drake wrote:



Hi Daniel, 

I typically vent them the way you do, which will allow any small amount of
hydrogen out. The customer is absolutely adamant about venting these to the
outside. I will cooperate so long as his method doesn't compromise the
system through cooling the batteries unnecessarily in the dead of winter. 

He is a lawyer and came to the conclusion of the need for venting to the
outside from reading the NEC which says that sealed batteries require the
same amount of ventilation as liquid lead acid batteries. The code also
says to vent appropriate to battery technology, so the code says two
conflicting things. On the other hand, it doesn't say that liquid
electrolyte batteries need to be vented to the outside. They will sure stink
if you vent them to the inside. 

Drake 

At 09:54 AM 10/29/2014, you wrote: 



I just re-read the original post Drake. These are AGM batteries. Do you have

a belt, suspenders,...then a rocket pack type of client here? 

We typically vent our AGM boxes with small louver vents top and bottom to 
allow the batteries to ventilate for cooling purposes, not H2 concerns. 

With Regards, 

Daniel Young, 
NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90 
NABCEP Certified Solar Heating InstallerTM: Cert #SH031409-13 

-Original Message- 
From: RE-wrenches [ mailto:re-wrenches-boun...@lists.re-wrenches.org
mailto:re-wrenches-boun...@lists.re-wrenches.org ] On 
Behalf Of Ray Walters 
Sent: Tuesday, October 28, 2014 11:12 PM 
To: RE-wrenches 
Subject: Re: [RE-wrenches] Passive Battery Venting 

That's why we usually have the batteries in a garage, basement, or out 
building that is not open to the living space. 
I've seen some cases of very well sealed and insulated enclosures allowing 
batteries to over heat, and also build up a lot of acid damaged connections.

Boxes I've seen with more air space and less sealing don't get this build 
up, but you're correct: they do occasionally allow H2S into the surrounding 
area. 

R.Ray Walters 
CTO, Solarray, Inc 
Nabcep Certified PV Installer, 
Licensed Master Electrician 
Solar Design Engineer 
303 505-8760 

On 10/28/2014 8:10 PM, Jerry Shafer wrote: 
 
 We do what we can to seal the enclosure so if or when a battery fails 
 and really gasses off the two vents on the same wall regardless of 
 wind direction will vent the gas. If it is not sealed