Re: [RE-wrenches] Load testing batteries?

2011-01-26 Thread Mick Abraham
Hello, Jesse~ Instead of trying for laboratory precision, here's a way to
measure the battery capacity using equipment that you may already own:

* Gather up appropriate safety stuff: gloves, goggles, baking soda,
distilled water, off duty fireman, blast protection, etc.

* Connect only two of the 6 volt batteries in series to make a 12 volt
battery string. Put those on charge once you're sure they're warmed up 
thawed out. Maintain about 75 degrees Fahrenheit air temperature in the
testing area. Recharge quality is important if you want to give the
batteries a fair opportunity to show what they can do.

* Install a DC breaker between battery positive and the positive DC terminal
on a 12 volt inverter. The inverter should be 500 watts or bigger with AC
plug in receptacles; you can connect inverter negative to battery negative 
power it up on the DC side.

* Plug into the inverter with an AC kilowatt-hour meter (such as
Kill-a-Watt, the Brand meter, WattsUp?, etc.) then plug into the kWh meter
with an adjustable blow dryer.

* Switch on the hair dryer at a low setting then dial up on the heat until
your AC meter shows about 360 watts of power draw. The battery pair, if new,
should be able to sustain a drain like this for about ten hours--this is
based on the 298 amp-hour rate for that battery on the Rolls spec sheet.

* Run the blow dryer until the inverter shuts off due to low voltage, then
read the number of AC watt-hours that were clocked by the kWh meter. 298 amp
hours X 12 volt nominal = 3,576 watt-hours. Battery professionals would
replace a battery if it fails to deliver 50% of the original rated power.

* Repeat this same test with the other battery pairs. As mentioned, this
approach is not scientifically perfect, but it might be done with minimal
outlays for new equipment...and the results will be close enough.

Jolliness~

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675


On Tue, Jan 25, 2011 at 10:53 PM, Jesse Dahl dahlso...@gmail.com wrote:

 Wrenches,

 I have some (4) rolls 6 volt batteries 4000 series S-460. They are from a
 stand alone system in Ely, MN I have mentioned in a previous question. I had
 mentioned in the previous post that they were suspected to have been frozen
 (bulged cases).  The owner took them out of the system, dumped the
 electrolyte out and added new electrolyte.  I have no idea what she added or
 any specifics.

 I did a SG test today, all of the cells seemed to have 50% SOC, but I don't
 think that means anything.

 Most of the info I got from the last post and from my knowledge tells me
 the batteries are shot. They are 10 years old at least.  What I'm asking, I
 guess, is what type of load tester would a person need to load test a
 battery like this.  I have a cheap one, up 160Ah I believe, but I'm not sure
 if it will work this test.  I have limited battery experience and would
 appreciate any help with testing methods.

 Thanks everyone,


 Jesse

 Sent from my iPad!!!
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing batteries?

2011-01-26 Thread Exeltech
Once the electrolyte has been changed out, all bets are off for using SG as an 
indicator for state of charge.  Jamie Surette gave excellent commentary  on a 
similar thread recently on how to handle a situation such as this.

Mick's suggested procedure (below) will work, with caveats.

Be sure you use a meter that records accumulated watt-hour usage in 
non-volatile memory.  You'll be connecting the meter on the AC-side of the 
inverter, and when the AC goes off due to low DC input voltage, the meter will 
go off as well.  The basic Kill-A-Watt meter (and perhaps others?) forget 
everything when the power goes off.   P3 (mfgr of the K-A-W meter) make a model 
P4460 that remembers values even when powered down.  Others likely do as well.

I would recommend using incandescent lamps as a safer and more easily 
adjustable load.  Parallel three 100 watt lamps on a power strip.  With a meter 
(above) measure the actual power drawn by the lamps.

As a backup timer for testing batteries, I use an ordinary analog clock .. 
the type with moving hands (remember those?).  Got mine from a big-box store.  
It uses 3 watts, so is an insignificant load compared to 300-400 watts.  Set 
the clock to 12 am and start your test.  The clock will stop with the total run 
time when the inverter shuts off.

Speaking of inverters .. use a model that requires a manual reset after 
low-voltage shutdown.  Some types will automatically start back up if the 
voltage rises high enough again.  This could give you a bit of a false reading 
as to total capacity

Be careful.


Dan


--- On Wed, 1/26/11, Mick Abraham m...@abrahamsolar.com wrote:

From: Mick Abraham m...@abrahamsolar.com
Subject: Re: [RE-wrenches] Load testing batteries?
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Wednesday, January 26, 2011, 9:19 AM

Hello, Jesse~ Instead of trying for laboratory precision, here's a way to 
measure the battery capacity using equipment that you may already own:

* Gather up appropriate safety stuff: gloves, goggles, baking soda, distilled 
water, off duty fireman, blast protection, etc.



* Connect only two of the 6 volt batteries in series to make a 12 volt battery 
string. Put those on charge once you're sure they're warmed up  thawed out. 
Maintain about 75 degrees Fahrenheit air temperature in the testing area. 
Recharge quality is important if you want to give the batteries a fair 
opportunity to show what they can do. 



* Install a DC breaker between battery positive and the positive DC terminal on 
a 12 volt inverter. The inverter should be 500 watts or bigger with AC plug in 
receptacles; you can connect inverter negative to battery negative  power it 
up on the DC side.



* Plug into the inverter with an AC kilowatt-hour meter (such as Kill-a-Watt, 
the Brand meter, WattsUp?, etc.) then plug into the kWh meter with an 
adjustable blow dryer. 

* Switch on the hair dryer at a low setting then dial up on the heat until your 
AC meter shows about 360 watts of power draw. The battery pair, if new, should 
be able to sustain a drain like this for about ten hours--this is based on the 
298 amp-hour rate for that battery on the Rolls spec sheet. 



* Run the blow dryer until the inverter shuts off due to low voltage, then read 
the number of AC watt-hours that were clocked by the kWh meter. 298 amp hours X 
12 volt nominal = 3,576 watt-hours. Battery professionals would replace a 
battery if it fails to deliver 50% of the original rated power. 



* Repeat this same test with the other battery pairs. As mentioned, this 
approach is not scientifically perfect, but it might be done with minimal 
outlays for new equipment...and the results will be close enough.



Jolliness~

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675



On Tue, Jan 25, 2011 at 10:53 PM, Jesse Dahl dahlso...@gmail.com wrote:


Wrenches,



I have some (4) rolls 6 volt batteries 4000 series S-460. They are from a stand 
alone system in Ely, MN I have mentioned in a previous question. I had 
mentioned in the previous post that they were suspected to have been frozen 
(bulged cases).  The owner took them out of the system, dumped the electrolyte 
out and added new electrolyte.  I have no idea what she added or any specifics.





I did a SG test today, all of the cells seemed to have 50% SOC, but I don't 
think that means anything.



Most of the info I got from the last post and from my knowledge tells me the 
batteries are shot. They are 10 years old at least.  What I'm asking, I guess, 
is what type of load tester would a person need to load test a battery like 
this.  I have a cheap one, up 160Ah I believe, but I'm not sure if it will work 
this test.  I have limited battery experience and would appreciate any help 
with testing methods.





Thanks everyone,





Jesse



Sent from my iPad!!!

___

List sponsored by Home Power magazine



List Address: RE-wrenches@lists.re-wrenches.org

Re: [RE-wrenches] Load testing batteries?

2011-01-26 Thread Mick Abraham
My Brand brand kWh meter has non-volatile capture of the kWh data even
when power is removed. I assumed that was true of the other kWh meters,
also, but one would certainly want to check on that point. Dan's other
points are helpful. If the clock is left out of the setup , one could still
get a useful capacity number for the batteries.

Batteries are rated in amp-hours...not watt-hours, of course, so there is
some conversion math to be done. Similar testing could be done with an
amp-hour meter on the DC side between battery and load...and that would be
more precise for a couple of reasons. My suggested setup does not account
for inverter inefficiency, for example, so it will tend to understate the
actual capacity.

The big advantage of my original suggested test rig is that the needed items
are less exotic and more usable for other purposes. If Jesse doesn't already
own one of those plug in watt-hour meters, he probably wants a good excuse
to get one. Ditto for the mini inverter.

Jolliness,

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675


On Wed, Jan 26, 2011 at 8:42 AM, Exeltech exelt...@yahoo.com wrote:

 Once the electrolyte has been changed out, all bets are off for using SG as
 an indicator for state of charge.  Jamie Surette gave excellent commentary
 on a similar thread recently on how to handle a situation such as this.

 Mick's suggested procedure (below) will work, with caveats.

 Be sure you use a meter that records accumulated watt-hour usage in
 non-volatile memory.  You'll be connecting the meter on the AC-side of the
 inverter, and when the AC goes off due to low DC input voltage, the meter
 will go off as well.  The basic Kill-A-Watt meter (and perhaps others?)
 forget everything when the power goes off.   P3 (mfgr of the K-A-W meter)
 make a model P4460 that remembers values even when powered down.  Others
 likely do as well.

 I would recommend using incandescent lamps as a safer and more easily
 adjustable load.  Parallel three 100 watt lamps on a power strip.  With a
 meter (above) measure the actual power drawn by the lamps.

 As a backup timer for testing batteries, I use an ordinary analog clock
 .. the type with moving hands (remember those?).  Got mine from a big-box
 store.  It uses 3 watts, so is an insignificant load compared to 300-400
 watts.  Set the clock to 12 am and start your test.  The clock will stop
 with the total run time when the inverter shuts off.

 Speaking of inverters .. use a model that requires a manual reset after
 low-voltage shutdown.  Some types will automatically start back up if the
 voltage rises high enough again.  This could give you a bit of a false
 reading as to total capacity

 Be careful.


 Dan


 --- On *Wed, 1/26/11, Mick Abraham m...@abrahamsolar.com* wrote:


 From: Mick Abraham m...@abrahamsolar.com
 Subject: Re: [RE-wrenches] Load testing batteries?
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Wednesday, January 26, 2011, 9:19 AM


 Hello, Jesse~ Instead of trying for laboratory precision, here's a way to
 measure the battery capacity using equipment that you may already own:

 * Gather up appropriate safety stuff: gloves, goggles, baking soda,
 distilled water, off duty fireman, blast protection, etc.

 * Connect only two of the 6 volt batteries in series to make a 12 volt
 battery string. Put those on charge once you're sure they're warmed up 
 thawed out. Maintain about 75 degrees Fahrenheit air temperature in the
 testing area. Recharge quality is important if you want to give the
 batteries a fair opportunity to show what they can do.

 * Install a DC breaker between battery positive and the positive DC
 terminal on a 12 volt inverter. The inverter should be 500 watts or bigger
 with AC plug in receptacles; you can connect inverter negative to battery
 negative  power it up on the DC side.

 * Plug into the inverter with an AC kilowatt-hour meter (such as
 Kill-a-Watt, the Brand meter, WattsUp?, etc.) then plug into the kWh meter
 with an adjustable blow dryer.

 * Switch on the hair dryer at a low setting then dial up on the heat until
 your AC meter shows about 360 watts of power draw. The battery pair, if new,
 should be able to sustain a drain like this for about ten hours--this is
 based on the 298 amp-hour rate for that battery on the Rolls spec sheet.

 * Run the blow dryer until the inverter shuts off due to low voltage, then
 read the number of AC watt-hours that were clocked by the kWh meter. 298 amp
 hours X 12 volt nominal = 3,576 watt-hours. Battery professionals would
 replace a battery if it fails to deliver 50% of the original rated power.

 * Repeat this same test with the other battery pairs. As mentioned, this
 approach is not scientifically perfect, but it might be done with minimal
 outlays for new equipment...and the results will be close enough.

 Jolliness~

 Mick Abraham, Proprietor
 www.abrahamsolar.com

 Voice: 970-731-4675


 On Tue, Jan 25, 2011 at 10:53 PM, Jesse Dahl