Mac,

Victron would work quite well as well. The biggest drawback is that they don't 
have a single unit for 120/240, but stacking two units works great and they 
have been really good for surge capacity in my opinion.

I admit that I am biased. I've been using Victron for 6 years, and 3 years ago. 
About 3 years ago, I switched away from Outback and Schneider and started 
primarily using Victron. When I did, my equipment failure rate plummeted. In my 
own experience, Victron has been significantly more reliable, so I've become a 
real Victron advocate. Obviously, the other brands do have some advantages. 
Outback's online platform (optics RE) is the best for making it easy to adjust 
settings remotely from any device like your phone. Contact me off-list if you 
are interested in Victron, and I'll give you a lot more info about Victron.

Thanks,
Kienan Maxfield


Green-Go Solar Distribution LLC
Maxfield Solar LLC (installation and consulting company)
maxfieldso...@hotmail.com<mailto:maxfieldso...@hotmail.com>
(801) 631-5584 (Cell)

From: RE-wrenches  on behalf of Mac 
Lewis via RE-wrenches 
Sent: Saturday, January 14, 2023 9:20 AM
To: RE-wrenches 
Cc: Mac Lewis 
Subject: Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

Fully appreciate everyone's input.

The Midnite Rosie sounds interesting for sure.  Midnite is a great company with 
great support.  Smart people answer the phone and that really counts for a lot.

How are you getting your hands on these?  I can't seem to find much info, no 
spec sheets etc.  None of my vendors have them and Midnite is estimating Apr 
2023 as the release date.



On Sat, Jan 14, 2023 at 8:34 AM William Bryce via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
I run the XW6848 in my shop. When running my CNC plasma table the XW will 
shutdown due to exceeding its output rating if it is a long cut on metal when 
the 4HP compressor kicks on.
I also have a Midnite Solar Rosey, both are connected to the same battery so 
it's an equal comparison. The Rosy inverter will surge right through and finish 
the job, the XW is not in  the same league when comparing surge capability.

 A bonus is that the Rosey is really quiet as it does not have that big heavy 
transformer making noise under heavy load. It is easy to install as it is not 
as heavy. So far it's a game changer in regards to inverter hardware that I 
have tested.

On Fri, Jan 13, 2023 at 9:54 PM Chris Sparadeo via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
I have a client with a large woodworking shop…cabinet table saw, large 20” 240V 
bench planer, chop saws, compressors and a vacuum system. A single Sol Ark 15K 
takes care of these loads flawlessly. It seems that that inductive load snag 
with the smaller models has been resolved with the 15K.

Best,

Chris

On Fri, Jan 13, 2023 at 7:34 PM Glenn Burt via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
According to a seminar I just attended, the new Midnite Solar Rosie will...

-Glenn
Sent from my 'smart'phone, so please excuse typos and spelling errors.

-- Original message--
From: Dave Angelini Offgrid Solar via RE-wrenches
Date: Fri, Jan 13, 2023 3:55 PM
To: RE-wrenches;
Cc: Dave Angelini Offgrid Solar;
Subject:Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

There is not anything I know of that will out surge XW pro 6948. A great 
monitoring platform and much better support/installer training in the last 18 
months. Perfect for a shop with unknown peak surges.



Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net<mailto:offgridso...@sti.net>
text 209 813 0060


On 2023-01-13 11:57 am, Jay via RE-wrenches wrote:


Hi Mac

The radian is low voltage transformer
Based. Has hella surge capacity

I would consider what web based monitoring system he wants and go with that 
platform.

Regardless of system I'd install soft start/vfd on the larger units. Just 
easier on everything.

The solark 12 doesn't seem to be good for larger loads and doesn't do out of 
balance well, and limited to 6kw per phase. The new 15 might be better, not 
sure. Numerous YouTube videos showing side by side vs XW and radian. Both run 
stuff over their rating which the SolA won't run even though its under its 
rating.

Good luck

Jay








On Jan 13, 2023, at 11:34 AM, Mac Lewis via RE-wrenches > 
wrote:<mailto:%3cre-wrenc...@lists.re-wrenches.org>

Hello Wrenches,

I have a new client that has ran a pretty decent wood shop for about 10 years 
on a Magnum 4448.  He's got some large loads, planers, saws, compressors 
vacuums etc.  They are really nice, heavy duty pieces of equipment.  Amazingly, 
the Magnum has been able to start these loads for the most part for

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-16 Thread Dave Angelini Offgrid Solar via RE-wrenches



Happy to hear that ! When it is on the market and gets reviewed and 
tested for split phase balance, surge, and has a networked/monitored all 
in one power system it will be great.


Costing, a 10 year warranty and training also.

Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

On 2023-01-13 4:33 pm, Glenn Burt wrote:

According to a seminar I just attended, the new Midnite Solar Rosie 
will...


-Glenn
Sent from my 'smart'phone, so please excuse typos and spelling errors.

-- Original message--
From: Dave Angelini Offgrid Solar via RE-wrenches
Date: Fri, Jan 13, 2023 3:55 PM
To: RE-wrenches;
Cc: Dave Angelini Offgrid Solar;
Subject:Re: [RE-wrenches] Low Frequency transformer off-grid inverter 
options


There is not anything I know of that will out surge XW pro 6948. A 
great monitoring platform and much better support/installer training in 
the last 18 months. Perfect for a shop with unknown peak surges.


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060 [1]

On 2023-01-13 11 [2]:57 am, Jay via RE-wrenches wrote:

Hi Mac

The radian is low voltage transformer
Based. Has hella surge capacity

I would consider what web based monitoring system he wants and go with 
that platform.


Regardless of system I'd install soft start/vfd on the larger units. 
Just easier on everything.


The solark 12 doesn't seem to be good for larger loads and doesn't do 
out of balance well, and limited to 6kw per phase. The new 15 might be 
better, not sure. Numerous YouTube videos showing side by side vs XW 
and radian. Both run stuff over their rating which the SolA won't run 
even though its under its rating.


Good luck

Jay

On Jan 13, 2023, at 11:34 AM, Mac Lewis via RE-wrenches > wrote:

Hello Wrenches,

I have a new client that has ran a pretty decent wood shop for about 10 
years on a Magnum 4448.  He's got some large loads, planers, saws, 
compressors vacuums etc.  They are really nice, heavy duty pieces of 
equipment.  Amazingly, the Magnum has been able to start these loads 
for the most part for 10 years, but he has reported that it has gotten 
worse lately (could be a load issue), brown outs, dimming etc


He wants to upgrade the system, get remote monitoring etc.  I tried a 
test with a Sol-Ark 12, and it won't start these large motor loads.  I 
was a little surprised by that but I know they aren't as good as the 
low freq transformer based inverters at these surges.


I confirmed that its not just an overload from imbalance because the 
240V loads will also overload it.  I got an inrush measurement of 48.5A 
Ac @240 (but it didn't start the load before Sol-Ark would shut off)


What are my options?
Schneider XW Pro 6848
Outback Radian 8048 (Is this a low freq device?)
Sunny Islands are beasts but weird to work with and not user friendly

Any others I should consider?  He does have some significant 120 only 
loads so I don't think the Outback vfxr are a good choice.


Is it as simple as saying if the Magnum can start this load, the Radian 
should?


I appreciate your input!

--
Mac Lewis

"Yo solo sé que no sé nada." -Sócrates 
___

List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Links:
--
[1] tel:2098130060
[2] tel:2023-01-1311___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When on

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-14 Thread Darryl Thayer via RE-wrenches
Hello i have an XW Pro that starts a 2 HP induction motor reliably, i
noticed th scope indicates battery voltage current issue,  be sure your
batteries can supply the starting surge.  I recently installed a new set of
batteries.  Some not all Li can surge.

On Sat, Jan 14, 2023, 5:13 PM bob--- via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

>
> Three (3) weeks is also what I am being told.   Part of the delay was that
> ETL/Intertek dropped the ball, big time.
>
> Actually, ETL ran out of brains and we had to go to another NRTL
> altogether for inverters.
>
> And yes, it does surge very well.
>
> Merry new year, all !
>
> 🌜boB🌛
>
>  On 1/14/2023 11:40 AM, William Bryce via RE-wrenches wrote:
>
> I am told the RE (off grid version) will be available through normal
> distribution in 3 weeks.
>  As a Beta tester for this inverter I can say the use of SiC Fets is a
> game changer.
>
> On Sat, Jan 14, 2023 at 11:22 AM Mac Lewis via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Fully appreciate everyone's input.
>>
>> The Midnite Rosie sounds interesting for sure.  Midnite is a great
>> company with great support.  Smart people answer the phone and that really
>> counts for a lot.
>>
>> How are you getting your hands on these?  I can't seem to find much info,
>> no spec sheets etc.  None of my vendors have them and Midnite is estimating
>> Apr 2023 as the release date.
>>
>>
>>
>> On Sat, Jan 14, 2023 at 8:34 AM William Bryce via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> I run the XW6848 in my shop. When running my CNC plasma table the XW
>>> will shutdown due to exceeding its output rating if it is a long cut on
>>> metal when the 4HP compressor kicks on.
>>> I also have a Midnite Solar Rosey, both are connected to the same
>>> battery so it's an equal comparison. The Rosy inverter will surge right
>>> through and finish the job, the XW is not in  the same league when
>>> comparing surge capability.
>>>
>>>  A bonus is that the Rosey is really quiet as it does not have that big
>>> heavy transformer making noise under heavy load. It is easy to install as
>>> it is not as heavy. So far it's a game changer in regards to inverter
>>> hardware that I have tested.
>>>
>>> On Fri, Jan 13, 2023 at 9:54 PM Chris Sparadeo via RE-wrenches <
>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>
>>>> I have a client with a large woodworking shop…cabinet table saw, large
>>>> 20” 240V bench planer, chop saws, compressors and a vacuum system. A single
>>>> Sol Ark 15K takes care of these loads flawlessly. It seems that that
>>>> inductive load snag with the smaller models has been resolved with the 15K.
>>>>
>>>> Best,
>>>>
>>>> Chris
>>>>
>>>> On Fri, Jan 13, 2023 at 7:34 PM Glenn Burt via RE-wrenches <
>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>
>>>>> According to a seminar I just attended, the new Midnite Solar Rosie
>>>>> will...
>>>>>
>>>>> -Glenn
>>>>> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>>>>>
>>>>> -- Original message--
>>>>> *From: *Dave Angelini Offgrid Solar via RE-wrenches
>>>>> *Date: *Fri, Jan 13, 2023 3:55 PM
>>>>> *To: *RE-wrenches;
>>>>> *Cc: *Dave Angelini Offgrid Solar;
>>>>> *Subject:*Re: [RE-wrenches] Low Frequency transformer off-grid
>>>>> inverter options
>>>>>
>>>>> There is not anything I know of that will out surge XW pro 6948. A
>>>>> great monitoring platform and much better support/installer training in 
>>>>> the
>>>>> last 18 months. Perfect for a shop with unknown peak surges.
>>>>>
>>>>>
>>>>>
>>>>> *Dave Angelini Offgrid Solar
>>>>> "we go where powerlines don't"
>>>>> http://members.sti.net/offgridsolar/ 
>>>>> <http://members.sti.net/offgridsolar/>
>>>>> e-mail  offgridso...@sti.net 
>>>>> text 209 813 0060 <209%20813%200060>*
>>>>>
>>>>>
>>>>> On 2023-01-13 11 <2023-01-13%2011>:57 am, Jay via RE-wrenches wrote:
>>>>>
>>>>>
>>>>> Hi Mac
>>>>>
>>>

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-14 Thread bob--- via RE-wrenches


Three (3) weeks is also what I am being told.   Part of the delay was 
that ETL/Intertek dropped the ball, big time.


Actually, ETL ran out of brains and we had to go to another NRTL 
altogether for inverters.


And yes, it does surge very well.

Merry new year, all !

🌜boB🌛

On 1/14/2023 11:40 AM, William Bryce via RE-wrenches wrote:
I am told the RE (off grid version) will be available through normal 
distribution in 3 weeks.
 As a Beta tester for this inverter I can say the use of SiC Fets is a 
game changer.


On Sat, Jan 14, 2023 at 11:22 AM Mac Lewis via RE-wrenches 
 wrote:


Fully appreciate everyone's input.

The Midnite Rosie sounds interesting for sure.  Midnite is a great
company with great support.  Smart people answer the phone and
that really counts for a lot.

How are you getting your hands on these?  I can't seem to find
much info, no spec sheets etc.  None of my vendors have them and
Midnite is estimating Apr 2023 as the release date.



On Sat, Jan 14, 2023 at 8:34 AM William Bryce via RE-wrenches
 wrote:

I run the XW6848 in my shop. When running my CNC plasma table
the XW will shutdown due to exceeding its output rating if it
is a long cut on metal when the 4HP compressor kicks on.
I also have a Midnite Solar Rosey, both are connected to the
same battery so it's an equal comparison. The Rosy inverter
will surge right through and finish the job, the XW is not in 
the same league when comparing surge capability.

 A bonus is that the Rosey is really quiet as it does not have
that big heavy transformer making noise under heavy load. It
is easy to install as it is not as heavy. So far it's a game
changer in regards to inverter hardware that I have tested.

On Fri, Jan 13, 2023 at 9:54 PM Chris Sparadeo via RE-wrenches
 wrote:

I have a client with a large woodworking shop…cabinet
table saw, large 20” 240V bench planer, chop saws,
compressors and a vacuum system. A single Sol Ark 15K
takes care of these loads flawlessly. It seems that that
inductive load snag with the smaller models has been
resolved with the 15K.

Best,

Chris

On Fri, Jan 13, 2023 at 7:34 PM Glenn Burt via RE-wrenches
 wrote:

According to a seminar I just attended, the new
Midnite Solar Rosie will...

-Glenn
Sent from my 'smart'phone, so please excuse typos and
spelling errors.

-- Original message--
*From: *Dave Angelini Offgrid Solar via RE-wrenches
*Date: *Fri, Jan 13, 2023 3:55 PM
*To: *RE-wrenches;
*Cc: *Dave Angelini Offgrid Solar;
        *Subject:*Re: [RE-wrenches] Low Frequency transformer
        off-grid inverter options

There is not anything I know of that will out surge XW
pro 6948. A great monitoring platform and much better
support/installer training in the last 18 months.
Perfect for a shop with unknown peak surges.

  


*Dave Angelini Offgrid Solar "we go where powerlines
don't" http://members.sti.net/offgridsolar/ e-mail
offgridso...@sti.net text 209 813 0060
*


On 2023-01-13 11 :57 am, Jay via
RE-wrenches wrote:


Hi Mac
The radian is low voltage transformer
Based. Has hella surge capacity
I would consider what web based monitoring system he
wants and go with that platform.
Regardless of system I'd install soft start/vfd on
the larger units. Just easier on everything.
The solark 12 doesn't seem to be good for larger
loads and doesn't do out of balance well, and limited
to 6kw per phase. The new 15 might be better, not
sure. Numerous YouTube videos showing side by side vs
XW and radian. Both run stuff over their rating which
the SolA won't run even though its under its rating.
Good luck
Jay


On Jan 13, 2023, at 11:34 AM, Mac Lewis via
RE-wrenches > wrote:
<mailto:%3cre-wrenc...@lists.re-wrenches.org>

Hello Wrenches,
I have a new client that has ran a pretty decent
wood shop for about 10 years on a Magnum 4448.  He's
got some large loads, planers, saws, compressors
vacuums etc. They are really nice, heavy duty pieces
of equipmen

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-14 Thread William Bryce via RE-wrenches
I am told the RE (off grid version) will be available through normal
distribution in 3 weeks.
 As a Beta tester for this inverter I can say the use of SiC Fets is a game
changer.

On Sat, Jan 14, 2023 at 11:22 AM Mac Lewis via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Fully appreciate everyone's input.
>
> The Midnite Rosie sounds interesting for sure.  Midnite is a great company
> with great support.  Smart people answer the phone and that really counts
> for a lot.
>
> How are you getting your hands on these?  I can't seem to find much info,
> no spec sheets etc.  None of my vendors have them and Midnite is estimating
> Apr 2023 as the release date.
>
>
>
> On Sat, Jan 14, 2023 at 8:34 AM William Bryce via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> I run the XW6848 in my shop. When running my CNC plasma table the XW will
>> shutdown due to exceeding its output rating if it is a long cut on metal
>> when the 4HP compressor kicks on.
>> I also have a Midnite Solar Rosey, both are connected to the same battery
>> so it's an equal comparison. The Rosy inverter will surge right through and
>> finish the job, the XW is not in  the same league when comparing surge
>> capability.
>>
>>  A bonus is that the Rosey is really quiet as it does not have that big
>> heavy transformer making noise under heavy load. It is easy to install as
>> it is not as heavy. So far it's a game changer in regards to inverter
>> hardware that I have tested.
>>
>> On Fri, Jan 13, 2023 at 9:54 PM Chris Sparadeo via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> I have a client with a large woodworking shop…cabinet table saw, large
>>> 20” 240V bench planer, chop saws, compressors and a vacuum system. A single
>>> Sol Ark 15K takes care of these loads flawlessly. It seems that that
>>> inductive load snag with the smaller models has been resolved with the 15K.
>>>
>>> Best,
>>>
>>> Chris
>>>
>>> On Fri, Jan 13, 2023 at 7:34 PM Glenn Burt via RE-wrenches <
>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>
>>>> According to a seminar I just attended, the new Midnite Solar Rosie
>>>> will...
>>>>
>>>> -Glenn
>>>> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>>>>
>>>> -- Original message--
>>>> *From: *Dave Angelini Offgrid Solar via RE-wrenches
>>>> *Date: *Fri, Jan 13, 2023 3:55 PM
>>>> *To: *RE-wrenches;
>>>> *Cc: *Dave Angelini Offgrid Solar;
>>>> *Subject:*Re: [RE-wrenches] Low Frequency transformer off-grid
>>>> inverter options
>>>>
>>>> There is not anything I know of that will out surge XW pro 6948. A
>>>> great monitoring platform and much better support/installer training in the
>>>> last 18 months. Perfect for a shop with unknown peak surges.
>>>>
>>>>
>>>>
>>>> *Dave Angelini Offgrid Solar
>>>> "we go where powerlines don't"
>>>> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
>>>> e-mail  offgridso...@sti.net 
>>>> text 209 813 0060 <209%20813%200060>*
>>>>
>>>>
>>>> On 2023-01-13 11:57 am, Jay via RE-wrenches wrote:
>>>>
>>>>
>>>> Hi Mac
>>>>
>>>> The radian is low voltage transformer
>>>> Based. Has hella surge capacity
>>>>
>>>> I would consider what web based monitoring system he wants and go with
>>>> that platform.
>>>>
>>>> Regardless of system I'd install soft start/vfd on the larger units.
>>>> Just easier on everything.
>>>>
>>>> The solark 12 doesn't seem to be good for larger loads and doesn't do
>>>> out of balance well, and limited to 6kw per phase. The new 15 might be
>>>> better, not sure. Numerous YouTube videos showing side by side vs XW and
>>>> radian. Both run stuff over their rating which the SolA won't run even
>>>> though its under its rating.
>>>>
>>>> Good luck
>>>>
>>>> Jay
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> On Jan 13, 2023, at 11:34 AM, Mac Lewis via RE-wrenches > wrote:
>>>> <%3cre-wrenc...@lists.re-wrenches.org&g

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-14 Thread Mac Lewis via RE-wrenches
Fully appreciate everyone's input.

The Midnite Rosie sounds interesting for sure.  Midnite is a great company
with great support.  Smart people answer the phone and that really counts
for a lot.

How are you getting your hands on these?  I can't seem to find much info,
no spec sheets etc.  None of my vendors have them and Midnite is estimating
Apr 2023 as the release date.



On Sat, Jan 14, 2023 at 8:34 AM William Bryce via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> I run the XW6848 in my shop. When running my CNC plasma table the XW will
> shutdown due to exceeding its output rating if it is a long cut on metal
> when the 4HP compressor kicks on.
> I also have a Midnite Solar Rosey, both are connected to the same battery
> so it's an equal comparison. The Rosy inverter will surge right through and
> finish the job, the XW is not in  the same league when comparing surge
> capability.
>
>  A bonus is that the Rosey is really quiet as it does not have that big
> heavy transformer making noise under heavy load. It is easy to install as
> it is not as heavy. So far it's a game changer in regards to inverter
> hardware that I have tested.
>
> On Fri, Jan 13, 2023 at 9:54 PM Chris Sparadeo via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> I have a client with a large woodworking shop…cabinet table saw, large
>> 20” 240V bench planer, chop saws, compressors and a vacuum system. A single
>> Sol Ark 15K takes care of these loads flawlessly. It seems that that
>> inductive load snag with the smaller models has been resolved with the 15K.
>>
>> Best,
>>
>> Chris
>>
>> On Fri, Jan 13, 2023 at 7:34 PM Glenn Burt via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> According to a seminar I just attended, the new Midnite Solar Rosie
>>> will...
>>>
>>> -Glenn
>>> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>>>
>>> -- Original message--
>>> *From: *Dave Angelini Offgrid Solar via RE-wrenches
>>> *Date: *Fri, Jan 13, 2023 3:55 PM
>>> *To: *RE-wrenches;
>>> *Cc: *Dave Angelini Offgrid Solar;
>>> *Subject:*Re: [RE-wrenches] Low Frequency transformer off-grid inverter
>>> options
>>>
>>> There is not anything I know of that will out surge XW pro 6948. A great
>>> monitoring platform and much better support/installer training in the last
>>> 18 months. Perfect for a shop with unknown peak surges.
>>>
>>>
>>>
>>> *Dave Angelini Offgrid Solar
>>> "we go where powerlines don't"
>>> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
>>> e-mail  offgridso...@sti.net 
>>> text 209 813 0060 <209%20813%200060>*
>>>
>>>
>>> On 2023-01-13 11:57 am, Jay via RE-wrenches wrote:
>>>
>>>
>>> Hi Mac
>>>
>>> The radian is low voltage transformer
>>> Based. Has hella surge capacity
>>>
>>> I would consider what web based monitoring system he wants and go with
>>> that platform.
>>>
>>> Regardless of system I'd install soft start/vfd on the larger units.
>>> Just easier on everything.
>>>
>>> The solark 12 doesn't seem to be good for larger loads and doesn't do
>>> out of balance well, and limited to 6kw per phase. The new 15 might be
>>> better, not sure. Numerous YouTube videos showing side by side vs XW and
>>> radian. Both run stuff over their rating which the SolA won't run even
>>> though its under its rating.
>>>
>>> Good luck
>>>
>>> Jay
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> On Jan 13, 2023, at 11:34 AM, Mac Lewis via RE-wrenches > wrote:
>>> <%3cre-wrenc...@lists.re-wrenches.org>
>>>
>>> Hello Wrenches,
>>>
>>> I have a new client that has ran a pretty decent wood shop for about 10
>>> years on a Magnum 4448.  He's got some large loads, planers, saws,
>>> compressors vacuums etc.  They are really nice, heavy duty pieces of
>>> equipment.  Amazingly, the Magnum has been able to start these loads for
>>> the most part for 10 years, but he has reported that it has gotten worse
>>> lately (could be a load issue), brown outs, dimming etc
>>>
>>> He wants to upgrade the system, get remote monitoring etc.  I tried a
>>> test with a Sol-Ark 12, and it won't start these

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-14 Thread William Bryce via RE-wrenches
I run the XW6848 in my shop. When running my CNC plasma table the XW will
shutdown due to exceeding its output rating if it is a long cut on metal
when the 4HP compressor kicks on.
I also have a Midnite Solar Rosey, both are connected to the same battery
so it's an equal comparison. The Rosy inverter will surge right through and
finish the job, the XW is not in  the same league when comparing surge
capability.

 A bonus is that the Rosey is really quiet as it does not have that big
heavy transformer making noise under heavy load. It is easy to install as
it is not as heavy. So far it's a game changer in regards to inverter
hardware that I have tested.

On Fri, Jan 13, 2023 at 9:54 PM Chris Sparadeo via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> I have a client with a large woodworking shop…cabinet table saw, large 20”
> 240V bench planer, chop saws, compressors and a vacuum system. A single Sol
> Ark 15K takes care of these loads flawlessly. It seems that that inductive
> load snag with the smaller models has been resolved with the 15K.
>
> Best,
>
> Chris
>
> On Fri, Jan 13, 2023 at 7:34 PM Glenn Burt via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> According to a seminar I just attended, the new Midnite Solar Rosie
>> will...
>>
>> -Glenn
>> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>>
>> -- Original message--
>> *From: *Dave Angelini Offgrid Solar via RE-wrenches
>> *Date: *Fri, Jan 13, 2023 3:55 PM
>> *To: *RE-wrenches;
>> *Cc: *Dave Angelini Offgrid Solar;
>> *Subject:*Re: [RE-wrenches] Low Frequency transformer off-grid inverter
>> options
>>
>> There is not anything I know of that will out surge XW pro 6948. A great
>> monitoring platform and much better support/installer training in the last
>> 18 months. Perfect for a shop with unknown peak surges.
>>
>>
>>
>> *Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
>> e-mail  offgridso...@sti.net 
>> text 209 813 0060 <209%20813%200060>*
>>
>>
>> On 2023-01-13 11:57 am, Jay via RE-wrenches wrote:
>>
>>
>> Hi Mac
>>
>> The radian is low voltage transformer
>> Based. Has hella surge capacity
>>
>> I would consider what web based monitoring system he wants and go with
>> that platform.
>>
>> Regardless of system I'd install soft start/vfd on the larger units. Just
>> easier on everything.
>>
>> The solark 12 doesn't seem to be good for larger loads and doesn't do out
>> of balance well, and limited to 6kw per phase. The new 15 might be better,
>> not sure. Numerous YouTube videos showing side by side vs XW and radian.
>> Both run stuff over their rating which the SolA won't run even though its
>> under its rating.
>>
>> Good luck
>>
>> Jay
>>
>>
>>
>>
>>
>>
>>
>>
>> On Jan 13, 2023, at 11:34 AM, Mac Lewis via RE-wrenches > wrote:
>> <%3cre-wrenc...@lists.re-wrenches.org>
>>
>> Hello Wrenches,
>>
>> I have a new client that has ran a pretty decent wood shop for about 10
>> years on a Magnum 4448.  He's got some large loads, planers, saws,
>> compressors vacuums etc.  They are really nice, heavy duty pieces of
>> equipment.  Amazingly, the Magnum has been able to start these loads for
>> the most part for 10 years, but he has reported that it has gotten worse
>> lately (could be a load issue), brown outs, dimming etc
>>
>> He wants to upgrade the system, get remote monitoring etc.  I tried a
>> test with a Sol-Ark 12, and it won't start these large motor loads.  I was
>> a little surprised by that but I know they aren't as good as the low freq
>> transformer based inverters at these surges.
>>
>> I confirmed that its not just an overload from imbalance because the 240V
>> loads will also overload it.  I got an inrush measurement of 48.5A Ac @240
>> (but it didn't start the load before Sol-Ark would shut off)
>>
>> What are my options?
>> Schneider XW Pro 6848
>> Outback Radian 8048 (Is this a low freq device?)
>> Sunny Islands are beasts but weird to work with and not user friendly
>>
>> Any others I should consider?  He does have some significant 120 only
>> loads so I don't think the Outback vfxr are a good choice.
>>
>> Is it as simple as saying if the Magnum can start this load, the Radian
>> should?
>>
>> I 

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Chris Sparadeo via RE-wrenches
I have a client with a large woodworking shop…cabinet table saw, large 20”
240V bench planer, chop saws, compressors and a vacuum system. A single Sol
Ark 15K takes care of these loads flawlessly. It seems that that inductive
load snag with the smaller models has been resolved with the 15K.

Best,

Chris

On Fri, Jan 13, 2023 at 7:34 PM Glenn Burt via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> According to a seminar I just attended, the new Midnite Solar Rosie will...
>
> -Glenn
> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>
> -- Original message--
> *From: *Dave Angelini Offgrid Solar via RE-wrenches
> *Date: *Fri, Jan 13, 2023 3:55 PM
> *To: *RE-wrenches;
> *Cc: *Dave Angelini Offgrid Solar;
> *Subject:*Re: [RE-wrenches] Low Frequency transformer off-grid inverter
> options
>
> There is not anything I know of that will out surge XW pro 6948. A great
> monitoring platform and much better support/installer training in the last
> 18 months. Perfect for a shop with unknown peak surges.
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> e-mail  offgridso...@sti.net 
> text 209 813 0060 <209%20813%200060>*
>
>
> On 2023-01-13 11:57 am, Jay via RE-wrenches wrote:
>
>
> Hi Mac
>
> The radian is low voltage transformer
> Based. Has hella surge capacity
>
> I would consider what web based monitoring system he wants and go with
> that platform.
>
> Regardless of system I'd install soft start/vfd on the larger units. Just
> easier on everything.
>
> The solark 12 doesn't seem to be good for larger loads and doesn't do out
> of balance well, and limited to 6kw per phase. The new 15 might be better,
> not sure. Numerous YouTube videos showing side by side vs XW and radian.
> Both run stuff over their rating which the SolA won't run even though its
> under its rating.
>
> Good luck
>
> Jay
>
>
>
>
>
>
>
>
> On Jan 13, 2023, at 11:34 AM, Mac Lewis via RE-wrenches > wrote:
> <%3cre-wrenc...@lists.re-wrenches.org>
>
> Hello Wrenches,
>
> I have a new client that has ran a pretty decent wood shop for about 10
> years on a Magnum 4448.  He's got some large loads, planers, saws,
> compressors vacuums etc.  They are really nice, heavy duty pieces of
> equipment.  Amazingly, the Magnum has been able to start these loads for
> the most part for 10 years, but he has reported that it has gotten worse
> lately (could be a load issue), brown outs, dimming etc
>
> He wants to upgrade the system, get remote monitoring etc.  I tried a test
> with a Sol-Ark 12, and it won't start these large motor loads.  I was a
> little surprised by that but I know they aren't as good as the low freq
> transformer based inverters at these surges.
>
> I confirmed that its not just an overload from imbalance because the 240V
> loads will also overload it.  I got an inrush measurement of 48.5A Ac @240
> (but it didn't start the load before Sol-Ark would shut off)
>
> What are my options?
> Schneider XW Pro 6848
> Outback Radian 8048 (Is this a low freq device?)
> Sunny Islands are beasts but weird to work with and not user friendly
>
> Any others I should consider?  He does have some significant 120 only
> loads so I don't think the Outback vfxr are a good choice.
>
> Is it as simple as saying if the Magnum can start this load, the Radian
> should?
>
> I appreciate your input!
>
> --
> Mac Lewis
>
> "Yo solo sé que no sé nada." -Sócrates
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
> <%0d+re-wrenc...@lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> h

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Glenn Burt via RE-wrenches
According to a seminar I just attended, the new Midnite Solar Rosie 
will...-GlennSent from my 'smart'phone, so please excuse typos and spelling 
errors.-- Original message--From: Dave Angelini Offgrid Solar via 
RE-wrenchesDate: Fri, Jan 13, 2023 3:55 PMTo: RE-wrenches;Cc: Dave Angelini 
Offgrid Solar;Subject:Re: [RE-wrenches] Low Frequency transformer off-grid 
inverter options
There is not anything I know of that will out surge XW pro 6948. A great 
monitoring platform and much better support/installer training in the last 18 
months. Perfect for a shop with unknown peak surges.
 
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060


On 2023-01-13 11:57 am, Jay via RE-wrenches wrote:



 
Hi Mac
 
The radian is low voltage transformer
Based. Has hella surge capacity 
 
I would consider what web based monitoring system he wants and go with that 
platform. 
 
Regardless of system I'd install
 soft start/vfd on the larger units. Just easier on everything.
 
The solark 12 doesn't seem to be good for larger loads and doesn't do out of 
balance well, and limited to 6kw per phase. The new 15 might be better, not 
sure. Numerous YouTube videos showing side by side vs XW and radian. Both run 
stuff over their rating which the SolA won't run even though its under its 
rating. 
 
Good luck
 
Jay
 
 
 
 
 
 
 

On Jan 13, 2023, at 11:34 AM, Mac Lewis via RE-wrenches > wrote:



Hello Wrenches,
 
I have a new client that has ran a pretty decent wood shop for about 10 years 
on a Magnum 4448.  He's got some large loads, planers, saws, compressors 
vacuums etc.  They are really nice, heavy duty pieces of equipment.  Amazingly, 
the Magnum has been able to start these loads for the most part for 10 years, 
but he has reported that it has gotten worse lately (could be a load issue), 
brown outs, dimming etc
 
He wants to upgrade the system, get remote monitoring etc.  I tried a test with 
a
 Sol-Ark 12, and it won't start these large motor loads.  I was a little 
surprised by that but I know they aren't as good as the low freq transformer 
based inverters at these surges.
 
I confirmed that its not just an overload from imbalance because the 240V loads 
will also overload it.  I got an inrush measurement of 48.5A Ac @240 (but it 
didn't start the load before Sol-Ark would shut off)  
 
What are my options?
Schneider XW Pro 6848
Outback Radian 8048 (Is this a low freq device?)
Sunny Islands are beasts but weird to work with and not user friendly
 
Any others I should consider?  He does have some significant 120 only loads so 
I don't think the Outback vfxr are a good choice.
 
Is it as simple as saying if the Magnum can start this load, the Radian should?
 
I appreciate your input!
 
--
Mac Lewis
"Yo solo sé que no sé nada." -Sócrates



___List sponsored by Redwood 
AlliancePay optional member dues here: http://re-wrenches.orgList
 Address: re-wrenc...@lists.re-wrenches.orgChange listserver email address & 
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere
 are two list archives for searching. When one doesn't work, try the 
other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList
 rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update 
participant bios:http://www.members.re-wrenches.org




___List sponsored by Redwood 
AlliancePay optional member dues here: http://re-wrenches.orgList Address: 
re-wrenc...@lists.re-wrenches.orgChange listserver email address & 
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere
 are two list archives for searching. When one doesn't work, try the
 
other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList
 rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update 
participant bios:http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Dave Angelini Offgrid Solar via RE-wrenches


There is not anything I know of that will out surge XW pro 6948. A great 
monitoring platform and much better support/installer training in the 
last 18 months. Perfect for a shop with unknown peak surges.


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

On 2023-01-13 11:57 am, Jay via RE-wrenches wrote:


Hi Mac

The radian is low voltage transformer
Based. Has hella surge capacity

I would consider what web based monitoring system he wants and go with 
that platform.


Regardless of system I'd install soft start/vfd on the larger units. 
Just easier on everything.


The solark 12 doesn't seem to be good for larger loads and doesn't do 
out of balance well, and limited to 6kw per phase. The new 15 might be 
better, not sure. Numerous YouTube videos showing side by side vs XW 
and radian. Both run stuff over their rating which the SolA won't run 
even though its under its rating.


Good luck

Jay

On Jan 13, 2023, at 11:34 AM, Mac Lewis via RE-wrenches 
 wrote:



Hello Wrenches,

I have a new client that has ran a pretty decent wood shop for about 
10 years on a Magnum 4448.  He's got some large loads, planers, saws, 
compressors vacuums etc.  They are really nice, heavy duty pieces of 
equipment.  Amazingly, the Magnum has been able to start these loads 
for the most part for 10 years, but he has reported that it has gotten 
worse lately (could be a load issue), brown outs, dimming etc


He wants to upgrade the system, get remote monitoring etc.  I tried a 
test with a Sol-Ark 12, and it won't start these large motor loads.  I 
was a little surprised by that but I know they aren't as good as the 
low freq transformer based inverters at these surges.


I confirmed that its not just an overload from imbalance because the 
240V loads will also overload it.  I got an inrush measurement of 
48.5A Ac @240 (but it didn't start the load before Sol-Ark would shut 
off)


What are my options?
Schneider XW Pro 6848
Outback Radian 8048 (Is this a low freq device?)
Sunny Islands are beasts but weird to work with and not user friendly

Any others I should consider?  He does have some significant 120 only 
loads so I don't think the Outback vfxr are a good choice.


Is it as simple as saying if the Magnum can start this load, the 
Radian should?


I appreciate your input!

--
Mac Lewis

"Yo solo sé que no sé nada." -Sócrates 
___

List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Jay via RE-wrenches
Hi Mac

The radian is low voltage transformer
Based. Has hella surge capacity 

I would consider what web based monitoring system he wants and go with that 
platform. 

Regardless of system I’d install soft start/vfd on the larger units. Just 
easier on everything.

The solark 12 doesn’t seem to be good for larger loads and doesn’t do out of 
balance well, and limited to 6kw per phase. The new 15 might be better, not 
sure. Numerous YouTube videos showing side by side vs XW and radian. Both run 
stuff over their rating which the SolA won’t run even though its under its 
rating. 

Good luck

Jay








> On Jan 13, 2023, at 11:34 AM, Mac Lewis via RE-wrenches 
>  wrote:
> 
> 
> Hello Wrenches,
> 
> I have a new client that has ran a pretty decent wood shop for about 10 years 
> on a Magnum 4448.  He's got some large loads, planers, saws, compressors 
> vacuums etc.  They are really nice, heavy duty pieces of equipment.  
> Amazingly, the Magnum has been able to start these loads for the most part 
> for 10 years, but he has reported that it has gotten worse lately (could be a 
> load issue), brown outs, dimming etc
> 
> He wants to upgrade the system, get remote monitoring etc.  I tried a test 
> with a Sol-Ark 12, and it won't start these large motor loads.  I was a 
> little surprised by that but I know they aren't as good as the low freq 
> transformer based inverters at these surges.
> 
> I confirmed that its not just an overload from imbalance because the 240V 
> loads will also overload it.  I got an inrush measurement of 48.5A Ac @240 
> (but it didn't start the load before Sol-Ark would shut off)  
> 
> What are my options?
> Schneider XW Pro 6848
> Outback Radian 8048 (Is this a low freq device?)
> Sunny Islands are beasts but weird to work with and not user friendly
> 
> Any others I should consider?  He does have some significant 120 only loads 
> so I don't think the Outback vfxr are a good choice.
> 
> Is it as simple as saying if the Magnum can start this load, the Radian 
> should?
> 
> I appreciate your input!
> 
> --
> Mac Lewis
> 
> "Yo solo sé que no sé nada." -Sócrates
> 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread bzp via RE-wrenches

Larry.


Hera's an idea. Put a 1:1 isolation transformer of suitable power rating 
between the inverter and load. The iron core will act as a energy 
storage element allowing for a cleaner ac waveform during start.



Frank BZP



On 1/13/2023 12:54 PM, Starlight via RE-wrenches wrote:
Any new AC equipment connected and running during test? Scope the 
waveform during equipment start to see if the distortion is severe. I 
have seen a 300W load make a mess of a Magnum AC waveform.


Larry Crutcher
Starlight Solar Power Systems



On Jan 13, 2023, at 11:48 AM, Mac Lewis  wrote:

Good question Larry,

Rock solid 52V on a lithium battery system. Doesn't appear to be a 
battery problem at all.


On Fri, Jan 13, 2023, 11:41 AM Starlight  wrote:

Mac,

What was the lowest voltage measured at inverter battery terminals
during the inrush measurement?

Larry Crutcher
Starlight Solar Power Systems



On Jan 13, 2023, at 11:33 AM, Mac Lewis via RE-wrenches
 wrote:

Hello Wrenches,

I have a new client that has ran a pretty decent wood shop for
about 10 years on a Magnum 4448.  He's got some large loads,
planers, saws, compressors vacuums etc.  They are really nice,
heavy duty pieces of equipment.  Amazingly, the Magnum has been
able to start these loads for the most part for 10 years, but he
has reported that it has gotten worse lately (could be a load
issue), brown outs, dimming etc

He wants to upgrade the system, get remote monitoring etc.  I
tried a test with a Sol-Ark 12, and it won't start these large
motor loads.  I was a little surprised by that but I know they
aren't as good as the low freq transformer based inverters at
these surges.

I confirmed that its not just an overload from imbalance because
the 240V loads will also overload it.  I got an inrush measurement
of 48.5A Ac @240 (but it didn't start the load before Sol-Ark
would shut off)

What are my options?
Schneider XW Pro 6848
Outback Radian 8048 (Is this a low freq device?)
Sunny Islands are beasts but weird to work with and not user friendly

Any others I should consider?  He does have some significant 120
only loads so I don't think the Outback vfxr are a good choice.

Is it as simple as saying if the Magnum can start this load, the
Radian should?

I appreciate your input!

--
Mac Lewis

*


*
___


___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Starlight via RE-wrenches
Any new AC equipment connected and running during test? Scope the waveform 
during equipment start to see if the distortion is severe. I have seen a 300W 
load make a mess of a Magnum AC waveform.

Larry Crutcher
Starlight Solar Power Systems



On Jan 13, 2023, at 11:48 AM, Mac Lewis  wrote:

Good question Larry, 

Rock solid 52V on a lithium battery system. Doesn't appear to be a battery 
problem at all. 

On Fri, Jan 13, 2023, 11:41 AM Starlight mailto:la...@starlightsolar.com>> wrote:
Mac,

What was the lowest voltage measured at inverter battery terminals during the 
inrush measurement?

Larry Crutcher
Starlight Solar Power Systems



On Jan 13, 2023, at 11:33 AM, Mac Lewis via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:

Hello Wrenches,

I have a new client that has ran a pretty decent wood shop for about 10 years 
on a Magnum 4448.  He's got some large loads, planers, saws, compressors 
vacuums etc.  They are really nice, heavy duty pieces of equipment.  Amazingly, 
the Magnum has been able to start these loads for the most part for 10 years, 
but he has reported that it has gotten worse lately (could be a load issue), 
brown outs, dimming etc

He wants to upgrade the system, get remote monitoring etc.  I tried a test with 
a Sol-Ark 12, and it won't start these large motor loads.  I was a little 
surprised by that but I know they aren't as good as the low freq transformer 
based inverters at these surges.

I confirmed that its not just an overload from imbalance because the 240V loads 
will also overload it.  I got an inrush measurement of 48.5A Ac @240 (but it 
didn't start the load before Sol-Ark would shut off)  

What are my options?
Schneider XW Pro 6848
Outback Radian 8048 (Is this a low freq device?)
Sunny Islands are beasts but weird to work with and not user friendly

Any others I should consider?  He does have some significant 120 only loads so 
I don't think the Outback vfxr are a good choice.

Is it as simple as saying if the Magnum can start this load, the Radian should?

I appreciate your input!

--
Mac Lewis



___
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Christopher Warfel via RE-wrenches

Have they already installed soft starts on these motors?  Chris

On 1/13/2023 1:41 PM, Starlight via RE-wrenches wrote:

Mac,

What was the lowest voltage measured at inverter battery terminals 
during the inrush measurement?


Larry Crutcher
Starlight Solar Power Systems



On Jan 13, 2023, at 11:33 AM, Mac Lewis via RE-wrenches 
 wrote:


Hello Wrenches,

I have a new client that has ran a pretty decent wood shop for about 
10 years on a Magnum 4448. He's got some large loads, planers, saws, 
compressors vacuums etc.  They are really nice, heavy duty pieces of 
equipment.  Amazingly, the Magnum has been able to start these loads 
for the most part for 10 years, but he has reported that it has gotten 
worse lately (could be a load issue), brown outs, dimming etc


He wants to upgrade the system, get remote monitoring etc.  I tried a 
test with a Sol-Ark 12, and it won't start these large motor loads.  I 
was a little surprised by that but I know they aren't as good as the 
low freq transformer based inverters at these surges.


I confirmed that its not just an overload from imbalance because the 
240V loads will also overload it.  I got an inrush measurement of 
48.5A Ac @240 (but it didn't start the load before Sol-Ark would shut 
off)


What are my options?
Schneider XW Pro 6848
Outback Radian 8048 (Is this a low freq device?)
Sunny Islands are beasts but weird to work with and not user friendly

Any others I should consider?  He does have some significant 120 only 
loads so I don't think the Outback vfxr are a good choice.


Is it as simple as saying if the Magnum can start this load, the 
Radian should?


I appreciate your input!

--
Mac Lewis

*

"Yo solo sé que no sé nada." -Sócrates

*
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


--
            Christopher Warfel
                 ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                401-466-8978


BEGIN:VCARD
VERSION:4.0
N:Warfel;Christopher;;;
TEL;VALUE=TEXT:401-447-5773 (c)
NOTE:Use the cell phone number for all communications.  Thank you.
URL:https://www.entech-engineering.com
END:VCARD
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Mac Lewis via RE-wrenches
Good question Larry,

Rock solid 52V on a lithium battery system. Doesn't appear to be a battery
problem at all.

On Fri, Jan 13, 2023, 11:41 AM Starlight  wrote:

> Mac,
>
> What was the lowest voltage measured at inverter battery terminals during
> the inrush measurement?
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
> On Jan 13, 2023, at 11:33 AM, Mac Lewis via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Hello Wrenches,
>
> I have a new client that has ran a pretty decent wood shop for about 10
> years on a Magnum 4448.  He's got some large loads, planers, saws,
> compressors vacuums etc.  They are really nice, heavy duty pieces of
> equipment.  Amazingly, the Magnum has been able to start these loads for
> the most part for 10 years, but he has reported that it has gotten worse
> lately (could be a load issue), brown outs, dimming etc
>
> He wants to upgrade the system, get remote monitoring etc.  I tried a test
> with a Sol-Ark 12, and it won't start these large motor loads.  I was a
> little surprised by that but I know they aren't as good as the low freq
> transformer based inverters at these surges.
>
> I confirmed that its not just an overload from imbalance because the 240V
> loads will also overload it.  I got an inrush measurement of 48.5A Ac @240
> (but it didn't start the load before Sol-Ark would shut off)
>
> What are my options?
> Schneider XW Pro 6848
> Outback Radian 8048 (Is this a low freq device?)
> Sunny Islands are beasts but weird to work with and not user friendly
>
> Any others I should consider?  He does have some significant 120 only
> loads so I don't think the Outback vfxr are a good choice.
>
> Is it as simple as saying if the Magnum can start this load, the Radian
> should?
>
> I appreciate your input!
>
> --
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Starlight via RE-wrenches
Mac,

What was the lowest voltage measured at inverter battery terminals during the 
inrush measurement?

Larry Crutcher
Starlight Solar Power Systems



On Jan 13, 2023, at 11:33 AM, Mac Lewis via RE-wrenches 
 wrote:

Hello Wrenches,

I have a new client that has ran a pretty decent wood shop for about 10 years 
on a Magnum 4448.  He's got some large loads, planers, saws, compressors 
vacuums etc.  They are really nice, heavy duty pieces of equipment.  Amazingly, 
the Magnum has been able to start these loads for the most part for 10 years, 
but he has reported that it has gotten worse lately (could be a load issue), 
brown outs, dimming etc

He wants to upgrade the system, get remote monitoring etc.  I tried a test with 
a Sol-Ark 12, and it won't start these large motor loads.  I was a little 
surprised by that but I know they aren't as good as the low freq transformer 
based inverters at these surges.

I confirmed that its not just an overload from imbalance because the 240V loads 
will also overload it.  I got an inrush measurement of 48.5A Ac @240 (but it 
didn't start the load before Sol-Ark would shut off)  

What are my options?
Schneider XW Pro 6848
Outback Radian 8048 (Is this a low freq device?)
Sunny Islands are beasts but weird to work with and not user friendly

Any others I should consider?  He does have some significant 120 only loads so 
I don't think the Outback vfxr are a good choice.

Is it as simple as saying if the Magnum can start this load, the Radian should?

I appreciate your input!

--
Mac Lewis

"Yo solo sé que no sé nada." -Sócrates

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org