Re: [RE-wrenches] PVC running through the house

2011-04-09 Thread Nick Soleil
As per the 2011 NEC, MC (metal clad cable) is now allowed to be run inside the 
building envelope for solar output circuits.  


 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037





From: Peter Parrish peter.parr...@calsolareng.com
To: Keith Cronin electrich...@yahoo.com; RE-wrenches 
re-wrenches@lists.re-wrenches.org
Sent: Thu, April 7, 2011 4:23:52 PM
Subject: Re: [RE-wrenches] PVC running through the house

The Code back then was a little vague back then and I am not sure it has
been improved.

First, there needs to be a DC disconnect just before or just after
penetrating the building shell. Most AHJ allowed us to place this disconnect
in the attic within reach of the access door. Once we needed to place the DC
disconnect on the roof and we were able to get away with a fused combiner
box. Another time we actually needed to put a 600V 3-pole fused disco on the
roof.

Second, and this is really an obscure point. Only conduit, raceways and the
like (not cable runs) were allowed in the attic space and walls. So FMC is
okay but MC is not. It is an issue of unfortunate terminology.

Third, you need to label the conduit “Caution – Solar Circuit”, even in the
walls.

Finally, where the conduit passes thru studs, you need protection plates on
the studs to prevent screws or nails piercing the conduit.

That’s my story and I’m sticking to it.

-Peter

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Keith Cronin
Sent: Thursday, April 07, 2011 3:05 PM
To: RE-Wrenches
Subject: [RE-wrenches] PVC running through the house

Hi folks

Was wondering- does anyone know back in 2005, if it was permissible to run
DC conductors from the roof, through the home to the inverter location,
inside the house, per the NEC?

Thanks 

Keith Cronin

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PVC running through the house

2011-04-07 Thread Hans Frederickson
690.31(E), requiring metallic raceways or enclosures for DC circuits inside
the building was introduced in the 2005 NEC. Depending on when the 2005 NEC
was adopted by your local authority, it may or may not have been required at
the time of the installation. 
 
-Hans

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Keith Cronin
Sent: Thursday, April 07, 2011 3:05 PM
To: RE-Wrenches
Subject: [RE-wrenches] PVC running through the house


Hi folks


Was wondering- does anyone know back in 2005, if it was permissible to run
DC conductors from the roof, through the home to the inverter location,
inside the house, per the NEC?


Thanks 

Keith Cronin
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PVC running through the house

2011-04-07 Thread Peter Parrish
The Code back then was a little vague back then and I am not sure it has
been improved.

First, there needs to be a DC disconnect just before or just after
penetrating the building shell. Most AHJ allowed us to place this disconnect
in the attic within reach of the access door. Once we needed to place the DC
disconnect on the roof and we were able to get away with a fused combiner
box. Another time we actually needed to put a 600V 3-pole fused disco on the
roof.

Second, and this is really an obscure point. Only conduit, raceways and the
like (not cable runs) were allowed in the attic space and walls. So FMC is
okay but MC is not. It is an issue of unfortunate terminology.

Third, you need to label the conduit “Caution – Solar Circuit”, even in the
walls.

Finally, where the conduit passes thru studs, you need protection plates on
the studs to prevent screws or nails piercing the conduit.

That’s my story and I’m sticking to it.

-Peter

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Keith Cronin
Sent: Thursday, April 07, 2011 3:05 PM
To: RE-Wrenches
Subject: [RE-wrenches] PVC running through the house

Hi folks

Was wondering- does anyone know back in 2005, if it was permissible to run
DC conductors from the roof, through the home to the inverter location,
inside the house, per the NEC?

Thanks 

Keith Cronin

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org