Re: [RE-wrenches] largest 240v GT inverter

2020-02-10 Thread Dave Angelini Offgrid Solar


Definitely far easier with less strings and BOS for 1000 vdc. I have
been begging for a 1000 vdc charge controller for offgrid!   
Dave Angelini
Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridso...@sti.net
[2]
text 209 813 0060

On Mon, 10 Feb 2020 07:19:55 -0800, jay  wrote: Here
are a few answers to ( thanks) the comments.   1. its already has a 400 amp
240v service, I don't see that changing, loads are not going up, they just
want to add solar.   2. I would rather do 4 Primo 15's at 1000v than, 8 SMA
7.7 at 600v, unless someone can convince me otherwise.   This project is
still just in the talking stages, and is months out before anything even
would begin to go forward with design. I'm just trying to get ahead of the
curve so I can have as many design options as possible.   Jay   

  On Feb
10, 2020, at 5:53 AM, Chris Sparadeo  wrote: 
  If this site requires a new
service, another option would be to have the utility install 3-phase
transformers and use higher capacity inverters. Now we're back to the CPS
60 kW... 
  On Mon, Feb 10, 2020 at 8:39 AM Chad Waits  wrote:  Biggest I
found was Fronius 15kW. 
  Chad Waits
President
 520-270-4873 HI All,


I'm wondering what the largest GT battery less inverter (and what people
recommend) for 240v 60hz is out there.

 I don't need MLPE, as project
would be ground mount, its large residential, potentially 60KW. 

 SE has
their 11.4KW, but I've heard lots of bad things about them recently. 

Fronius has a 10KW?

 Thanks in advance

 jay

 Peltz power


___
 List sponsored by Redwood
Alliance

 List Address: RE-wrenches@lists.re-wrenches.org [6]

 Change
listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [7]


List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[8]

 List rules & etiquette:
 www.re-wrenches.org/etiquette.htm [9]


Check out or update participant bios:
 www.members.re-wrenches.org [10]
  
___
 List sponsored by Redwood
Alliance

 List Address: RE-wrenches@lists.re-wrenches.org [11]

 Change
listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [12]


List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[13]

 List rules & etiquette:
 www.re-wrenches.org/etiquette.htm [14]


Check out or update participant bios:
 www.members.re-wrenches.org [15]

  
-- 
  Chris Sparadeo C_802-369-4458 H_802-728-3059   
___
List sponsored by Redwood
Alliance

List Address: RE-wrenches@lists.re-wrenches.org [16]

Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[17]

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List
rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update
participant bios:
www.members.re-wrenches.org



Links:
--
[1]
http://members.sti.net/offgridsolar/
[2] mailto:offgridso...@sti.net
[3]
mailto:sparadeo.ch...@gmail.com
[4] mailto:chadwa...@netzerosolar.net
[5]
mailto:jay.pe...@gmail.com
[6] mailto:RE-wrenches@lists.re-wrenches.org
[7]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[8]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[9]
http://www.re-wrenches.org/etiquette.htm
[10]
http://www.members.re-wrenches.org/
[11]
mailto:RE-wrenches@lists.re-wrenches.org
[12]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[13]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[14]
http://www.re-wrenches.org/etiquette.htm
[15]
http://www.members.re-wrenches.org/
[16]
mailto:RE-wrenches@lists.re-wrenches.org
[17]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] largest 240v GT inverter

2020-02-10 Thread jay
Here are a few answers to ( thanks) the comments.

1. its already has a 400 amp 240v service, I don’t see that changing, loads are 
 not going up, they just want to add solar.

2. I would rather do 4 Primo 15’s at 1000v than, 8 SMA 7.7 at 600v, unless 
someone can convince me otherwise.

This project is still just in the talking stages, and is months out before 
anything even would begin to go forward with design.  I’m just trying to get 
ahead of the curve so I can have as many  design options as possible.

Jay



> On Feb 10, 2020, at 5:53 AM, Chris Sparadeo  wrote:
> 
> If this site requires a new service, another option would be to have the 
> utility install 3-phase transformers and use higher capacity inverters.  Now 
> we're back to the CPS 60 kW...
> 
> On Mon, Feb 10, 2020 at 8:39 AM Chad Waits  > wrote:
> Biggest I found was Fronius 15kW.
> 
> Chad Waits
> President
> 520-270-4873
> 
> 
> 
> On Sat, Feb 8, 2020 at 6:48 PM jay  > wrote:
> HI All,
> 
> I’m wondering what the largest GT battery less inverter  (and what people 
> recommend) for 240v 60hz is out there.
> 
> I don’t need MLPE, as project would be ground mount, its large residential, 
> potentially 60KW. 
> 
> SE has their 11.4KW, but I’ve heard lots of bad things about them recently.  
> Fronius has a 10KW?
> 
> Thanks in advance
> 
> 
> jay
> 
> Peltz power
> 
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> 
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> 
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
> 
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm 
> 
> Check out or update participant bios:
> www.members.re-wrenches.org 
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> 
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> 
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
> 
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm 
> 
> Check out or update participant bios:
> www.members.re-wrenches.org 
> 
> 
> 
> -- 
> Chris Sparadeo
> 
> 
> C_802-369-4458
> H_802-728-3059
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] largest 240v GT inverter

2020-02-10 Thread Chris Sparadeo
If this site requires a new service, another option would be to have
the utility install 3-phase transformers and use higher capacity
inverters.  Now we're back to the CPS 60 kW...

On Mon, Feb 10, 2020 at 8:39 AM Chad Waits 
wrote:

> Biggest I found was Fronius 15kW.
>
> Chad Waits
> President
> 520-270-4873
>
>
>
> On Sat, Feb 8, 2020 at 6:48 PM jay  wrote:
>
>> HI All,
>>
>> I’m wondering what the largest GT battery less inverter  (and what people
>> recommend) for 240v 60hz is out there.
>>
>> I don’t need MLPE, as project would be ground mount, its large
>> residential, potentially 60KW.
>>
>> SE has their 11.4KW, but I’ve heard lots of bad things about them
>> recently.
>> Fronius has a 10KW?
>>
>> Thanks in advance
>>
>>
>> jay
>>
>> Peltz power
>>
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Sparadeo


C_802-369-4458
H_802-728-3059
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] largest 240v GT inverter

2020-02-10 Thread Chad Waits
Biggest I found was Fronius 15kW.

Chad Waits
President
520-270-4873



On Sat, Feb 8, 2020 at 6:48 PM jay  wrote:

> HI All,
>
> I’m wondering what the largest GT battery less inverter  (and what people
> recommend) for 240v 60hz is out there.
>
> I don’t need MLPE, as project would be ground mount, its large
> residential, potentially 60KW.
>
> SE has their 11.4KW, but I’ve heard lots of bad things about them
> recently.
> Fronius has a 10KW?
>
> Thanks in advance
>
>
> jay
>
> Peltz power
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] largest 240v GT inverter

2020-02-09 Thread Jeff Clearwater

Hey Jay,

Why not just use 8 SMA SB 7.7's = 61.6 KW rated, 32 Amps 240 each.

Then use a dedicated 320 Amp Rated (Typical nominal bus of a 400 A 
panel) Supply Side fed Breaker panel as you'll have 256 x 1.25 Amps of 
Solar bus = 320 - right at the limit but you are good to go!


Jeff



Chris Sparadeo wrote on 2/8/20 7:42 PM:

Jay,

Sorry, I missed the 120/240v part. That CPS product is 3 phase. 
Fronius has the Primo 15kW in split phase. Have had good luck with them.


On Sat, Feb 8, 2020 at 10:30 PM Chris Sparadeo 
mailto:sparadeo.ch...@gmail.com>> wrote:


Hi Jay,

CPS has a 60 kW -1000v string inverter that might be a good fit
for your project.

https://www.chintpowersystems.com/commercial-60kw.shtml


Best,

Chris

On Sat, Feb 8, 2020 at 8:54 PM jay mailto:jay.pe...@gmail.com>> wrote:

HI All,

I’m wondering what the largest GT battery less inverter  (and
what people recommend) for 240v 60hz is out there.

I don’t need MLPE, as project would be ground mount, its large
residential, potentially 60KW.

SE has their 11.4KW, but I’ve heard lots of bad things about
them recently.
Fronius has a 10KW?

Thanks in advance


jay

Peltz power


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org


Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm


Check out or update participant bios:
www.members.re-wrenches.org 

-- 
Chris Sparadeo



C_802-369-4458
H_802-728-3059

--
Chris Sparadeo


C_802-369-4458
H_802-728-3059


___
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




--
~~~
Jeff Clearwater
Village Power Design
linkedin 
www.villagepowerdesign.com 
cell - 413-559-9763
~~~
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] largest 240v GT inverter

2020-02-08 Thread Chris Sparadeo
Jay,

Sorry, I missed the 120/240v part. That CPS product is 3 phase. Fronius has
the Primo 15kW in split phase. Have had good luck with them.

On Sat, Feb 8, 2020 at 10:30 PM Chris Sparadeo 
wrote:

> Hi Jay,
>
> CPS has a 60 kW -1000v string inverter that might be a good fit for your
> project.
>
> https://www.chintpowersystems.com/commercial-60kw.shtml
>
>
> Best,
>
> Chris
>
> On Sat, Feb 8, 2020 at 8:54 PM jay  wrote:
>
>> HI All,
>>
>> I’m wondering what the largest GT battery less inverter  (and what people
>> recommend) for 240v 60hz is out there.
>>
>> I don’t need MLPE, as project would be ground mount, its large
>> residential, potentially 60KW.
>>
>> SE has their 11.4KW, but I’ve heard lots of bad things about them
>> recently.
>> Fronius has a 10KW?
>>
>> Thanks in advance
>>
>>
>> jay
>>
>> Peltz power
>>
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
>
-- 
Chris Sparadeo


C_802-369-4458
H_802-728-3059
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] largest 240v GT inverter

2020-02-08 Thread Chris Sparadeo
Hi Jay,

CPS has a 60 kW -1000v string inverter that might be a good fit for your
project.

https://www.chintpowersystems.com/commercial-60kw.shtml


Best,

Chris

On Sat, Feb 8, 2020 at 8:54 PM jay  wrote:

> HI All,
>
> I’m wondering what the largest GT battery less inverter  (and what people
> recommend) for 240v 60hz is out there.
>
> I don’t need MLPE, as project would be ground mount, its large
> residential, potentially 60KW.
>
> SE has their 11.4KW, but I’ve heard lots of bad things about them
> recently.
> Fronius has a 10KW?
>
> Thanks in advance
>
>
> jay
>
> Peltz power
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> --
Chris Sparadeo


C_802-369-4458
H_802-728-3059
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org