Ok, I'll bite.First, some  diffnitions.. from Delmer's Standard (ISBN-13: 978-1-4180-6580-5):Apparent  Power (VA) is the value found by multiplying the applied voltage by the  total current of an AC circuit. Apparent power is measured in volt-amps  (VA) and should not be confused with true power, measured in watts."Power  Factor (PF) is a comparison of the true power (Resistive, or Watts) to  the Apparent power (Volt Amps) in an AC circuit.""Reactive  power (VARs or Volt Amps Reactive... sometimes called "wattless  power"), is calculated by multiplying reactive voltage by reactive  current. Which can be produced by inductive or capacitive loads.".  (The key concept here is the notion that there is funny reactive stuff going  on opposing input stuff).. there's also a  few different resistances to get your head around (I've tried to attach a  cheat Sheet from E2.. but I guess the file was too big, so it got kicked back... contact me off list and I can send it along)..anyway, Assuming you're in single phase parallel land  (AC).. : First, there's a pure resistance  measured in ohms (Greek letter omega), opposing current flow across any  purely resistive loads.. (power in this part of the circuit is measured  in watts.. current is in phase with voltage)...   there's also a current limiting property opposing current flow across  any inductive loads.. it's also measured in ohms, but is called XL.. or  Inductive Reactance... funny thing about this stuff is that it's not  really a resistance.. it's more of a reaction to magnetic fields.. so  the current wave form lags the voltage wave form by 90 degrees... Power  in this part of the circuit is tabbed VARsL...   similarly there's a resistance opposing current flow (or something like  it) in capacitive loads.. also measured in ohms. this resistance is  given the handle of Xc... or Capacitive Reactance. Power in  this part of the circuit is tabbed VARsc .. this current leads the voltage  wave form by 90 degrees, and is 180 degrees out of phase with any  inductive current .. so you can subtract the smaller from the larger,  and come up with a total VARs for the circuit.. which might be either inductive or  capacitive..  and because the relationship of either wave form is 90  degrees out of phase from resistive power, we can use right angle trig.  to keep tabs. Chuck Thompson (E1) taught us the phrase "ELI the ICE man"  to help us keep things straight.  Finally, there's Z (or total circuit impedance or "total opposition to  current flow in an AC circuit"), and is calculated from ohms, XL and Xc. Z can be substituted for R total circuit calculations... I think..--So--  The way I like to make sense of it.. when you  stuff AC power into a purely resistive circuit, it consumes watts.  the current wave form is in phase with the voltage wave form so the  resistive force pushes straight back on applied power... (twinkle,  twinkle little star, power = I squared R). When  you stuff AC power into a combination AC circuit (resistive, inductive,  and maybe capacitive.. like a motor), really funny things happen.. you  can still walk up and measure stuff with your meter (and you still see  Volts and Amps ), but you're seeing "apparent power".. (VA).. the  current wave form is likely not in phase with the voltage wave form, so  rather than there being a resistance opposing current flow directly,  there's now a "funny power" pushing back the on the applied power.. a  reactive power (VARs). which can be either inductive (lagging), or  capacitive (leading). that means VARs is oppositional to VA... And  Power Factor (PF) is the ratio of Watts/ Volt Amps (VA).So,  the way I see it, VA is total apparent power.. stuff you can see...  VARs is reactive power.. (funny power pushing back on applied power)...  So that means that if there is no VARs, (XL=Xc), there is no out  of phase (funny power) opposing input power... which would make the  Power Factor (PF= W/VA)=1. Now I have been known to be full of... beans, so if I've oopsied some, please chime in.. thanks. hope this helps. dbComments?Dan  BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP  #092907-44Dan BrownPresidentFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44


---- Original Message 
Subject: Re: [RE-wrenches] var/ power factor
From: Kent Osterberg k...@coveoregon.com
Date: Fri, May 14, 2010 1:35 pm
To: RE-wrenches re-wrenches@lists.re-wrenches.org

  Todd,  You are getting credit for all the energy your system can produce. Turn off the humidify and you'll see the power factor go up to nearly 1.0. That's what the inverter is operating at, regardless of whether the humidifier is on or off.   Say the PF is 80% without the inverter running. That means the utility is providing some reactive power or VARs. With the inverter running, the real power deli

Re: [RE-wrenches] var/ power factor

2010-05-14 Thread Kent Osterberg




Todd,

You are getting credit for all the energy your system can produce.
Turn off the humidify and you'll see the power factor go up to nearly
1.0. That's what the inverter is operating at, regardless of whether
the humidifier is on or off. 

Say the PF is 80% without the inverter running. That means the utility
is providing some reactive power or VARs. With the inverter running,
the real power delivered by the utility is reduced, but the reactive
power is not changed. To see it mathematically: the VA delivered by
the utility is the square root of the sum of the squares of VAR and
Watts. PF = W/VA = W/sqrt(W^2+VAR^2). Reduce W without changing VAR
and the power factor goes down, possibly even to zero.

Kent Osterberg
Blue Mountain Solar




toddc...@finestplanet.com wrote:
I have a question about my
personal home system. It is an Outback battery based grid tie. My
digital utility meter is capable of reading var and power factor. So
often (like just now) when I read this it is not even close to unity.
Today's reading was 1.57 VAR, 56 PF. What is
going on here? Am I not being credited for everything I am selling? The
only significant load I have running is a dehumidifier... so an
inductive load.
  
Todd
  
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
  


No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 9.0.819 / Virus Database: 271.1.1/2873 - Release Date: 05/13/10 23:26:00

  



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org