That sounds like something the utility would make financially unrealistic to do.
Are you sure that your state public service commission and consequently the 
utility would not see that as purely a competitive generator and require all 
the normal protective relaying necessary for that?

-Original Message-
From: "Ron Young" 
Sent: ‎9/‎20/‎2014 20:50
To: "RE-wrenches" 
Subject: [RE-wrenches] wood gasification to grid

I have a customer who wants to use a 50kw generator converted to wood 
gasification to tie into the grid. Any recommendations on the type of grid tie 
gear that will be appropriate? It’s a preliminary inquiry but I’m guessing a 
240v output from the generator, single phase but may be 3ph. I see Solectria 
and SatCon make inverters in this range. Any suggestions appreciated

Ron Young



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] wood gasification to grid

2014-09-21 Thread RE Ellison
The inverter portion of the process at this point in time would be
relatively east to do. That's not saying that the inverter will like the
power quality. Most generators will not put out smooth enough power to allow
an inverter to connect. The engines that I have seen running on wood gas
were nowhere near smooth enough to meet an inverters interconnect standards.


After all that you get to deal with the regulatory hoops and I doubt that
would be easy.

Just some thoughts.
Bob Ellison



-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Ron Young
Sent: Saturday, September 20, 2014 8:51 PM
To: RE-wrenches
Subject: [RE-wrenches] wood gasification to grid

I have a customer who wants to use a 50kw generator converted to wood
gasification to tie into the grid. Any recommendations on the type of grid
tie gear that will be appropriate? It's a preliminary inquiry but I'm
guessing a 240v output from the generator, single phase but may be 3ph. I
see Solectria and SatCon make inverters in this range. Any suggestions
appreciated

Ron Young



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4765 / Virus Database: 4015/8211 - Release Date: 09/14/14

-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4765 / Virus Database: 4015/8211 - Release Date: 09/14/14

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] wood gasification to grid

2014-09-21 Thread toddcory

i saw a commercial unit doing this here in mountshasta about 12 years ago.
 
the gas (from gasified wood) was fed into a ford engine, which turned a dc 
generator charging a small "buffer bank" of batteries. a standard trace sw4024 
did the selling to the grid. the grid interface was the easy part. getting the 
engine to consistently run off of the gasified wood chips was what nixed the 
demonstration project. moisture variations and dirt in the chips was the 
biggest problem.
 
todd
 
 
 
 
On Sunday, September 21, 2014 2:08am, "RE Ellison"  said:



> The inverter portion of the process at this point in time would be
> relatively east to do. That's not saying that the inverter will like the
> power quality. Most generators will not put out smooth enough power to allow
> an inverter to connect. The engines that I have seen running on wood gas
> were nowhere near smooth enough to meet an inverters interconnect standards.
> 
> 
> After all that you get to deal with the regulatory hoops and I doubt that
> would be easy.
> 
> Just some thoughts.
> Bob Ellison
> 
> 
> 
> -Original Message-
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of Ron Young
> Sent: Saturday, September 20, 2014 8:51 PM
> To: RE-wrenches
> Subject: [RE-wrenches] wood gasification to grid
> 
> I have a customer who wants to use a 50kw generator converted to wood
> gasification to tie into the grid. Any recommendations on the type of grid
> tie gear that will be appropriate? It's a preliminary inquiry but I'm
> guessing a 240v output from the generator, single phase but may be 3ph. I
> see Solectria and SatCon make inverters in this range. Any suggestions
> appreciated
> 
> Ron Young
> 
> 
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> -
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2014.0.4765 / Virus Database: 4015/8211 - Release Date: 09/14/14
> 
> -
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2014.0.4765 / Virus Database: 4015/8211 - Release Date: 09/14/14
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 


Sent from Finest Planet WebMail.
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] wood gasification to grid

2014-09-21 Thread Ron Young
The comments are interesting and helpful. This is a proposed college research 
project that will be sponsored by a grant and all these bridges would have to 
be crossed. 

Ron

On Sep 21, 2014, at 2:08 AM, RE Ellison  wrote:

> The inverter portion of the process at this point in time would be
> relatively east to do. That's not saying that the inverter will like the
> power quality. Most generators will not put out smooth enough power to allow
> an inverter to connect. The engines that I have seen running on wood gas
> were nowhere near smooth enough to meet an inverters interconnect standards.
> 
> 
> After all that you get to deal with the regulatory hoops and I doubt that
> would be easy.
> 
> Just some thoughts.
> Bob Ellison
> 
> 
> 
> -Original Message-
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of Ron Young
> Sent: Saturday, September 20, 2014 8:51 PM
> To: RE-wrenches
> Subject: [RE-wrenches] wood gasification to grid
> 
> I have a customer who wants to use a 50kw generator converted to wood
> gasification to tie into the grid. Any recommendations on the type of grid
> tie gear that will be appropriate? It's a preliminary inquiry but I'm
> guessing a 240v output from the generator, single phase but may be 3ph. I
> see Solectria and SatCon make inverters in this range. Any suggestions
> appreciated
> 
> Ron Young
> 
> 
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> -
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2014.0.4765 / Virus Database: 4015/8211 - Release Date: 09/14/14
> 
> -
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2014.0.4765 / Virus Database: 4015/8211 - Release Date: 09/14/14
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] wood gasification to grid

2014-09-21 Thread jay peltz
Why not do this system like a AC hydro system.

They drive an AC motor, through some control mechanisms, but no inverter, 
batteries etc.
I think that Thompson and Howe is one company that provides such equipment.

In working this through a standard inverter, you would have to rectify it, 
easy.  But how do you deal with the MPPT working with the generator output?  It 
wouldn't work like a PV output.

I know from experience that trying to use standard batteryless inverters on 
motors ( such as hydros) doesn't always work.  Some inverters ( brands) work, 
some don't

jay

peltz power






On Sep 21, 2014, at 10:22 AM, toddc...@finestplanet.com wrote:

> i saw a commercial unit doing this here in mountshasta about 12 years ago.
>  
> the gas (from gasified wood) was fed into a ford engine, which turned a dc 
> generator charging a small "buffer bank" of batteries. a standard trace 
> sw4024 did the selling to the grid. the grid interface was the easy part. 
> getting the engine to consistently run off of the gasified wood chips was 
> what nixed the demonstration project. moisture variations and dirt in the 
> chips was the biggest problem.
>  
> todd
>  
>  
>  
>  
> On Sunday, September 21, 2014 2:08am, "RE Ellison"  said:
> 
> > The inverter portion of the process at this point in time would be
> > relatively east to do. That's not saying that the inverter will like the
> > power quality. Most generators will not put out smooth enough power to allow
> > an inverter to connect. The engines that I have seen running on wood gas
> > were nowhere near smooth enough to meet an inverters interconnect standards.
> > 
> > 
> > After all that you get to deal with the regulatory hoops and I doubt that
> > would be easy.
> > 
> > Just some thoughts.
> > Bob Ellison
> > 
> > 
> > 
> > -Original Message-
> > From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> > Behalf Of Ron Young
> > Sent: Saturday, September 20, 2014 8:51 PM
> > To: RE-wrenches
> > Subject: [RE-wrenches] wood gasification to grid
> > 
> > I have a customer who wants to use a 50kw generator converted to wood
> > gasification to tie into the grid. Any recommendations on the type of grid
> > tie gear that will be appropriate? It's a preliminary inquiry but I'm
> > guessing a 240v output from the generator, single phase but may be 3ph. I
> > see Solectria and SatCon make inverters in this range. Any suggestions
> > appreciated
> > 
> > Ron Young
> > 
> > 
> > 
> > ___
> > List sponsored by Redwood Alliance
> > 
> > List Address: RE-wrenches@lists.re-wrenches.org
> > 
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> > 
> > List-Archive:
> > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> > 
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> > 
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> > 
> > -
> > No virus found in this message.
> > Checked by AVG - www.avg.com
> > Version: 2014.0.4765 / Virus Database: 4015/8211 - Release Date: 09/14/14
> > 
> > -
> > No virus found in this message.
> > Checked by AVG - www.avg.com
> > Version: 2014.0.4765 / Virus Database: 4015/8211 - Release Date: 09/14/14
> > 
> > ___
> > List sponsored by Redwood Alliance
> > 
> > List Address: RE-wrenches@lists.re-wrenches.org
> > 
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> > 
> > List-Archive:
> > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> > 
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> > 
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> > 
> >
> 
> 
> 
> Sent from Finest Planet WebMail.
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org