Some things to think about.....

The rated operating voltage of the MOV needs to be greater than the PEAK AC
voltage, not the RMS.  During an over voltage event (spike or otherwise) the
MOV conducts, generating heat.  The higher the heat the lower the resistance
causing them to go into thermal runaway quickly!  This may result in a fire
if the circuit is not properly protected by a thermal cutout.  All recently
UL listed surge protection devices (SPDs) are required to have a thermal
cutout next to the MOV to disconnect power in the event of thermal runaway.
I have seen many instances where an MOV has been installed without the
thermal cutout and the result has been a fire.  Many MOV devices will go
into thermal runaway before they draw enough current to open a fuse of 10 or
15 Amps, typical of some of the larger power supplies.  It only takes a
small amount of current to cause thermal runaway where the MOV starts to
flame and maybe cause damage to other items or cause a fire if not well
contained in a non flammable compartment.  As pointed out, the MOV degrades
with every over voltage spike.  Depending on the electrical environment,
their effectiveness may be short lived.  The best protection is achieved
with a properly coordinated SAD (silicon avalanche diode) and MOV
combination.   UL1449, Edition 3 is an excellent reference.  I would
recommend that any surge protection device installed be UL1449, Edition 3,
listed to ensure it does not cause a fire.  I am referencing commercial
devices, not individual components we may install in a project of our own as
the individual components are typically not UL listed, only a complete
product.  When reviewing a product for purchase ensure that it has the
UL1449 Ed 3 listing.  Not just a UL seal as that could mean anything.  Many
protected outlet strips have a UL seal affixed but that only applies to the
outlet strip portion being UL listed and not the surge protection portion.
Generally if the manufacturer has a UL listing for the device as a surge
protection device (SPD also previously known as TVSS devices) they will be
proud of their UL listing and will have it printed on the label.  Be sure
you see Ed 3 appended to the UL1449 as the original 1449 of a few years ago
did not require the thermal cutout device.  Only after several fires was the
standard changed to require the thermal cutout on the MOV (actually
physically next to and electrically in series with the MOV)

With respect to the generator surges....  Just from reading the post, my
thought is that the only load on the generator was the power supply or maybe
with an additional small resistive load.  I suspect this was a switched
power supply without power factor correction.  I also suspect that the
generator governor was not designed with a tolerance suitable for powering
sensitive electronic loads and that there was no voltage and little  speed
regulation built in.  AC power generators like a power factor of nearly 1.
Therefore, we must ensure that a goodly portion of the generator load is
resistive or has a PF of nearly 1.  Many switched supplies have a PF of as
low as 0.7.  Without an appropriate resistive load to offset this low PF and
help get this closer to a PF of 1, the generator may do strange things.
Also, generators may exhibit strange operating characteristics when used
with power supplies that have PF correction circuits built in.  The wrong
combination of load and generator may cause damage to the load (power
supply).  Products designed for international distribution have power factor
correction circuits installed, such as several Motorola products.  Be
cautious when powering these products from small generators that you may
typically purchase at your local home center.  Those generators are not
designed to power sensitive electronic equipment and may cause damage to the
equipment.  I have seen that happen all too often.  Don't try a Motorola
Quantar on one of these generators.  You may be disappointed.

A generator suitable for powering your sensitive electronic loads must have
suitable speed (frequency) and voltage regulation built into the product.
A reminder to evaluate your field day generator with respect to your load.
I have heard stories where folks have brought their valued home station to a
field day site only to take the power supply home damaged.

I hope this is helpful.

73
Bruce, W3YVV

Reply via email to