Salt Water for Fire Sprinkler System

2009-08-20 Thread Brian Harris
Has anyone had any experience with a fire pump taking suction from Brackish
water. Can not find anything in the code that indicates this is not allowed.
Are there any special issues that need to be addressed outside galvanized
pipe and fittings?
 
Any input on this issue would be greatly appreciated.
 

Regards,

 http://www.firstdefensefire.com/  

 

 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Re: Salt Water for Fire Sprinkler System

2009-08-20 Thread Stewart Kidd
Brian

I had several systems in the Gulf where brackish water was used - I  
always speciified gunmetal pump casings and volutes and this seems to  
have been satisfactory.

Stewart Kidd
On 20 Aug 2009, at 14:13, Brian Harris wrote:

 Has anyone had any experience with a fire pump taking suction from  
 Brackish
 water. Can not find anything in the code that indicates this is not  
 allowed.
 Are there any special issues that need to be addressed outside  
 galvanized
 pipe and fittings?

 Any input on this issue would be greatly appreciated.


 Regards,

 http://www.firstdefensefire.com/




 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Salt Water for Fire Sprinkler System

2009-08-20 Thread Craig.Prahl
NFPA 20, 2007, A.5.6.4 states Water sources containing salt or other materials 
deleterious to the fire protection systems should be avoided.

Strainer/suction screening on the intake.  (NFPA 20, 2007, 5.14.8)

Freeze protection for the suction line as it exits the water (unless you're 
using vertical turbine pumps)  (NFPA 20, 2007, 5.14.6.2.2)

There is a reference to pumps taking suction from brackish water in the 
appendix while discussing boilers,  so you could take this as an inference that 
it is done, while not preferable, it is acceptable.
NFPA 20, 2007 A.13.3(3) This method should not be used when there is any 
danger of contaminating a potable water supply. In situations where the fire
pump is handling salt or brackish water, it might also be undesirable to make 
this emergency boiler feed connection. In such situations,
an effort should be made to secure some other secondary boiler feed supply that 
will always be available.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Thursday, August 20, 2009 9:13 AM
To: sprinklerforum@firesprinkler.org
Subject: Salt Water for Fire Sprinkler System

Has anyone had any experience with a fire pump taking suction from Brackish 
water. Can not find anything in the code that indicates this is not allowed.
Are there any special issues that need to be addressed outside galvanized pipe 
and fittings?
 
Any input on this issue would be greatly appreciated.
 

Regards,

 http://www.firstdefensefire.com/  

 

 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Salt Water for Fire Sprinkler System

2009-08-20 Thread Charles Thurston
Hello Brian,

I would check the section of 13 for Marine Systems, Several tidbits in
there.

Thursday, August 20, 2009, 9:13:25 AM, you wrote:

 Has anyone had any experience with a fire pump taking suction from Brackish
 water. Can not find anything in the code that indicates this is not allowed.
 Are there any special issues that need to be addressed outside galvanized
 pipe and fittings?
  
 Any input on this issue would be greatly appreciated.
  

 Regards,

  http://www.firstdefensefire.com/  

  

  



-- 
Best regards,
 Charles Thurstonmailto:coastalf...@sc.rr.com
  Coastal Fire Protection

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Salt Water for Fire Sprinkler System

2009-08-20 Thread tgw
Talk to the pump supliers. The last ones I did (for a high-speed ferry boat) 
were Monel.

--Original Message--
From: Brian Harris
Sender: sprinklerforum-boun...@firesprinkler.org
To: sprinklerforum@firesprinkler.org
ReplyTo: sprinklerforum@firesprinkler.org
Sent: Aug 20, 2009 9:13 AM
Subject: Salt Water for Fire Sprinkler System

Has anyone had any experience with a fire pump taking suction from Brackish
water. Can not find anything in the code that indicates this is not allowed.
Are there any special issues that need to be addressed outside galvanized
pipe and fittings?
 
Any input on this issue would be greatly appreciated.
 

Regards,

 http://www.firstdefensefire.com/  

 

 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Sent from my Verizon Wireless BlackBerry
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Salt Water for Fire Sprinkler System

2009-08-20 Thread Thom McMahon
It's not just about the Pump, you need to think about the system your
supplying. What we see in our PACDIV projects is everything is filled and
tested using fresh (potable) water after flushing the systems. That way the
only part of the system which has Brackish water sitting in it is the pump
suction and a short piece of the discharge piping. Is this a vertical
turbine pump? Is the intake protected from Marine growth, Mussels?
Removable, cleanable screens?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Thursday, August 20, 2009 7:13 AM
To: sprinklerforum@firesprinkler.org
Subject: Salt Water for Fire Sprinkler System

Has anyone had any experience with a fire pump taking suction from Brackish
water. Can not find anything in the code that indicates this is not allowed.
Are there any special issues that need to be addressed outside galvanized
pipe and fittings?
 
Any input on this issue would be greatly appreciated.
 

Regards,

 http://www.firstdefensefire.com/  

 

 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Salt Water for Fire Sprinkler System

2009-08-20 Thread Stewart Kidd
Thom

In many part of the world the public water mains supply water which  
may be technically within WHO guidelines for potability is essentially  
brackish.  In the Arabian Gulf this is produced by blending ground  
water with distilled/desalted water.  People use this for general  
household duties, flushing and irrigating but not drinking. Drinking  
water is supplied via tank trucks and is referred to as 'sweet water'

There is no possibility of marine growth as the salinity is too low  
and the water is taken from aquifers which are now suffering from  
years of over abstraction.  While it's possible to use sweet water to  
charge a sprinkler system or fire main after installation or servicing  
it is very hard to keep to this fill.  Hence the primary problem being  
pumps - as has been suggested there are a good range of sprinkler  
valve sets and components which are intended for marine use - I  have  
seen some really good kit from Tyco on production platforms in the  
North Sea

It does seem however that it is the pumps which really suffer in such  
environments and I have seen some horrific impeller blade erosion in  
Nigeria on pumps that are less than 5 years old.

Incidentally, Hong Kong has salt water fire mains in many parts of  
Kowloon - look for the yellow hydrants !  (The ones on the old Kai Tak  
airport approach have nine 64mm outlets !)

Regards

Stewart

On 20 Aug 2009, at 16:18, Thom McMahon wrote:

 It's not just about the Pump, you need to think about the system your
 supplying. What we see in our PACDIV projects is everything is  
 filled and
 tested using fresh (potable) water after flushing the systems. That  
 way the
 only part of the system which has Brackish water sitting in it is  
 the pump
 suction and a short piece of the discharge piping. Is this a vertical
 turbine pump? Is the intake protected from Marine growth, Mussels?
 Removable, cleanable screens?

 Thom McMahon, SET
 Firetech, Inc.
 2560 Copper Ridge Dr
 P.O. Box 882136
 Steamboat Springs, CO 80488
 Tel:  970-879-7952
 Fax: 970-879-7926


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian  
 Harris
 Sent: Thursday, August 20, 2009 7:13 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Salt Water for Fire Sprinkler System

 Has anyone had any experience with a fire pump taking suction from  
 Brackish
 water. Can not find anything in the code that indicates this is not  
 allowed.
 Are there any special issues that need to be addressed outside  
 galvanized
 pipe and fittings?

 Any input on this issue would be greatly appreciated.


 Regards,

 http://www.firstdefensefire.com/





 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Salt Water for Fire Sprinkler System

2009-08-20 Thread Thom McMahon
Do I hear ROAD TRIP! 

Used to be Join the Navy, See the world Now it's Become a Fire Sprinkler
Designer (layout Tech.) and see the world.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



f Stewart Kidd
Sent: Thursday, August 20, 2009 10:31 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Salt Water for Fire Sprinkler System

Incidentally, Hong Kong has salt water fire mains in many parts of Kowloon -
look for the yellow hydrants !  (The ones on the old Kai Tak airport
approach have nine 64mm outlets !)

Regards

Stewart


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Salt Water for Fire Sprinkler System

2009-08-20 Thread Stewart Kidd
Thom

HK is probably the most intensely sprinklered place on earth so lots  
to see !

Stewart
On 20 Aug 2009, at 18:19, Thom McMahon wrote:

 Do I hear ROAD TRIP!

 Used to be Join the Navy, See the world Now it's Become a Fire  
 Sprinkler
 Designer (layout Tech.) and see the world.

 Thom McMahon, SET
 Firetech, Inc.
 2560 Copper Ridge Dr
 P.O. Box 882136
 Steamboat Springs, CO 80488
 Tel:  970-879-7952
 Fax: 970-879-7926



 f Stewart Kidd
 Sent: Thursday, August 20, 2009 10:31 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Salt Water for Fire Sprinkler System

 Incidentally, Hong Kong has salt water fire mains in many parts of  
 Kowloon -
 look for the yellow hydrants !  (The ones on the old Kai Tak airport
 approach have nine 64mm outlets !)

 Regards

 Stewart


 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Inspection of fire doors

2009-08-20 Thread Bobby Gillett
Does anyone know or have a standardized form for the inspection of fire
doors (Vertical metal doors - Link-n-Lever) per NFPA?

 

Thank You,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 mailto:bobby.gill...@keyfireprotection.com
bobby.gill...@keyfireprotection.com

 

 

 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Inspection of fire doors

2009-08-20 Thread cherokeefirepro
Its in a manual I have in the office from the NFPA, I will check when I 
get back in and let you know.


-Original Message-
From: Bobby Gillett gillet...@keyfireprotection.com
To: sprinklerforum@firesprinkler.org
Sent: Thu, 20 Aug 2009 14:38:00 -0500
Subject: Inspection of fire doors

Does anyone know or have a standardized form for the inspection of fire
doors (Vertical metal doors - Link-n-Lever) per NFPA?



Thank You,



Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax

(731) 267-4853 cell

 mailto:bobby.gill...@keyfireprotection.com
bobby.gill...@keyfireprotection.com







___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: 
techsupp...@firesprinkler.org

To Unsubscribe, send an email 
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Pockets

2009-08-20 Thread Geoff Dyce
When is a pocket considered a pocket??  What is the depth.  I say over 12.
What do you say?

 

Geoffrey H. Dyce

Operations Manager/NICET IV

DELTA Fire Sprinklers, Inc.

A Veteran Owned Small Business

Ph:  407-328-3000 ext 143

Fx:  407-575-9991

E-Mail:  ghd...@delta-fire.com

 

 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pockets

2009-08-20 Thread Reed Roisum
Geoff,

A ceiling pocket could probably be defined as any elevation increase from the 
rest of the ceiling, but whether it needs to be sprinklered is probably what 
you are wondering??
I'm sure you have looked at 8.6.7.2 which has a long list of requirements that 
all have to be met in order to not include sprinklers within the pocket.  One 
of which is that it does not exceed 36 inches in depth.  So, theoretically you 
could have a 36 in. deep pocket and not need sprinklers within.  I think you 
would still call it a ceiling pocket though.  Also, you could have a 5 ft x 5 
ft x 10 in. deep pocket that was within 10 ft to another 5 ft x 5 ft x 10 in. 
deep pocket and they would require sprinklers within.  At least that is how I 
see it.
Is that why you are asking?

Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain 
confidential and privileged material, and are for the sole use of the intended 
recipient.  Use or distribution by an unintended recipient is prohibited, and 
may be a violation of law.  If you believe that you received this in error, 
please do not read the body of this e-mail and please inform the sender that 
you have deleted the e-mail and any copies.  Thank you.


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Geoff Dyce
Sent: Thursday, August 20, 2009 4:57 PM
To: Sprinklerforum@firesprinkler.org
Subject: Pockets

When is a pocket considered a pocket??  What is the depth.  I say over 12.
What do you say?



Geoffrey H. Dyce

Operations Manager/NICET IV

DELTA Fire Sprinklers, Inc.

A Veteran Owned Small Business

Ph:  407-328-3000 ext 143

Fx:  407-575-9991

E-Mail:  ghd...@delta-fire.com





___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pockets

2009-08-20 Thread Thom McMahon
See 8.6.4.1.1.1 and 8.6.4.1.1.3 then move on to 8.6.7 and 8.8.7.

Finally remember that by having unprotected pockets allowed by 8.6.7 and
8.8.7 you will not be able to use the area reduction for QR heads if the
pockets exceed 32 SF.

Read the text carefully as it say's Deflector up to 12 below ceiling.
I'm assuming you've got a smooth flat non-combustible ceiling, but last
question I assumed wet system and it turned out to be a dry system.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Geoff Dyce
Sent: Thursday, August 20, 2009 3:57 PM
To: Sprinklerforum@firesprinkler.org
Subject: Pockets

When is a pocket considered a pocket??  What is the depth.  I say over 12.
What do you say?

 

Geoffrey H. Dyce

Operations Manager/NICET IV

DELTA Fire Sprinklers, Inc.

A Veteran Owned Small Business

Ph:  407-328-3000 ext 143

Fx:  407-575-9991

E-Mail:  ghd...@delta-fire.com

 

 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pockets

2009-08-20 Thread Geoff Dyce
Reed,
We have a flat ceiling with 5 deep hollow beams every 8-0.  Our sprinklers
are located on 16-0 centers located in every other beam.  Since a sprinkler
can be up to 12 down, I contend that these are not even considered pockets
but obstructions at worst but not even obstructions because our deflectors
are below the beams.  Whew

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Thursday, August 20, 2009 6:28 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Pockets

Geoff,

A ceiling pocket could probably be defined as any elevation increase from
the rest of the ceiling, but whether it needs to be sprinklered is probably
what you are wondering??
I'm sure you have looked at 8.6.7.2 which has a long list of requirements
that all have to be met in order to not include sprinklers within the
pocket.  One of which is that it does not exceed 36 inches in depth.  So,
theoretically you could have a 36 in. deep pocket and not need sprinklers
within.  I think you would still call it a ceiling pocket though.  Also, you
could have a 5 ft x 5 ft x 10 in. deep pocket that was within 10 ft to
another 5 ft x 5 ft x 10 in. deep pocket and they would require sprinklers
within.  At least that is how I see it.
Is that why you are asking?

Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain
confidential and privileged material, and are for the sole use of the
intended recipient.  Use or distribution by an unintended recipient is
prohibited, and may be a violation of law.  If you believe that you received
this in error, please do not read the body of this e-mail and please inform
the sender that you have deleted the e-mail and any copies.  Thank you.


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Geoff Dyce
Sent: Thursday, August 20, 2009 4:57 PM
To: Sprinklerforum@firesprinkler.org
Subject: Pockets

When is a pocket considered a pocket??  What is the depth.  I say over 12.
What do you say?



Geoffrey H. Dyce

Operations Manager/NICET IV

DELTA Fire Sprinklers, Inc.

A Veteran Owned Small Business

Ph:  407-328-3000 ext 143

Fx:  407-575-9991

E-Mail:  ghd...@delta-fire.com





___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Be a hero

2009-08-20 Thread Ed Vining
Anyone want to be a hero to the National Park Service?  Just let the guy
below know if you can help.

Thanks

-- 
Ed Vining, Guest, Retired
4819 John Muir Rd
Martinez CA 94553
925-228-8792

I am looking for a LCD-FC73 Remote Annunciator and a ZDM-FC73 Zone expander
for a FCI FC-73 Alarm Panel

That would be WONDERFUL if we could locate those.used parts are fine.

Thanks for all the assistance!

Tony

Tony Sudnick
U.S. Park Ranger, Law Enforcement
National Park Service
Minute Man National Historical Park
174 Liberty Street
Concord, MA  01742
(781) 674-1913 office
(618) 444-5378 cell
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pockets

2009-08-20 Thread Reed Roisum
I concur.  FWIW.

Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain 
confidential and privileged material, and are for the sole use of the intended 
recipient.  Use or distribution by an unintended recipient is prohibited, and 
may be a violation of law.  If you believe that you received this in error, 
please do not read the body of this e-mail and please inform the sender that 
you have deleted the e-mail and any copies.  Thank you.



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Geoff Dyce
Sent: Thursday, August 20, 2009 5:34 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pockets

Reed,
We have a flat ceiling with 5 deep hollow beams every 8-0.  Our sprinklers
are located on 16-0 centers located in every other beam.  Since a sprinkler
can be up to 12 down, I contend that these are not even considered pockets
but obstructions at worst but not even obstructions because our deflectors
are below the beams.  Whew

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Thursday, August 20, 2009 6:28 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Pockets

Geoff,

A ceiling pocket could probably be defined as any elevation increase from
the rest of the ceiling, but whether it needs to be sprinklered is probably
what you are wondering??
I'm sure you have looked at 8.6.7.2 which has a long list of requirements
that all have to be met in order to not include sprinklers within the
pocket.  One of which is that it does not exceed 36 inches in depth.  So,
theoretically you could have a 36 in. deep pocket and not need sprinklers
within.  I think you would still call it a ceiling pocket though.  Also, you
could have a 5 ft x 5 ft x 10 in. deep pocket that was within 10 ft to
another 5 ft x 5 ft x 10 in. deep pocket and they would require sprinklers
within.  At least that is how I see it.
Is that why you are asking?

Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain
confidential and privileged material, and are for the sole use of the
intended recipient.  Use or distribution by an unintended recipient is
prohibited, and may be a violation of law.  If you believe that you received
this in error, please do not read the body of this e-mail and please inform
the sender that you have deleted the e-mail and any copies.  Thank you.


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Geoff Dyce
Sent: Thursday, August 20, 2009 4:57 PM
To: Sprinklerforum@firesprinkler.org
Subject: Pockets

When is a pocket considered a pocket??  What is the depth.  I say over 12.
What do you say?



Geoffrey H. Dyce

Operations Manager/NICET IV

DELTA Fire Sprinklers, Inc.

A Veteran Owned Small Business

Ph:  407-328-3000 ext 143

Fx:  407-575-9991

E-Mail:  ghd...@delta-fire.com





___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Fire Pump Alternate Power

2009-08-20 Thread Reed Roisum
NFPA 20 (2007) Article 9.3.3 states An alternate source of power is not 
required where a back-up engine driven or back-up steam turbine driven fire 
pump is installed in accordance with this standard.

Does the use of an emergency generator serving only the fire pump (no other 
power) qualify as a back-up engine driven fire pump?



Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain 
confidential and privileged material, and are for the sole use of the intended 
recipient.  Use or distribution by an unintended recipient is prohibited, and 
may be a violation of law.  If you believe that you received this in error, 
please do not read the body of this e-mail and please inform the sender that 
you have deleted the e-mail and any copies.  Thank you.
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Fire Pump Alternate Power

2009-08-20 Thread Bob Caputo personal
An emergency generator serving just the pump or a generator serving
other/additional building needs (such as a hospital/Life Safety Code)
satisfies the requirement for back up to the electric motor driven fire
pump.  

A back up isn't necessarily required by NFPA 20 unless your power source
isn't reliable or unless there are other considerations for the requirement.
Have I missed your point?


Bob Caputo, CFPS
657 Cantara Lane - Vista, CA 92081
Fire  Life Safety America Company
3017 Vernon Rd - Richmond, VA 23228 
Office: (804) 222-1381  Cell: (804) 263-1577
   
   




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Thursday, August 20, 2009 4:18 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: Fire Pump Alternate Power

NFPA 20 (2007) Article 9.3.3 states An alternate source of power is not
required where a back-up engine driven or back-up steam turbine driven fire
pump is installed in accordance with this standard.

Does the use of an emergency generator serving only the fire pump (no other
power) qualify as a back-up engine driven fire pump?



Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain
confidential and privileged material, and are for the sole use of the
intended recipient.  Use or distribution by an unintended recipient is
prohibited, and may be a violation of law.  If you believe that you received
this in error, please do not read the body of this e-mail and please inform
the sender that you have deleted the e-mail and any copies.  Thank you.
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Fire Pump Alternate Power

2009-08-20 Thread Reed Roisum
There is no utility connection.  The generator is the only source of power.  
The question is, can an electric pump powered by a diesel generator be 
considered the normal source...
I think I found that answer... NFPA 20 2007 ed. 9.2.2(2) says that On-site 
power production facility connection dedicated to the fire pump installation 
can be considered the normal source of power.  And the commentary says An 
on-site standby or emergency generator satisfies the requirement in 9.2.2(2).

Thanks Bob.

Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain 
confidential and privileged material, and are for the sole use of the intended 
recipient.  Use or distribution by an unintended recipient is prohibited, and 
may be a violation of law.  If you believe that you received this in error, 
please do not read the body of this e-mail and please inform the sender that 
you have deleted the e-mail and any copies.  Thank you.



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob Caputo 
personal
Sent: Thursday, August 20, 2009 6:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Pump Alternate Power

An emergency generator serving just the pump or a generator serving
other/additional building needs (such as a hospital/Life Safety Code)
satisfies the requirement for back up to the electric motor driven fire
pump.

A back up isn't necessarily required by NFPA 20 unless your power source
isn't reliable or unless there are other considerations for the requirement.
Have I missed your point?


Bob Caputo, CFPS
657 Cantara Lane - Vista, CA 92081
Fire  Life Safety America Company
3017 Vernon Rd - Richmond, VA 23228
Office: (804) 222-1381  Cell: (804) 263-1577






-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Thursday, August 20, 2009 4:18 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: Fire Pump Alternate Power

NFPA 20 (2007) Article 9.3.3 states An alternate source of power is not
required where a back-up engine driven or back-up steam turbine driven fire
pump is installed in accordance with this standard.

Does the use of an emergency generator serving only the fire pump (no other
power) qualify as a back-up engine driven fire pump?



Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain
confidential and privileged material, and are for the sole use of the
intended recipient.  Use or distribution by an unintended recipient is
prohibited, and may be a violation of law.  If you believe that you received
this in error, please do not read the body of this e-mail and please inform
the sender that you have deleted the e-mail and any copies.  Thank you.
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Salt Water for Fire Sprinkler System

2009-08-20 Thread Steve Kowkabany
Brian,

There is nothing prohibiting this, but be prepared to pony up for the cost
of some exotic metals in the flow path if you want any type of decent life
out of it.

Good luck,


Steve Kowkabany, P.E.
Fire Protection Engineer
Neptune Fire Protection Engineering LLC
616 Davis Street
Neptune Beach, FL 32266
904-652-4200 Phone
904-212-0868 Fax 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of t...@fpdc.com
Sent: Thursday, August 20, 2009 10:38 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Salt Water for Fire Sprinkler System

Talk to the pump supliers. The last ones I did (for a high-speed ferry boat)
were Monel.

--Original Message--
From: Brian Harris
Sender: sprinklerforum-boun...@firesprinkler.org
To: sprinklerforum@firesprinkler.org
ReplyTo: sprinklerforum@firesprinkler.org
Sent: Aug 20, 2009 9:13 AM
Subject: Salt Water for Fire Sprinkler System

Has anyone had any experience with a fire pump taking suction from Brackish
water. Can not find anything in the code that indicates this is not allowed.
Are there any special issues that need to be addressed outside galvanized
pipe and fittings?
 
Any input on this issue would be greatly appreciated.
 

Regards,

 http://www.firstdefensefire.com/  

 

 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Sent from my Verizon Wireless BlackBerry
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 8.5.392 / Virus Database: 270.13.61/2312 - Release Date: 08/20/09
06:05:00

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Fire Pump Alternate Power

2009-08-20 Thread Reed Roisum
John,

Thanks for the NEC verbiage.  I don't believe an alternate source is required 
if the normal source is considered reliable.  (20-9.3.2)  Correct?  Or are you 
saying the generator is not a reliable primary source??  What does continually 
available mean (20-9.2.1)?

Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain 
confidential and privileged material, and are for the sole use of the intended 
recipient.  Use or distribution by an unintended recipient is prohibited, and 
may be a violation of law.  If you believe that you received this in error, 
please do not read the body of this e-mail and please inform the sender that 
you have deleted the e-mail and any copies.  Thank you.



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
Sent: Thursday, August 20, 2009 7:24 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Pump Alternate Power

Hi Reed,

Heres some more from the NEC

The 2008 NEC commentary provides;
695.3 (2) For an on-site power production facility to be considered a
reliable power source for an electric motor driven fire pump(s) fire
protection measures must be in place to protect the source and maintain a
reliable power supply.  The commentary goes on to reference NFPA 850-2005.

Assuming the generator qualifies as on-site power production and thus the
primary source of power what's the backup source ?, assuming one is
required. You only get one bite at that apple.

John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Thursday, August 20, 2009 8:02 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Fire Pump Alternate Power

There is no utility connection.  The generator is the only source of power.
The question is, can an electric pump powered by a diesel generator be
considered the normal source...
I think I found that answer... NFPA 20 2007 ed. 9.2.2(2) says that On-site
power production facility connection dedicated to the fire pump
installation can be considered the normal source of power.  And the
commentary says An on-site standby or emergency generator satisfies the
requirement in 9.2.2(2).

Thanks Bob.

Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain
confidential and privileged material, and are for the sole use of the
intended recipient.  Use or distribution by an unintended recipient is
prohibited, and may be a violation of law.  If you believe that you received
this in error, please do not read the body of this e-mail and please inform
the sender that you have deleted the e-mail and any copies.  Thank you.



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob Caputo
personal
Sent: Thursday, August 20, 2009 6:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Pump Alternate Power

An emergency generator serving just the pump or a generator serving
other/additional building needs (such as a hospital/Life Safety Code)
satisfies the requirement for back up to the electric motor driven fire
pump.

A back up isn't necessarily required by NFPA 20 unless your power source
isn't reliable or unless there are other considerations for the requirement.
Have I missed your point?


Bob Caputo, CFPS
657 Cantara Lane - Vista, CA 92081
Fire  Life Safety America Company
3017 Vernon Rd - Richmond, VA 23228
Office: (804) 222-1381  Cell: (804) 263-1577






-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Thursday, August 20, 2009 4:18 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: Fire Pump Alternate Power

NFPA 20 (2007) Article 9.3.3 states An alternate source of power is not
required where a back-up engine driven or back-up steam turbine driven fire
pump is installed in accordance with this standard.

Does the use of an emergency generator serving only the fire pump (no other
power) qualify as a back-up engine driven fire pump?



Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain
confidential and privileged material, and are 

RE: Fire Pump Alternate Power

2009-08-20 Thread John Drucker
What does continually available mean (20-9.2.1)?  

Energized at all times whether its needed or not, as opposed to saying on
demand or as needed. Alternate sources are generally considered on
demand. Keep in mind this section of the standard is addressing Normal
Power.

So ask the EE's if the generator runs continuously and just as importantly
what happens when it needs to be serviced where does the power come from
then ?  Remember the guidance NFPA-20, NFPA-25 and the NEC provide to
determine reliable, 

The source power plant has not experienced any shutdowns
of longer than 4 continuous hours in the year prior

No power outages have been experienced in the area of the
protected facility caused by failures in the power grid that
were not due to natural disasters or electric grid management
failure.

If its not then an alternate source is in order.

Hope that helps
 

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Thursday, August 20, 2009 8:57 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Fire Pump Alternate Power

John,

Thanks for the NEC verbiage.  I don't believe an alternate source is
required if the normal source is considered reliable.  (20-9.3.2)  Correct?
Or are you saying the generator is not a reliable primary source??  What
does continually available mean (20-9.2.1)?

Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain
confidential and privileged material, and are for the sole use of the
intended recipient.  Use or distribution by an unintended recipient is
prohibited, and may be a violation of law.  If you believe that you received
this in error, please do not read the body of this e-mail and please inform
the sender that you have deleted the e-mail and any copies.  Thank you.



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
Sent: Thursday, August 20, 2009 7:24 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Pump Alternate Power

Hi Reed,

Heres some more from the NEC

The 2008 NEC commentary provides;
695.3 (2) For an on-site power production facility to be considered a
reliable power source for an electric motor driven fire pump(s) fire
protection measures must be in place to protect the source and maintain a
reliable power supply.  The commentary goes on to reference NFPA 850-2005.

Assuming the generator qualifies as on-site power production and thus the
primary source of power what's the backup source ?, assuming one is
required. You only get one bite at that apple.

John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Thursday, August 20, 2009 8:02 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Fire Pump Alternate Power

There is no utility connection.  The generator is the only source of power.
The question is, can an electric pump powered by a diesel generator be
considered the normal source...
I think I found that answer... NFPA 20 2007 ed. 9.2.2(2) says that On-site
power production facility connection dedicated to the fire pump
installation can be considered the normal source of power.  And the
commentary says An on-site standby or emergency generator satisfies the
requirement in 9.2.2(2).

Thanks Bob.

Reed A. Roisum, CET
Fire Protection

Ulteig Engineers, Inc.
3350 38th Avenue S.
Fargo, ND 58104
701.280.8580 direct
701.212.8810 cell
www.ulteig.com

Energy | Water | Built-Environment

CONFIDENTIAL COMMUNICATION:Emails from this company normally contain
confidential and privileged material, and are for the sole use of the
intended recipient.  Use or distribution by an unintended recipient is
prohibited, and may be a violation of law.  If you believe that you received
this in error, please do not read the body of this e-mail and please inform
the sender that you have deleted the e-mail and any copies.  Thank you.



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob Caputo
personal
Sent: Thursday, August 20, 2009 6:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Pump Alternate Power

An emergency generator serving just the pump or a generator serving
other/additional building needs (such as a hospital/Life Safety Code)
satisfies the requirement for back up to the electric 

RE: Pockets

2009-08-20 Thread Sprinkler Academy - C Bilbo

 
Go ahead  TRY to come up with a definition for ceiling pocket.  We spent 
two hours (literally) in heated debate on this very issue in the Definitions 
Task Group at the NFPA 13 Committee Meetings.  We hammered it out and came to 
the following definition:
 
Ceiling Pocket. An architectural ceiling feature that consists of a bounded
area of ceiling located at a higher elevation than the attached lower ceiling.
   
Now... the trick in this discussion is to remember that the definition only 
happens to count if you are going to try to figure out if it is an unprotected 
ceiling pocket.  And what we did as a Committee was to say that pockets 
(what's a pocket again?) less than 12 deep should not be considered 
unprotected ceiling pockets if the sprinklers cover all of the area below the 
pocket itself. (thanks to some nifty wording from some guy named Isman...) 
 
THANK YOU!  THANK YOU!!  you've been a beautiful audience Goodnight.. 
 
Oh wait!  Four days until the world's first degree program specifically for 
fire sprinkler designers opens its doors  Yeah baby!  (Not to late 
to register for online classes there  thanks for your indulgence Mr. 
Muncy...)


It should be recognized that the above is my opinion as a member of the NFPA 13 
Committee on Installation Criteria representing the NFSA, and has not been 
processed as a formal interpretation in accordance with the NFPA Regulations 
Governing Committee Projects and should therefore not be considered, nor relied 
upon, as the official position of the NFSA nor the NFPA, nor any of their 
technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
845-878-4200 x138
www.sprinkleracademy.com







 From: ghd...@delta-fire.com
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pockets
 Date: Thu, 20 Aug 2009 18:33:56 -0400

 Reed,
 We have a flat ceiling with 5 deep hollow beams every 8-0. Our sprinklers
 are located on 16-0 centers located in every other beam. Since a sprinkler
 can be up to 12 down, I contend that these are not even considered pockets
 but obstructions at worst but not even obstructions because our deflectors
 are below the beams. Whew

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
 Sent: Thursday, August 20, 2009 6:28 PM
 To: 'sprinklerforum@firesprinkler.org'
 Subject: RE: Pockets

 Geoff,

 A ceiling pocket could probably be defined as any elevation increase from
 the rest of the ceiling, but whether it needs to be sprinklered is probably
 what you are wondering??
 I'm sure you have looked at 8.6.7.2 which has a long list of requirements
 that all have to be met in order to not include sprinklers within the
 pocket. One of which is that it does not exceed 36 inches in depth. So,
 theoretically you could have a 36 in. deep pocket and not need sprinklers
 within. I think you would still call it a ceiling pocket though. Also, you
 could have a 5 ft x 5 ft x 10 in. deep pocket that was within 10 ft to
 another 5 ft x 5 ft x 10 in. deep pocket and they would require sprinklers
 within. At least that is how I see it.
 Is that why you are asking?

 Reed A. Roisum, CET
 Fire Protection

 Ulteig Engineers, Inc.
 3350 38th Avenue S.
 Fargo, ND 58104
 701.280.8580 direct
 701.212.8810 cell
 www.ulteig.com

 Energy | Water | Built-Environment

 CONFIDENTIAL COMMUNICATION: Emails from this company normally contain
 confidential and privileged material, and are for the sole use of the
 intended recipient. Use or distribution by an unintended recipient is
 prohibited, and may be a violation of law. If you believe that you received
 this in error, please do not read the body of this e-mail and please inform
 the sender that you have deleted the e-mail and any copies. Thank you.


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Geoff Dyce
 Sent: Thursday, August 20, 2009 4:57 PM
 To: Sprinklerforum@firesprinkler.org
 Subject: Pockets

 When is a pocket considered a pocket?? What is the depth. I say over 12.
 What do you say?



 Geoffrey H. Dyce

 Operations Manager/NICET IV

 DELTA Fire Sprinklers, Inc.

 A Veteran Owned Small Business

 Ph: 407-328-3000 ext 143

 Fx: 407-575-9991

 E-Mail: ghd...@delta-fire.com





 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: