RE: UL list concrete anchor

2021-04-20 Thread Kyle.Montgomery via Sprinklerforum
Hilti HDI appears to be UL-Listed for fire protection.

-Original Message-
From: Sprinklerforum  On Behalf 
Of Sean Lockyer via Sprinklerforum
Sent: Tuesday, April 20, 2021 2:48 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Sean Lockyer 
Subject: [EXTERNAL] UL list concrete anchor

Is there a UL listed concrete anchor on the market (similar to the Sammy screw) 
? I am having an engineer require a UL listed anchor and to my knowledge, this 
isn't any sort of concrete anchor that has a listed or approval beyond that of 
FM. Any help would be greatly appreciated.

Thanks
Sean Lockyer
AIT Life Safety











___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=jBgl8Ey-FSzlE34GFBN369kmHdJEfSarwsBAvt5R6Tg=kJuCzAJoYt-7EWuE0bICYu-xBgX3Ogk-GLQYtr6boTA=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


UL list concrete anchor

2021-04-20 Thread Sean Lockyer via Sprinklerforum
Is there a UL listed concrete anchor on the market (similar to the Sammy screw) 
? I am having an engineer require a UL listed anchor and to my knowledge, this 
isn't any sort of concrete anchor that has a listed or approval beyond that of 
FM. Any help would be greatly appreciated.

Thanks
Sean Lockyer
AIT Life Safety











___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC & Pump Suction

2021-04-20 Thread Matt Grise via Sprinklerforum
If you just cant get the FDC moved, maybe add a pressure regulating valve or 
relief valve to prevent system overpressure? Not the most-best way to go, but 
better than blowing the system apart?

Matt 


-Original Message-
From: Sprinklerforum  On Behalf 
Of Mike Morey via Sprinklerforum
Sent: Tuesday, April 20, 2021 2:11 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey ; Brian Harris 
Subject: RE: FDC & Pump Suction

Is cap it and put one on the building an option?  Generally that's what we'd do 
in that scenario as there isn't much else you can safely do because of the 
compound pressure increase potential with a fire pump.  Presumably you have to 
put a test header somewhere, just add an FDC as well?  Of course then hydrant 
distance comes in to play as well.  

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell 
260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



-Original Message-
From: Sprinklerforum  On Behalf 
Of Brian Harris via Sprinklerforum
Sent: Tuesday, April 20, 2021 3:09 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Brian Harris 
Subject: FDC & Pump Suction

 
BE ADVISED - This email originated outside EMCOR. 
 

8.17.2.4.8 (2016) States the FDC cannot be located on the suction side of a 
pump. If a pump is being added to an existing system and the current FDC is in 
the yard what is the best way to handle this?

Brian Harris, CET
BVS Systems Inc.
Design Manager
https://urldefense.com/v3/__http://bvssystemsinc.com__;!!FaxH778!Oa95dsu6TI9Hj7kAeXEmYhi-WKVOTMpEuNpYZClEf07ApkGuVdkxvIwISy803Y3I$
 

Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!Oa95dsu6TI9Hj7kAeXEmYhi-WKVOTMpEuNpYZClEf07ApkGuVdkxvIwISwwwknZk$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org=E,1,Lpx3tcRLpwiaxhRN_jgQvczpWoBVrpZ-_cMaxqSwti-hybygSBkkctPb9h9BqHqASuUDRZpIpde_X8ZfGbcUopm8WVscaRNi-wydT9N_rQ,,=1
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC & Pump Suction

2021-04-20 Thread Mike Morey via Sprinklerforum
Is cap it and put one on the building an option?  Generally that's what we'd do 
in that scenario as there isn't much else you can safely do because of the 
compound pressure increase potential with a fire pump.  Presumably you have to 
put a test header somewhere, just add an FDC as well?  Of course then hydrant 
distance comes in to play as well.  

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email mmo...@shambaugh.com



-Original Message-
From: Sprinklerforum  On Behalf 
Of Brian Harris via Sprinklerforum
Sent: Tuesday, April 20, 2021 3:09 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Brian Harris 
Subject: FDC & Pump Suction

 
BE ADVISED - This email originated outside EMCOR. 
 

8.17.2.4.8 (2016) States the FDC cannot be located on the suction side of a 
pump. If a pump is being added to an existing system and the current FDC is in 
the yard what is the best way to handle this?

Brian Harris, CET
BVS Systems Inc.
Design Manager
https://urldefense.com/v3/__http://bvssystemsinc.com__;!!FaxH778!Oa95dsu6TI9Hj7kAeXEmYhi-WKVOTMpEuNpYZClEf07ApkGuVdkxvIwISy803Y3I$
 

Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!Oa95dsu6TI9Hj7kAeXEmYhi-WKVOTMpEuNpYZClEf07ApkGuVdkxvIwISwwwknZk$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


FDC & Pump Suction

2021-04-20 Thread Brian Harris via Sprinklerforum
8.17.2.4.8 (2016) States the FDC cannot be located on the suction side of a 
pump. If a pump is being added to an existing system and the current FDC is in 
the yard what is the best way to handle this?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] Re: Fire pump test through flow meter

2021-04-20 Thread Kyle.Montgomery via Sprinklerforum
Not to beat a moot horse, but one thing to be careful of with flowmeters is to 
make sure that you have the appropriate amount of straight pipe upstream and 
downstream of device. There will be a manufacturer's recommendation for these 
lengths and from my experience it does seem to make a difference. 

-Kyle M

-Original Message-
From: Sprinklerforum  On Behalf 
Of Fpdcdesign via Sprinklerforum
Sent: Monday, April 19, 2021 2:29 PM
To: Sprinklerforum 
Cc: Fpdcdesign 
Subject: [EXTERNAL] Re: Fire pump test through flow meter

  
  

 The question is now moot because they went and tested the pump by actually 
flowing water and it ran fine. The problem lies in the testing process and that 
is someone else’s headache.   
  
  
  

  

  
  
>   
> On Apr 19, 2021 at 5:05 PM,   (mailto:sprinklerforum@lists.firesprinkler.org)>  wrote:
>   
>   
>   
>  I bet if there was a partially closed gate, or a check, or a blockage; that 
> might cause it. Are they’re any good resources about testing a fire pump with 
> a flow meter where it feeds back into the suction piping? I have been given a 
> couple of tests with very screwy results. Thanks Todd G Williams, PE Fire 
> Protection Design/Consulting Stonington, CT  860-535-2080 (tel:860-535-2080)  
> (tel:860-535-2080) (ofc)  860-554-7054 (tel:860-554-7054)  (tel:860-554-7054) 
> (fax)  860-608-4559 (tel:860-608-4559)  (tel:860-608-4559) (cell) 
> ___ Sprinklerforum mailing list  
> Sprinklerforum@lists.firesprinkler.org 
> (mailto:Sprinklerforum@lists.firesprinkler.org)   
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwIGaQ=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=kQGO6Mkp82Ong9rNP0Gk1v7gBkCoh7uNy6YJIC9ycyU=aGUTvW_qogJiISwgJdgeTLrVd5j61MXTh-CEAmaaF7g=
> 
>
>   
  
  
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwIGaQ=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=kQGO6Mkp82Ong9rNP0Gk1v7gBkCoh7uNy6YJIC9ycyU=aGUTvW_qogJiISwgJdgeTLrVd5j61MXTh-CEAmaaF7g=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org