Re: [Biofuel] diesel generator

2008-01-02 Thread Zeke Yewdall
Yeah.  If you use an inverter setup, you can run the generator full
out, which is generally more efficient than at low load, and avoids
wet stacking though if you are doing heat recovery from the
exhaust, you are intentionally inducing wet stacking -- hopefully just
not in the valve seats...  Just make sure the acid doesn't drain back
from whatever stainless steel heat exchanger, back into the engine.
You can do three phase with inverters, but it requires three inverters
-- a minimum of about 10kW.  For 120/240, you can get as small as 4kW
now.

Z

On Jan 2, 2008 5:40 PM, Tom Thiel <[EMAIL PROTECTED]> wrote:
> Hi Zeke,
> If you calculate the relative power per wattage of single and
> three-phase motors, there will be a slight advantage to 3-phase. The
> value of 3-phase motors also extends to their better torque and
> start-load characteristics and lack of starting capacitor(s) to
> maintain. I would base my system on availability and overall usefulness
> rather than those relatively modest advantages of 3-phase motors. A
> single-phase, dual voltage (as in 240 / 120 volt in the USA) setup
> allows use of higher voltage for motors and the lower voltage for
> appliances and lighting. Single-phase inverters are the norm for
> converting stored Direct Current energy to useful Alternating Current
> power. You're on the right track to run your generator while running
> your motors. If you have inverters, they can augment the output of your
> generator to help with start-loads (up to 5 times the run-load of the
> motor). The battery bank can be charged by the excess generator power
> and by photovoltaic, wind, etc. at all times. In capturing generator
> heat, don't forget the waste heat of the exhust stream, harder to
> capture than the coolant heat, but about equal to it in power.
> Good luck with your project.
>
> Tom Thiel
>
>
>
>
>
> On 2 Jan, 2008, at 7:19 PM, Zeke Yewdall wrote:
>
> > Are the three phase motors really more efficient?  Or are they just
> > lower amperage, but the same wattage?  The formula for calculating
> > three phase power, instead of being V*A*PF  is V(line to
> > line)*A*1.732*PF, I believe.
> >
> > Z
> >
> > On Jan 2, 2008 5:11 PM,  <[EMAIL PROTECTED]> wrote:
> >>
> >>  -- Original message --
> >> i want to set up a small diesel generator to run my milking parlor
> >> and use the engine heat to supply the hot water. Since the pumps and
> >> refrigeration are my biggest load, but are only on for a few hours a
> >> day, i was thinking  a 3 phase generator would be better because the
> >> motors operate at about half the amperage and would reduce the size
> >> of the generator i need to run. I was thinking a 6/1 or a 12/2 lister
> >> diesel. the fuel consumption on these is about 2 liters per hour. I
> >> only need to run about 2 -1 hp motors and 1- 2hp for milking and
> >> cooling ,then i could run the generator to charge batteries for the
> >> house and help heat the house in the winter. Any suggestions? it just
> >> seems to easy to change out the motors to 3 phase and reduce the kw
> >> size of my generator.
> >>
> >> ___
> >> Biofuel mailing list
> >> Biofuel@sustainablelists.org
> >> http://sustainablelists.org/mailman/listinfo/sustainablelorgbiofuel
> >>
> >> Biofuel at Journey to Forever:
> >> http://journeytoforever.org/biofuel.html
> >>
> >> Search the combined Biofuel and Biofuels-biz list archives (70,000
> >> messages):
> >> http://www.mail-archive.com/biofuel@sustainablelists.org/
> >>
> >
> > ___
> > Biofuel mailing list
> > Biofuel@sustainablelists.org
> > http://sustainablelists.org/mailman/listinfo/sustainablelorgbiofuel
> >
> > Biofuel at Journey to Forever:
> > http://journeytoforever.org/biofuel.html
> >
> > Search the combined Biofuel and Biofuels-biz list archives (70,000
> > messages):
> > http://www.mail-archive.com/biofuel@sustainablelists.org/
> >
>
>
> ___
> Biofuel mailing list
> Biofuel@sustainablelists.org
> http://sustainablelists.org/mailman/listinfo/sustainablelorgbiofuel
>
> Biofuel at Journey to Forever:
> http://journeytoforever.org/biofuel.html
>
> Search the combined Biofuel and Biofuels-biz list archives (70,000 messages):
> http://www.mail-archive.com/biofuel@sustainablelists.org/
>

___
Biofuel mailing list
Biofuel@sustainablelists.org
http://sustainablelists.org/mailman/listinfo/sustainablelorgbiofuel

Biofuel at Journey to Forever:
http://journeytoforever.org/biofuel.html

Search the combined Biofuel and Biofuels-biz list archives (70,000 messages):
http://www.mail-archive.com/biofuel@sustainablelists.org/


Re: [Biofuel] diesel generator

2008-01-02 Thread Tom Thiel
Hi Zeke,
If you calculate the relative power per wattage of single and 
three-phase motors, there will be a slight advantage to 3-phase. The 
value of 3-phase motors also extends to their better torque and 
start-load characteristics and lack of starting capacitor(s) to 
maintain. I would base my system on availability and overall usefulness 
rather than those relatively modest advantages of 3-phase motors. A 
single-phase, dual voltage (as in 240 / 120 volt in the USA) setup 
allows use of higher voltage for motors and the lower voltage for 
appliances and lighting. Single-phase inverters are the norm for 
converting stored Direct Current energy to useful Alternating Current 
power. You're on the right track to run your generator while running 
your motors. If you have inverters, they can augment the output of your 
generator to help with start-loads (up to 5 times the run-load of the 
motor). The battery bank can be charged by the excess generator power 
and by photovoltaic, wind, etc. at all times. In capturing generator 
heat, don't forget the waste heat of the exhust stream, harder to 
capture than the coolant heat, but about equal to it in power.
Good luck with your project.

Tom Thiel




On 2 Jan, 2008, at 7:19 PM, Zeke Yewdall wrote:

> Are the three phase motors really more efficient?  Or are they just
> lower amperage, but the same wattage?  The formula for calculating
> three phase power, instead of being V*A*PF  is V(line to
> line)*A*1.732*PF, I believe.
>
> Z
>
> On Jan 2, 2008 5:11 PM,  <[EMAIL PROTECTED]> wrote:
>>
>>  -- Original message --
>> i want to set up a small diesel generator to run my milking parlor 
>> and use the engine heat to supply the hot water. Since the pumps and 
>> refrigeration are my biggest load, but are only on for a few hours a 
>> day, i was thinking  a 3 phase generator would be better because the 
>> motors operate at about half the amperage and would reduce the size 
>> of the generator i need to run. I was thinking a 6/1 or a 12/2 lister 
>> diesel. the fuel consumption on these is about 2 liters per hour. I 
>> only need to run about 2 -1 hp motors and 1- 2hp for milking and 
>> cooling ,then i could run the generator to charge batteries for the 
>> house and help heat the house in the winter. Any suggestions? it just 
>> seems to easy to change out the motors to 3 phase and reduce the kw  
>> size of my generator.
>>
>> ___
>> Biofuel mailing list
>> Biofuel@sustainablelists.org
>> http://sustainablelists.org/mailman/listinfo/sustainablelorgbiofuel
>>
>> Biofuel at Journey to Forever:
>> http://journeytoforever.org/biofuel.html
>>
>> Search the combined Biofuel and Biofuels-biz list archives (70,000 
>> messages):
>> http://www.mail-archive.com/biofuel@sustainablelists.org/
>>
>
> ___
> Biofuel mailing list
> Biofuel@sustainablelists.org
> http://sustainablelists.org/mailman/listinfo/sustainablelorgbiofuel
>
> Biofuel at Journey to Forever:
> http://journeytoforever.org/biofuel.html
>
> Search the combined Biofuel and Biofuels-biz list archives (70,000 
> messages):
> http://www.mail-archive.com/biofuel@sustainablelists.org/
>


___
Biofuel mailing list
Biofuel@sustainablelists.org
http://sustainablelists.org/mailman/listinfo/sustainablelorgbiofuel

Biofuel at Journey to Forever:
http://journeytoforever.org/biofuel.html

Search the combined Biofuel and Biofuels-biz list archives (70,000 messages):
http://www.mail-archive.com/biofuel@sustainablelists.org/


Re: [Biofuel] diesel generator

2008-01-02 Thread Zeke Yewdall
Are the three phase motors really more efficient?  Or are they just
lower amperage, but the same wattage?  The formula for calculating
three phase power, instead of being V*A*PF  is V(line to
line)*A*1.732*PF, I believe.

Z

On Jan 2, 2008 5:11 PM,  <[EMAIL PROTECTED]> wrote:
>
>  -- Original message --
> i want to set up a small diesel generator to run my milking parlor and use 
> the engine heat to supply the hot water. Since the pumps and refrigeration 
> are my biggest load, but are only on for a few hours a day, i was thinking  a 
> 3 phase generator would be better because the motors operate at about half 
> the amperage and would reduce the size of the generator i need to run. I was 
> thinking a 6/1 or a 12/2 lister diesel. the fuel consumption on these is 
> about 2 liters per hour. I only need to run about 2 -1 hp motors and 1- 2hp 
> for milking and cooling ,then i could run the generator to charge batteries 
> for the house and help heat the house in the winter. Any suggestions? it just 
> seems to easy to change out the motors to 3 phase and reduce the kw  size of 
> my generator.
>
> ___
> Biofuel mailing list
> Biofuel@sustainablelists.org
> http://sustainablelists.org/mailman/listinfo/sustainablelorgbiofuel
>
> Biofuel at Journey to Forever:
> http://journeytoforever.org/biofuel.html
>
> Search the combined Biofuel and Biofuels-biz list archives (70,000 messages):
> http://www.mail-archive.com/biofuel@sustainablelists.org/
>

___
Biofuel mailing list
Biofuel@sustainablelists.org
http://sustainablelists.org/mailman/listinfo/sustainablelorgbiofuel

Biofuel at Journey to Forever:
http://journeytoforever.org/biofuel.html

Search the combined Biofuel and Biofuels-biz list archives (70,000 messages):
http://www.mail-archive.com/biofuel@sustainablelists.org/


Re: [Biofuel] diesel generator

2008-01-02 Thread fresheggs141

 -- Original message --
i want to set up a small diesel generator to run my milking parlor and use the 
engine heat to supply the hot water. Since the pumps and refrigeration are my 
biggest load, but are only on for a few hours a day, i was thinking  a 3 phase 
generator would be better because the motors operate at about half the amperage 
and would reduce the size of the generator i need to run. I was thinking a 6/1 
or a 12/2 lister diesel. the fuel consumption on these is about 2 liters per 
hour. I only need to run about 2 -1 hp motors and 1- 2hp for milking and 
cooling ,then i could run the generator to charge batteries for the house and 
help heat the house in the winter. Any suggestions? it just seems to easy to 
change out the motors to 3 phase and reduce the kw  size of my generator.

___
Biofuel mailing list
Biofuel@sustainablelists.org
http://sustainablelists.org/mailman/listinfo/sustainablelorgbiofuel

Biofuel at Journey to Forever:
http://journeytoforever.org/biofuel.html

Search the combined Biofuel and Biofuels-biz list archives (70,000 messages):
http://www.mail-archive.com/biofuel@sustainablelists.org/


Re: [biofuel] diesel generator

2004-05-03 Thread Ken Richardson

Try Utterpower.com it is a very interesting site
Ken

[Non-text portions of this message have been removed]




 Yahoo! Groups Sponsor -~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com.  Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/FGYolB/TM
-~->

Biofuel at Journey to Forever:
http://journeytoforever.org/biofuel.html

Biofuels list archives:
http://infoarchive.net/sgroup/biofuel/

Please do NOT send Unsubscribe messages to the list address.
To unsubscribe, send an email to:
[EMAIL PROTECTED] 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
 http://groups.yahoo.com/group/biofuel/

<*> To unsubscribe from this group, send an email to:
 [EMAIL PROTECTED]

<*> Your use of Yahoo! Groups is subject to:
 http://docs.yahoo.com/info/terms/