[time-nuts] OT question about liquid cooling

2012-10-03 Thread Javier Herrero

Hello all,

Please excuse me for the OT, but since this list is plenty of very 
knowledgeable colleagues, I'm tempted to ask...


I need to cool several resistive loads, in the order of 5kW, and I plan 
to use a cold plate and a liquid-to-liquid heat exchanger like the 
Lytron LCS-20, but this unit is quite big, and an overkill (it has 20kW 
capability).


If someone could suggest me a smaller liquid-to-liquid heat exchanger, 
and preferably a rack mount unit (and share any experience), it would be 
most welcome.


Since this has not too much to do with time and frequency, please answer 
off list.


Thank you very much! Best regards,

Javier



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] OT question about liquid cooling

2012-10-03 Thread Chris Albertson
5KW of power but that is only 1/4 of the spec.  What temperature will
the loads operate at?  It is quite hard to cool anything to ambient
with water.  The cooler the operating point the larger the heat sink.
Using a very oversize heat exchanger s not unreasonable of you want  a
relative low temperature.

The other side of the loop matters LOT also.  How will you cool the
water?  Do you have chilled water that can run open loop or do you
need to chill and re-cycle the water in a closed loop system.   Then
again temperature matters.  What is the inlet temperature?   How much
flow rate can your system provide.

If you don't wnt to learn a loot about this the easy solultion it to
simply over-spec the components by a large factor.  This also gives
you some margin for accients like a plumbing leak or a pump failure.
Do plan for these practical issues.When a pump fails the 5KW load
can boil water in the heat exchanger quickly and then your plumbing
comes apart.  To prevent that  use enough water volume and thermal
mass.  Again an over sized heat exchanger is good.  As is a thermal
shutdown switch.   These are cheap and work just like a fuse.  They
open the AC mains power at a set temperature,  you bolt them to the
heat sink.   They are common in high power audio amplifiers.


I don't have experience with a system like you need.  Mine is with
water cooling that involved TEC (thermo electric, or Peltier devices.)
 But I know that you do need to plan for mechanical failures, water
leaks and so on.Just like with a domestic hot water heaters you
place a basin and drain under them.



On Wed, Oct 3, 2012 at 9:01 AM, Javier Herrero jherr...@hvsistemas.es wrote:
 Hello all,

 Please excuse me for the OT, but since this list is plenty of very
 knowledgeable colleagues, I'm tempted to ask...

 I need to cool several resistive loads, in the order of 5kW, and I plan to
 use a cold plate and a liquid-to-liquid heat exchanger like the Lytron
 LCS-20, but this unit is quite big, and an overkill (it has 20kW
 capability).

 If someone could suggest me a smaller liquid-to-liquid heat exchanger, and
 preferably a rack mount unit (and share any experience), it would be most
 welcome.

 Since this has not too much to do with time and frequency, please answer off
 list.

 Thank you very much! Best regards,

 Javier



 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.



-- 

Chris Albertson
Redondo Beach, California

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] OT question about liquid cooling

2012-10-03 Thread Tom Harris
My day job is large industrial power supplies. The test racks have large
resistive loads with big fans exhausting to the outside. Cheap  simple.
Safety is by several strings of temperature cutouts wired in series. We
usually get work experience students in to wire them up.

Tip: to make a funny valued power resistor, just get the next value up and
wrap some nichrome wire around it to bring it down to the correct value.

I met an engineer who made a battery charger for one of our submarines.
This was tested by putting the load bank in a dumpmaster, and keeping it
filled up with water using a firehose!

On 4 October 2012 02:01, Javier Herrero jherr...@hvsistemas.es wrote:

 Hello all,

 Please excuse me for the OT, but since this list is plenty of very
 knowledgeable colleagues, I'm tempted to ask...

 I need to cool several resistive loads, in the order of 5kW, and I plan to
 use a cold plate and a liquid-to-liquid heat exchanger like the Lytron
 LCS-20, but this unit is quite big, and an overkill (it has 20kW
 capability).

 If someone could suggest me a smaller liquid-to-liquid heat exchanger, and
 preferably a rack mount unit (and share any experience), it would be most
 welcome.

 Since this has not too much to do with time and frequency, please answer
 off list.

 Thank you very much! Best regards,

 Javier



 __**_
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/**
 mailman/listinfo/time-nutshttps://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.




-- 

Tom Harris celephi...@gmail.com
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] OT question about liquid cooling

2012-10-03 Thread bownes
BWIWY (back when I was young) we needed a dummy load for a supercomputer (think 
Cray YMP size) that drew many many kw. 

Our test load was about 250' of 3/4 copper tubing coiled at about 12 dia and 
1 spacing. The load was varied by changing where the + and - leads were bolted 
onto the coil with u bolts. 

The whole mess was cooled by running water through it. A hose barb on the input 
connected up to the cold water supply and the output was run into a drain. You 
had too little resistance dialed in when all thy came out the output end was 
steam. :)

Anyway such a test load could be replicated using 1/4 ice machine copper 
tubing available at the hardware store, some hose clamps, and or hose barbs.

Bob

On Oct 3, 2012, at 19:35, Tom Harris celephi...@gmail.com wrote:

 My day job is large industrial power supplies. The test racks have large
 resistive loads with big fans exhausting to the outside. Cheap  simple.
 Safety is by several strings of temperature cutouts wired in series. We
 usually get work experience students in to wire them up.
 
 Tip: to make a funny valued power resistor, just get the next value up and
 wrap some nichrome wire around it to bring it down to the correct value.
 
 I met an engineer who made a battery charger for one of our submarines.
 This was tested by putting the load bank in a dumpmaster, and keeping it
 filled up with water using a firehose!
 
 On 4 October 2012 02:01, Javier Herrero jherr...@hvsistemas.es wrote:
 
 Hello all,
 
 Please excuse me for the OT, but since this list is plenty of very
 knowledgeable colleagues, I'm tempted to ask...
 
 I need to cool several resistive loads, in the order of 5kW, and I plan to
 use a cold plate and a liquid-to-liquid heat exchanger like the Lytron
 LCS-20, but this unit is quite big, and an overkill (it has 20kW
 capability).
 
 If someone could suggest me a smaller liquid-to-liquid heat exchanger, and
 preferably a rack mount unit (and share any experience), it would be most
 welcome.
 
 Since this has not too much to do with time and frequency, please answer
 off list.
 
 Thank you very much! Best regards,
 
 Javier
 
 
 
 __**_
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/**
 mailman/listinfo/time-nutshttps://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.
 
 
 
 -- 
 
 Tom Harris celephi...@gmail.com
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] OT question about liquid cooling

2012-10-03 Thread J. Forster
It actually takes supprisingly little water flow to dissipate 5 kW.

Very roughly 5 kW = 1250 cal/sec  (4.18 J/cal)

so, for a 1 C degree = 1.25 liters/sec

at 50C degrees = 25 mL / sec. = 1.5 L/min.

-John

==


 BWIWY (back when I was young) we needed a dummy load for a supercomputer
 (think Cray YMP size) that drew many many kw.

 Our test load was about 250' of 3/4 copper tubing coiled at about 12 dia
 and 1 spacing. The load was varied by changing where the + and - leads
 were bolted onto the coil with u bolts.

 The whole mess was cooled by running water through it. A hose barb on the
 input connected up to the cold water supply and the output was run into a
 drain. You had too little resistance dialed in when all thy came out the
 output end was steam. :)

 Anyway such a test load could be replicated using 1/4 ice machine copper
 tubing available at the hardware store, some hose clamps, and or hose
 barbs.

 Bob

 On Oct 3, 2012, at 19:35, Tom Harris celephi...@gmail.com wrote:

 My day job is large industrial power supplies. The test racks have large
 resistive loads with big fans exhausting to the outside. Cheap  simple.
 Safety is by several strings of temperature cutouts wired in series. We
 usually get work experience students in to wire them up.

 Tip: to make a funny valued power resistor, just get the next value up
 and
 wrap some nichrome wire around it to bring it down to the correct value.

 I met an engineer who made a battery charger for one of our submarines.
 This was tested by putting the load bank in a dumpmaster, and keeping it
 filled up with water using a firehose!

 On 4 October 2012 02:01, Javier Herrero jherr...@hvsistemas.es wrote:

 Hello all,

 Please excuse me for the OT, but since this list is plenty of very
 knowledgeable colleagues, I'm tempted to ask...

 I need to cool several resistive loads, in the order of 5kW, and I plan
 to
 use a cold plate and a liquid-to-liquid heat exchanger like the Lytron
 LCS-20, but this unit is quite big, and an overkill (it has 20kW
 capability).

 If someone could suggest me a smaller liquid-to-liquid heat exchanger,
 and
 preferably a rack mount unit (and share any experience), it would be
 most
 welcome.

 Since this has not too much to do with time and frequency, please
 answer
 off list.

 Thank you very much! Best regards,

 Javier



 __**_
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/**
 mailman/listinfo/time-nutshttps://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.



 --

 Tom Harris celephi...@gmail.com
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] OT question about liquid cooling

2012-10-03 Thread Tom Miller

If you let the water boil, it takes even (much) less.

Tom

- Original Message - 
From: J. Forster j...@quikus.com
To: Discussion of precise time and frequency measurement 
time-nuts@febo.com

Sent: Wednesday, October 03, 2012 8:14 PM
Subject: Re: [time-nuts] OT question about liquid cooling


It actually takes supprisingly little water flow to dissipate 5 kW.

Very roughly 5 kW = 1250 cal/sec  (4.18 J/cal)

so, for a 1 C degree = 1.25 liters/sec

at 50C degrees = 25 mL / sec. = 1.5 L/min.

-John

==



BWIWY (back when I was young) we needed a dummy load for a supercomputer
(think Cray YMP size) that drew many many kw.

Our test load was about 250' of 3/4 copper tubing coiled at about 12 dia
and 1 spacing. The load was varied by changing where the + and - leads
were bolted onto the coil with u bolts.

The whole mess was cooled by running water through it. A hose barb on the
input connected up to the cold water supply and the output was run into a
drain. You had too little resistance dialed in when all thy came out the
output end was steam. :)

Anyway such a test load could be replicated using 1/4 ice machine copper
tubing available at the hardware store, some hose clamps, and or hose
barbs.

Bob

On Oct 3, 2012, at 19:35, Tom Harris celephi...@gmail.com wrote:


My day job is large industrial power supplies. The test racks have large
resistive loads with big fans exhausting to the outside. Cheap  simple.
Safety is by several strings of temperature cutouts wired in series. We
usually get work experience students in to wire them up.

Tip: to make a funny valued power resistor, just get the next value up
and
wrap some nichrome wire around it to bring it down to the correct value.

I met an engineer who made a battery charger for one of our submarines.
This was tested by putting the load bank in a dumpmaster, and keeping it
filled up with water using a firehose!

On 4 October 2012 02:01, Javier Herrero jherr...@hvsistemas.es wrote:


Hello all,

Please excuse me for the OT, but since this list is plenty of very
knowledgeable colleagues, I'm tempted to ask...

I need to cool several resistive loads, in the order of 5kW, and I plan
to
use a cold plate and a liquid-to-liquid heat exchanger like the Lytron
LCS-20, but this unit is quite big, and an overkill (it has 20kW
capability).

If someone could suggest me a smaller liquid-to-liquid heat exchanger,
and
preferably a rack mount unit (and share any experience), it would be
most
welcome.

Since this has not too much to do with time and frequency, please
answer
off list.

Thank you very much! Best regards,

Javier



__**_
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/**
mailman/listinfo/time-nutshttps://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.




--

Tom Harris celephi...@gmail.com
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.






___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to 
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts

and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] OT question about liquid cooling

2012-10-03 Thread Peter Gottlieb
Perhaps, but unless you plan on just draining the water, you need a liquid to 
air heat exchanger (LAHE) to cool the water in your loop. Perhaps for a lab it's 
no big deal, but if you intend to operate where it can get cold (needing glycol) 
or where there is very limited water supply (remote locations) this matters.


I'm installing a 96.5% efficient 9 MVA inverter right now and it needs a minimum 
of 65 GPM through the LAHE of a 40% glycol solution (glycol moves less heat than 
water).  The heat exchanger is *substantial*, much larger than the items + cold 
plates it's keeping cool.



On 10/3/2012 8:14 PM, J. Forster wrote:

It actually takes supprisingly little water flow to dissipate 5 kW.

Very roughly 5 kW = 1250 cal/sec  (4.18 J/cal)

so, for a 1 C degree = 1.25 liters/sec

at 50C degrees = 25 mL / sec. = 1.5 L/min.

-John

==



BWIWY (back when I was young) we needed a dummy load for a supercomputer
(think Cray YMP size) that drew many many kw.

Our test load was about 250' of 3/4 copper tubing coiled at about 12 dia
and 1 spacing. The load was varied by changing where the + and - leads
were bolted onto the coil with u bolts.

The whole mess was cooled by running water through it. A hose barb on the
input connected up to the cold water supply and the output was run into a
drain. You had too little resistance dialed in when all thy came out the
output end was steam. :)

Anyway such a test load could be replicated using 1/4 ice machine copper
tubing available at the hardware store, some hose clamps, and or hose
barbs.

Bob

On Oct 3, 2012, at 19:35, Tom Harris celephi...@gmail.com wrote:


My day job is large industrial power supplies. The test racks have large
resistive loads with big fans exhausting to the outside. Cheap  simple.
Safety is by several strings of temperature cutouts wired in series. We
usually get work experience students in to wire them up.

Tip: to make a funny valued power resistor, just get the next value up
and
wrap some nichrome wire around it to bring it down to the correct value.

I met an engineer who made a battery charger for one of our submarines.
This was tested by putting the load bank in a dumpmaster, and keeping it
filled up with water using a firehose!

On 4 October 2012 02:01, Javier Herrero jherr...@hvsistemas.es wrote:


Hello all,

Please excuse me for the OT, but since this list is plenty of very
knowledgeable colleagues, I'm tempted to ask...

I need to cool several resistive loads, in the order of 5kW, and I plan
to
use a cold plate and a liquid-to-liquid heat exchanger like the Lytron
LCS-20, but this unit is quite big, and an overkill (it has 20kW
capability).

If someone could suggest me a smaller liquid-to-liquid heat exchanger,
and
preferably a rack mount unit (and share any experience), it would be
most
welcome.

Since this has not too much to do with time and frequency, please
answer
off list.

Thank you very much! Best regards,

Javier



__**_
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/**
mailman/listinfo/time-nutshttps://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.



--

Tom Harris celephi...@gmail.com
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1427 / Virus Database: 2441/5308 - Release Date: 10/03/12





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] OT question about liquid cooling

2012-10-03 Thread J. Forster
9 MVA is somewhat bigger than 5 kW.

I was assuming fairly short duration tests, perhaps a few hours, where
open-cycle water is practical.

If you are going to use a water loop, getting rid of the heat is certainly
an issue.

-John

==

 Perhaps, but unless you plan on just draining the water, you need a liquid
 to
 air heat exchanger (LAHE) to cool the water in your loop. Perhaps for a
 lab it's
 no big deal, but if you intend to operate where it can get cold (needing
 glycol)
 or where there is very limited water supply (remote locations) this
 matters.

 I'm installing a 96.5% efficient 9 MVA inverter right now and it needs a
 minimum
 of 65 GPM through the LAHE of a 40% glycol solution (glycol moves less
 heat than
 water).  The heat exchanger is *substantial*, much larger than the items +
 cold
 plates it's keeping cool.


 On 10/3/2012 8:14 PM, J. Forster wrote:
 It actually takes supprisingly little water flow to dissipate 5 kW.

 Very roughly 5 kW = 1250 cal/sec  (4.18 J/cal)

 so, for a 1 C degree = 1.25 liters/sec

 at 50C degrees = 25 mL / sec. = 1.5 L/min.

 -John

 ==


 BWIWY (back when I was young) we needed a dummy load for a
 supercomputer
 (think Cray YMP size) that drew many many kw.

 Our test load was about 250' of 3/4 copper tubing coiled at about 12
 dia
 and 1 spacing. The load was varied by changing where the + and - leads
 were bolted onto the coil with u bolts.

 The whole mess was cooled by running water through it. A hose barb on
 the
 input connected up to the cold water supply and the output was run into
 a
 drain. You had too little resistance dialed in when all thy came out
 the
 output end was steam. :)

 Anyway such a test load could be replicated using 1/4 ice machine
 copper
 tubing available at the hardware store, some hose clamps, and or hose
 barbs.

 Bob

 On Oct 3, 2012, at 19:35, Tom Harris celephi...@gmail.com wrote:

 My day job is large industrial power supplies. The test racks have
 large
 resistive loads with big fans exhausting to the outside. Cheap 
 simple.
 Safety is by several strings of temperature cutouts wired in series.
 We
 usually get work experience students in to wire them up.

 Tip: to make a funny valued power resistor, just get the next value up
 and
 wrap some nichrome wire around it to bring it down to the correct
 value.

 I met an engineer who made a battery charger for one of our
 submarines.
 This was tested by putting the load bank in a dumpmaster, and keeping
 it
 filled up with water using a firehose!

 On 4 October 2012 02:01, Javier Herrero jherr...@hvsistemas.es
 wrote:

 Hello all,

 Please excuse me for the OT, but since this list is plenty of very
 knowledgeable colleagues, I'm tempted to ask...

 I need to cool several resistive loads, in the order of 5kW, and I
 plan
 to
 use a cold plate and a liquid-to-liquid heat exchanger like the
 Lytron
 LCS-20, but this unit is quite big, and an overkill (it has 20kW
 capability).

 If someone could suggest me a smaller liquid-to-liquid heat
 exchanger,
 and
 preferably a rack mount unit (and share any experience), it would be
 most
 welcome.

 Since this has not too much to do with time and frequency, please
 answer
 off list.

 Thank you very much! Best regards,

 Javier



 __**_
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/**
 mailman/listinfo/time-nutshttps://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.


 --

 Tom Harris celephi...@gmail.com
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.




 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.


 -
 No virus found in this message.
 Checked by AVG - www.avg.com
 Version: 10.0.1427 / Virus Database: 2441/5308 - Release Date: 10/03/12




 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] OT question about liquid cooling

2012-10-03 Thread J. Forster
And the heat transfer to the fluid s better too. However, boiling has it's
own serious issues.

-John

=


 If you let the water boil, it takes even (much) less.

 Tom

 - Original Message -
 From: J. Forster j...@quikus.com
 To: Discussion of precise time and frequency measurement
 time-nuts@febo.com
 Sent: Wednesday, October 03, 2012 8:14 PM
 Subject: Re: [time-nuts] OT question about liquid cooling


 It actually takes supprisingly little water flow to dissipate 5 kW.

 Very roughly 5 kW = 1250 cal/sec  (4.18 J/cal)

 so, for a 1 C degree = 1.25 liters/sec

 at 50C degrees = 25 mL / sec. = 1.5 L/min.

 -John

 ==


 BWIWY (back when I was young) we needed a dummy load for a supercomputer
 (think Cray YMP size) that drew many many kw.

 Our test load was about 250' of 3/4 copper tubing coiled at about 12
 dia
 and 1 spacing. The load was varied by changing where the + and - leads
 were bolted onto the coil with u bolts.

 The whole mess was cooled by running water through it. A hose barb on
 the
 input connected up to the cold water supply and the output was run into
 a
 drain. You had too little resistance dialed in when all thy came out the
 output end was steam. :)

 Anyway such a test load could be replicated using 1/4 ice machine
 copper
 tubing available at the hardware store, some hose clamps, and or hose
 barbs.

 Bob

 On Oct 3, 2012, at 19:35, Tom Harris celephi...@gmail.com wrote:

 My day job is large industrial power supplies. The test racks have
 large
 resistive loads with big fans exhausting to the outside. Cheap 
 simple.
 Safety is by several strings of temperature cutouts wired in series. We
 usually get work experience students in to wire them up.

 Tip: to make a funny valued power resistor, just get the next value up
 and
 wrap some nichrome wire around it to bring it down to the correct
 value.

 I met an engineer who made a battery charger for one of our submarines.
 This was tested by putting the load bank in a dumpmaster, and keeping
 it
 filled up with water using a firehose!

 On 4 October 2012 02:01, Javier Herrero jherr...@hvsistemas.es wrote:

 Hello all,

 Please excuse me for the OT, but since this list is plenty of very
 knowledgeable colleagues, I'm tempted to ask...

 I need to cool several resistive loads, in the order of 5kW, and I
 plan
 to
 use a cold plate and a liquid-to-liquid heat exchanger like the Lytron
 LCS-20, but this unit is quite big, and an overkill (it has 20kW
 capability).

 If someone could suggest me a smaller liquid-to-liquid heat exchanger,
 and
 preferably a rack mount unit (and share any experience), it would be
 most
 welcome.

 Since this has not too much to do with time and frequency, please
 answer
 off list.

 Thank you very much! Best regards,

 Javier



 __**_
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/**
 mailman/listinfo/time-nutshttps://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.



 --

 Tom Harris celephi...@gmail.com
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.





 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.





___