Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-18 Thread Dave M

Chris Albertson wrote:

On Thu, Oct 16, 2014 at 7:51 PM, Dave M dgmin...@mediacombb.net
wrote:


Thanks, Chris.
I've done a bit or research on the subject, and think I have a
reasonable grip on the necessary steps.  I have an 8' ground rod
driven into the ground directly under the spot where my antennas
mount.  #6 solid copper from the rod to a heavy aluminum plate,
where the arrestors will be mounted.  A #6 solid copper wire from
the plate to the antenna mounting structure.



About the only thing you left out is the interconnection between this
new ground rod and the existing house ground.

Sounds like you must live in Florida.  The best source of information
is the lightening lab at University of FL.

I've never read a good research backed paper on plastic v. metal
conduit. I bet it does matter.  I use iron pipe outdoors then after
it gets indoors switch to plastic.  Practical reasons.  The flexible
plastic conduit is just easier to use


Actually, I lived in Florida for about 40 years, retiring to north Alabama 
about 5 years ago.  about 6 of those years were spent working at a Motorola 
2-way radio shop.  So, yes, I'm pretty familiar with the damages that 
lightning can cause, and some of the precautions that help minimize 
susceptability and damage.


As I posted earlier, I've seen writings promoting metallic and non-metallic 
conduit for the antenna coax.  I can see reasons for placing the coax in 
metallic conduit.  But, one thing that I've read that is consistent, is NOT 
to run the earth ground wire in metallic conduit.  That's to keep the 
current to ground in a solid, unbroken path, which the fittings used to join 
conduit can't provide.  OK to run it in non-metallic conduit to keep it out 
of the weather.  Since my coax run is only about 20 ft, I'm thinking that I 
should be OK with the coax in 1/2 galvanized steel conduit. I agree that 
the metallic conduit should stay outside, and not be connected to the 
equipment ground inside.  I'll run a separate ground wire from the equipment 
rack to the ground rod outside.


Cheers,
Dave M


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-18 Thread Bill Hawkins
FWIW, when grounding the metal mast of a boat, three inch wide copper
strap is used because it is a better RF conductor. The strap is
available
in marine supply stores.

You really don't want lightning punching one or more holes in your boat,
so whatever hits the mast (usually the full stroke, not a side shoot)
gets directed directly to the keel.

IIRC, gas discharge tubes take some time to ignite, so something faster
is required to take the initial current.

Bill Hawkins


-Original Message-
From: time-nuts [mailto:time-nuts-boun...@febo.com] On Behalf Of Dave M
Sent: Saturday, October 18, 2014 12:48 PM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] Lightning arrestors for GPSDO antenna

Chris Albertson wrote:
 On Thu, Oct 16, 2014 at 7:51 PM, Dave M dgmin...@mediacombb.net
 wrote:

 Thanks, Chris.
 I've done a bit or research on the subject, and think I have a 
 reasonable grip on the necessary steps.  I have an 8' ground rod 
 driven into the ground directly under the spot where my antennas 
 mount.  #6 solid copper from the rod to a heavy aluminum plate, where

 the arrestors will be mounted.  A #6 solid copper wire from the plate

 to the antenna mounting structure.


 About the only thing you left out is the interconnection between this 
 new ground rod and the existing house ground.

 Sounds like you must live in Florida.  The best source of information 
 is the lightening lab at University of FL.

 I've never read a good research backed paper on plastic v. metal 
 conduit. I bet it does matter.  I use iron pipe outdoors then after it

 gets indoors switch to plastic.  Practical reasons.  The flexible 
 plastic conduit is just easier to use

Actually, I lived in Florida for about 40 years, retiring to north
Alabama about 5 years ago.  about 6 of those years were spent working at
a Motorola 2-way radio shop.  So, yes, I'm pretty familiar with the
damages that lightning can cause, and some of the precautions that help
minimize susceptability and damage.

As I posted earlier, I've seen writings promoting metallic and
non-metallic conduit for the antenna coax.  I can see reasons for
placing the coax in metallic conduit.  But, one thing that I've read
that is consistent, is NOT to run the earth ground wire in metallic
conduit.  That's to keep the current to ground in a solid, unbroken
path, which the fittings used to join conduit can't provide.  OK to run
it in non-metallic conduit to keep it out of the weather.  Since my coax
run is only about 20 ft, I'm thinking that I should be OK with the coax
in 1/2 galvanized steel conduit. I agree that the metallic conduit
should stay outside, and not be connected to the equipment ground
inside.  I'll run a separate ground wire from the equipment rack to the
ground rod outside.

Cheers,
Dave M


___
time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-18 Thread Jim Lux

On 10/18/14, 2:05 PM, Bill Hawkins wrote:

FWIW, when grounding the metal mast of a boat, three inch wide copper
strap is used because it is a better RF conductor. The strap is
available
in marine supply stores.


It's actually more about being convenient to install, and tradition.

If you have a 1 square centimeter conductor at 1x1 cm, the inductance is 
about 1.5 uH/meter, and when it's 10cmx 1mm (4 wide) the inductance is 
1.15 uH/meter.  That's not a big difference in the voltage due to a 
transient.


What does go down dramatically (at frequencies where the skin effect 
thickness is small) is the AC resistance, which will be 0.2 for the 
10x0.1 (20cm perimeter) relative to the 1x1 bar (4 cm perimeter).
Skin depth in copper at 1 MHz is about 0.06mm.  so the bar has a 
effective RF cross-section of 2.4 square mm, for a AC resistance of 
about 7 milliOhm/meter.


However, for lightning, with rise times in the microsecond range (e.g. 
MHz kind of frequency), the voltage due to inductance is huge (1 
uH/meter * 10 kA/microsecond = 10kV/meter) compared to the voltage due 
to resistance (10kA*7mOhm/m = 70V/meter)




Now, if that strap is part of an RF ground for your transmitting 
antenna, then the lower resistance of the strap is a good thing. 
Inductance is lossless, but AC resistance sure isn't.



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-18 Thread Dave M

John Allen wrote:

Hello All - There is a 500+ page document on grounding, lightning
protection and more - Google for: 


STANDARDS AND GUIDELINES FOR COMMUNICATION SITES Motorola R56 2005

Regards, John  K1AE




Great document!  Thanks for the link
Dave M

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-17 Thread George Dubovsky
If anyone is interested, I have a few NOS Zap-Tech 30-105 (now called CX-TF
apparently) surge suppressors available. These are basically a single shunt
gas tube (the coaxial center conductor runs through the center of a custom
gas tube), and they were sold as GPS in-line suppressors. I use them at the
far end of the rf spectrum: all of my receive-only wire antennas
(Beverages) for 1.8-7 MHz have one on each feedline where they enter the
house. These antennas are up to 800' long, and I know for a fact they pick
up surges from every passing storm and, so far, the elephants have stayed
away... ;-)

These units have TNC female adapters on both ends, but if the TNCs are
screwed off (they are loc-tite'd on), there are F-female connectors
underneath. $20 will get one mailed in the US.

73,

geo - n4ua

On Fri, Oct 17, 2014 at 1:23 AM, ed breya e...@telight.com wrote:

 Of all device types, I think gas tubes are the best for this sort of
 application - very low C, and high surge current rating. I'm picturing the
 kind that are used in power supplies and such for limiting line transients
 - about 1 cm dia and length with axial leads. I don't know what kind are
 used in lightning arrestors, if they are the same or scaled up in size.

 Whether you make it able to take a direct hit depends on how big of a hit,
 your budget, and the environment of the antenna and lines. If it's the
 tallest thing in a huge field in a lightning-prone area, then it could be a
 big issue, but I don't think most people have that situation.

 You may want to look at the US National Electrical Code (NEC) for ideas -
 I believe that subject is covered there. The main thing there would be
 safety against injuries and fire, even if the equipment is destroyed.

 I think what you would want is kind of a pi network - the lowest impedance
 path to ground at the antenna zone that can be practically realized, then a
 high common-mode impedance (or even fusible) line to carry the signal to
 the building, then another low impedance path to ground at the building.
 This means that in my opinion, you should not put the feedline in metal
 conduit unless it's essential for protection - or underground, which should
 improve the grounding. You want the antenna zone to absorb the brunt of any
 discharge, then use the higher line Zcm to hopefully give some degree of
 isolation from there to the building.

 Ed


 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/
 mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-17 Thread John C. Westmoreland, P.E.
Hello Dave,

I think we had a similar question recently - and I have been told the
PolyPhaser products are gas tubes - I haven't opened one up yet.
TESSCO sells these online - you can find them here:
https://www.tessco.com/products/displayProducts.do?groupId=90143subgroupId=91046

Regards,
John W.


On Thu, Oct 16, 2014 at 10:23 PM, ed breya e...@telight.com wrote:

 Of all device types, I think gas tubes are the best for this sort of
 application - very low C, and high surge current rating. I'm picturing the
 kind that are used in power supplies and such for limiting line transients
 - about 1 cm dia and length with axial leads. I don't know what kind are
 used in lightning arrestors, if they are the same or scaled up in size.

 Whether you make it able to take a direct hit depends on how big of a hit,
 your budget, and the environment of the antenna and lines. If it's the
 tallest thing in a huge field in a lightning-prone area, then it could be a
 big issue, but I don't think most people have that situation.

 You may want to look at the US National Electrical Code (NEC) for ideas -
 I believe that subject is covered there. The main thing there would be
 safety against injuries and fire, even if the equipment is destroyed.

 I think what you would want is kind of a pi network - the lowest impedance
 path to ground at the antenna zone that can be practically realized, then a
 high common-mode impedance (or even fusible) line to carry the signal to
 the building, then another low impedance path to ground at the building.
 This means that in my opinion, you should not put the feedline in metal
 conduit unless it's essential for protection - or underground, which should
 improve the grounding. You want the antenna zone to absorb the brunt of any
 discharge, then use the higher line Zcm to hopefully give some degree of
 isolation from there to the building.

 Ed


 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/
 mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-17 Thread Chris Albertson
On Thu, Oct 16, 2014 at 7:51 PM, Dave M dgmin...@mediacombb.net wrote:

 Thanks, Chris.
 I've done a bit or research on the subject, and think I have a reasonable
 grip on the necessary steps.  I have an 8' ground rod driven into the
 ground directly under the spot where my antennas mount.  #6 solid copper
 from the rod to a heavy aluminum plate, where the arrestors will be
 mounted.  A #6 solid copper wire from the plate to the antenna mounting
 structure.


About the only thing you left out is the interconnection between this new
ground rod and the existing house ground.

Sounds like you must live in Florida.  The best source of information is
the lightening lab at University of FL.

I've never read a good research backed paper on plastic v. metal conduit.
I bet it does matter.  I use iron pipe outdoors then after it gets indoors
switch to plastic.  Practical reasons.  The flexible plastic conduit is
just easier to use

-- 

Chris Albertson
Redondo Beach, California
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-17 Thread Jim Lux

On 10/17/14, 6:26 AM, Chris Albertson wrote:

On Thu, Oct 16, 2014 at 7:51 PM, Dave M dgmin...@mediacombb.net wrote:


Thanks, Chris.
I've done a bit or research on the subject, and think I have a reasonable
grip on the necessary steps.  I have an 8' ground rod driven into the
ground directly under the spot where my antennas mount.  #6 solid copper
from the rod to a heavy aluminum plate, where the arrestors will be
mounted.  A #6 solid copper wire from the plate to the antenna mounting
structure.



About the only thing you left out is the interconnection between this new
ground rod and the existing house ground.

Sounds like you must live in Florida.  The best source of information is
the lightening lab at University of FL.

I've never read a good research backed paper on plastic v. metal conduit.


You can use metal conduit as the bonding conductor between grounding 
systems, for one thing.



I bet it does matter.  I use iron pipe outdoors then after it gets indoors
switch to plastic.  Practical reasons.  The flexible plastic conduit is
just easier to use



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-17 Thread Chris Albertson
 You can use metal conduit as the bonding conductor between grounding
 systems, for one thing.


That works fine, but I think it is disallowed  by the electrical code.   If
you used metallic conduit it MUST be grounded but you can't use it for
grounding.  That said, it does work.   I think the danger the electric code
addresses is that connections between conduit sections become loose over
time and might corrode.

I think the threaded conduit would work fine.  That stuff is like water
pipe but smoother inside.

-- 

Chris Albertson
Redondo Beach, California
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-17 Thread Martin A Flynn

Dave,
We have a 26 dB Lucent  (TMG-HR-26NCM) antenna mounted on the gable end 
of the N2MO station.  The feed line (1/2 superflex) runs straight down 
to a watertight steel box with a Polyphaser GPS protector.   The 
superflex shield is tied to the ground with the standard Andrew kit.


Both the antenna mounting pipe and protector have a #2 grounding wire to 
an 8' rod.   When the ring ground is replaced we will weld it to 
existing rod from two directions.


I can prove links to pictures if it helps.

Martin Flynn

.



 26dB
On Thu, Oct 16, 2014 at 4:34 PM, Dave M dgmin...@mediacombb.net wrote:

I'm looking for effective coaxial lightning arrestors for my GPSDO
antennas.
I've seen several types; those completely enclosed in a one-piece metal
enclosure (no replaceable components) and those having a replaceable gas
discharge tube seem to predominate the list.
I'm looking closely at the gas discharge tube types, and am curious as to
their effectiveness and durability.  I'd like to know stuff like; are they
effective in dissipating a static charge, how do I know when the gas tube
needs to be replaced, are the gas tubes of a special type, are replacement
gas tube easily available, etc.

I'm interested in opinions and experiences with arrestors and
recommendations for which type is most effective.

Thanks for comments,
Dave M
_


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-17 Thread Jim Lux

On 10/17/14, 8:17 AM, Chris Albertson wrote:

You can use metal conduit as the bonding conductor between grounding
systems, for one thing.



That works fine, but I think it is disallowed  by the electrical code.   If
you used metallic conduit it MUST be grounded but you can't use it for
grounding.  That said, it does work.   I think the danger the electric code
addresses is that connections between conduit sections become loose over
time and might corrode.


The metallic raceway (code speak for conduit) is allowed to be the 
bonding conductor  (bonding conductor = greenwire or electrical 
safety ground in code speak).  Properly installed conduit will have a 
good connection, etc..




When interconnecting multiple grounding electrodes or electrode systems 
is where the requirements for particular gauges of wire come in, and 
mostly it has to do with mechanical strength and reliability.  You can 
use a smaller conductor if it is protected inside something, for 
instance. The other rule is that the bonding conductor has to be 
continuous (the concern you mentioned about connections becoming loose, 
etc).


http://lightning.org/wp-content/uploads/2013/04/Bonding-2013-ULPA-LPI-rev1.pdf 


is a very nice summary

Mike Holt (http://www.mikeholt.com/) has a great website on all code 
related issues, and he's written a bunch of articles that explain the 
code and the rationale behind the requirements.

http://ecmweb.com/code-basics/grounding-and-bonding-part-1-3



And when it comes to antennas and the like, you're in a different 
section of the code 810, 820, and the requirements for the grounding 
conductor (and whether coax shield can be that grounding conductor) are 
all laid out there.


In many case, the coax shield can serve as the grounding conductor, but 
only if there are no connectors in the path (i.e. you have to have a 
clamp that directly contacts the shield where it interconnects with the 
building grounding system).  A barrel feedthrough in a grounded metal 
panel doesn't meet the strict requirements of the code (although 
personally, I think it's a fine solution)


One thing to remember about the NEC requirements is that the threat 
they are protecting against with the grounding and bonding requirements 
is NOT a lightning strike.  It's contact with an energized conductor 
(e.g. a power line touches your antenna or supporting structure). 
That's a whole lot more common (wind storms, etc.)  NFPA 780 is the 
lightning protection code, and has a lot more lightning protection 
aspects.


The NEC cares almost nothing about transient protection, the concern is 
more about electrical shocks and burning the building down. 
Furthermore, the NEC really only regulates the wiring in your building, 
and nothing that is connected to it, nor does it regulate the wiring of 
the power company.


There are two tomes of reference I use for transient protection: one is 
IEEE 1100 (the Emerald Book) which has gone under many names over the 
years (politics.. computer manufacturers did not want their equipment 
described as sensitive electronic equipment)

http://standards.ieee.org/findstds/standard/1100-2005.html

The other is Protection of Electronic Circuits from Overvoltages by 
R.B. Standler.

http://www.amazon.com/gp/search?index=bookslinkCode=qskeywords=9780486425528
http://store.doverpublications.com/0486425525.html

And, if you're at the Dover Pubs store.. take a look at the books about 
lightning from Martin Uman.  Very readable, lots of technical info.






I think the threaded conduit would work fine.  That stuff is like water
pipe but smoother inside.



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-17 Thread John Allen
Hello All - There is a 500+ page document on grounding, lightning protection 
and more - Google for:

STANDARDS AND GUIDELINES FOR COMMUNICATION SITES Motorola R56 2005

Regards, John  K1AE


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-17 Thread Jim Sanford

All:
Some very good information here.

I use NFPA codes in my day job.

JUST YESTERDAY, I learned that you can read their standards for free.  
Go to their site, and you'll see a link for free access to any of their 
standards.  You can't save or print, but you can read. You will have to 
create an account, but they don't demand anything that isn't already public.


73,
Jim
wb4...@amsat.org

On 10/17/2014 12:11 PM, Jim Lux wrote:

On 10/17/14, 8:17 AM, Chris Albertson wrote:

You can use metal conduit as the bonding conductor between grounding
systems, for one thing.



That works fine, but I think it is disallowed  by the electrical 
code.   If

you used metallic conduit it MUST be grounded but you can't use it for
grounding.  That said, it does work.   I think the danger the 
electric code

addresses is that connections between conduit sections become loose over
time and might corrode.


The metallic raceway (code speak for conduit) is allowed to be the 
bonding conductor  (bonding conductor = greenwire or electrical 
safety ground in code speak).  Properly installed conduit will have a 
good connection, etc..




When interconnecting multiple grounding electrodes or electrode 
systems is where the requirements for particular gauges of wire come 
in, and mostly it has to do with mechanical strength and reliability.  
You can use a smaller conductor if it is protected inside something, 
for instance. The other rule is that the bonding conductor has to be 
continuous (the concern you mentioned about connections becoming 
loose, etc).


http://lightning.org/wp-content/uploads/2013/04/Bonding-2013-ULPA-LPI-rev1.pdf 


is a very nice summary

Mike Holt (http://www.mikeholt.com/) has a great website on all code 
related issues, and he's written a bunch of articles that explain the 
code and the rationale behind the requirements.

http://ecmweb.com/code-basics/grounding-and-bonding-part-1-3



And when it comes to antennas and the like, you're in a different 
section of the code 810, 820, and the requirements for the grounding 
conductor (and whether coax shield can be that grounding conductor) 
are all laid out there.


In many case, the coax shield can serve as the grounding conductor, 
but only if there are no connectors in the path (i.e. you have to have 
a clamp that directly contacts the shield where it interconnects with 
the building grounding system).  A barrel feedthrough in a grounded 
metal panel doesn't meet the strict requirements of the code (although 
personally, I think it's a fine solution)


One thing to remember about the NEC requirements is that the threat 
they are protecting against with the grounding and bonding 
requirements is NOT a lightning strike.  It's contact with an 
energized conductor (e.g. a power line touches your antenna or 
supporting structure). That's a whole lot more common (wind storms, 
etc.)  NFPA 780 is the lightning protection code, and has a lot more 
lightning protection aspects.


The NEC cares almost nothing about transient protection, the concern 
is more about electrical shocks and burning the building down. 
Furthermore, the NEC really only regulates the wiring in your 
building, and nothing that is connected to it, nor does it regulate 
the wiring of the power company.


There are two tomes of reference I use for transient protection: one 
is IEEE 1100 (the Emerald Book) which has gone under many names over 
the years (politics.. computer manufacturers did not want their 
equipment described as sensitive electronic equipment)

http://standards.ieee.org/findstds/standard/1100-2005.html

The other is Protection of Electronic Circuits from Overvoltages by 
R.B. Standler.
http://www.amazon.com/gp/search?index=bookslinkCode=qskeywords=9780486425528 


http://store.doverpublications.com/0486425525.html

And, if you're at the Dover Pubs store.. take a look at the books 
about lightning from Martin Uman.  Very readable, lots of technical info.






I think the threaded conduit would work fine.  That stuff is like water
pipe but smoother inside.



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to 
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts

and follow the instructions there.




---
This email is free from viruses and malware because avast! Antivirus protection 
is active.
http://www.avast.com

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-16 Thread Bob Camp
Hi

There are a number of them on the auction sites. They are fairly specific in 
terms of frequency band and application.

Bob

 On Oct 16, 2014, at 7:34 PM, Dave M dgmin...@mediacombb.net wrote:
 
 I'm looking for effective coaxial lightning arrestors for my GPSDO antennas.
 I've seen several types; those completely enclosed in a one-piece metal 
 enclosure (no replaceable components) and those having a replaceable gas 
 discharge tube seem to predominate the list.
 I'm looking closely at the gas discharge tube types, and am curious as to 
 their effectiveness and durability.  I'd like to know stuff like; are they 
 effective in dissipating a static charge, how do I know when the gas tube 
 needs to be replaced, are the gas tubes of a special type, are replacement 
 gas tube easily available, etc.
 
 I'm interested in opinions and experiences with arrestors and 
 recommendations for which type is most effective.
 
 Thanks for comments,
 Dave M 
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-16 Thread Chris Albertson
Lightening arrestors are an important part of a protection system but just
installing some in the antenna cable is not going to help so much.  You
need a system approach.  If you do it right you can take a direct hit

The big problem with grounding is Ohm's Law.  That is if any current flows
in a conductor that has resistance there will be a voltage across the
conductor equal to the current times the resistance.  But with lightening
you can have 100,000 amps of current in a ground wire.  If that wires has
0.01 ohms of resistance you have 1,000 volts above true ground on your
ground connector on the lightening arrestor.  Your ground is no longer at
ground.

You need some very tiny resistances and to get that you are going to need
to do things like using multiple ground rods and large conductors.  And
connecting grounds together.

On Thu, Oct 16, 2014 at 4:34 PM, Dave M dgmin...@mediacombb.net wrote:

 I'm looking for effective coaxial lightning arrestors for my GPSDO
 antennas.
 I've seen several types; those completely enclosed in a one-piece metal
 enclosure (no replaceable components) and those having a replaceable gas
 discharge tube seem to predominate the list.
 I'm looking closely at the gas discharge tube types, and am curious as to
 their effectiveness and durability.  I'd like to know stuff like; are they
 effective in dissipating a static charge, how do I know when the gas tube
 needs to be replaced, are the gas tubes of a special type, are replacement
 gas tube easily available, etc.

 I'm interested in opinions and experiences with arrestors and
 recommendations for which type is most effective.

 Thanks for comments,
 Dave M
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.




-- 

Chris Albertson
Redondo Beach, California
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-16 Thread Dave M

Thanks, Chris.
I've done a bit or research on the subject, and think I have a reasonable 
grip on the necessary steps.  I have an 8' ground rod driven into the ground 
directly under the spot where my antennas mount.  #6 solid copper from the 
rod to a heavy aluminum plate, where the arrestors will be mounted.  A #6 
solid copper wire from the plate to the antenna mounting structure.
I will also have an arrestor at the antenna input of each GPSDO unit, which 
will be mounted on a 2 wide copper strap, which will be then run to the 
outside ground rod with a doubled 1 wide copper braid.
I realize that extremely low ground resistance is fantastic, but I don't 
have access to a ground resistance set, so I'll have to accept what I have 
and accept the consequences if something happens.  A second ground rod isn't 
out of the question, but will have to wait until my broken wrist heals so I 
can swing a sledge hammer.


I'd still like to hear comments on the effectiveness of gas discharge type 
arrestors.


A question has bothered me for a while, but can't find a definitive answer. 
Should I enclose the antenna feedline in metal conduit or nonmetal conduit? 
I've seen documents that state that metal conduit is the best way, and 
others stating that metal conduit shouldn't be used Anyone have a good 
answer  (talking about antenna feedline; not the grounding wire)?


Thanks,
Dave M

---

Chris Albertson wrote:

Lightening arrestors are an important part of a protection system but
just installing some in the antenna cable is not going to help so
much.  You need a system approach.  If you do it right you can take a
direct hit

The big problem with grounding is Ohm's Law.  That is if any current
flows in a conductor that has resistance there will be a voltage
across the conductor equal to the current times the resistance.  But
with lightening you can have 100,000 amps of current in a ground
wire.  If that wires has
0.01 ohms of resistance you have 1,000 volts above true ground on your
ground connector on the lightening arrestor.  Your ground is no
longer at ground.

You need some very tiny resistances and to get that you are going to
need to do things like using multiple ground rods and large
conductors.  And connecting grounds together.

On Thu, Oct 16, 2014 at 4:34 PM, Dave M dgmin...@mediacombb.net
wrote:


I'm looking for effective coaxial lightning arrestors for my GPSDO
antennas.
I've seen several types; those completely enclosed in a one-piece
metal enclosure (no replaceable components) and those having a
replaceable gas discharge tube seem to predominate the list.
I'm looking closely at the gas discharge tube types, and am curious
as to their effectiveness and durability.  I'd like to know stuff
like; are they effective in dissipating a static charge, how do I
know when the gas tube needs to be replaced, are the gas tubes of a
special type, are replacement gas tube easily available, etc.

I'm interested in opinions and experiences with arrestors and
recommendations for which type is most effective.

Thanks for comments,
Dave M
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


When the people fear the government, there is tyranny. When the
government fears the people, there is liberty -- Thomas Jefferson


Dave M 



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-16 Thread Jim Lux

On 10/16/14, 6:27 PM, Chris Albertson wrote:

Lightening arrestors are an important part of a protection system but just
installing some in the antenna cable is not going to help so much.  You
need a system approach.  If you do it right you can take a direct hit

The big problem with grounding is Ohm's Law.  That is if any current flows
in a conductor that has resistance there will be a voltage across the
conductor equal to the current times the resistance.  But with lightening
you can have 100,000 amps of current in a ground wire.  If that wires has
0.01 ohms of resistance you have 1,000 volts above true ground on your
ground connector on the lightening arrestor.  Your ground is no longer at
ground.



For lightning transients 1 us kind of rise times...inductance is a MUCH 
bigger deal than resistance, and inductance is very weakly dependent on 
conductors size and shape.





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-16 Thread Bill Hawkins
Years ago, I visited an installation that used a large triggered spark
gap to discharge a large bank of caps at 100 KV into the primary of an
air wound (about 8 feet in diameter) 1:10 step up pulse transformer
connected to two aluminum plates about 30 feet square separated by
several feet of water (the dielectric). At the center of the plates was
a spark gap that was used to study EMP phenomena.

There certainly was high power RF associated with the discharge, a tiny
fraction of what a lightning bolt produces.

All of the electronic measuring equipment was contained in a room-sized
double-walled copper screen Faraday cage, so that the jumping lines on
Tektronix 545 oscilloscopes didn't just show noise from the 100 KV gap
firing.

Even though grounding couldn't neutralize the effects of the pulse, the
Faraday cage isolated the contents from the fields. The next best thing
to a Faraday cage is a ground plane that has one connection to Earth
ground. And if you can't get a great metal plate, a single point for all
instrument grounds is the last best thing - if you have to have an
elevated antenna.

When I had a mast with two HP conical GPS antennas to a pair of HP
Z3801A receivers, I chose a single Earth-grounded lightning rod for the
plastic pipe mast. Nothing else connected to that ground. It was
intended to discharge local induced static electricity, not take a
direct hit. The equipment (and the antennas via the RG-8 cables) was all
connected to a common ground point connected to the house electrical
ground. The computer connections to the house network were wireless. No
lightning arrestors were used.

This system got one test when the neighbor took a direct hit to a tree
close to his house. An arc jumped to a nearby outdoor floodlight and did
considerable damage in his house. My antennas were about 100 feet away.
The one nearest the strike died, but there were no other effects. Sadly,
I was not motivated to examine the effect on the GPS receivers, although
I still have the GPSCon data here somewhere.

I gave the dead antenna to the man who bought my GPS setup (downsizing
for the next stage of old age). He later told me that he fixed the
antenna by replacing one of the amplifier chips. Sounds like EMP damage
to me, the kind no arrestor could have helped.

But I would not dissuade anyone from employing lightning arrestors, for
the peace of mind it brings -- until a direct hit occurs.
However, I'm in Minnesota with less than a tenth of the probability of a
hit in, say, Florida.

While there's not much about precision time in this posting, I hope it
was useful to those who probe the sky with antennas.

Bill Hawkins



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Lightning arrestors for GPSDO antenna

2014-10-16 Thread ed breya
Of all device types, I think gas tubes are the best for this sort of 
application - very low C, and high surge current rating. I'm 
picturing the kind that are used in power supplies and such for 
limiting line transients - about 1 cm dia and length with axial 
leads. I don't know what kind are used in lightning arrestors, if 
they are the same or scaled up in size.


Whether you make it able to take a direct hit depends on how big of a 
hit, your budget, and the environment of the antenna and lines. If 
it's the tallest thing in a huge field in a lightning-prone area, 
then it could be a big issue, but I don't think most people have that 
situation.


You may want to look at the US National Electrical Code (NEC) for 
ideas - I believe that subject is covered there. The main thing there 
would be safety against injuries and fire, even if the equipment is destroyed.


I think what you would want is kind of a pi network - the lowest 
impedance path to ground at the antenna zone that can be practically 
realized, then a high common-mode impedance (or even fusible) line to 
carry the signal to the building, then another low impedance path to 
ground at the building. This means that in my opinion, you should not 
put the feedline in metal conduit unless it's essential for 
protection - or underground, which should improve the grounding. You 
want the antenna zone to absorb the brunt of any discharge, then use 
the higher line Zcm to hopefully give some degree of isolation from 
there to the building.


Ed

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.