Anyone aware of what seems as a typo to me
in EN 60950-1:2006 in par 5.3.4
it say that clearance and creepage distances for functional isolation
must be respected for INaccessible parts ...
Whats the sense of guarding the isolation to not accessible parts
At the same time,
Hi Gert,
Remember that clause 5.3.4 deals with 'functional insulation' only.
It talks about the insulation between a SECONDARY CIRCUIT and an
'inaccessible' conductive part that is earthed for functional reasons.
There needs to be some insulation where the inaccessible conductive part is
Hi Kevin,
Thanks,
This means that for a PC (secondary GND is Earthed)
all SECONDARY circuits not GND must meet
1. functional clearance and creepage to GND as per table 2M and or
2N, or
2. withstand the 500 Vac (or higher) dielectrical test, or
3. be short circuit safe
Any country in EU who use 120VAC? I don't think so, but want to check with
you guys ..
#Amund
-
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send
Officialy not, but some old houses still have 130VAC
Best regards,
Kris Carpentier
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Amund Westin
Sent: donderdag 31 mei 2012 12:08
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: 120VAC in Europe?
Any country in EU who use 120VAC? I
110V supplied from a centre tapped to earth isolating transformer is commonly
used on construction and industrial sites in the UK.
Nick.
On 31 May 2012, at 11:07, Amund Westin wrote:
Any country in EU who use 120VAC? I don’t think so, but want to check with
you guys ….
#Amund
-
So, for CE marking, 110-120VAC should be tested in addition to 230VAC?
The EUT has a switch to choose 120VAC or 230VAC supply voltage.
#Amund
Fra: Nick Williams [mailto:nick.willi...@conformance.co.uk]
Sendt: 31. mai 2012 12:18
Til: amund
Kopi: EMC-PSTC@LISTSERV.IEEE.ORG
Emne: Re:
Only for equipment intended for the industrial/construction sites where this
voltage are used (mainly lighting and portable tools).
Nick.
On 31 May 2012, at 11:25, Amund Westin wrote:
So, for CE marking, 110-120VAC should be tested in addition to 230VAC?
The EUT has a switch to choose
Amund
Depends on Directive - Medical Devices covered by EN60601 have to have some
tests done at both voltages.
Regards
Charlie
From: Amund Westin [mailto:am...@westin-emission.no]
Sent: 31 May 2012 11:26
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] SV: 120VAC in Europe?
So, for CE marking,
Charlie
RTTE here .
EMC, radio and LVD tests will be carried out, but we have only planned to do
with EUT in 230VAC mode, since we're only doing CE mark for this EUT.
#Amund
Fra: Charlie Blackham [mailto:char...@sulisconsultants.com]
Sendt: 31. mai 2012 12:36
Til: amund;
Gert,
It would seem a motherboard is SELV circuitry and not subject to functional
spacings or a dielectric test. Or am I misunderstanding your application?
Doug
Douglas E Powell
doug...@gmail.com
http://www.linkedin.com/in/dougp01
Sent from my Verizon Wireless BlackBerry
-Original
That is what I thought first too.
But that is not true. If there are earthed
conductors on board (not GND, earthed)
connected to inaccessible part(s) (so accessible also I presume)
clearances are required to table 2N , for the best conditions
that is 0.2 mm (all ic packages comply).
This
Colleagues,
ISO TC199 Safety of Machinery is working on revisions to ISO 13849-1 and the
merger of this standard with IEC 62061. The Joint Working Group is looking for
feedback from users of these and other functional safety standards on how they
use these standards and the challenges they
And don't forget that there are still quite a lot of US military bases
around Europe where 120Vac may be available - Possibly no CE either! J
John
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Amund Westin
Sent: 31 May 2012 11:08
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject:
Hi All,
I just published a few details on an EMC troubleshooting kit I use. Part 1
provides some detail on the emission tools I use. Part 2 (to be published
later) will describe a few immunity tools. I'd appreciate any other thoughts or
ideas you might have on tools you might use for
Hi Ken,
The kit you have described is very useful for EMC road warriors. Thanks
you. You have captured and organized most every tool that an EMC engineer
needs for everyday emissions troubleshooting in this article. I have used
all these tools for troubleshooting, and plan on making a couple of
We've had an intermittent one recently during development. Running Gigabit
Ethernet across it and USB too. Otherwise it runs ok.
From: John Woodgate j...@jmwa.demon.co.uk
To: EMC-PSTC@LISTSERV.IEEE.ORG
Sent: Thursday, May 3, 2012 1:35 PM
Subject: Re: Slip
17 matches
Mail list logo