Re: [PSES] SCCR Rating Question

2024-05-14 Thread Scott Aldous
Starting on page 7, the white paper that Rich linked to also references UL 508A, supplement SB, which is a method of determining SCCR for industrial control panels without test. The method at a high level involves carrying over the SCCR rating of the "weakest link in the chain" from a protective

Re: [PSES] SCCR Rating Question

2024-05-14 Thread Richard Nute
Hi Brian: See the very last line of: https://www.mouser.com/pdfDocs/littelfuse_industrial_whitepaper_increase_sccr.pdf Best regards, Rich From: Ralph McDiarmid Sent: Tuesday, May 14, 2024 11:41 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] SCCR Rating

Re: [PSES] SCCR Rating Question

2024-05-14 Thread Ralph McDiarmid
Could this number to used to select a suitable circuit breaker and so the interrupting voltage is an important parameter? The nameplate rating on the machine should be the information an electrician needs during installation and selection of wire size and type. Ralph From: Brian

[PSES] SCCR Rating Question

2024-05-14 Thread Brian Kunde
Greetings to all. I am new to SCCR ratings on industrial machinery. The ratings I have seen sometimes has a "Maximum Voltage" included, such as; SCCR: 22kA, 600V Maximum Where does the voltage value come from? In one case, the machine had a line voltage rating of "120/208 Vac", but the SCCR