.23(a)?
Why would plug-and-cord loads be treated separately if they could be
classified as continuous or noncontinuous anyway?
Best regards,
JP Hare
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Robert Johnson
Sent: Monday, May 05, 2003 10:48 AM
To:
Hi Rocky,
Article 210 of the NEC lists the requirements for branch circuits and
associated receptacles. Table 210.21(B)(2) shows the receptacle load limits
and section 210.23 discusses the permissible loads in more detail.
On a related topic, I recently had a discussion with a colleague regardi
Hi Alan,
Your confusion over 3 and 6dB is understandable.
Sometimes "sound intensity" and "sound pressure" are improperly used
interchangeably. Intensity is proportional to the square of pressure. If
the intensity is doubled, one would say that there is a 3dB increase in
sound intensity; 10*lo
Hi Mark,
If you understand the fact that adding two sources of the same level gives
you a 3dB increase, you can do some quick addition.
Let's say one of your small chassis has a noise level of 75dB. If you add a
second one you would get a total noise level of 78dB. (Of course this does
not con
Hey Dave,
You might try looking at GR-78-CORE. I know it has guidance for ESD
requirements on circuit packs and stand-alone assemblies.
Later,
Paul Hare
-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of David Heald
Sent: T
ssage-
From: Barbara Judge [mailto:bju...@ccsemc.com]
Sent: Monday, July 01, 2002 7:18 PM
To: 'JP Hare'; Pierre SELVA; Forum Safety-emc
Subject: RE: FCC Authorization (Form 731) for ITE class B ; Do I need a
TCB ?
Paul,
Forgive me, but you are incorrect in your description of the ser
Dear Selva,
Can you tell us a little more about your product? You mention that it is
ITE class B. Does it have a transmitter section? If not, then you should
be aware that class B IT equipment falls under the Declaration of Conformity
rules (See 47 CFR 15.19, I think...) There is no need to c
Hi Dan,
I saw your previous post and was wondering if it would receive any
attention. As I recall, you are trying to shield a 200A DC power cord.
I am assuming you want a shielded cable because of radiated EMI problems.
Usually shielded power cords are not theoretically sound solutions for EMI