Joe,

Short-Circuit Tests
NOTE: The short-circuit tests that follow are intended to be performed only on 
out-of-service equipment.
NOTE: Discrete equipment assemblies that have been listed by an NRTL to UL 
60950[31] generally need not be subjected to the short circuit tests in Section 
9.10.1 and Section 9.10.2 and are considered compliant with this section. 
However, if the EUT has a DC or AC power source rated at >20 VA which would not 
be required to be tested as part of the NRTL listing program, it shall be 
tested as described in Section 9.10.1 and Section 9.10.2 as appropriate.
9.10.1 DC Power Sources
R9-27 [92] Except as noted below, at least one short-circuit test shall be 
performed on each type of dc power source having a rated power rating of 
greater than twenty (20) VA associated with the network equipment. Typical 
types of dc supplies are rectifiers, rectifiers and associated battery, and 
dc-to-dc converters.  The short circuit test need not be applied for a source 
consisting of a battery or a string of batteries that is not equipped with an 
overcurrent protective device. If the output of a rectifier or similar source 
is normally connected in parallel with batteries, the batteries shall be 
disconnected during the fault current tests on this source.
The short-circuit tests need not be applied for a source that solely provides 
power to a single telecommunications port if an equivalent short-circuit would 
be performed in accordance with Section 4.6.5.
These tests shall verify that the fault-current path will safely conduct the 
fault current resulting from the short circuit, and in the case of power 
supplies required to be grounded (R9-9 [79]), shall verify that the supplies 
are solidly grounded. For ungrounded power supplies, the short circuit shall be 
initiated between the positive and negative output terminals. The short circuit 
shall first be initiated at the power supply output terminals, and repeated at 
the load if the load is remote from the power supply output terminals. For 
grounded power supplies, short circuits shall be initiated between the 
ungrounded side of the source and the return conductor, and between the 
ungrounded side of the source and the metalwork of the enclosure.
Suggested points to initiate the short circuits are at points on the output 
circuit that are farthest from the source and downstream from over-current 
devices intended to protect equipment and wiring.
Short-circuit tests shall be applied to embedded dc power supplies that are 
mounted on (on-board) and intended to power individual circuit packs, as well 
as to supplies intended to power a complete shelf or rack of circuit packs. For 
onboard power supplies, the short circuit shall first be applied at the power 
supply output terminals, and repeated downstream (within the circuit pack) from 
the power supply output to ensure that printed wiring paths and components will 
not be damaged or become a fire hazard. A representative sample of test points 
shall be chosen to cover variations in wiring path lengths and affected 
components.
Where the architecture includes a separate power supply for an entire shelf or 
rack of circuit packs, the short shall first be applied at the output terminals 
of the power supply, and repeated at a point within the individual circuit 
pack(s) being powered.
If there are a number of circuit pack types or configurations, then a 
representative sample of each type or configuration shall be tested.
For both grounded and ungrounded power supplies, conformance to this 
requirement shall be demonstrated by the following conditions.
• The EUT shall not become a fire, fragmentation, or electrical safety hazard 
as described in Section 4.
• There shall be no damage to any component of the fault current path.
• The circuit pack, module, or sub-assembly where the short-circuit is applied, 
including any power supplies within the unit assembly, need not be in full 
working order after the short-circuit is removed. Damage to other circuit 
cards, modules, and subassemblies within the unit assembly shall not occur. 
Damage to other equipment or wiring shall not occur. Fuse replacement is 
permitted.
• A power supply that supplies multiple units shall be restorable by operator 
intervention (e.g. fuse replacement) after the removal of the short-circuit, 
except where the short is applied upstream of the protective circuit for the 
power supply.
Each short circuit shall be applied for one minute. When the supply ceases 
delivering current (e.g., overcurrent protection operates) the short circuit 
can be removed. If, after one minute, the supply continues to deliver 
non-negligible (>1A) current into the short circuit, the short circuit shall be 
maintained until the current ceases or for 15 minutes, whichever occurs first.
If the circuit is interrupted by opening of a component other than a NRTL 
listed or recognized fuse, the test shall be repeated twice using new 
components as necessary.

Compiled from Issue 3 GR-1089

Alain Servais
Compliance Engineer


 -----Original Message-----
From:   j...@aol.com [mailto:j...@aol.com] 
Sent:   Monday, November 25, 2002 1:25 PM
To:     emc-p...@majordomo.ieee.org; t...@world.std.com
Subject:        Short circuit tests in GR-1089

 << File: Short circuit tests in GR-1089.TXT >> Hello All:

I am hoping that some of you can help clarify the intent of requirement R9-20 
in Telcordia GR-1089.  Taken literally, the requirement says that there shall 
be no damage to equipment, conductors, or components when the DC power supply 
is shorted at the load.  This could even be interpreted to preclude the use 
of a fuse that has to be replaced.

One test lab has told me that as long as no fire hazard is created from this 
test, it is considered to have been passed.  Needless to say, this differs a 
bit from the literal interpretation.

I guess it would help if I had a better feel for the overall goal of the 
short circuit testing.  Any insight on this would be most appreciated.


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848
http://www.randolph-telecom.com


============================================================
The information contained in this message may be privileged 
and confidential and protected from disclosure.  If the 
reader of this message is not the intended recipient, or an 
employee or agent responsible for delivering this message to 
the intended recipient, you are hereby notified that any 
reproduction, dissemination or distribution of this 
communication is strictly prohibited. If you have received 
this communication in error, please notify us immediately by 
replying to the message and deleting it from your computer.

Thank you.
Tellabs
============================================================

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@attbi.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to