RE: AC outlet max current

2003-05-08 Thread JP Hare
'; emc-p...@majordomo.ieee.org Subject: RE: AC outlet max current A noncontinuous load is permitted to use 100% of the circuit rating. Only continuous loads need the derating. Bob Johnson ITE Safety From: owner-emc-p...@majordomo.ieee.org [mailto:owner-emc-p...@majordomo.ieee.org] On Behalf

RE: AC outlet max current

2003-05-07 Thread Robert Johnson
and conduit to conditions which will not degrade insulation. Bob Johnson ITE Safety From: Tyra, John [mailto:john_t...@bose.com] Sent: Wednesday, May 07, 2003 9:13 AM To: 'Robert Johnson'; 'JP Hare'; emc-p...@majordomo.ieee.org Subject: RE: AC outlet max current At what duty cycle From: Robert

RE: AC outlet max current

2003-05-07 Thread Tyra, John
At what duty cycle From: Robert Johnson [mailto:john...@itesafety.com] Sent: Monday, May 05, 2003 10:48 AM To: 'JP Hare'; emc-p...@majordomo.ieee.org Subject: RE: AC outlet max current A noncontinuous load is permitted to use 100% of the circuit rating. Only continuous loads need

RE: AC outlet max current

2003-05-06 Thread Robert Johnson
, Kenneth P (Rocky); emc-p...@majordomo.ieee.org Subject: RE: AC outlet max current Hi Rocky, Article 210 of the NEC lists the requirements for branch circuits and associated receptacles. Table 210.21(B)(2) shows the receptacle load limits and section 210.23 discusses the permissible loads in more

RE: AC outlet max current

2003-05-02 Thread JP Hare
outlet max current Group It was my understanding that one could only draw 80% of the max current from an AC wall outlet. Is this true? Where does the NEC specify this? Thanks to all, Kenneth Gonzalez Intergraph Solutions Group This message is from the IEEE EMC Society Product Safety

Re: AC outlet max current

2003-05-02 Thread John Barnes
Kenneth, NEC 2002 Section 210.20(A) says Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load. overcurrent rating/125%

RE: AC outlet max current

2003-05-01 Thread Wagner, John P (John)
...@majordomo.ieee.org Subject: AC outlet max current Group It was my understanding that one could only draw 80% of the max current from an AC wall outlet. Is this true? Where does the NEC specify this? Thanks to all, Kenneth Gonzalez Intergraph Solutions Group This message is from the IEEE EMC

RE: AC outlet max current

2003-05-01 Thread richwo...@tycoint.com
: Wednesday, April 30, 2003 6:10 PM To: emc-p...@majordomo.ieee.org Subject: AC outlet max current Group It was my understanding that one could only draw 80% of the max current from an AC wall outlet. Is this true? Where does the NEC specify this? Thanks to all, Kenneth Gonzalez Intergraph

RE: AC outlet max current

2003-05-01 Thread Robert Johnson
, 2003 6:10 PM To: emc-p...@majordomo.ieee.org Subject: AC outlet max current Group It was my understanding that one could only draw 80% of the max current from an AC wall outlet. Is this true? Where does the NEC specify this? Thanks to all, Kenneth Gonzalez Intergraph Solutions Group

AC outlet max current

2003-04-30 Thread Gonzalez, Kenneth P (Rocky)
Group It was my understanding that one could only draw 80% of the max current from an AC wall outlet. Is this true? Where does the NEC specify this? Thanks to all, Kenneth Gonzalez Intergraph Solutions Group This message is from the IEEE EMC Society Product Safety Technical