> Dan wrote: > I’ve left it on the charger the rest of the day and will leave > it overnight. This is a 25 year old automatic variable rate > charger - will it make the battery happy, or do I need to buy > one of those newer ones to recover it?
If you can provide 16 V, (maybe the "start" setting?) I'd try an equalizing charge. This effectively means a controlled over-charge. It will shorten the life of the battery - but if it's junk (or nearly so) that's not much of a risk. But if you don't have a way to set the charge 16 V, it may not be practical. Here is the text of an article on the topic. ~'^`~ ~'^`~ ~'^`~ ~'^`~ ~'^`~ ~'^`~ ~'^`~ ~'^`~ from https://shop.pkys.com/Battery-Equalization_ep_44.html Battery Equalization Equalizing lead acid batteries is a process designed to de-sulphate the battery plates by carrying out a controlled overcharge. Battery plates tend to acquire a sulphate coating over time which then hinders the chemical action between the electrolyte and the plate. By equalizing the battery in this controlled overcharge the outer layer of the plate, including the sulphate coating, is blown off, thereby rejuvenating the battery and allowing all the surface area of the plates to interact with the electrolyte. It also causes the electrolyte to bubble and in wet cell batteries this mixes up the acid and distributes it evenly throughout the cell. Recommendations on the frequency at which equalization be carried out vary from monthly to once or twice a year. Some manufacturers only recommend it be carried out when necessary, (Trojan), or once every six months or as necessary, (Rolls). My personal experience is that equalizing the batteries is a rather tedious, worrisome and smelly process so once or twice a year is more than enough. I particularly recommend it though for boats that rarely come to the dock. Such vessels get their batteries fully charged less often and seem to report tired batteries on a more frequent basis than boats that get fully charged on a regular basis. Equalizing the batteries is a tool that can be used to rejuvenate tired batteries or to prevent batteries from becoming tired. As a tool it is a double edged sword of course, this removal of the outer layer of the plates reduces their size and volume and thus their longevity. The material removed will fall to the bottom and may eventually short out the plates. I find that the best way to decide on whether to equalize and how often is to consult the information from the relevant battery manufacturer. You will find different opinions even among battery manufacturers on the way equalization is to be carried out. Victron Amp Hour MeterIf you are reading this article it is probably because you are having battery trouble. One of the best ways of heading off trouble in the future is to install an amp hour meter to give you a better idea of how your batteries are performing. Scroll to the end of this article for more information. Equalizing wet cell batteries 1. The batteries must be fully charged to begin with. 2. Disconnect all loads. You are going to allow the battery voltage to rise higher than normal; to 15 or 16 volts for a 12 volt battery bank. You don't want to damage sensitive electronic equipment that might be connected. 3. Remove any hydrocaps fitted to the cells 4. Connect the charger and set it to the equalizing voltage. (For Trojan wet cell batteries the recommended equalizing voltage is 15.5 volts for a 12 volt bank, for Rolls the equivalent voltage is 15.5 - 16 volts) 5. Batteries will begin gassing and bubbling vigorously 6. Don't allow the battery temperature to rise much above 115 degrees F and never above 125 degrees. Measure from a center cell. 7. Take the specific gravity at hourly intervals 8. Equalization is complete when the specific gravity no longer rises. For Rolls batteries the end of the instructions were more specific 9. If severely sulfated, it may take many hours for the specific gravity to rise. 10. Once the specific gravity begins to rise the bank voltage will most likely drop or the charging current will increase. The charging current may need to be lowered if temperature approaches 125F (46C). If the charge controller was by passed, it should now be used or put back in line. 11. Continue measuring the specific gravity until 1.265 is reached. 12. Charge for another 3 hours. Add water to maintain the electrolyte above the plates. 13. Allow bank to cool and check and record the specific gravity of each cell. The gravities should be 1.265 0.005 or lower. Check the cell electrolyte levels and add water IF necessary. _______________________________________ http://www.okiebenz.com To search list archives http://www.okiebenz.com/archive/ To Unsubscribe or change delivery options go to: http://mail.okiebenz.com/mailman/listinfo/mercedes_okiebenz.com