Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2017-01-09 Thread Charles Lepple
On Jan 9, 2017, at 9:46 AM, Merk - Oliver wrote: > > I then connected to my QNAP and set the UPS settings on the web interface to > "Shutdown server if power loss is 5 min", the UPS is configured to an > SNMP-Connection with its IP-address. Started runtime calibration and after > 5min. the QN

Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2017-01-09 Thread Merk - Oliver
Here are the results from the output of upsc under different conditions from my Debian Test system with NUT 2.7.2 : Normal: ups.status: OL No wall power: ups.status: OB Runtime calibration (started from AP9630 web interface): ups.status: OB CAL So at this stage there is a difference! I then co

Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2017-01-09 Thread Merk - Oliver
Thanks for your reply. Sorry for the delay, but until yet I haven't had a subscription, so I haven't seen your answer. I can test this, I have three APC USVs, each equipped with the AP9630 network card. I need to setup a Linux test VM with NUT first. I will give the feedback as soon as I can.